PC-Series
PC-Series
GFCI/ELCI & PANEL SEAL
Resources:
Download 3D CAD Files
The PC-Series, AC Residual Current Circuit Breaker with Overcurrent Protection (RCBO), combines the ground
fault protection of a GFCI with the familiar overcurrent tripping characteristics of a normal circuit breaker. It
detects lower level ground faults that do not trip ordinary circuit breakers, but could lead to shock hazards and fires
in installations near water. Innovative features include status LED indicators distinguishing if a breaker is closed
with line voltage present, or has opened due to leakage current, or has opened due to over current, or is closed with
no line voltage present. It also offers an optional Hot/Neutral reversal detection and protection.
IGS
STP
Product Highlights:
Meets latest UL 943 standards
GFCI self-test auto-monitoring & end-of-life
indication
Integrated push-to-reset button
Overload, short circuit and ground fault protection
in a single package
Status LED indicators
Single circuit solution for AC branch ground fault
protection
Optional panel seal
Typical Applications:
Generators
Water Heaters
Battery Chargers
Marine
AC main ground fault protection for
a boat’s entire AC electrical system
Carling Technologies, Inc.
60 Johnson Avenue, Plainville, CT
06062
Email:
sales
@
carlingtech.com
Application Support:
team2
@
carlingtech.com
Phone:
860.793.9281
Fax:
860.793.9231
www.carlingtech.com
2 |
PC-Series Circuit Breaker - General Specifications
PC-Series Switch
DESIGN FEATURES
MOUNTING PLATE
Available in stainless steal or zinc
chromate plated carbon steel
OPTIONAL SEAL
IP66/67 panel seals provide ideal
protection against salt spray,
ozone, dust, water and most acids
LEDs
Two separate lights that indicate
power, ground fault leakage and
end-of-life
*Manufacturer reserves the right to change product specification without prior notice.
Email: sales
@
carlingtech.com Application Support: team2@carlingtech.com
Phone: (860) 793–9281 Fax: (860) 793–9231
www.carlingtech.com
PC-Series Circuit Breaker - General Specifications
| 3
Electrical Tables
Table A:
UL Listed & CSA Certified configurations as a Ground Fault Circuit Interruptor
PC-SERIES TABLE A: UL Listed / CSA 22.2 No. 144.1 Configurations as a Ground Fault Circuit Interruptor
Voltage
Current Short Circuit Ground Fault
Rating
(Amps)
1 - 50
1 - 50
Capacity
(Amps)
5000
5000
Trip Level
(Milliamps)
6
6
Notes
Circuit
Configuration Max Rating Frequency Phase
(Hertz)
Series
120
120 / 240
60
60
1
1
1 or 2 Poles. One pole of a two pole unit must be Neutral
2 or 3 Poles. One pole of a three pole unit must be Neutral
Table B:
UL Recognized as an Earth Leakage Circuit Interruptor - 120 and 120/240V
PC-SERIES TABLE B: UL Recognized Configurations as an Earth Leakage Circuit Interruptor
Voltage
Current Short Circuit Ground Fault
Rating
(Amps)
1 - 50
1 - 50
1 - 50
1 - 50
Capacity
(Amps)
5000
5000
3000
5000
Trip Level
(Milliamps)
30
30
30
30
Notes
Circuit
Configuration Max Rating Frequency Phase
(Hertz)
120
120 / 240
120
Series Ignition
Protection
120 / 240
Series
50 / 60
50 / 60
50 / 60
50 / 60
1
1
1
1
1 or 2 Poles. One pole of a two pole unit must be Neutral
2 or 3 Poles. One pole of a three pole unit must be Neutral
1 or 2 Poles. One pole of a two pole unit must be Neutral
2 or 3 Poles. One pole of a three pole unit must be Neutral
Table C:
UL Recognized as an Earth Leakage Circuit Interruptor - 240V
PC-SERIES TABLE C: UL Recognized Configurations as an Earth Leakage Circuit Interruptor - 240V
Voltage
Current Short Circuit Ground Fault
Capacity
(Amps)
5000
5000
Trip Level
(Milliamps)
30
30
Notes
Circuit
Rating
Configuration Max Rating Frequency Phase (Amps)
(Hertz)
Series
Series Ignition
Protection
240
240
50 / 60
50 / 60
1
1
1 - 30
1 - 50
2 or 3 Poles. One pole of a three pole unit must be Neutral. Suffix 11
2 or 3 Poles. One pole of a three pole unit must be Neutral. Suffix 12
Impedance (Across Circuit breaker only)
RESISTANCE, IMPEDANCE VALUES
from Line to Load Terminals
(Values Based on Series Trip Circuit Braker)
1000
100
CURRENT
(AMPS)
TOLERANCE
(%)
10
O
H
M
S
1
0.10 - 5.0
5.10 - 20.0
20.10 - 50.0
± 15
± 25
± 35
0.1
0.01
0.001
0.01
0.1
1
10
100
AMPERE RATING
Agency Certifications
UL Standard 489
UL Standard 1077
UL Standard 943 & CSA 22.2 No. 144.1
UL Standard 1053
UL Standard 1500
Circuit Breakers, Molded Case,
(Guide DIVQ, File E129899)
Supplementary Protectors
Class A Ground Fault Circuit Interrupters
Ground Fault Sensing and Relaying Equipment
Ignition Protection
Email: sales
@
carlingtech.com Application Support: team2@carlingtech.com
Phone: (860) 793–9281 Fax: (860) 793–9231
www.carlingtech.com
4 |
PC-Series Circuit Breaker - General Specifications
Electrical
50 Amps maximum
120 VAC, 120/240 VAC
1480 VAC, 60Hz for 1 minute
between all electrically isolated
terminals
Insulation Resistance
Minimum of 100 Megohms at
500VDC
Leakage Current Trip Level 5±1 mA
Leakage Current Trip Time ≤ 25 ms complies with UL 943
EMI
UL 943 / IEC 61000-4-6, 0.5V
150KHz ~ 230 MHz
Operating Frequency
50/60 Hz
Reverse Polarity
A reversed Line / Load connection
to the circuit breaker shall not cause
damage to the device
Grounded Neutral
When neutral is grounded on load
side of circuit
Overload
50 operations @ 600% of rated
current on Breakers
Switched Neutral
2nd Pole on 120V and 3rd Pole on
120/240V, Optional
Manual Test
To be performed at least every
month by pressing the test button
on the GFCI to verify the device’s
ability to respond and trip when
subjected to simulated leakage.
Current imbalance is sufficient
to cause tripping at 85% of rated
voltage. Line Power at L1 is required.
GFCI Auto-Monitoring
Performed automatically without
opening circuit breaker contacts
or compromising ability to respond
to ground or neutral faults.
Automatic Self-Test performed
automatically every time power is
supplied within 5 seconds.
Automatic Self-Test Frequency: 3
seconds. Line Power at L1 is
required. Feedback when auto-
monitoring Self-Test fails: Circuit
breaker trips and cannot be reset
and a visual indication is displayed
(See Next Page).
GFCI Heartbeat Indicator Successful Self Tests are followed
by a flash of light per Next Page
GFCI End of Life
Circuit breaker trips and cannot be
reset. A visual indication is
displayed via the LED’s located on
the front of the device (See Next
Page). Line Power at L1 is required.
Current Ratings
Voltage Rating
Dielectric Strength
Physical
Number of Poles
Termination
Mounting
Actuator
Internal Configuration
Weight
Standard Colors
1-pole (1 Circuit Breaker + 1 GFCI
Sensor Module), 120V. 2-pole
(2 Circuit Breakers + 1 GFCI Sensor
Module), 120/240V or 120V with
Switched Neutral. 3-pole (3 Circuit
Breakers + 1 GFCI Sensor Module),
120/240V with Switched Neutral.
Circuit Breaker Line Side: #10-32
GFCI Sensor Module Load Side:
#10-32. Neutral pigtail provided with
non-switched neutral units.
Front Panel, #6-32 or M3 threaded
inserts.
Handle, Flat Rocker, Curved Rocker
(with or without rocker guard),
Push-to-Reset Rocker
Circuit Breaker, Series Trip
Switch only (without over-current
protection)
1-pole: approximately 300 grams
(10.6 ounces)
2-pole: approximately 375 grams
(13.2 ounces)
3-pole: approximately 500 grams
(17.6 ounces)
Housing – Black, Test Button –
White, Text – White
Environmental
Shock
Designed and tested in accordance with requirements of
specification MIL-PRF- 55629 and MIL-STD-202G as follows:
Thermal Shock
Vibration
Moisture Resistance
Operating Temperature
Corrosion
Mechanical
Endurance
Trip Free
10,000 “On-Off” Operations at 6 per
minute; 6000 with Rated Current &
Voltage (3000 test button and 3000
manual operations) and 4000
on/off operations with no load.
Trips on short circuit, overload or
leakage to ground, even when
actuator is forcibly held in the
“On” position
Withstands 100 G, 6ms, sawtooth
at rated current per Method 213,
Test Condition “I”.
Method 107D, Condition A (5-cycle
at -55ºC to +25ºC to +85ºC to +25ºC)
Withstands 0.06” excursion from
10-55 Hz, and 10 G 55-500 Hz, at
rated current per Method 204C, Test
Condition A. Instantaneous &
ultrashort curves tested at 90% of
rated current.
93% RH at 30°C for 168 Hours.
-35°C to +66°C
UL-943-6.21, 3 weeks
Humidity: 30±2°C, 70±2% relative
humidity
Mixed Flowing Gases:
100 ppb H
2
S,
20 ppb CI
2
,
200±50 ppb NO
2
*Manufacturer reserves the right to change product specification without prior notice.
Email: sales
@
carlingtech.com Application Support: team2@carlingtech.com
Phone: (860) 793–9281 Fax: (860) 793–9231
www.carlingtech.com
PC-Series Circuit Breaker - General Specifications
| 5
GFCI LED Indication
Condition
Power with Open Circuit
Circuit Manually Opened
Power with Closed Circuit
Ground Fault Leakage
Grounded Neutral
Passed Automatic, Self-Test
Failed Automatic, Self-Test
Manual GFCI Monthly Test
Over Current
End of Life
Breaker
Open
Open
Closed
Trips Open
Trips Open
Closed
Trips Open
Trips Open
Trips Open
Trips Open
LED Output
None
None
Green (solid)
Red (solid)
Red (solid)
Red (flash lasting 2 ms, every 3 seconds)
Red (continuous flashing, every 0.10 seconds)
Red (solid)
None
Red (continuous flashing, every 0.10 seconds)
Loss of line power results in no LED output and no continuous trip
GFCI Test Instructions
1.
2.
3.
4.
5.
Turn “OFF” the GFCI Breaker actuator. Turn on the power to the panel. The green and red LED’s should be off.
Turn “ON” the GFCI Breaker actuator. The green “POWER” LED should show steady illumination and the red “LEAKAGE
FAULT” LED should flash every 3 seconds to indicate a successful self-test.
Depress the “TEST” button. This will cause the actuator to move to the “OFF” position and the red LED to turn on and show
steady illumination, indicating that the GFCI is functioning properly. The green LED will also go from steady to off. If the actuator
fails to move to the “OFF” position or the red LED fails to illuminate, the unit MUST be replaced.
Turn the GFCI Breaker actuator to the “ON” position. The red LED should flash every 3 seconds and the green LED should
show steady illumination.
This test is to be performed on a monthly basis and recorded on the “Monthly Test Reminder” label.
ELCI LED Indication
Indicator -
Two integrated LEDs, Red & Green
•
Green LED On, Red LED Off - Line Voltage is present, the breaker is closed, and the device is protecting the circuits against
over current and leakage current.
•
Green LED Off, Red LED On - The device has detected leakage current and has opened the circuit breaker.
•
Green LED Flashing, Red LED Off - The circuit breaker has opened due to over current or has been turned off manually
•
Green LED Off, Red LED Off - Line Voltage is not present
•
Green LED Flashing, Red LED Off, Amber LED ON - Indicates Hot & Neutral are reversed and the circuit breaker is open
Neutral Protection - When neutral is grounded on load side of circuit
Test Button - Located on Ground Fault Module
Email: sales
@
carlingtech.com Application Support: team2@carlingtech.com
Phone: (860) 793–9281 Fax: (860) 793–9231
www.carlingtech.com