Inputs/Outputs the analog signal of 0-5V or 4-20mA, etc., and executes A/D
or D/A conversion.
•
Encoder Input Terminal
•
Expansion Units
Performs conversion for pulse input signals from an encoder.
Attached to the Digital I/O Unit to expands the I/O points.
Can be attached to a two-tier terminal block type with 16 inputs, 16 outputs,
and 16 relay outputs.
General Specifications
It is common specifications of Digital I/O Terminal, Analog I/O Terminal and Encoder Input Terminal GX-Series. Refer to the pages of specifications
for individual I/O terminals for details.
For General Specification of IO-Link Master Unit(GX-ILM08C), refer to page 31.
Item
Unit power supply voltage
I/O power supply voltage
Noise resistance
Vibration resistance
20.4 to 26.4 VDC (24 VDC
−15%
to +10%)
20.4 to 26.4 VDC (24 VDC
−15%
to +10%)
Conforms to IEC 61000-4-4, 2 kV (power line)
Malfunction 10 to 60 Hz with amplitude of 0.7 mm, 60 to 150Hz and 50 m/s
2
in X, Y, and Z directions for 80 minutes
<Relay Output Unit GX-OC1601 only>
10 to 55 Hz with double-amplitude of 0.7 mm X, Y, and Z directions for 80 minutes
150 m/s
2
with amplitude of 0.7 mm
<Relay Output Unit GX-OC1601 only>
100 m/s
2
(3 times each in 6 directions on 3 axes)
600 VAC (between isolated circuits)
20 MΩ or more (between isolated circuits)
−10
to 55
°C
25% to 85% (with no condensation)
No corrosive gases
−25
to 65
°C
25% to 85% (with no condensation)
M3 wiring screws: 0.5 N•m
M3 terminal block mounting screws: 0.5 N•m
35-mm DIN track mounting
Specification
Impact resistance
Dielectric strength
Isolation resistance
Ambient operating temperature
Operating humidity
Operating atmosphere
Storage temperature
Storage humidity
Terminal block screws
tightening torque
*
Mounting method
*
Applicable only to 2-tier terminal block and 3-tier terminal block type slaves.
Sysmac is a trademark or registered trademark of OMRON Corporation in Japan and other countries for OMRON factory automation products.
EtherCAT
®
is a registered trademark of Beckhoff Automation GmbH for their patented technology.
EtherNet/IP
TM
is the trademarks of ODVA.
Other company names and product names in this document are the trademarks or registered trademarks of their respective companies.
1
GX-Series
EtherCAT Communications Specifications
Communications Specifications of GX-Series EtherCAT Remote I/O Terminal
Item
Communication protocol
Modulation
Baud rate
Physical layer
Connectors
Topology
Communications media
Communications distance
Noise resistance
Node address setting method
Node address range
Specification
Dedicated protocol for EtherCAT
Base band
100 Mbps
100BASE-TX (IEEE802.3)
RJ45 shielded connector
×
2
CN IN: EtherCAT input
CN OUT: EtherCAT output
Daisy chain
Category 5 or higher (cable with double, aluminum tape and braided shielding is recommended.)
Distance between nodes (slaves): 100 m max.
Conforms to IEC 61000-4-4, 1 kV or higher
Set with decimal rotary switch or Sysmac Studio
1 to 99: Set with rotary switch
1 to 65535: Set with Sysmac Studio
PWR
×
1
L/A IN (Link/Activity IN)
×
1
L/A OUT (Link/Activity OUT)
×
1
RUN
×
1
ERR
×
1
Fixed PDO mapping
2 bit to 256 byte
Emergency messages, SDO requests, SDO responses, and SDO information
Digital I/O Slave Unit and Analog I/O Slave Unit: Free Run mode (asynchronous)
Encoder Input Slave Unit: DC mode 1
LED display
Process data
PDO size/node
Mailbox
SYNCHRONIZATION mode
Version Information
Unit Versions
Units
GX-Series EtherCAT Slave Units
Compatible Sysmac Studio version
Models
Unit version 1.0
GX-@@@@@@
Supported
Version1.00 or higher
*
Supported
Version1.00 or higher
Unit Version
Unit version 1.1
*
The function that was enhanced by the upgrade for Unit version1.1 can not be used. For detail, refer to "Function Support by Unit Version".
Function Support by Unit Version
The following tables show the relationship between unit versions and CX-Programmer versions.
Unit Versions and Programming Devices
Unit
Model
Unit version
Item
Sysmac error status
Save the node address setting
Serial Number Display
ESI standard (1.0)
SII data check
Unit version 1.0
No Supported
No Supported
No Supported
Supported
No Supported
Supported
Supported
Supported
Supported
Supported
GX-Series EtherCAT Slave Units
GX-@@@@@@
Unit version 1.1
2
Digital I/O Terminal 2-tier Terminal Block Type
GX-@D16@1/OC1601
High-speed digital I/O terminal with the
screw type terminal block for EtherCAT
communications
• Detachable screw terminal block facilitates the maintenance.
• The expansion unit can be connected.
(One expansion unit per one I/O terminal unit.)
Input/output point can be flexibly increased depending on the
system.
• Input response time can be switched for high-speed processing.
• Selectable node address setting methods: setting with rotary
switch and with tool software.
When setting the nodes with rotary switch, setting is easy and
node identification becomes possible for maintenance.
Expansion Units
One Expansion Unit can be combined with one Digital I/O Terminal (GX-ID16@1/OD16@1/OC1601). The following Expansion Units are available.
They can be combined in various ways for flexible I/O capacity expansion.
Model
XWT-ID08
XWT-ID08-1
XWT-OD08
XWT-OD08-1
XWT-ID16
XWT-ID16-1
XWT-OD16
XWT-OD16-1
I/O points
8 DC inputs (NPN)
8 DC inputs (PNP)
8 transistor outputs (NPN)
8 transistor outputs (PNP)
16 DC inputs (NPN)
16 DC inputs (PNP)
16 transistor outputs (NPN)
16 transistor outputs (PNP)
Input capacity
8
8
0
0
16
16
0
0
Output capacity
0
0
8
8
0
0
16
16
3
GX-Series
Digital I/O Terminal 2-tier Terminal Block Type
General Specifications
For Common Specifications of I/O terminals, refer to page 1.
Input Section Specifications
16-point Input Terminals
Item
Input capacity
Internal I/O common
ON voltage
OFF voltage
OFF current
Input current
ON delay
OFF delay
Input filter value
Number of circuits per common
Input indicators
Isolation method
I/O power supply method
Unit power supply current con-
sumption
I/O power supply current con-
sumption
Weight
Expansion functions
16 points
NPN
Specification
GX-ID1611
PNP
5 VDC max. (between each input terminal and the G terminal)
GX-ID1621
15 VDC min. (between each input terminal and the V terminal) 15 VDC min. (between each input terminal and the G terminal)
5 VDC max. (between each input terminal and the V terminal)
1.0 mA max.
6.0 mA max./input (at 24-VDC)
3.0 mA min./input (at 17-VDC)
0.1 ms max.
0.2 ms max.
Without filter, 0.5 ms, 1 ms, 2 ms, 4 ms, 8 ms, 16 ms, 32 ms (Default setting: 1 ms)
16 inputs/common
LED display (yellow)
Photocoupler isolation
Supply by I/O power supply
90 mA max. (for 20.4 to 26.4-VDC power supply voltage)
5 mA max. (for 20.4 to 26.4-VDC power supply voltage)
180 g max.
Enabled
Short-circuit protection function
No
Note:
For the I/O power supply current value to V and G terminals, refer to GX Series Operation Manual (Cat. No. W488).
Output Section Specifications
16-point Output Terminals
Item
Output capacity
Rated current (ON current)
Internal I/O common
Specification
GX-OD1611
16 points
0.5 A/output, 4.0 A/common
NPN
1.2 V max.
(0.5 ADC, between
each output termi-
nal and the G ter-
minal)
0.1 mA max.
0.5 ms max.
1.5 ms max.
16 points/common
LED display (yellow)
Photocoupler isolation
Supply by I/O power supply
90 mA max. (for 20.4 to 26.4-VDC power
supply voltage)
5 mA max. (for 20.4 to 26.4-VDC power
supply voltage)
180 g max.
Enabled
Select either hold or clear
PNP
1.2 V max.
(0.5 ADC, between
each output termi-
nal and the V termi-
nal)
Rated load
Rated ON current
Maximum contact voltage
Maximum contact current
Maximum switching capacity
Minimum applicable load
(reference value)
Mechanical service life
Electrical service life
Number of circuits per common
Output indicators
Isolation method
I/O power supply method
Unit power supply current con-
sumption
Weight
Expansion functions
GX-OD1621
Relay 16-point Output Terminals
Item
Output capacity
Mounted relays
16 points
DRTA-NY5W-K
Resistance load
250 VAC 2 A/output, common 8 A
30 VDC 2 A/output, common 8 A
3 A/output
250 VAC, 125 VDC
3 A/output
750 VAAC, 90 WDC
5 VDC 1mA
20,000,000 operations min.
100,000 operations min.
8 points/common
LED display (yellow)
Relay isolation
The relay drive power is supplied from
the unit power supply.
210 mA max. (for 20.4 to 26.4-VDC pow-
er supply voltage)
290 g max.
Enabled
Specification
GX-OC1601
Residual voltage
Leakage current
ON delay
OFF delay
Number of circuits per common
Output indicators
Isolation method
I/O power supply method
Unit power supply current con-
sumption
I/O power supply current con-
sumption
Weight
Expansion functions
Output handling for communications
errors
Short-circuit protection function
No
Output handling for communica-
Select either hold or clear
tions errors
Short-circuit protection function
No
Note:
For the I/O power supply current value to V and G terminals,
refer to GX Series Operation Manual (Cat. No. W488).
Precautions for Correct Use
•
With a current of between 2 and 3 A (8 to 10 A per common), either ensure that the number of points per common that simultaneously turn ON does not exceed
4 or ensure that the ambient temperature does not exceed 45
°C.
Also, there are no restrictions if the current does not exceed 2 A (8 A per common).
•
The rated current is the value for assuring normal operation, and not for assuring durability of the relays. The relay service life depends greatly on factors such
as the operating temperature, the type of load, and switching conditions. The actual equipment must be checked under actual operating conditions.
4
GX-Series
Digital I/O Terminal 2-tier Terminal Block Type
Input and Output Section Specifications
8-point Input and 8-point output Terminals
General Specifications
Item
Internal I/O common
I/O indicators
NPN
LED display (yellow)
Specification
GX-MD1611
PNP
GX-MD1621
Unit power supply
80 mA max. (for 20.4 to 26.4-VDC power supply volt-
current consumption
age)
Weight
Expansion functions
Short-circuit protec-
tion function
190 g max.
No
No
Input Section
Item
Input capacity
ON voltage
Specification
GX-MD1611
8 points
15 VDC min.
15 VDC min.
(between each input ter- (between each input ter-
minal and the V terminal) minal and the G terminal)
5 VDC max.
5 VDC max.
(between each input ter- (between each input ter-
minal and the V terminal) minal and the G terminal)