Duty cycle 0.1 to 100.0% (increments of 0.1%), Output pulse frequency 15 to 5,000 Hz (increments of 1 Hz): 4 points (Q0, Q2, Q4, Q6) (Adjust 5µs minimum as ON
time and 15µs minimum as OFF time.)
USB mini-B (maintenance communication)
Maintenance communication (server), user communication TCP (server/client),
user communication UDP, Modbus TCP (server/client), Email, Web Server, PING, SNTP, FTP server/client
Maintenance communication (server), user communication TCP (server/client),
user communication UDP, Modbus TCP (server/client), PING
Two cartridges can be added (when using FC6A–HPH1)/One cartridge can be added (when using FC6A–PH1)
Embedded
Yes
Pulse Output
(transistor output model
only)
*1: 1 step equals 8 bytes.
*2: Not including expansion I/O service time, counter timer processing time, data link processing time, and interrupt processing time.
*3: A maximum of 5 modules can be connected when using the expansion interface module separate type master.
*4: Transistor output model
*5: Communication module cannot be connected.
INPUT SPECIFICATIONS
Part No.
Input Points
Rated Input Voltage
Input Voltage Range
Rated Input Current
Input Impedance
Turn ON Time
Input Delay
Turn OFF Time
Isolation
Input Type
External Load for I/O Interconnection
Signal Determination Method
Effect of Improper Input Connection
Cable Length
Insertion Durability
Connector
Applicable Ferrule
FC6A–D16R1CEE
FC6A–D16P1CEE
FC6A–D16K1CEE
8 (8/1 common)
24V DC: 24V DC sink/source input signal
0 to 28.8V DC
High speed input port 5mA/pt, middle/normal speed input port 7mA/pt
High speed input port 4.9kΩ, middle/normal speed input port: 3.4kΩ
High speed input port:
5μs + filter value
Middle speed input port:
35μs + filter value
Normal speed input port:
35μs + filter value
High speed input port:
5us + filter value
Middle speed input port:
35us + filter value
Normal speed input port: 100us + filter value
Between input terminals: Not isolated
Internal circuit:
Optocoupler-isolated
FC6A–D32P3CEE
FC6A–D32K3CEE
16 (16/1 common)
Type1 (IEC 61131-2)
Not needed
Static
Both sinking and sourcing input signals can be connected, therefore reverse connection does not cause damage.
If any input exceeding the rated value is applied, permanent damage may be caused.
20,000,000 operations minimum (no load 18,000 operations/hour)
Resistive load: 240V AC 2A, 30V DC 2A
Inductive load: 240V AC 2A (cos ø = 0.4), 30V DC 2A (L/R =7 ms)
100 times minimum
1-wire: AI 0.5-8 WH (Phoenix Contact)
2-wire: AI-TWIN 2×0.5-8 WH (Phoenix Contact)
TRANSISTOR OUTPUT SPECIFICATIONS
Part No.
Transistor Output Points
Output Type
Transistor Sink
Transistor Source
FC6A-C16P1CEE
FC6A-C16K1CEE
8 (8/1 common)
FC6A–D16K1CEE/FC6A–D32K3CEE
FC6A–D16P1CEE/FC6A–D32P3CEE
24V DC
19.2 to 28.8V DC
Per Point
Per Common
Turn ON Time
Output Delay
Turn OFF Time
Isolation
Voltage Drop (ON Voltage)
Inrush Current
Leakage Current
Clamping Voltage
Maximum Lamp Load
Inductive Load
Overcurrent Protection
External Current Draw
Insertion Durability
Connector
Applicable Ferrule
0.5A
4.0A
High speed input port: 5μs
Normal speed input port: 300μs
High speed input port: 5μs
Normal speed input port: 300μs
Between output terminal and Internal circuit:
Between output terminals: Not isolated
1A
0.1mA maximum
39V ±1V
12W
L/R=10ms (28.8V DC, 1Hz)
Transistor Sink Output:
No
Transistor Source Output: Overcurrent is detected by current limit resistance. (*1)
100mA maximum, 24V DC (power voltage at the +V terminal, -V terminal at source)
100 times minimum
1-wire: AI 0.5-8 WH (Phoenix Contact)
2-wire: AI-TWIN 2×0.5-8 WH (Phoenix Contact)
—
2.4W
0.1A
1.6A
FC6A–D32P3CEE
FC6A–D32K3CEE
16 (16/1 common)
Rated Load Voltage
Voltage Tolerance
Rated Load
Current
Optocoupler-isolated
1V max (voltage between COM and output terminal when output is on.)
0.2A
*1: This overcurrent signals consist of one signal per 4 point outputs. When microprocessor gets this overcurrent signal by interrupt input, microprocessor turns off 4pt outputs of this category at fixed time (approx. 1sec).