USA SINCE 1936
RELIABILITY BEYOND MEASURE
AMIK 200 / 201
Technical Data Sheet
AMIK
Special Features
MODBUS (RS-485) Communication is included
on Amik 201
On site Programmable CT/PT Ratios
User selectable CT Secondary 1A/5A
User selectable PT Secondary from 100 VLL to 500 VLL
L
Don’t require PT for the voltage measurement up
to 500 ACV
t
Programmable Energy format & Energy rollover count
Wide auxilliary Power Supply which can accept any
input between 40V – 300V AC/DC
Amik 200/ 201
is a compact multifunction instrument which Measures important electrical
parameters in 3 phase 4 Wire and 3 phase 3 Wire Network & replaces the multiple analog panel
meters.
Parameter measurement and Display
Sr No
1.
2.
3.
4.
5.
6.
7.
8.
9.
10.
11.
12.
13.
14.
15.
16.
17.
18.
Parameter
System Volts
System Current
Volts R–N (Phase Voltage for Single phase)
Volts Y–N
Volts B–N
Volts R-Y
Volts Y–B
Volts B–R
Current R (Phase Current for Single phase)
Current Y
Current B
Frequency
System Active Power
(kW)
Active Power R (Phase Power for Single phase) (kW)
Active Power Y
(kW)
Active Power B
(kW)
System Re-active Power
(kVAr)
Re-active Power R (Phase Power for Single phase) (kVAr)
- Not available
3 Phase 4 Wire
3 Phase 3 Wire
1 Phase 2 Wire
- Available
www.simpsonelectric.com
Page 1 of 8
Version No. :AMK200-201/2016/07/28
Parameter measurement and Display
Sr No
19.
20.
21.
22.
23.
24.
25.
26.
27.
28.
29.
30.
31.
Parameter
Re-active Power Y
(kVAr)
Re-active Power B
(kVAr)
System Apparent Power
(kVA)
Apparent Power R (Phase Power for Single phase) (kVA)
Apparent Power Y
Apparent Power B
System Phase Angle
System Power Factor
Power Factor R
Power Factor Y
Power Factor B
Phase Angle R
Phase Angle Y
(kVA)
(kVA)
3 Phase 4 Wire
3 Phase 3 Wire
1 Phase 2 Wire
32.
33.
34.
35.
36.
37.
38.
39.
40.
41.
42.
43.
44.
45.
46.
47.
48.
49.
50.
51.
Phase Angle B
Active Energy Import (kWh)
Active Energy Export (kWh)
Reactive Energy Import (kVArh)
Reactive Energy Export (kVArh)
Apparent Energy (kVAh)
RPM
Max (System Voltage / System Current)
Min (System Voltage / System Current)
Hour Run
ON Hour
Number of auxiliary interrupt
Current Demand
kVA Demand
kW Demand Import
kW Demand Export
Max Current Demand
Max kVA Demand
Max kW Demand Import
Max kW Demand Export
- Not available
- Available
www.simpsonelectric.com
Page 2 of 8
Version No. :AMK200-201/2016/07/28
Ordering Information
Product Code
System Type
Input Voltage
Input Current
Power Supply
RS 485 (For AMIK 201)
Amik 200 (Without MODBUS)
Amik 201 (With MODBUS)
3 Ph. (PR. 3W or 4W)
1 Ph.
100 TO 500VL-L
1/5A
40 V – 300 VAC /DC
With RS 485 (Available only on Amik 201).
Without RS 485 (Amik 200)
Catalog No. A200
Catalog No. A201
Accessories – Three-Phase Current Transformer
A three-phase terminal style current transformer must be used
with A M I K three phase meters.
The current transformer is equipped with terminals to
permit easy connection to the AMI K units.
These terminals are #8-32 brass studs and come with a
flatwasher, lockwasher and a regular nut (leads are not
provided).
Ordering Information
Catalog
Number
37026
37027
37028
37029
37030
Current
Ratio
50:5
100:5
150:5
200:5
300:5
Accuracy
@ 60 Hz
± 3%
± 2%
± 1%
± 1%
± 1%
Burden VA
@ 60 Hz
2.0
2.0
4.0
5.0
10.0
www.simpsonelectric.com
Page 3 of 8
Version No. :AMK200-201/2016/07/28
Amik 200 /201
Application
Amik
200/ 201
Measures important electrical parameters in 3 phase 4 Wire and 3 phase 3 Wire Network & replaces the multiple analog
panel meters. It measures electrical parameters like AC Voltage, AC Current, Frequency, Active, Reactive, Apparent Power, Import
Export Energy & many more.
Product Features
On site
programmable
PT / CT ratios
User selectable
CT Secondary
5A /1A
User selectable
PT Secondary
It is possible to program primary of external
potential Transformer (PT), primary of
external Current Transformer (CT) on site via
front panel keys by entering into
Programming mode.
The secondary of external Current
Transformer (CT) can be programmed on
site to either 5A or 1A using front panel keys.
Optional Pulse
Output /
Limit switch
(Relay output)
Pulse Output
Not Available
Not Available
Limit Switch
Not Available
Low back depth
The instrument has very low back depth
(behind the panel) of less than 55 mm
(Without output option).
Using the four function key, it is possible to
go desired parameter screen instantly..
Measures & Displays Current Demand,
kVA Demand, kW Import Demand,
kW Export Demand. Any of the parameters
can be assigned to optional Limit switch.
Simultaneous display of 3 Parameters.
The instrument display Rotation per minutes
for generator applications. Number of poles
can be set on site depending upon
application requirement.
In case of power failure, the instrument
memorizes the last energy count. Every
1 min, the instrument updates the energy
counter in the non-volatile memory.
User can program on site the network
connection as either
3 Phase 3 Wire or 4 Wire or single phase
network using front panel keys.
3 Phase 4 wire or single phase network is
available.
Optional
MODBUS
(RS485) Output
The optional Modbus output enables the
instrument to transmit all the measured
parameters over standard MODBUS (RS-485).
Four function
keys
Demand
Measurement
RS-485
The MODBUS com
3 line 4 digits
LED display
RPM
Measurement
Storage of
parameters
possible
The instrument stores minimum and
maximum values for System Voltage, System
Current, Run Hour, ON Hour & number of
Interrupts. Every 60 sec stored values are
updated.
Conforms to IP 50 (for front face) & IP 20
(for back)
IEC60529.
Compliance to International standard
IEC 61326.
IEC 61326-1 : 2005, Class A
IEC 61326-1 : 2005
IEC 61000-4-2 -- 4kV/8kV
IEC 61000-4-3 -- 10 V/m
(80 MHz to 1 GHz)
– 3 V/m (1.4 Ghz to 2 GHz)
-- 1 V/m (2 GHz to 2.7 GHz)
Energy Count
Storage
Enclosure
Protection for
dust and water
EMC
Compatibility
Interference
Emission
Interference
Immunity
Electrostatic
discharge contact
/air. (ESD)
EM Field
User selectable
3 phase 3 Wire
or 4Wire or
Single phase
Network
Onsite selection
of Auto scroll /
Fixed Screen
www.simpsonelectric.com
Page 4 of 8
Version No. :AMK200-201/2016/07/28
Amik 200 /201
Product Features
True RMS
measurement
Energy
Measurement
(Import & Export)
The instrument measures distorted wave
form up to 15th Harmonic.
Active Energy (kWh), Reactive Energy
(kVArh), Apparent Energy (kVAh).
Any of the parameters can be assigned to
optional Pulse output.
Customer can assign the format for energy
display on MODBUS (RS-485) in terms of
W, kW or MW. Additional to this, customer
can also set a rollover count from 7 to 14 digits
depending on the energy format, after which
the energy will roll back to zero.
Burst
Surge
Conducted RF
Rated Power
Frequency
magnetic Field
Voltage dip
IEC 61000-4-4 -- 2 kV (5/50 ns, 5 kHz)
IEC 61000-4-5 -- 1 kVLL / 2 kVLN.
IEC 61000-4-5 -- 3 V (150 kHz to 80 MHz)
IEC 61000-4-8 -- 30 A/m
IEC 61000-4-11 -- 0% during 1 cycle.
-- 40% during 10/12 cycles.
-- 70% during 25/30 cycles.
IEC 61000-4-11 -- 0% during 25/30 cycles.
25 cycles for 50 Hz test.
30 cycles for 60 Hz test.
Programmable
Energy format &
Energy rollover
count
Short
interruptions
cycles.
Dimension Details
Reference conditions for Accuracy
Reference temperature
Input waveform
Input frequency
Auxiliary supply voltage
Auxiliary supply frequency
Voltage Range
Current Range
Power
23°C +/- 2°C
Sinusoidal (distortion factor 0.005)
50 or 60 Hz ±2%
Rated Value ±1%
Rated Value ±1%
20... 100% of Nominal Value.
10... 100% of Nominal Value.
Cos phi / sin phi = 1 for Active /
Reactive Power & Energy.
10... 100% of Nominal Current &
20... 100% of Nominal Voltage.
Power Factor / Phase Angle 40... 100% of Nominal Current &
20... 100% of Nominal Voltage.
With optional MODBUS / Limit switch
96 mm
Display Area
96 mm
Accuracy
Voltage
Current
Frequency
Active Power
Re-Active Power
Apparent Power
Active Energy
Reactive Energy
Apparent Energy
Power Factor
Phase angle
± 1% of Nominal Value.
± 1% of Nominal Value.
0.5% of mid frequency
± 1% of Nominal Value.
± 1% of Nominal Value.
92mm+0.8
92mm+0.8
± 1% of Nominal Value.
± 1%
± 1%
± 1%
2% of Unity
2% of range
Panel Cutout
www.simpsonelectric.com
Page 5 of 8
Version No. :AMK200-201/2016/07/28