DPF1000 SERIES
Dual output
1000W front end
EN61000-3-2 compliant
11 x 6.0 x 5.0 inch size
Hot pluggable
N+1 redundancy
Full set of status signals
EN55022, EN55011 conducted emissions level A
UL, VDE and CSA safety approvals
[ 2 YEAR WARRANTY ]
The DPF1000 is a 1000W universal input AC/DC front end power supply in a fully
enclosed hot pluggable case with built-in fan, handle, IEC input connector, on/off
switch and DIN output signal connector. Providing dual 48V and 5V outputs with a full
set of status signals. The DPF1000 is designed for use as a front end in medium
power communication applications adopting distributed power architecture. The
DPF1000 is fully compliant with EN61000-3-2. Standard features include current
sharing and full protection against overvoltage, overload and short circuit. Remote or
local system monitoring is possible via a full set of status signals that include fan fail,
DC good, power fail, remote inhibit and current monitoring. The DPF1000, with full
international safety approval and the CE mark, meets conducted emissions EN55022
level A. The DPF1000 can be used in conjunction with our complete range of 3 to
200W DC/DC converters to fully configure a distributed power system.
SPECIFICATION
OUTPUT SPECIFICATIONS
Voltage set point
Total regulation
(Full load to no load)
Rise time
Transient response
All specifications are typical at nominal input, full load at 25°C unless otherwise stated
EMC CHARACTERISTICS
-48V ±0.1V @ 10A
EN55022/11, FCC part 15
EN55022/11
FCC part 15
Harmonic current emm. EN61000-3-2
Electrical fast
EN61000-4-4
transients/bursts
Surge susceptibility
EN61000-4-5
GENERAL SPECIFICATIONS
Hold-up time
Efficiency
110VAC, 60Hz
110VAC @ 1kW
Input/output
Input/chassis
20ms @ 1000W
77% min.
3000VAC
1500VAC
200kHz
VDE0805, EN60950, IEC950
UL1950, BABT
CSA C22.2 No. 950
4.3kg (9.5Ibs)
MIL-HDBK-217F
@ 25°C full load
80,000 hours
Radiated noise
Conducted noise
Level A
Level A
Level A
Compliant
Level 3
Level 3
Main output
±5.0%
Auxiliary output, 5V, 0.5A max. ±5.0%
At turn-on
Main output
75% to 100%
step at 0.1A/µs
Main output
latching
1.0s, max.
5.0% max. dev.,
1ms recovery
1.0V pk-pk,
-57V to -60V min.
1200W
Yes
±10% sharing
0.1V/A droop
1/3L to FL
Ripple and noise
(20MHz)
Overvoltage protection
Output power limit
Short circuit protection
Current sharing
Isolation voltage
Switching frequency
Approvals and
standards
Weight
INPUT SPECIFICATIONS
Input voltage range
Input frequency range
Input surge current
Input surge
Safety ground
leakage current
Input current
Input fuse
Power factor
Notes
1
3 orthogonal axes, random vibration, 10 minute test per axis.
1000W
1200W
90 to 264VAC
108 to 264VAC
47Hz to 63Hz
MTBF
ENVIRONMENTAL SPECIFICATIONS
Thermal performance
Operating ambient, FL
0°C to +50°C
Non-operating
-40°C to +70°C
50°C to 70°C
Derate linearly
ambient
to 50% at +70°C
Built-in fan
Operating
Operating
Non-operating
5Hz to 500Hz
MIL-STD-810E
5% to 85% RH
10,000 feet max.
30,000 feet max.
2.4G rms peak
516.4 Part IV
25°C cold start
300VAC
254.4VAC, 50Hz
90VAC, 1000W
Replaceable
110VAC
220VAC
36A typ.
20ms
2.5mA
Cooling
14A rms max.
20A
0.99
0.98
Relative humidity
Altitude
Vibration (See Note 1)
Shock
PAGE 1
DISTRIBUTED POWER FRONT END AC/DC POWER SUPPLIES
|
1000W AC/DC
1000 Watt
AC/DC PFC front-end for distributed power architectures
OUTPUT
VOLTAGE
-48V
+5V
MIN
0A
0A
OUTPUT CURRENT
RIPPLE
MAX
21A
0.5A
1000mV
100mV
Protection features
Overvoltage protection
The unit will shutdown and latch off if the output voltage exceeds the OVP
threshold. Input power recycling is necessary to restart the unit.
Overcurrent and short circuit protection
The unit is protected against an overload on its output in the range 25 to 30A,
with automatic recovery on overload removal. Under short circuit conditions,
the unit shuts down.
Over temperature protection
If the internal temperature of the unit exceeds a safe limit, the unit shuts down
and will need power recycling to re-start.
Input voltage sags
A user supplied jumper inhibits operation of the unit in the 110V range. This
limits the input current to a safe level when operating at 230V to prevent
circuit breakers tripping under brown out. This programmable jumper can be
accessible by removing the cover plate. Refer to view A on page 102.
TOTAL
REGULATION
±5.0%
MODEL NUMBER
DPF1000-9617PE
±5.0%
Control and supervisory functions
Bias Supply H
(Pin 1)
Isolated 5V bias supply, maximum current 0.5A. Allows the system designer
to power system control circuitry.
PFC Fail L
(Pin 2)
A failure in the Power Factor Correction stage, i.e. loss of the 400V internal
bus, is indicated by this open collector signal, asserted low.
Bias Return L
(Pin 3)
Return path for the 5V bias supply. All signals are referenced to this return.
Remote Inhibit H
(Pin 4)
The output is inhibited when this signal is tied high. IIL max. = 10mA.
Voltage Trim
(Pin 5)
The output voltage can be adjusted up to -56V by connecting a 100k variable
resistor between pin 5 and pin 14.
Current Monitor
(Pins 13, 14)
Value: 0.1 x Iout. Tolerance: 10%. Range: 5 to 25A
Power Good L
(Pin 15)
An open collector signal, asserted low. Threshold asserted: 44.5 to 46V,
deasserted: 56.5 to 58V. See Figure 1.
Fan Fail Detect L
(Pin 16)
An open collector signal, asserted low, indicates fan failure. See Figure 1.
Power Fail Detect H
(Pin 17)
An open collector signal, asserted high, indicating AC line failure. The output
voltage will stay within regulation 4ms after PFD is asserted.
Figure 1:
AC Input
48V Output
PFD Signal
PIN CONNECTIONS
PIN NUMBER
1
2
3
4
5
6 to 12
13
14
15
16
17
18 to 24
SIGNAL
5V Bias
PFC Fail
5V Bias Return/Signal Return
Remote Inhibit H
Voltage Trim
-48V Return
Current Monitor +
Current Monitor -
Power Good L
Power Good Signal
t1
t2
t1 varies with line and load
t2 > = 4ms t1 + t2 > =20ms
Load sharing
The DPF1000-9617PE power supply provides load sharing capability for
implementing parallel operation. An internal OR-ing diode is used in each
output to provide N+1 redundancy. The power supplies will share the load
current within ±10% from full load down to
1
/
3
of the rated current of each
power supply.
Method of current sharing of -48V output shall be via the "droop method", as
illustrated in Figure 2 below:
Figure 2: Droop and Regulation Characteristics
Fan Fail Detect L
Power Fail Detect H
-48V
48V
46.9V
46.5V
50.4V
(+5%)
Setting Tolerance
+0.10V (48.1V)
-0.10V (47.9V)
Output
Voltage
Total Output
Tolerance
Band
International Safety Standard Approvals
VDE0805/EN60950/IEC950 File No. 10401-3336-1090
UL1950 File No. E136005
CSA C22.2 No. 950 File No. LR50913/LR101320
Certificate No. PS/606473
45.6V
(-5%)
10A
Output Current
21A
25A
(1000W) (1200W)
http://www.artesyn.com
PAGE 2
1000W AC/DC
|
DISTRIBUTED POWER FRONT END AC/DC POWER SUPPLIES
1000 Watt
AC/DC PFC front-end for distributed power architectures
3.00
(76.20)
VIEW A
SEE DETAIL 'B'
.98
(24.90)
VIEW B
J1
N
L
0.25
(6.40)
J1
24
23
22
21
20
19
18
17
16
15
14
13
12
11
10
9
8
7
6
5
4
3
2
1
N
L
G
6.00
(152.40)
6.52
(165.60)
DETAIL 'B'
1.606 (40.79)
SEE DETAIL 'A'
2.149
(54.58)
5.00
(127.00)
11.00
(279.40)
24
23
22
21
20
19
18
17
16
15
12
11
10
9
8
7
6
5
4
3
2
1
VIEW A
VIEW B
14
13
J2
DETAIL 'A'
ALL DIMENSIONS IN INCHES (mm)
(J2) DC connector
Molex BMI receptacle 42474 part number 15-06-0240 or equivalent with Molex
5556 female crimp terminal part number 39-00-0182 or equivalent.
(J2) DC mating connector
Molex BMI plug 42475 part number 15-06-0246 or equivalent with Molex 5558
male crimp terminal part number 39-00-0220 or equivalent.
(J1) AC connector
Standard IEC connector.
(J1) AC mating connector
Standard IEC plug.
PAGE 3
DS_DPF1000_19980401.PDF
Data Sheet © Artesyn Technologies® 2000
The information and specifications contained in this data sheet are believed to be correct at time of publication. However, Artesyn Technologies accepts no responsibility for consequences arising
from printing errors or inaccuracies. Specifications are subject to change without notice. No rights under any patent accompany the sale of any such product(s) or information contained herein.
http://www.artesyn.com
PAGE 4

DPF1000-9617PE Related Products

DPF1000-9617PE DFP1000
Description Dual output 1000 Watt AC/DC PFC front-end for distributed power architectures Dual output 1000 Watt AC/DC PFC front-end for distributed power architectures
Designing TMS320C2X/C5X Application Programs with C Language
1. Memory Mode The TMS320C2X/C5X fixed-point processor has two types of memory: program memory and data memory. The program memory mainly contains executable program code, while the data memory mainly...
Jacktang Microcontroller MCU
The example provided by TI is suspected to be wrong
The following is an example of the Time_A output PWM waveform provided by TI: TI said in the example explanation: P1.2|--> TACCR1 - 75% PWM P2.0|--> TACCR2 - 25% PWM But I think: P1.2|--> TACCR1 The d...
songyi160 Microcontroller MCU
Five requirements for PCB processing and production
1. PCB size【Background】 The size of the PCB is limited by the capacity of the electronic processing production line equipment. Therefore, the appropriate PCB size should be considered when designing t...
造物工场kbidm PCB Design
DIY CD-ROM controller set of information
I once collected some information about making a CD-ROM controller on a forum. I wanted to make one myself, but I never had the time.Now put it on our website. Who is interested in making one and see ...
某某人 MCU
I'll be going home tomorrow, Ooo, Ooo, Ooo... I'll share my blessings with you.
[b]First, a very cliché opening remark (O(∩_∩)O hahahaha~)[/b]: 2009 was an extraordinary year. . . . . . I had a lot of fun in EEworld in the first half of the year, was extremely busy in the second ...
mq13947193109 Embedded System
How to solve the problem when the routing needs to be bifurcated
As the title says, can I use the method shown in the figure below when the line needs to be split? Or is there any recommended method?Is it okay to have a sharp angle like in Figure 2? Is it okay to h...
z45217 PCB Design

EEWorld
subscription
account

EEWorld
service
account

Automotive
development
circle

Robot
development
community

Index Files: 2687  2930  928  1122  8  55  59  19  23  1 
Datasheet   0 1 2 3 4 5 6 7 8 9 A B C D E F G H I J K L M N O P Q R S T U V W X Y Z
Room 1530, 15th Floor, Building B, No. 18 Zhongguancun Street, Haidian District, Beijing Telephone: (010) 82350740 Postal Code: 100190
Copyright © 2005-2026 EEWORLD.com.cn, Inc. All rights reserved 京ICP证060456号 京ICP备10001474号-1 电信业务审批[2006]字第258号函 京公网安备 11010802033920号