circuit breakers
Thermal Circuit Breaker, rocker actuated, 1-, 2- or 3-pole
TA35 1-pole
TA35 2-pole with CZM25
IP 65, antibacterial cover according
ISO 22196
TA35 3-pole
(pending)
Description
–
–
–
–
–
–
–
–
Thermal circuit breaker 1-, 2- or 3-pole
Supplementary protector for general industrial use
Positively trip-free release
Snap-in mounting
Version with illuminated rocker
Different rocker colours
Antibacterial cover IP65 CZM25
«Dead-Man»-version (Momentary switch)
Applications
–
–
–
–
–
–
–
Power tools
Industrial equipment
Equipment for building construction
Medical equipment
Cleaning equipment
Power generators
Commercial and household kitchen appliances
Standards
– IEC 60934
– UL 1077
– CSA C22.2 235
– GB 17701 (pending)
Weblinks
Approvals: http://www.schurter.com/approvals
RoHS: http://www.schurter.com/rohs
TeChniCAl DATA
Rated voltage U
e
1-pole
2-pole
3-pole
Rated current I
n
1- / 2-pole
3-pole
1- / 2-pole, AC 240 V
3-pole, AC 415 V
Accessible range
Terminal side
50 Hz
Impulse 1.2/50 µs
DC 500 V
AC 240 V / 50/60 Hz
DC 32 V
AC 240 V / 50/60 Hz
DC 60 V
AC 415 Y/240 V / 50/60 Hz
0.05 – 20 A
0.05 – 12 A
0.05…20 A: 2000 A, SC (C1)
0.05…12 A: 2000 A
Shock resistance
Degree of protection
IP 40
IP 00
> 2500 V
> 4000 V
> 100 MOhm
Max. switching capacity 1-, 2-pole
for switch only types
3-pole
(without bimetal)
20 A
12 A
Type of tripping
Weight
1-pole
2-pole
3-pole
Overload
IEC 60934
UL 1077
min. 40 cycles @ 6 x I
n
,
cos phi 0.6
min. 50 cycles @ 1.5 x I
n
,
cos phi 0.75 (OLØ)
–30 °C to +60 °C
Admissible ambient
air temperature
Resistance to vibration
IEC 60068-2-6, Test Tc
Conditional short
circuit I
nc
10…60 Hz: ±0.75 mm
60…500 Hz: 10 G
IEC 60068-2-27, Test Ea 30 G / 18 ms
Thermal positively trip free
19 g
32 g
45 g
Dielectric strength
Insulation resistance
Endurance (typical)
Mechanical
50’000 cycles
AC: 1 x I
n
, cos phi 0.6
50’000 cycles
DC: 1 x I
n
, L/R = 2…3ms 50’000 cycles
2
circuit breakers
TA35
www.schurter.com/pg17_18_19
Tripping ChArACTeriSTiCS
[ min ] [ sec ]
10'000
Type
Rated current
TA35
<3 A (TC-1)
1, 2 pole
3 pole
Ambient temp.
+23 °C
[ min ] [ sec ]
10'000
Type
Rated current
TA35
>3–20A (TC-1)
(3 pole, max. 12A)
1,2,3 pole
Ambient temp.
+23 C °
60
30
20
10
5
200
100
1
50
2`000
1`000
500
60
30
20
10
5
200
100
1
50
2`000
1`000
500
20
10
5
2
1
0,5
Tripping time
0,3
0,2
0,1
1,05 1,35
2
3
4
5
8
10
Multiple of rated current
[ x In ]
Tripping time
20
10
5
2
1
0,5
0,3
0,2
0,1
1,05 1,35
2
3
4
5
8
10
Multiple of rated current
[ x In ]
The above tripping characteristics apply to symmetrical overloads on all poles on the TA35 only.
At asymmetric overloads on multi-pole types, the tripping characteristic will change.
– If a 2-pole type TA35 is loaded at one pole only, the tripping current will be shifted by factor
1.05
(TC-2).
– If a 3-pole type TA35 is loaded at one pole only, the tripping current will be shifted by factor
1.10
(TC-2).
To meet the above tripping characteristic at asymmetric overloads on multi-pole types, the value of the rated current of the CBE has to be multiplied
by the factor mentioned above.
effect of ambient temperature
The unit is calibrated for an ambient temperature of +23 °C. To
determine the rated current for lower or higher ambient temperature,
use a correction factor from the table below.
Ambient
temperature [°C]
–30
–20
0
+23
+40
+50
+60
Correction factor
1-pole
0.77
0.81
0.90
1.00
1.03
1.04
1.06
2-pole
0.76
0.81
0.90
1.00
1.03
1.04
1.06
3-pole
0.76
0.81
0.90
1.00
1.06
1.10
1.14
example for 2-pole type:
Rated current at +23 °C
Ambient temperature
Correction factor
Chosen rated current at +40 °C
ambient temperature:
5.0 A
+50 °C
1.04
5 A x 1.04 = 5.2 A
circuit breakers
3
circuit breakers
Standard rated currents and typical internal resistance
Code
J01
J05
J10
J15
J20
J25
J28
030
040
050
060
070
080
100
120
140
150
160
180
200
In
0.1
0.5
1.0
1.5
2.0
2.5
2.8
3.0
4.0
5.0
6.0
7.0
8.0
10.0
12.0
14.0
15.0
16.0
18.0
20.0
Ri [Ohm]
70.000
2.750
0.720
0.340
0.187
0.115
0.089
0.059
0.059
0.044
0.028
0.0142
0.0142
0.0109
0.0086
0.0072
0.0056
0.0056
0.0052
0.0052
Unprotected poles (without bimetal) 2.2 mΩ
ApprovAlS
# of poles
UL
UL 1077
1
2
3
UL
CSA C22.2 235
1
2
3
VDE
IEC 60934
1
2
3
CQC
GB 17701
1*
2*
3*
* Approvals pending
Rated currents
0.05…20 A
0.05…20 A
0.05…12 A
0.05…20 A
0.05…20 A
0.05…12 A
0.05…20 A
0.05…20 A
0.05…12 A
0.05…20 A
0.05…20 A
0.05…12 A
Rated voltage AC
240 V
240 V
415 Y/240 V
240 V
240 V
415 Y/240 V
240 V
240 V
415 Y/240 V
240 V
240 V
415 Y/240 V
Rated voltage DC
32 V
60 V
—
32 V
60 V
—
32 V
60 V
—
32 V
60 V
—
Actual information about approvals can be found on: www.schurter.com/approvals.
4
circuit breakers
TA35
www.schurter.com/pg17_18_19
orDer CoDe
Number of switched poles
Number of protected poles
1-pole
0
LINE
P1
1
LINE
P1
0
LINE
P1
P2
2-pole
1
LINE
P1
P2
3-pole
2
LINE
P1
P2
0
P1
3
LINE
P2
LINE
P3
P1
P2
P3
4
5
6
4
7
LOAD
LOAD
7
4
4
5
LOAD
LOAD
8
7
8
9
LOAD
LOAD
8
LOAD
Switch
without
Illumination
illuminated
415 V
240 V
120 V
24 V
12 V
5V
CFC
CFT
CBC
CBT
CBD
CKC
CKD
Switch
CK1
CF2
CF4
CF7
CF8
CF9
CgC
C2F
C4F
C7F
C8F
C9F
CgT
C02
C04
C07
C08
C09
CeC
C12
C14
C17
C18
C19
CeT
C32
C34
C37
C38
C39
CeD
ClC
CD1
Momentary without
switch
illumination
ClD
Other versions on request
TA35-
CBD
W
F
120
C0
–
CZM21
Only factory mounted
accessories are integreated
in the Order Code.
No other
features
Colours
Switch front
W
B
r
g
Y
X
1
3
4
6
7
black
black
black
black
black
black
black
black
black
black
black
rocker
non-illuminated
illuminated
Accessories, factory mounted (optional)
CZM21
Transparent cover,
2-pole, IP65
Raised collar with transparent
cover, 2-pole, IP65
Raised collar without cover,
2-pole, IP40
Transparent cover antibacterial,
2-pole, IP65
antibacterial according ISO 22196
white
black
red
green
yellow
orange
–
–
–
–
–
–
–
–
–
–
–
clear transparent
red transparent
green transparent
orange transparent
blue transparent
CZM23
CZM24
CZM25
Other colours on request
rocker legend
Surface
F
h
K
l
embossed
printed
printed
printed
illustration
0
l
Without thermal overload protection: code C00
Colour of print
With thermal overload protection: rated current i
n
(A)
I
n
Code
Z05
J01
J02
J03
J04
J05
J08
I
n
1.0
1.2
1.5
2.0
2.5
3.0
3.5
Code
J10
J12
J15
J20
J25
030
035
I
n
4.0
5.0
6.0
7.0
8.0
10.0
12.0
Code
040
050
060
070
080
100
120
I
n
14.0
15.0
16.0
18.0
20.0
Code
140 *
150 *
160 *
180 *
200 *
0.05
0.1
0.2
0.3
0.4
0.5
0.8
OFF OFF
ON
white
black
white
black
ON
l
l
M
printed
Other legends on request
0
0
Other rated currents on request
* 3-pole max. 12A
circuit breakers
5
circuit breakers
DiMenSionS
TA35, 1-pole
36
34
7.2
1.7
17.5
9.9
14.5
+0.2
0
+0.3
44.1
7
4
P1
LINE
5
2.8 x 0.4 mm
(illuminated version only)
21.3
33.8
2.3
12.5
14.5
6.3 x 0.8 mm
10.6
34
Panel thickness 1.0 to 4.0 mm
L
TA35, 1-pole, Accessories
CZZ11, Srew-on Collar with Cover, IP65
Part. No. 4435.0052
34
10.3
9.8
36
34
1.7
20
17.5
9.9
14.5
+0.2
0
7.2
9.7
33.5
7.8
+0.2
0
Label
+
+0.3
44.1
52
7
4
P1
5.7
LINE
5
23.5
10.6
3
34
L
Quick connect terminal
IEC 61210 A2.8-0.4
27.8
44
±0.15
13.8
21.3
33.8
2.3
12.5
14.5
Panel thickness 1.0 to 4.0 mm
Quick connect terminal
IEC 61210 A6.3-0.8
6
circuit breakers
2.5
44
±0.15
33.5
7.8
+0.2
0
Label