AXL F UTH8 1F
Axioline F temperature module,
8 inputs for connection of thermocouple sensors
Data sheet
8267_en_04
1
Description
© PHOENIX CONTACT 2015-09-11
The module is designed for use within an Axioline F station.
It is used to acquire signals from standard thermocouples in
industrial applications.
The module supports various types of thermocouple con-
forming to DIN EN 60584-1 and DIN 46710 as well as linear
voltages from -100 mV to +100 mV.
It also offers a voltage input from -5 V to +5 V. Heating cur-
rents can be monitored here, for example, using a measur-
ing transducer.
The four Pt 100 inputs (CJ1 ... CJ4) can each be used as a
sensor input or as an external cold junction.
Features
–
–
–
–
–
8 analog input channels to connect thermocouples or
linear voltages from -100 mV to +100 mV
1 analog input channel to connect voltages from -5 V to
+5 V
Connection of sensors in 2-wire technology
Internal detection and compensation of cold junction
temperature (can be parameterized)
External connection of Pt 100 cold junction sensors
possible
–
–
–
–
–
–
–
–
–
Easy to use due to internal linearization of the sensor
characteristic curves
High level of accuracy (typically ±0.01% sensor type K)
High level of accuracy, even in various mounting posi-
tions, thanks to built-in space compensation of the inter-
nal cold junction
High temperature stability (typically 5 ppm/K)
High level of immunity to EMI (Class A)
"Channel scout" function
Device type label stored
Diagnostic and status indicators
Installation monitoring with indication via diagnostic
LED for each channel
This data sheet is only valid in association with the UM EN AXL F SYS INST user manual.
Make sure you always use the latest documentation.
It can be downloaded from the product at
phoenixcontact.net/products.
AXL F UTH8 1F
2
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
Table of contents
Description .............................................................................................................................. 1
Table of contents ..................................................................................................................... 2
Ordering data .......................................................................................................................... 3
Technical data ......................................................................................................................... 4
Additional technical data.......................................................................................................... 7
Internal circuit diagram .......................................................................................................... 14
Terminal point assignment..................................................................................................... 15
Connection examples ............................................................................................................ 15
Connection notes .................................................................................................................. 19
Configuration notes ............................................................................................................... 19
Local status and diagnostic indicators ................................................................................... 20
Process data.......................................................................................................................... 22
Open circuit ........................................................................................................................... 22
Significant values in various formats...................................................................................... 23
Parameter, diagnostics and information (PDI) ....................................................................... 24
Standard objects ................................................................................................................... 25
Application objects ................................................................................................................ 31
Writing the analog values over the PDI channel..................................................................... 37
Device descriptions ............................................................................................................... 37
8267_en_04
PHOENIX CONTACT
2
AXL F UTH8 1F
3
Ordering data
Type
AXL F UTH8 1F
Description
Axioline?F temperature module, 8 inputs for connection of thermocouple
sensors (including bus base module and connectors)
Order No.
2688417
Pcs./Pkt.
1
Accessories
Axioline F bus base module for housing type F (Replacement item)
Type
AXL F BS F
Order No.
2688129
2700984
2700518
0829579
Pcs./Pkt.
5
1
1
25
Axioline F connector set (for e.g., AXL F AI8 1F, AXL F AO8 1F) (Replace- AXL CNS 4L-O/D/UA/E1/E2
ment item)
Axioline shield connection set (contains 2 busbar holders and 2 SK 5 shield
connection clamps)
AXL SHIELD SET
Zack marker strip for Axioline F (device labeling), in 2 x 20.3 mm pitch, un- ZB 20,3 AXL UNPRINTED
printed, 25-section, for individual labeling with B-STIFT 0.8, X-PEN, or
CMS-P1-PLOTTER (Marking)
Zack marker strip, flat, in 10 mm pitch, unprinted, 10-section, for individual
labeling with M-PEN 0,8, X-PEN, or CMS-P1-PLOTTER (Marking)
Thermoelectric voltage terminal block, cross section: 0.2 - 2.5 mm², width:
10.4 mm, color: gray
Thermoelectric voltage terminal block, cross section: 0.2 - 2.5 mm², width:
10.4 mm, color: gray
Thermoelectric voltage terminal block, cross section: 0.2 - 2.5 mm², width:
10.4 mm, color: gray
Thermoelectric voltage terminal block, cross section: 0.2 - 2.5 mm², width:
10.4 mm, color: gray
Thermoelectric voltage terminal block, cross section: 0.2 - 2.5 mm², width:
10.4 mm, color: gray
Thermoelectric voltage terminal block, cross section: 0.2 - 2.5 mm², width:
10.4 mm, color: gray
Insert label, Roll, white, unlabeled, can be labeled with: THERMOMARK
ROLL, THERMOMARK ROLL X1, THERMOMARK X, THERMOMARK
S1.1, Mounting type: snapped into marker carrier, Lettering field: 35 x 46
mm (Marking)
ZBF 10/5,8 AXL UNPRINTED
MTKD-CU/CUNI
MTKD-FE/CUNI
MTKD-NICR/CUNI
MTKD-NICR/NI
MTKD-E-CU/A-CU
MTKD-S-CU/E-CU
EMT (35X46)R
0829580
3100059
3100046
3100075
3100062
3100091
3100101
0801604
50
50
50
50
50
50
50
1
Documentation
User manual, English, Axioline F: System and installation
Type
UM EN AXL F SYS INST
Order No.
-
-
Pcs./Pkt.
-
-
User manual, English, Axioline F: Diagnostic registers, and error messages UM EN AXL F SYS DIAG
8267_en_04
PHOENIX CONTACT
3
AXL F UTH8 1F
4
Technical data
Dimensions (nominal sizes in mm)
53,6
54
122,4
Width
Height
Depth
Note on dimensions
126,1
53.6 mm
126.1 mm
54 mm
The depth is valid when a TH 35-7.5 DIN rail is used (according to EN 60715).
General data
Color
Weight
Ambient temperature (operation)
Ambient temperature (storage/transport)
Permissible humidity (operation)
Permissible humidity (storage/transport)
Air pressure (operation)
Air pressure (storage/transport)
Degree of protection
Protection class
Mounting position
traffic grey A RAL 7042
203 g (with connectors and bus base module)
-25 °C ... 60 °C
-40 °C ... 85 °C
5 % ... 95 % (non-condensing)
5 % ... 95 % (non-condensing)
70 kPa ... 106 kPa (up to 3000 m above sea level)
70 kPa ... 106 kPa (up to 3000 m above sea level)
IP20
III, IEC 61140, EN 61140, VDE 0140-1
Any (no temperature derating; Parameterize the mounting position using the ob-
ject 0080
hex
ParaTable!)
Connection data
Designation
Connection method
Conductor cross section solid / stranded
Conductor cross section [AWG]
Stripping length
Axioline F connector
Push-in connection
0.2 mm² ... 1.5 mm² / 0.2 mm² ... 1.5 mm²
24 ... 16
8 mm
Please observe the information provided on conductor cross sections in the “Axioline F: system and installation” user manual.
Interface Axioline F local bus
Connection method
Transmission speed
Bus base module
100 MBit/s
8267_en_04
PHOENIX CONTACT
4
AXL F UTH8 1F
Communications power
Communications power U
Bus
Current consumption from U
Bus
Power consumption at U
Bus
5 V DC (via bus base module)
typ. 115 mA, max. 180 mA
typ. 0.55 W, max. 0.9 W
I/O supply
Supply for analog modules U
A
Maximum permissible voltage range
Current consumption from U
A
Power consumption at U
A
Surge protection of the supply voltage
Polarity reversal protection of the supply voltage
Transient protection
24 V DC
19.2 V DC ... 30 V DC (including all tolerances, including ripple)
typ. 45.3 mA
max. 70 mA
typ. 1.09 W, max. 1.68 W
Electronic (35 V, 0.5 s)
Polarity protection diode
Suppressor diode
Total power consumption of the module
Power consumption
typ. 1.63 W (entire device), max. 2.58 W (entire device)
Analog inputs
Number of inputs
Connection method
Connection method
Sensor types that can be used (TC)
Sensor types (RTD) that can be used
Resolution A/D
Measuring principle
Measured value representation
Input filter time
Relative accuracy
Absolute accuracy
Short-circuit protection, overload protection of the inputs
Transient protection of inputs
Crosstalk attenuation
8 +1 (8 inputs for thermocouples or linear voltage, plus 1 input -5 V to +5 V)
Spring-cage connection with direct connector-in method
2-wire (shielded, twisted pair)
U, T, L, J, E, K, N, S, R, B, C, W, HK
Pt 100 (4 external cold junctions, can also be used as a sensor input)
24 bit
Sigma/Delta process
16 bits (15 bits + sign bit)
40 ms, 60 ms, 100 ms, 120 ms (adjustable)
typ. 0.01 % (Thermocouple type K, NiCr-Ni; see tables under tolerance values)
typ. ± 0.19 K (Thermocouple type K, plus tolerance of cold junction)
yes
yes
typ. 110.7 dB (Channel/channel, sensor type K)
typ. 110.5 dB (Channel/channel, sensor type linear voltage ±100 mV)
typ. 109.1 dB (Channel/channel, external Pt 100 connection)
min. 100 dB (Sensor type K)
typ. 152 dB (Sensor type K)
min. 100 dB (Sensor type linear voltage ±100 mV)
typ. 154 dB (Sensor type linear voltage ±100 mV)
typ. 20 MΩ (With 24 V I/O supply voltage present)
typ. 5 MΩ (With 24 V I/O supply voltage present)
max. 40 V DC (1 min.)
Common mode rejection (CMR): TC inputs/linear voltage
Common mode rejection (CMR): TC inputs/linear voltage
Common mode rejection (CMR): TC inputs/linear voltage
Common mode rejection (CMR): TC inputs/linear voltage
Input resistance: TC inputs/linear voltage
Input resistance: Voltage input -5 V ... +5 V
Voltage at the TC input
Configuration and parameter data in a PROFIBUS system
Required parameter data
Need for configuration data
27 Byte (20 bytes for configuration with GSD AXL UTH 8 (packed))
7 Byte
8267_en_04
PHOENIX CONTACT
5