is a 1200 Watt, power-factor-corrected (PFC) front-end power supply for hot-swapping redun-
dant systems. The main output is 48V and standby output of either 12V, 5V or 3.3V. Packaged in 1U low profile, it is
designed to deliver reliable bulk power to servers, workstations, storage systems or any 48V distributed power archi-
tecture systems requiring high power density. The highly efficient electrical and thermal design with internal cooling
fans supports reliable operation conditions. The D1U-W-1200 is designed to auto-recover from over-temperature
faults. Status information is provided with front panel LEDs, logic signals and I
2
C management interface. Three units
can be packaged into an optional 19" 1U power shelf to provide up to 3.6kW of power.
The S1U-3X
is a 1U x 19" EIA Rack Mount Power Shelf designed for holding three D1U Front End Power Supplies
in current sharing applications. It is intended for distributed power architecture applications in the Servers, Storage
Networking and Data Communications markets. There are two lug terminal connections for #2 AWG cabling for the DC
output. System connection through the I
2
C bus reports the performance status of the power supplies within the power
shelf. Two Power Shelves can operate in parallel by an optional Shelf-to-Shelf cable, doubling the power output to the
maximum capability of 7.2kW for two 48V power shelves.
SELECTION GUIDE
FEATURES
compliant
RoHS
1200W (220Vac), 900W (110Vac)
Output power
Main output,
48V
3.3V, 5V or 12V standby output
sized; dimensions 4.75"x12.00"x1.61"
1U
Watts per cubic inch density
13.2
redundancy capable, including hot-docking
N+1
Active current sharing on main output
Over-voltage, over-current,
over-temperature protection
Internal cooling fans
Bus Interface with status indicators
I²C
Optional 1U x 19" power-shelf
Part Number
D1U-W-1200-48-HC2C
D1U-W-1200-48-HA2C
D1U-W-1200-48-HB2C
D1U-W-1200-48-HC1C
D1U-W-1200-48-HA1C
D1U-W-1200-48-HB1C
Power Output
High Line AC
1200W
1200W
1200W
1200W
1200W
1200W
Power Output
Low Line AC
900W
900W
900W
900W
900W
900W
Main Output
48V
48V
48V
48V
48V
48V
Standby
Output
3.3V
5V
12V
3.3V
5V
12V
Airflow
Back to front
Back to front
Back to front
Front to back
Front to back
Front to back
Part Number
S1U-3X-16-A-48-RC
Description
Power shelf for 48V D1U
INPUT CHARACTERISTICS
Parameter
Input Voltage Operating Range
Input Frequency
Turn-on Input Voltage
Turn-off Input Voltage
Maximum Input Current
Inrush Current
Power Factor
Conditions
Ramp up
Ramp down
Low Line AC 90Vac
High Line AC 180Vac
Cold start between 0-1msec
Output load >90%
Output load >50%
Min.
90
47
78.5
70.5
Typ.
115/230
50/60
Max.
264
63
86.5
78
15
10
90
Units
Vac
Hz
Vac
Arms
Apk
95%
75%
For full details go to
www.murata-ps.com/rohs
www.murata-ps.com/support
CPS_D1U-W-1200-48-Hx.D02
Page 1 of 7
D1U-W-1200-48-Hx Series
AC/DC Front End Power Supply + S1U Power Shelf
OUTPUT VOLTAGE CHARACTERISTICS
Output
Voltage
Parameter
Voltage Set Point Accuracy
Line and Load Regulation
Ripple Voltage & Noise
1
Output Current
Load Capacitance
Voltage Set Point Accuracy
Line and Load Regulation
Ripple Voltage & Noise
1
Operating Range
Load Capacitance
Voltage Set Point Accuracy
Line and Load Regulation
Ripple Voltage & Noise
1
Operating Range
Load Capacitance
Voltage Set Point Accuracy
Line and Load Regulation
Ripple Voltage & Noise
1
Operating Range
Load Capacitance
Conditions
Min.
46.54
Typ.
48
Max.
49.44
480
24.6
10000
Units
Vdc
mV p-p
A
µF
Vdc
mV p-p
A
µF
Vdc
mV p-p
A
µF
Vdc
mV p-p
A
µF
48V
20MHz Bandwidth
2
3.3
3.2
20MHz Bandwidth
0
5
4.85
20MHz Bandwidth
0
12
11.6
20MHz Bandwidth
0
3.3Vsb
3.4
50
4.5
1530
5.15
50
4
1530
12.4
120
1.7
1530
5Vsb
12Vsb
OUTPUT CHARACTERISTICS
Parameter
Remote Sense
Efficiency
Output Rise Monotonicity
Start-up Time
Conditions
Min.
Typ.
Max.
Units
mV
%
s
ms
mV
Transient Response
240
220Vac
90.6
Overshoot less than 10% for all outputs, no voltage negative between 10% to 95% during ramp up
AC ramp up
1.5
PS_On activated
150
48V Ramp 1A/μs, 50% load step
±2700
3.3Vsb Ramp 1A/μs, 50% load step
±165
5Vsb Ramp 1A/μs, 50% load step
±250
12Vsb Ramp 1A/μs, 50% load step
±600
At 100% load
All outputs within regulation
Max. load, nominal Vin
20
±10
Current sharing accuracy (up to 6 in parallel)
Hot Swap Transients
Hold-up Time
%
ms
GENERAL CHARACTERISTICS
Parameter
Storage Temperature Range
Operating Temperature Range
Operating Humidity
Storage Humidity
Shock
Sinusoidal Vibration
MTBF
Acoustic
Safety Approvals
Input Fuse
Material Flammability
Switching Frequency
Weight
1
Conditions
Non-condensing
Non-condensing
Min.
-40
0
10
5
Typ.
Max.
70
50
90
90
Units
°C
%
30G non operating
0.5G, 5 – 500 Hz operating
Calculated per Bellcore at Ta=30°C
200
Demonstrated
200
ISO 7779-1999
c-CSA-us (CSA 60950-1-03/UL 60950-1, Second Edition)
TUV approval (Bauart) EN 60950-1:2001
60
Khrs
Khrs
dB LpAm
Power Supply has internal 20A/250V fast blow fuse on the AC line input
UL 94V-0
90KHz for Boost PFC Converter
165KHz for Main Output Converter
200KHz for Standby Output Converter
2.1kg
Ripple and noise are measured with 0.1 uF of ceramic capacitance and 10 uF of tantalum capacitance on each of the power supply outputs. The output noise requirements apply
over a 0 Hz to 20 MHz bandwidth. A short coaxial cable with 50ohm scope termination is used.
www.murata-ps.com/support
CPS_D1U-W-1200-48-Hx.D02
Page 2 of 7
D1U-W-1200-48-Hx Series
AC/DC Front End Power Supply + S1U Power Shelf
PROTECTION CHARACTERISTICS
Output
Voltage
48V
12Vsb
3.3Vsb
5Vsb
Parameter
Over-temperature
Over Voltage
Over Current
Over Voltage
Over Current
Over Voltage
Over Current
Over Voltage
Over Current
Conditions
Auto-restart
Latching
Latching
Latching
Latching
Latching
Latching
Latching
Latching
Min.
55
54
28
13
2.5
3.57
6.5
5.6
5
Typ.
Max.
65
59
33
14
3
4.02
8
6
7
Units
°C
V
A
V
A
V
A
V
A
ISOLATION CHARACTERISTICS
Parameter
Insulation Safety Rating / Test Voltage
Isolation
Material Flammability
Grounding
Conditions
Min.
Typ.
Max.
Units
Input to Output - Reinforced
3000
Vrms
Input to Chassis - Basic
1500
Vrms
Output to Chassis
Output to Output
UL 94V-0
Main Output Return and Standby Output Return are connected internally. 100kΩ resistor parallel with 100nF
capacitor is connected between Return and power supply chassis. Main Output Return should be connected to
DC and Signal Connector: Tyco Part # 1-6450332-7, or FCI PowerBlade # 51732-028
P1
P2
P3
P4
P5
P6
x1
AC_OK
PS_ON
V
OUT
V
OUT
V
OUT
V
RTN
V
RTN
V
RTN
I_SHARE
PS_KILL
I
2
C ADR0
V
OUT
SENSE+
I
2
C ADR1
V
OUT
SENSE-
I
2
C ADR2
I
2
C DATA
PS_
PRESENT
I
2
C
CLOCK
B
A
x2
P_GOOD
V_
SB
+OUT
x3
V_
SB
+OUT
V_
SB
+OUT
x4
V_
SB
RETURN
V_
SB
RETURN
x5
V_
SB
RETURN
V_
SB
RETURN
D
C
Pin Assignment
P1, P2, P3
P4, P5, P6
A2
A3
C2, C3, D3
C4, C5, D4, D5
B1
D1
Signal Name
V
OUT
V
RTN
Sense +
Sense -
V_
SB
V_
SB
Return
I_Share
AC_OK
Description
Main output voltage
Main output voltage, return
V
OUT
remote sense, positive node input, connected to the
+ve load point
V
OUT
remote sense, negative node input, connected to the
-ve load point
Standby voltage output
Standby voltage, return, tied internally to Output Return
Active load sharing bus
Input AC Voltage “OK” signal output (Internal pull up is
10kΩ to Vsb)
High Level
Low Level
I Max
0 – 8V
>2.4V (active, OK)
<0.4V
>2.4V (active, Good)
<0.4V
>2.1V (open, or Vsb)
<0.7V (active, PS:On)
0V
>2.1V (open, or Vsb)
<0.7V (active, PS:On)
Vsb
Vsb
>2.1V, < Vsb
<0.8V
>2.1V, <Vsb
<0.8V
>2.1V, <Vsb
<0.8V
-4 mA / +5 mA
+4 mA
-2 mA
+4 mA
-2 mA
D2
P_Good
Power good signal output (Internal pull up is 10kΩ to Vsb)
Floating pin will turn off P/S (shorter pin, last-make and
first-break contact for hot plugging). This signal overrides
PS-On in disabling the Main Output
Internally tied to Vsb return
Internal 1K ohm pull-up to Vsb, (accepts open collector/
drain drive), This signal to be pulled low to turn-on power
supply
I
2
C serial data bus
I
2
C serial clock bus
Address input 0, internal pull-up to Vsb
Address input 1, internal pull-up to Vsb
Address input 2, internal pull-up to Vsb
A1
B5
C1
A4
A5
B2
B3
B4
PS_Kill
PS_Present
PS_On
I
2
C Data
I
2
C Clock
I
2
C Adr0
I
2
C Adr1
I
2
C Adr2
N/A
-4 mA
-1 mA
±1 mA
±1 mA
±1 mA
D1U MATING CONNECTORS
48V D1U mat-
ing connector
MPS
FCI
Tyco
2
Press Fit
Straight
N/A
51742-10602000CALF
TBD
Solder
2
Right Angle
Straight
N/A
51742-10602000AALF
TBD
Right Angle
36-0440026-0
51762-10602000ABLF
TBD
Pending
51762-10602000CBLF
TBD
Solder connector recommended for board thickness of <0.090
www.murata-ps.com/support
CPS_D1U-W-1200-48-Hx.D02
Page 4 of 7
D1U-W-1200-48-Hx Series
AC/DC Front End Power Supply + S1U Power Shelf
CONNECTOR TO CUSTOMER SYSTEM
Signal Connector: MOLEX # 39-28-5204 OR TYCO # 281282-1
Mating Connector: MOLEX # 0039521204
Pin Assignment
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
Signal Name
AC_OK1
1
P_Good1
2
PS_On1
3
NOT USED
AC_OK0
1
P_Good0
2
PS_OnO
3
NOT USED
I
2
C Adr2
I
2
C Clock
4
I
2
C Data
4
I_SHARE
SENSE +
5
SENSE -
5
Vsb
Vsb
Vsb
GND
GND
GND
Description
Input AC Voltage ‘OK’ signal output for the 2nd shelf
Power good signal output for the 2nd shelf
Power enable for the 2nd shelf
High Level
Low Level
open drain
< 0.7V
open drain
< 0.7V
> 2.1V (open, or Vsb)
< 0.7V (active, PS:On)
open drain
< 0.7V
open drain
< 0.7V
> 2.1V (open, or Vsb)
< 0.7V (active, PS:On)
> 2.1V, < Vsb
< 0.8V
Vsb
Vsb
I Max
- 2 mA
+ 4 mA
- 2 mA
+ 4 mA
- 1 mA
- 4 mA
- 2 mA
+ 4 mA
- 2 mA
+ 4 mA
- 1 mA
- 4 mA
± 1 mA
Input AC Voltage “OK” signal output for the local shelf
Power good signal output for the local shelf
Power enable for the local shelf
Address input 2
I
2
C serial clock bus
I
2
C serial data bus
Standby voltage output
Standby voltage output
Standby voltage output
GROUND
GROUND
GROUND
All control signals are with respect to Ground. Negative currents exit the power supply.
Signal goes low when any one of the three power supplies loses AC
Signal goes low when any one of the three power supplies fail
3
In a standalone shelf (without I2C control) Pull this pin to GND to turn on three power supplies at the same time. With I2C control, leave this signal float and Use I2C to turn on one power supply at a time.
4
Recomended 10KOhm pull up resistor to host 3.3 or 5V rail
5
Short Sense+ to +Vout and Sens- to GND at the point of load
1
2
SHELF TO SHELF CONNECTION
Signal Connector: MOLEX # 39-28-5164 OR TYCO # 281281-1
Pin Assignment
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
Signal Name
AC_OK1
1
P_Good1
2
PS_On1
3
NOT USED
NOT USED
I
2
C Clock
4
I
2
C Data
4
I_SHARE
SENSE +
5
SENSE -
5
Vsb
Vsb
Vsb
GND
GND
GND
Description
Input AC Voltage ‘OK’ signal output for the 2nd shelf
After applying MDKto execute the code char *test="Chinese characters", the content in test is the AnsiCode internal code of "Chinese characters": BABAD7D6.I hope that the content in test is the UniCod...
[font=微软雅黑][size=3]It's the Spring Festival again. Many people who are eager to go home are struggling with how to buy train tickets. Ticket grabbing software launched by major portals has emerged. I ...
What PCB drawing software do you use now?What is the current scale of Altium Designer?Does Altium Designer have the sch and pcb package libraries for msp430?Thanks...
[color=Red][b]Hello everyone, why is it that when the baud rate is 9600, the sending and receiving are consistent, but it is not working at 115200? The sending and receiving of the serial assistant ar...
Is it necessary to connect the board and the computer to the Internet when using the WinCE system on a 2410 board to call a webservice? Is it possible to use a USB connection? How can I configure the ...
1. Equipment Overview
Shell-and-tube heat exchangers are a common heat exchange device used in chemical evaporation and heating equipment. Currently, the tubesheets of shell-and-tube heat exch...[Details]
Tesla and BYD, vying for dominance in the global electric vehicle market, are reportedly considering adopting Samsung's AMOLED (active-matrix organic light-emitting diode) technology for their next...[Details]
introduction
With the development of digital and network technologies, broadcasting technology has become increasingly diversified, with the most significant trend being the transition from an...[Details]
Some time ago, I attended the 4th Energy Chemistry Forum of the Chinese Chemical Society and learned about high-energy-density and high-safety batteries. I would like to summarize and share this wi...[Details]
Recently,
Xpeng Motors and Xinlian Integrated Circuit jointly announced the mass production of China's first hybrid silicon carbide product.
Designed and developed by Xpeng Motors and joint...[Details]
On August 25th, SK Hynix announced that it has completed development and entered mass production of its 321-layer, 2Tb QLC NAND flash memory product. This achievement marks the world's first applic...[Details]
On August 20th, Tiantai Robotics Co., Ltd., along with strategic partners including Shandong Future Robotics Technology Co., Ltd., Shandong Future Data Technology Co., Ltd., and Gangzai Robotics Gr...[Details]
Since its invention in the mid-1940s, the microwave oven has evolved from a humble beginning to commercial use, entering homes in the 1960s and rapidly gaining popularity. Its basic functionality a...[Details]
A multilevel inverter converts a DC signal into a multilevel staircase waveform. Instead of a straight positive-negative output waveform, the output waveform of a multilevel inverter alternates in ...[Details]
The 2025 China International Automotive Testing Exhibition will be held at the Shanghai World Expo Exhibition and Convention Center from August 27 to 29, 2025.
Clacton Seafront, UK, ...[Details]
On August 22, the Wall Street Journal reported on the 21st local time that the new US government does not plan to acquire equity in semiconductor wafer foundry giant TSMC and Micron, one of the thr...[Details]
With the support and encouragement of national policies, some Internet car manufacturers have also joined the new energy vehicle manufacturing industry. From the perspective of new car manufacturer...[Details]
With growing environmental awareness, the continuous improvement of three-electric technology and the increasing deployment of infrastructure such as charging stations, the electrification of new e...[Details]
Charging is an essential topic for electric vehicles. Batteries are a core component of new energy vehicles. So, what's the optimal charge level for electric vehicles? Based on current battery tech...[Details]
Speaking of the problem of vehicle spontaneous combustion, whether it is a pure electric vehicle or a fuel vehicle, there will be incidents of spontaneous combustion. For the same spontaneous combu...[Details]