Digital Temperature Controller
E5CC
(48
×
48 mm)
Large White PV Display That’s Easier to Read.
Easy to Use, from Model Selection to
Setup and Operation.
A Complete Range of I/O Capacities,
Functions, and Performance.
Handles More Applications.
• The white PV display with a height of 15.2 mm improves visibility.
• High-speed sampling at 50 ms.
48
×
48 mm
E5CC
• Models are available with up to 3 auxiliary outputs, up to 4 event
inputs, a transfer output, and a remote SP input to cover a wide
Refer to your OMRON website for the most recent
information on applicable safety standards.
range of applications.
• Short body with depth of only 60 mm.
• Set up the Controller without wiring the power supply by
Refer to Safety Precautions on page 50.
connecting to the computer with a Communications Conversion
Cable (sold separately). Setup is easy with the CX-Thermo (sold
separately).
• Easy connections to a PLC with programless communications. Use component communications to link
Temperature Controllers to each other.
Main I/O Functions
Sensor Input
Universal input
•
Thermocouple
•
Pt
•
Analog current/voltage
Indication Accuracy
•
Thermocouple input:
±0.3%
of PV
•
Pt input:
±0.2%
of PV
•
Analog input:
±0.2%
of FS
Sampling Period
•
50 ms
Auxiliary Outputs
Event Inputs
•
None
•
2
•
4
Remote SP Input
•
None
•
1
Serial Communications
•
None
•
RS-485
•
PF (shift) Key
•
Temperature status display
•
Simple programming
•
Independent heating and
cooling PID control
•
Changed parameter display
•
Display brightness setting
•
3
Transfer Output
•
None
•
1
E5CC
Dual displays: PV/SV
4-digit displays
Control Output 1
•
Relay output
•
Voltage output (for driving SSR)
•
Linear current output
Control Output 2
•
None
•
Voltage output (for driving SSR)
This datasheet is provided as a guideline for selecting products.
Be sure to refer to the following manuals for application precautions and other information required for operation before attempting
to use the product.
E5@C Digital Temperature Controllers User’s Manual (Cat. No. H174)
E5@C Digital Temperature Controllers Communications Manual (Cat. No. H175)
2
E5CC
Model Number Legend and Standard Models
Model Number Legend
E5CC-@@
@ @ @ @
-@@@ (Example: E5CC-RX3A5M-000)
−− − − − − −−−
A
B C D E
F
A
Model
E5CC
RX
QX
*1 *3
CX
QQ
CQ
3
A
D
5
M
Control outputs
1 and 2
B
C
D
E
Input
type
F
Options
Meaning
48
×
48 mm
Control output 1
Relay output
Voltage output
(for driving SSR)
Linear current output *2
Voltage output
(for driving SSR)
Linear current output *2
No. of Power
Terminal
auxiliary supply
type
outputs voltage
Control output 2
None
None
None
Voltage output
(for driving SSR)
Voltage output
(for driving SSR)
*1
*1
*3
000
001
003
004
005
006
007
3 (one common)
100 to 240 VAC
24 VAC/DC
Screw terminals (with cover)
Universal input
Event
Remote Transfer
HB alarm and
Communications
HS alarm
inputs
SP Input output
---
---
---
---
---
1
---
2
---
---
2
(for 3-phase
RS-485
---
---
---
heaters)
---
RS-485
2
---
---
---
---
4
---
---
---
---
2
Provided.
---
---
2
Provided.
---
*1. Options with HB and HS alarms (001 and 003) cannot be selected if a linear current output is selected for the control output.
*2. The control output cannot be used as a transfer output.
*3. Option 004 can be selected only when
"
CX
"
is selected for the control outputs.
Heating and Cooling Control
●
Using Heating and Cooling Control
A
Control Output Assignment
If there is no control output 2, an auxiliary output is used as the cooling control output.
If there is a control output 2, the two control outputs are used for heating and cooling.
(It does not matter which output is used for heating and which output is used for cooling.)
B
Control
If PID control is used, you can set PID control separately for heating and cooling.
This allows you to handle control systems with different heating and cooling response characteristics.
3
E5CC
Specifications
Ratings
Power supply voltage
Operating voltage range
Power consumption
A in model number: 100 to 240 VAC, 50/60 Hz
D in model number: 24 VAC, 50/60 Hz; 24 VDC
85% to 110% of rated supply voltage
Models with option selection of 000: 5.2 VA max. at 100 to 240 VAC, and 3.1 VA max. at 24 VAC or
1.6 W max. at 24 VDC
All other models: 6.5 VA max. at 100 to 240 VAC, and 4.1 VA max. at 24 VAC or 2.3 W max. at 24 VDC
Temperature input
Thermocouple: K, J, T, E, L, U, N, R, S, B, W, or PL II
Platinum resistance thermometer: Pt100 or JPt100
Infrared temperature sensor (ES1B): 10 to 70°C, 60 to 120°C, 115 to 165°C, or 140 to 260°C
Analog input
Current input: 4 to 20 mA or 0 to 20 mA
Voltage input: 1 to 5 V, 0 to 5 V, or 0 to 10 V
Current input: 150
Ω
max., Voltage input: 1 MΩ min.
(Use a 1:1 connection when connecting the ES2-HB/THB.)
ON/OFF control or 2-PID control (with auto-tuning)
SPST-NO, 250 VAC, 3 A (resistive load), electrical life: 100,000 operations,
minimum applicable load: 5 V, 10 mA *
Output voltage: 12 VDC
±20%
(PNP), max. load current: 21 mA, with short-circuit protection circuit
4 to 20 mA DC/0 to 20 mA DC, load: 500
Ω
max., resolution: approx. 10,000*
3
SPST-NO relay outputs, 250 VAC, Models with 3 outputs: 2 A (resistive load),
Electrical life: 100,000 operations, Minimum applicable load: 10 mA at 5 V
2 or 4 (depends on model)
Contact input: ON: 1 kΩ max., OFF: 100 kΩ min.
Non-contact input: ON: Residual voltage: 1.5 V max., OFF: Leakage current: 0.1 mA max.
Current flow: Approx. 7 mA per contact
1 (only on models with a transfer output)
Contact output: 4 to 20 mA DC, load: 500
Ω
max., resolution: approx. 10,000
Linear voltage output: 1 to 5 VDC, load: 1 kΩ max, resolution: Approx. 10,000
Digital setting using front panel keys
Current input: 4 to 20 mA DC or 0 to 20 mA DC (input impedance: 150
Ω
max.)
Voltage input: 1 to 5 V, 0 to 5 V, or 0 to 10 V (input impedance: 1 MΩ min.)
11-segment digital display and individual indicators
Character height: PV: 15.2 mm, SV: 7.1 mm
Up to eight set points (SP0 to SP7) can be saved and selected using event inputs, key operations, or
serial communications.
None
Manual output, heating/cooling control, loop burnout alarm, SP ramp, other alarm functions, heater
burnout (HB) alarm (including SSR failure (HS) alarm), 40% AT, 100% AT, MV limiter, input digital
filter, self tuning, robust tuning, PV input shift, run/stop, protection functions, extraction of square root,
MV change rate limit, simple calculations, temperature status display, simple programming, moving
average of input value, and display brightness setting
-10 to 55°C (with no condensation or icing),
for 3-year warranty: -10 to 50°C (with no condensation or icing)
25% to 85%
-25 to 65°C (with no condensation or icing)
Sensor input
Input impedance
Control method
Relay output
Control
output
Voltage output
(for driving SSR)
Linear current output
Number of outputs
Output specifications
Number of inputs
Event input External contact input
specifications
Transfer
output
Number of outputs
Output specifications
Auxiliary
output
Setting method
Remote SP input
Indication method
Multi SP
Bank switching
Other functions
Ambient operating temperature
Ambient operating humidity
Storage temperature
* You cannot select a relay output or linear current output for control output 2.