Power Supply Featuring OMRON’s Unique, New Undervoltage Alarm Function with
Compact Body Contributing to Machine Downsizing
• New undervoltage alarm function assists in determining causes of errors (S8VM-@@@24A@/P@ only).
• Power failure alarm function provides notification of output voltage errors (300-, 600-, and 1,500-W models only).
• Broad range of possibilities with 8 capacities and 29 models to choose from.
• RoHS-compliant
• New, attentive design prevents screws from falling out of terminal block (except for output terminals of 300-, 600-, and 1,500-W
models).
• Finger protection prevents electric shock.
• DIN Rail mounting.
• Safety standards: UL508/60950-1/1604, CSA C22.2 No. 14/No. 60950-1/No. 213, EN50178, EN60950-1 (The 300-, 600-, and
1,500-W models will not conform to safety standards if the customer replaces the fan.)
• Conforms to SEMI F47-0200 (when 200-V input is used).
• Harmonic current emissions: Conforms to EN61000-3-2 (except for 15- and 30-W models).
!
Refer to
Safety Precautions for All Power Supplies
and
Safety Precautions
on page 32.
Model Number Structure
■
Model Number Legend
Note:
Not all combinations are possible. Refer to
List of Models
in
Ordering Information
on page 2.
S8VM-
@@@@@@@
1
1. Power Ratings
015:
15 W
030:
30 W
050:
50 W
100: 100 W
150: 150 W
300: 300 W
600: 600 W
152: 1,500 W
2. Output Voltage
05: 5 V
12: 12 V
15: 15 V
24: 24 V
2
3 4
3. Configuration/Functions
None: Open-frame type Standard type
C:
Covered type
Standard type
A:
Covered type
Undervoltage alarm type
(Sinking (emitter COM))
(See note 2.)
P:
Covered type
Undervoltage alarm type
(Sourcing (collector COM))
(See note 2.)
4. Configuration
None: Bottom mounting type (See note 3.)
D:
DIN Rail mounting bracket type
Note: 1.
A forced-air cooling method with a fan is used with 300-, 600-, and 1,500-W models.
2.
The housing and terminal of the connector for the undervoltage alarm output are provided with the S8VM-05024A@/P@, S8VM-
10024A@/P@ and S8VM-15024A@/P@.
3.
Bottom mounting models cannot be used for front mounting. For a front mounting configuration, use a DIN Rail Mounting Bracket model
or Mounting Brackets (sold separately).
1
S8VM
Ordering Information
■
List of Models
Note:
For details on normal stock models, contact your nearest OMRON representative.
Configura-
tion
Power
ratings
Input voltage
Output voltage
Output current
Standard
model
100 to 240 VAC
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
3A
1.3 A
1A
0.65 A
6A
2.5 A
2A
1.3 A
10 A
4.3 A
3.5 A
2.2 A
20 A
8.5 A
7A
4.5 A
27 A
S8VM-01505
S8VM-01512
S8VM-01515
S8VM-01524
S8VM-03005
S8VM-03012
S8VM-03015
S8VM-03024
S8VM-05005
S8VM-05012
S8VM-05015
S8VM-05024
S8VM-10005
S8VM-10012
S8VM-10015
S8VM-10024
S8VM-15005
(See note 2.)
12.5 A
S8VM-15012
10 A
S8VM-15015
6.5 A (See note 6.) S8VM-15024
3A
S8VM-01505C
1.3 A
S8VM-01512C
1A
S8VM-01515C
0.65 A
S8VM-01524C
6A
S8VM-03005C
2.5 A
S8VM-03012C
2A
S8VM-03015C
1.3 A
S8VM-03024C
10 A
S8VM-05005C
4.3 A
S8VM-05012C
3.5 A
S8VM-05015C
2.2 A
S8VM-05024C
20 A
S8VM-10005C
8.5 A
S8VM-10012C
7A
S8VM-10015C
4.5 A
S8VM-10024C
27 A
S8VM-15005C
(See note 2.)
12.5 A
S8VM-15012C
10 A
S8VM-15015C
6.5 A (See note 6.) S8VM-15024C
60 A
S8VM-30005C
27 A
S8VM-30012C
22 A
S8VM-30015C
14 A
S8VM-30024C
Peak current:
16.5 A (200 VAC)
120 A
S8VM-60005C
53 A
S8VM-60012C
43 A
S8VM-60015C
27 A
S8VM-60024C
Peak current:
31 A (200 VAC)
65 A (100 VAC)
S8VM-15224C
70 A (200 VAC)
(See note 3.)
Peak current:
105 A (200 VAC)
Bottom mounting
Undervoltage alarm model
Sinking
Sourcing
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
S8VM-01524A (See note 1.)
---
---
---
---
---
---
S8VM-03024A (See note 1.)
---
---
---
---
---
---
S8VM-05024A S8VM-05024P
---
---
---
---
---
---
S8VM-10024A S8VM-10024P
---
---
---
---
S8VM-15024A
---
---
---
---
---
---
S8VM-15024P
---
---
---
---
DIN Rail mounting bracket
Standard
Undervoltage alarm model
model
Sinking
Sourcing
S8VM-01505D
S8VM-01512D
S8VM-01515D
S8VM-01524D
S8VM-03005D
S8VM-03012D
S8VM-03015D
S8VM-03024D
S8VM-05005D
S8VM-05012D
S8VM-05015D
S8VM-05024D
S8VM-10005D
S8VM-10012D
S8VM-10015D
S8VM-10024D
S8VM-15005D
(See note 2.)
S8VM-15012D
S8VM-15015D
S8VM-15024D
S8VM-01505CD
S8VM-01512CD
S8VM-01515CD
S8VM-01524CD
S8VM-03005CD
S8VM-03012CD
S8VM-03015CD
S8VM-03024CD
S8VM-05005CD
S8VM-05012CD
S8VM-05015CD
S8VM-05024CD
S8VM-10005CD
S8VM-10012CD
S8VM-10015CD
S8VM-10024CD
S8VM-15005CD
(See note 2.)
S8VM-15012CD
S8VM-15015CD
S8VM-15024CD
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
Open-frame 15 W
type
30 W
50 W
100 W
150 W
Covered
type
15 W
100 to 240 VAC
30 W
50 W
100 W
150 W
---
---
---
---
---
---
---
---
---
---
---
---
S8VM-01524AD (See note 1.)
---
---
---
---
---
---
S8VM-03024AD (See note 1.)
---
---
---
---
---
---
S8VM-05024AD S8VM-05024PD
---
---
---
---
---
---
S8VM-10024AD S8VM-10024PD
---
---
---
---
S8VM-15024AD
---
---
---
---
---
---
S8VM-15024PD
---
---
---
---
300 W
(See note
4.)
600 W
(See note
4.)
5V
12 V
15 V
24 V
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
1,500 W
(See note
4.)
24 V
---
---
---
---
---
Note: 1.
2.
3.
4.
5.
6.
No outputs are built into these models.
The output capacity of the S8VM-15005@@ is 135 W.
M8 bolts and nuts for the output terminals are not included with the S8VM-15224C.
The 300-, 600-, and 1,500-W models use a forced cooling method with built-in fans.
To perform front mounting using the bottom mounting models, use the Mounting Brackets (S82Y-VM@@F, sold separately).
The output current for UL1604 certification is 6.3 A.
2
S8VM
Specifications
■
Ratings/Characteristics
Item
Efficiency
Power rating
5-V models
12-V models
15-V models
24-V models
Voltage (See note 1.)
Frequency (See note 1.)
Current
100-V input
200-V input
Power factor
100-V input
200-V input
Harmonic current emissions
Leakage
100-V input
current
200-V input
Inrush current 100-V input
(See note 2.)
200-V input
Voltage adjustment range (See note 3.)
Ripple
15 W
30 W
50 W
100 W
75% min.
75% min.
80% min.
81% min.
78% min.
79% min.
79% min.
81% min.
78% min.
79% min.
79% min.
81% min.
80% min.
81% min.
80% min.
82% min.
100 to 240 VAC (85 to 264 VAC)
50/60 Hz (47 to 63 Hz)
0.5 A max.
0.9 A max.
0.8 A max.
1.4 A max.
0.25 A max.
0.45 A max.
0.4 A max.
0.7 A max.
---
0.98 min.
---
0.94 min.
---
Conforms to EN 61000-3-2
0.4 mA max. (at rated output)
0.75 mA max. (at rated output)
17.5 A max. (for cold start at 25°C)
35 A max. (for cold start at 25°C)
−20%
to 20% (with V. ADJ) (S8VM-@@@24A@/P@:
−10%
to 20%)
3.2% (p-p) max. (5 V),
3.2% (p-p) max. (5 V),
1.5% (p-p) max. (12 V),
1.5% (p-p) max. (12 V),
1.2% (p-p) max. (15 V),
1.2% (p-p) max. (15 V),
1.0% (p-p) max. (24 V),
0.75% (p-p) max. (24 V),
(at rated input/output voltage)
(at rated input/output voltage)
0.4% max. (at 85 to 264 VAC input, 100%)
0.8% max. (with rated input, 0 to 100% load)
150 W
81% min.
81% min.
81% min.
83% min.
Input
2.0 A max.
1.0 A max.
Output
Input variation influence
Load variation influence (rated input
voltage)
Temperature variation influence
Startup time (See note 2.)
Hold time (See note 2.)
Additional Overload protection (See note 2.)
functions
Overvoltage protection (See note 2.)
Undervoltage alarm indication
Undervoltage alarm output
Series operation
Parallel operation
Remote sensing function
Ambient operating temperature
Storage temperature
Ambient operating humidity
Dielectric strength
Other
Insulation resistance
Vibration resistance
Shock resistance
Output indicator
EMI
Conducted Emission
Radiated Emission
EMS
Approved
UL
standards
cUL
cUR
EN/TÜV
0.02%/°C max.
1,100 ms max. (at rated input/output voltage) 800 ms max. (at rated input/output voltage)
20 ms typ. (15 ms min.) (at rated input/output voltage)
105% to 160% of rated load current, voltage 105% to 160% of rated load current,
drop, intermittent, automatic reset
voltage drop (12 V, 15 V, and 24 V),
voltage drop, intermittent (5 V), automatic reset
Yes (See note 4.)
Yes (color: Yellow (DC LOW1), red (DC LOW2)) (S8VM-@@@24A@/P@ only)
No
Yes (S8VM-@@@24A@/P@ only)
(Transistor output), 30 VDC max., 50 mA max. (See note 8.)
Yes for up to 2 Power Supplies (with external diode)
No
No
Yes
Refer to the derating curve in
Engineering Data (15-W, 30-W, 50-W, 100-W, 150-W Models).
(with no icing or conden-
sation) (See note 2.)
−25
to 65°C
30% to 85% (Storage humidity: 25% to 90%)
3.0 kVAC for 1 min. (between all inputs and outputs; detection current: 20 mA)
2.0 kVAC for 1 min. (between all inputs and PE/FG terminals; detection current: 20 mA)
500 VAC for 1 min. (between all outputs and PE/FG terminals; detection current: 100 mA)
500 VAC for 1 min. (between all outputs (except the detection output terminals) and detection output terminals; de-
tection current: 20 mA) (S8VM-@@@24A@/P@ only)
100 MΩ min. (between all outputs and all inputs, PE/FG terminals) at 500 VDC
10 to 55 Hz, 0.375-mm single amplitude for 2 hours each in X, Y, and Z directions
150 m/s
2
, 3 times each in
±X, ±Y, ±Z
directions
Yes (color: Green)
Conforms to EN61204-3 EN55011 Class B and based on FCC Class B (See note 5.)
Conforms to EN61204-3 EN55011 Class B (See note 6.)
Conforms to EN61204-3 High severity levels
UL508 (Listing), UL60950-1, UL1604 (Listing; Class
I/Division
2, Group A, B, C, D Hazardous Locations) (See note 9.)
CSA C22.2 No.14, No. 213 (Class
I/Division
2, Group A, B, D, D Hazardous Locations)
CSA No. 60950-1
EN50178, EN60950-1
SELV (EN60950-1)
According to VDE0160/P100
SEMI F47-0200 (200 VAC input)
180 g max.
220 g max.
290 g max.
460 g max.
530 g max.
SEMI
Weight (See note 7.)
Note: 1.
Do not use an Inverter output for the Power Supply. Inverters with an output frequency of 50/60 Hz are available, but the rise in the internal temperature of the Power
Supply may result in ignition or burning.
2.
Refer to
Engineering Data (15-W, 30-W, 50-W, 100-W, 150-W Models)
on page 9 to 11 for details.
3.
If the output voltage adjuster (V. ADJ) is turned, the voltage will increase by more than +20% of the voltage adjustment range. If the adjuster is turned too far, it may
activate the overvoltage protection function and interrupt the output.
When adjusting the output voltage, confirm the actual output voltage from the Power Supply and be sure that the load is not damaged.
4.
To reset the protection, turn OFF the input power for three minutes or longer and then turn it back ON.
5.
Conducted emissions: The noise value is affected by factors such as the wiring method. The Power Supply conforms to Class B when the aluminum plate is laid under
the Power Supply. For 15-W models, insert a clamp filter (ZCAT2436-1330 by TDK: 50
Ω
min. [50 to 500 MHz], or the equivalent) in the output wire to reduce noise.
6.
Radiated emissions: The noise value is affected by factors such as the wiring method. The Power Supply conforms to Class B when the aluminum plate is laid under the
Power Supply. For 150-W models, insert a clamp filter (ZCAT2017-0930 by TDK: 35
Ω
min. [50 to 500 MHz], or the equivalent) in the input wire to reduce noise.
7.
The weight indicated is for bottom mounting, open-frame models.
8.
A@: Sinking type (NPN)
P@: Sourcing type (PNP)
9.
With the S8VM-15024@@, the output current for UL1604 certification is 6.3 A.
UL1604 (Listing; Class I/Division 2, Group A, B, C, D Hazardous Locations) (24 V)
CSA C22.2 No.14, No. 213 (Class I/Division 2, Group A, B C, D Hazardous Loca-
tions) (24 V)
CSA No. 60950-1
EN50178, EN60950-1
SELVE (EN60950-1)
SEMI F47-0200 (200-VAC input)
1,100 g max.
1,700 g max.
Other
Insulation resistance
Vibration resistance
Shock resistance
Output indicator
EMI
Conducted Emission
Radiated Emission
EMS
Approved
standards
(See note 8.)
Conforms to EN61204-3 EN55011 Class A
and based on FCC Class A (See note 6.)
Conforms to EN61204-3 EN55011 Class A
(See note 6.)
UL508, UL60950-1
UL
cUR
cUR
EN/TÜV
SEMI
CSA C22.2 No.14, CSA No. 60950-1
EN50178, EN60950-1
SELVE (EN60950-1)
3,800 g max.
Weight
Note: 1.
Do not use an Inverter output for the Power Supply. Inverters with an output frequency of 50/60 Hz are available, but the rise in the internal temperature of
the Power Supply may result in ignition or burning.
2.
Refer to
Engineering Data (300-W, 600-W, 1,500-W Models)
on page 15 to 17 for details.
3.
If the output voltage adjuster (V. ADJ) is turned, the voltage will increase by more than +20% of the voltage adjustment range.
If the adjuster is turned too far,
it may activate the overvoltage protection function and interrupt the output.
When adjusting the output voltage, confirm the actual output voltage from the Power
Supply and be sure that the load is not damaged.
4.
To reset the protection, turn OFF the input power for three minutes or longer and then turn it back ON. Alternatively, turn OFF the remote control signal and
then turn it back ON again.
5.
Conducted emissions: The noise value is affected by factors such as the wiring method. The Power Supply conforms to Class B when the aluminum plate
is laid under the Power Supply. For 600-W models, insert a clamp filter (ZCAT3035-1330 by TDK: 100
Ω
min. [50 to 500 MHz], or the equivalent) in the input
wire, and ring core (HF60T38X14X22 by TDK: 16
Ω
typ. [1 MHz], 46
Ω
typ. [10 MHz], or the equivalent) in the output wire to reduce noise
6.
Radiated emissions: The noise value is affected by factors such as the wiring method. The Power Supply conforms to Class A when the aluminum plate is
laid under the Power Supply (1,500-W models).
7.
The measuring method conforms to JEITA standard RC-9131A. Refer to
Ripple
under
Safety Precautions
on page 32.
8.
The Power Supply will not conform to safety standards if the customer replaces the fan.