Datasheet
HAC Series
•
Load Voltage range 24 to 660 VAC
•
Output rating up to 150 Arms
•
Zero Voltage or Instantaneous Turn-on options
•
AC or DC input control options
•
Locking Input Connector
•
Optional Transient Protection & installed Thermal Pad
Panel Mount
PRODUCT SELECTION
Control Voltage
3-32 VDC
90-140 VAC
150-270 VAC
HAC24D150 ,HAC60D150
HAC24B150 ,HAC60B150
HAC24A150 ,HAC60A150
150 A
AVAILABLE OPTIONS
Control Voltage
A:
150-270 VAC
B:
90-140 VAC
D:
4-32 VDC
Overvoltage Protection
Blank:
Not Included
P:
Included
(6)
Switching Type
Blank:
Zero Voltage Turn-On
-10:
Instantaneous Turn-On
(5)
Series
HAC
24
A
150
P
H
-10
Operating Voltage
24:
24-280 VAC
60:
48-660 VAC
Rated Load Current
150:
150 Amps
Thermal Pad
Blank:
Not Included
H:
Included
Required for valid part number
For options only and not required for valid part number
OUTPUT SPECIFICATIONS
(1)
Description
Operating Voltage (47-63Hz) [Vrms]
Transient Overvoltage [Vpk]
Maximum Off-State Leakage Current @ Rated Voltage [mA]
Maximum Off-State dv/dt @ Maximum Rated Voltage [V/µSec]
Maximum Load Current [Arms](2)
Minimum Load Current [Arms]
Maximum Surge Current [Apk] 1 Cycle 50/60 Hz
Maximum I²t for fusing (10msec)/(8.33msec)[A²sec]
Maximum On-State Voltage Drop @ Rated Current [Vrms]
Thermal Resistance Juncti on to Case (Rjc) [°C/W]
Minimum Power Factor (with Maximum load)
Wire Size max (solid/stranded) [AWG/ IEC mm²]
(3)
Output Terminal Nut Torque Range [in lb (Nm)
HP Rating UL 508/IEC60957 [HP (KW)]: 240 VAC
HP Rating UL 508/IEC60947 [HP (KW)]: 480 VAC
HAC24x150
24-280
600
1
500
150
0.15
1670/1750
13950/12709
1.15
0.15
0.5
2/0 / 67.4
225-300 (25.4-33.9)
10 (7.5)
N/A
HAC60x150
48-660
1200
1
500
150
0.15
1670/1750
13950/12709
1.15
0.15
0.5
2/0 / 67.4
225-300 (25.4-33.9)
N/A
25 (18.75)
Do not forget to visit us at:
www.crydom.com
Copyright © 2016 Crydom Inc. Specifications subject to change without notice.
Datasheet
INPUT SPECIFICATIONS
(1)
Description
HACxxD150
4-32 VDC
(10)
4 VDC
1 VDC
9
15
Current Regulated
½ Cycle
½ Cycle
Panel Mount
HACxxB150
90-140 VAC
90 VAC
10 VAC
7
12
Current Regulated
20
30
HACxxA150
150-270 VAC
150 VAC
10 VAC
6
10
Current Regulated
20
30
Control Voltage Range
Minimum Turn-Off Voltage
Must Turn-Off Voltage
Minimum Input Current (for on-state) [mA]
Maximum Input Current [mA]
Nominal Input Impedance [Ohms]
Maximum Turn-On Time [msec]
(4)
Maximum Turn-Off Time [msec]
GENERAL SPECIFICATIONS
(1)
Description
Dielectric Strength, Input/Output (50/60Hz)
Dielectric Strength, Input/Output/Base (50/60Hz)
Minimum Insulation Resistance (@ 500 V DC)
Maximum Capacitance, Input/Output
Ambient Operating Temperature Range
Ambient Storage Temperature Range
Weight (typical) lbs/grams
Housing Material
SSR Mounting Torque Range [in lbs/Nm]
LED Input Status Indicator (color)
Humidity
Input Terminal
(7)
Parameters
3750 Vrms
2500 Vrms
10
9
Ohm
10 pF
-30 to 80 °C
-40 to 125 °C
0.75/340.2
PBT 30% GF, UL 94 V-0
18-20 (2-2.2)
YES (Green)
85% non-condensing
Detachable barrier strip
GENERAL NOTES
(1)
All parameters at 25°C unless otherwise specified.
(2)
Heat sinking required, see derating curves.
(3)
TRM3/0 lug terminal must be used.
(4)
Turn-on time for Instantaneous turn-on versions is 0.02 msec.
(5)
Instantaneous turn-on version is not recommended for capacitive loads. Use zero turn-on only.
(6)
Output will self-trigger (450-600Vpk for HAC24 and 900-1200Vpk for HAC60), not suitable for capacitive loads.
(7)
Connector/Plug Not included. See Suggested Mating Connectors/Plugs
(8)
Elective Overvoltage Protection, “P” option.
(9)
Load can be wired to either SSR output terminal 1 or 2.
(10)
Increase minimum voltage by 1V for operations from -20 to -30°C
WIRING DIAGRAM
AC
V
Load
L2 ( )
L1 ( )
25
Input Current vs Input Voltage
Standard Regulated “DC” Inputs
L2
L1
Input Current (mA)
LOAD SIDE
20
15
10
5
0
0
5
10
15
20
25
30
S O L I D S TAT E C O N TA C T O R
HAC60D150
INPUT
STATUS
4-32 VDC
DC Input Voltage
(-
/
)
(+
/
)
Do not forget to visit us at:
www.crydom.com
Copyright © 2016 Crydom Inc. Specifications subject to change without notice.
Datasheet
MECHANICAL SPECIFICATIONS
Tolerances: ±0.02 in / 0.5 mm
All dimensions are in: inches [millimeters]
Panel Mount
Standard Stud
0.375 [9.52] -24
LOAD SIDE
L2
L1
2.90
[73.7]
1.87
[47.6]
INPUT
STATUS
Mounting
Hole/Slot
0.20 [5.0] DIA.
2.51 [63.7]
3.62 [92.0]
4.12 [104.6]
1.70
[43.2]
Max
0.82
[20.8]
1.00
[25.4]
SUGGESTED MATING
CONNECTORS/PLUGS
(7)
FRONT WIRE ENTRY
Molex: 0395332002
Phoenix: MVSTBW 2,5/ 2
-ST-5,08
RIGHT ANGLE
Molex: 0395300002
Phoenix: MSTB 2,5/ 2
-ST-5,08
REAR WIRE ENTRY
Molex: 39533
-3002
Phoenix: MVSTBR 2,5/ 2
-ST-5,08
Do not forget to visit us at:
www.crydom.com
Copyright © 2016 Crydom Inc. Specifications subject to change without notice.
Datasheet
SURGE CURRENT INFORMATION
Panel Mount
150 A
1800
1600
1400
1200
1000
800
600
400
200
0
0.01
Surge Current (Amp)
0.1
1
Surge Duration (Secs)
10
Non repetitive peak surge current at Tj initial 40°C
THERMAL DERATE INFORMATION
(2)
HACxxA150
0.25ºC/W
150
Load Current (Amps)
Load Current (Amps)
125
100
75
50
25
0
20
30
40
50
60
70
Ambient Temperature (ºC)
80
0.36ºC/W
0.50ºC/W
150
125
100
75
50
25
0
20
HACxxB150,HACxxD150
0.25ºC/W
0.36ºC/W
0.50ºC/W
30
40
50
60
70
Ambient Temperature (ºC)
80
Do not forget to visit us at:
www.crydom.com
Copyright © 2016 Crydom Inc. Specifications subject to change without notice.
Datasheet
EQUIVALENT CIRCUIT BLOCK DIAGRAM
Diagram:
HAC AC control
AC
AC/DC
Converter
AC
Current
Limiter
Panel Mount
L2
AC
Trigger
Circuit
(8)
(9)
AC
L1
Diagram:
HAC DC control
-DC
Trigger
Circuit
+DC
L2
AC
(8)
(9)
AC
Current
Limiter
L1
ACCESSORIES
Recommended Accessories
Hardware Kit
HK1
Heat Sink
Part No.
HS053
HS033
HS023
Thermal Resistance
Lug Terminal
[ºC/W]
0.5
0.36
0.25
TRM3/0
Thermal Pad
HSP-5
AGENCY APPROVALS
Agency Approvals
Designed in accordance with the requirements of IEC 62314
IEC 61000-4-2 : Electrostatic Discharge: Level 3
IEC 61000-4-4 : Electrically Fast Transients: Level 3
IEC 61000-4-5 : Electricsl Surges: Level 3
E 116949
Rev. 091316
Do not forget to visit us at:
www.crydom.com