Safety Relay Unit
G9SB
CSM_G9SB_DS_E_6_2
Ultra Slim Safety Relay Unit
• Models of width 17.5 mm available with 2 or 3 poles. Models
of width 22.5 mm with 3 poles also available.
• Conforms to EN standards. (TÜV approval)
• DIN track mounting possible.
Be sure to read the
“Safety Precautions”
on page 9.
For the most recent information on models that have been certified for
safety standards, refer to your OMRON website.
Model Number Structure
Model Number Legend
G9SB-@@@@@-@
1.
2.
3.
4.
Note:
Please see “Ordering Information” below for the actual models that can be ordered.
1 2 3 4 5 6
Function
None: Emergency stop
Contact Configuration (Safety Output)
2:
DPST-NO
3:
3PST-NO
Contact Configuration (OFF-delay Output)
0:
None
Contact Configuration (Auxiliary Output)
0:
None
1:
SPST-NC
5. Input Configuration
None: 1-channel or 2-channel input possible
0:
None (direct breaking)
2:
2-channel input
6. Miscellaneous
A:
Auto-reset, inverse input
B:
Auto-reset, + common input
C:
Manual reset, inverse input
D:
Manual reset, + common input
Ordering Information
Main contacts
Auxiliary
contact
Number of input channels
2 channels
DPST-NO
None
1 channel or 2 channels
2 channels
1 channel or 2 channels
None
(direct breaking)
3PST-NO
SPST-NC
2 channels
1 channel or 2 channels
2 channels
1 channel or 2 channels
Manual reset
Reset mode
Auto-reset
Manual reset
Input type
Inverse
+ common
Inverse
+ common
---
Auto-reset
Inverse
+ common
Inverse
+ common
24 VAC/VDC
24 VDC
24 VAC/VDC
Rated voltage
Model
G9SB-2002-A
G9SB-200-B
G9SB-2002-C
G9SB-200-D
G9SB-3010
*
G9SB-3012-A
G9SB-301-B
G9SB-3012-C
G9SB-301-D
Note: 1.
Relays with inverse inputs are used mainly when inputting signals from two mechanical switches.
2.
Relays with positive commons are used mainly when inputting signals from a safety sensor or from one mechanical switch.
*
The G9SB-3010 can be applied to Safety Category 3 of the EN954-1 if double breaking is used.
1
G9SB
Specifications
Ratings
Power Input
Item
Model
G9SB-200@-@
G9SB-3010
24 VAC/VDC: 24 VAC, 50/60 Hz, or 24 VDC
24 VDC: 24 VDC
85% to 110% of rated power supply voltage
1.6 VA/1.4 W max.
1.7 W max.
2.0 VA/1.7 W max.
G9SB-301@-@
Power supply voltage
Operating voltage
range
Power consumption
Inputs
Item
Model
G9SB-200@-@
G9SB-3010
60 mA max.
*
G9SB-301@-@
30 mA max.
Input current
25 mA max.
*
Indicates the current between terminals A1 and A2.
Contacts
Model
Item
Rated load
Rated carry current
Load
G9SB-200@-@
G9SB-3010
Resistive load
250 VAC, 5 A
30 VDC, 5 A
5A
G9SB-301@-@
Characteristics
Item
Contact resistance
*1
Operating time
*2
Response time
*3
Insulation resistance
*4
Between different
outputs
Dielectric strength
Between inputs
and outputs
Between power
inputs and outputs
Vibration resistance
Shock resistance
Durability
*5
Destruction
Malfunction
Mechanical
Electrical
10 to 55 to 10 Hz, 0.375-mm single amplitude (0.75-mm double amplitude)
300 m/s
2
100 m/s
2
5,000,000 operations min. (at approx. 7,200 operations/hr)
100,000 operations min. (at approx. 1,800 operations/hr)
5 VDC, 1 mA
−25
to 55°C (with no icing or condensation)
35% to 85%
0.5 N·m
Approx. 115 g
Approx. 135 g
Approx. 120 g
2,500 VAC, 50/60 Hz for 1 min
Model
100 mΩ
30 ms max.
10 ms max.
100 MΩ min. (at 500 VDC)
G9SB-200@-@
G9SB-3010
G9SB-301@-@
Failure rate (P level) (reference value)
Ambient operating temperature
Ambient operating humidity
Terminal tightening torque
Weight
*1.
*2.
*3.
*4.
*5.
The contact resistance was measured with 1 A at 5 VDC using the voltage-drop method.
Not including bounce time.
The response time is the time it takes for the main contact to open after the input is turned OFF. Includes bounce time.
The insulation resistance was measured with 500 VDC at the same places that the dielectric strength was checked.
The durability is for an ambient temperature of 15 to 35°C and an ambient humidity of 25% to 75%.
2
G9SB
Connections
Internal Connections
G9SB-2002-A/C (24 VAC/VDC)
G9SB-3012-A/C (24 VAC/VDC)
* *
A1 A2 T11
G9SB-3010 (24 VDC)
A1
A2
T31
T32
13
23
33
41
+
TH
-
+ -
T12
T31
T32
13
23
(33) (41)
K1
K2
K1
TH
SA
K1
K2
K1
K1
K2
K2
SA
K1
K2
a
K2
K1
a
K2
a
Control
circuit
K1
Control
circuit
a
K2
14
T21
T22
14
24
(34) (42)
24
34 42
* *
G9SB-200-B/D (24 VAC/VDC)
G9SB-301-B/D (24 VAC/VDC)
* *
A1 A2
T21
T11
T12
T22
T31
T32
13
23
(33) (41)
Note: 1.
For 1-channel input with G9SB-@@@-B/D models, short
terminals T12 and T22. It is not possible to wire
G9SB-@@@2-A/C models for 1-channel input.
2.
Always provide a protective ground externally, e.g., on the
power supply.
*
Only G9SB-301@-@ models have terminals 33-34 and 41-42.
+ -
TH
SA
K1
K2
K1
K2
K1
a
K1
a
Control
circuit
K2
K2
14
24
(34) (42)
* *
Wiring of Inputs and Outputs
Signal name
Power supply input
Safety input 1
*1
Safety input 2
*1
Feedback/reset input
Instantaneous safety outputs
Auxiliary output
Terminal name
A1, A2
T11, T12
T21, T22
T31, T32
See below.
*2
See below.
*2
Description of operation
The input terminals for power supply. Connect the power source to the A1 and A2 terminals.
DC inputs have polarity, so A1 should be connected to the positive side and A2 to the negative side.
To set the safety outputs in the ON state, the ON state signals must be input to both safety input 1 and
safety input 2. Otherwise the safety outputs cannot be in the ON state.
To set the safety outputs in the ON state, the ON state signal must be input to T31 - T32. Otherwise the
safety outputs cannot be in the ON state.
Turns ON/OFF according to the state of the safety inputs and feedback/reset inputs.
Synchronized with Instant Safety Output.
Note:
Grounding
Be sure to ground externally, such as at the power supply.
*1.
Safety Inputs
(1) G9SB-3010 directly cuts off power, and has no Safety Input.
(2) For 1-channel input with G9SB-@@@-B/D, short circuit T12-T22 and then input.
(3) With G9SB-@@@2-A/C, 1-channel input wiring is not possible.
*2.
Output Contacts
G9SB-2002-A/C: Safety Output Contacts 13-14, 23-24.
G9SB-3012-A/C: Safety Output Contacts 13-14, 23-24, 33-34. Auxiliary Contact 41-42.
G9SB-200-B/D: Safety Output Contacts 13-14, 23-24.
G9SB-301-B/D: Safety Output Contacts 13-14, 23-24, 33-34. Auxiliary Contact 41-42.
G9SB-3010: Safety Output Contacts 13-14, 23-24, 33-34. Auxiliary Contact 41-42.
3
G9SB
Dimensions and Terminal Arrangement
G9SB-200@-@
G9SB-3010
(Unit: mm)
83
Terminal Arrangement
G9SB-200@-@
13 23 T31
T11 T12 A1
G9SB-3010
13 23 33
41 T31 A1
18
PWR
K1
K2
2.5
(green)
(orange)
(orange)
PWR
K1
K2
(green)
(orange)
(orange)
2
×
5 = 10
T21 T22 A2
42 T32 A2
14 24 34
112 max.
2.6
14 24 T32
100 max.
68
48
18 max.
(Average: 17.5)
G9SB-301-@-@
Terminal Arrangement
83
G9SB-301-@-@
13 23 33 41
T11 T12 T31 A1
18
2.5
PWR
(green)
K1
(orange)
K2
(orange)
T21 T22 T32 A2
3
×
5 = 15
112 max.
2.6
14 24 34 42
100 max.
68
48
23 max.
(Average: 22.5)
4
G9SB
Application Examples
G9SB-2002-A (24 VAC/VDC) or G9SB-3012-A (24 VAC/VDC) with 2-channel Limit Switch Input/Auto-reset
Highest achievable PL/
safety category
PLe/4 equivalent
Model
Safety Limit Switch D4B-N/D4N/D4F
Safety Relay Unit G9SB-2002-A/3012-A (24VAC/VDC)
Stop category
0
Reset
Auto
Note:
The above PL is only the evaluation result of the example. The PL must be evaluated in an actual application by the customer after confirming the usage conditions.
●
Application Overview
•
The power supply to the motor M is turned OFF when the S1 and S2 detect that the guard is opened.
•
The power supply to the motor M is kept OFF until the guard is closed.
Timing Chart
Guard
S2
S1
KM1
KM2
Open
Feedback loop
Limit switches S1 and S2
KM1 and KM2 (NO)
*
A1 A2 T11
T12
T31
T32
13
23
*
(33) (41)
S1:
S2:
KM1 and KM2:
M:
Safety limit switch
Limit switch
Magnetic contactor
Motor
+ -
K2
K2
a
K1
a
K2
K1
K1
Control
Circuit
K2
KM1
TH
SA
K1
KM2
T21
T22
14
24
(34) (42)
*
*
KM1 KM2
M
Note:
External connections and timing charts for G9SB-200-B/301-B models are the same as those for G9SB-2002-A/3012-A models.
*
Only the G9SB-3012-A model has terminals 33-34 and 41-42.
5