Thermal Overcurrent Circuit Breaker 127-...
Description
Single pole thermal circuit breaker with push-to-reset, tease-free,
trip-free, snap action mechanism (R-type TO CBE to EN 60934; M-type
when fitted with optional manual release feature). Available in versions
for plug-in or integral mounting, track mounting, or with a frame for
snap-in panel mounting. The optional -KF housing is particularly suited
to high humidity and other damp conditions.
Approved to CBE standard EN 60934 (IEC 60934).
Typical applications
Motors, transformers, solenoids, battery chargers, extra low voltage
systems.
1
127-P10-H-KF
Technical data
For further details please see: www.e-t-a.de/ti_e
Voltage rating
AC 250 V; DC 28 V
(UL: AC 250 V; DC 50 V)
Current ratings
0.05...25 A
Typical life
0.05...16 A 5,000 operations at 2 x I
N
, inductive
17...25 A 5,000 operations at 2 x I
N
, resistive
Ambient temperature
-20...+60 °C (-4...+140 °F)
Insulation co-ordination
rated impulse
pollution
(IEC 60664 and 60664 A) withstand voltage
degree
2.5 kV
2
reinforced insulation in operating area
Dielectric strength
(IEC 60664 and 60664A) test voltage
operating area
AC 3,000 V
Insulation resistance
> 100 MΩ (DC 500 V)
Interrupting capacity I
cn
0.05...2.5 A
8 x I
N
3...5 A
20 x I
N
6...12 A
200 A
13...25 A
300 A
Interrupting capacity
I
N
U
N
(UL 1077)
0.05...20 A
AC 250 V
2,000 A
0.05...25 A
DC 50 V
2,500 A
Degree of protection
operating area IP40
(IEC 60529/DIN 40050)
terminal area IP00
Vibration
8 g (57-500 Hz) ± 0.61 mm (10-57 Hz)
to IEC 60068-2-6, test Fc,
10 frequency cycles/axis
Shock
25 g (11 ms), to IEC 60068-2-27, test Ea
Corrosion
96 hours at 5 % salt mist,
to IEC 60068-2-11, test Ka
Humidity
240 hours at 95 % RH
to IEC 60068-2-78, test Cab
Mass
127-P10-..: approx. 20 g
127-T..-:
approx. 35 g
127-T12-H
Ordering information
Type No.
127
Mounting options
leave blank for integral/plug-in option
T12
track mounting with screw terminals M4
Terminal design (for use with and without flange -F)
P10
blade terminals A6.3-0.8 (QC .250)
Manual release
H
manual release facility
Special housing
KF
for tropical and high humidity conditions
Current ratings
0.05...25 A
127 - F - P10 - H - KF - 10 A
ordering example
Please be informed that we have minimum ordering quantities to be observed.
Standard current ratings and typical internal resistance values
Current
rating (A)
0.05
0.08
0.1
0.15
0.2
0.25
0.3
0.35
0.4
0.45
0.5
0.6
0.7
0.8
0.9
1
1.2
Internal
resistance (Ω)
280
100
110
56
29
18
14
9.8
7
5.9
4.9
3.4
2.5
1.8
1.5
1.2
0.8
Current
rating (A)
1.5
1.8
2
2.5
3
3.5
4
4.5
5
6
7
8
10
15
16
20
25
Internal
resistance (Ω)
0.6
0.4
0.3
0.2
0.1
0.06
0.06
0.05
0.05
0.02
0.02
0.02
< 0.02
< 0.02
< 0.02
< 0.02
< 0.02
Approvals
Authority
VDE
UL
CSA
CQC
Standard
IEC / EN 60934
UL 1077
C22.2 No 235
GB 17701
Rated voltage
AC 250 V
DC 28 V
AC 250 V
DC 50 V
AC 250 V
DC 50 V
AC 250 V
DC 28 V
Current ratings
0.05 A…25 A
0.05 A…25 A
0.05 A…20 A
0.05 A…25 A
0.05 A…20 A
0.05 A…25 A
0.05 A…25 A
0.05 A…25 A
1833
www.e-t-a.de
1
Thermal Overcurrent Circuit Breaker 127-...
Dimensions
127-P10-H-KF
0.05...25 A
OFF
Internal connection diagram
1
13.5
.531
8
.315
ON
ø4
.157
2
45
1.77
1
Typical time/current characteristics at +23 °C/+73.4 °F
1
9.4
.370
19.8
.780
31
1.22
32
10000
11.5
.453
blade terminal
DIN 46244-A6.3-0.8
(QC .250)
Trip time in seconds
0.05 - 2.7 A
2.8 - 23 A
25 A
1000
127-T12-H
ø4
.157
100
31
1.22
ON
OFF
11.5
.453
10
6
.236
12
.472
63
2.48
52
2.05
47
1.85
13
.512
1
M4
7
.276
0.1
1
2
4 6
8 10
... times rated current
20
40
44
1.73
54
2.13
tightening torque
for M4 max. 1.2 Nm
G profile
EN 50035-G...
14
.551
spacing
The time/current characteristic curve depends on the ambient temperature
prevailing. In order to eliminate nuisance tripping, please multiply the
circuit breaker current ratings by the derating factor shown below. See also
section Technical information.
Ambient temperature °F
°C
Derating factor
-4
-20
0.76
+14
-10
0.84
+32
0
0.92
+73.4
+23
1
+104
+40
1.08
+122
+50
1.16
+140
+60
1.24
Installation drawings
max. 2
max .079
34
1.34
127-T12-H
operating area
53
2.09
35
1.38
1
.039
max. 2
max .079
mounting area
max. 2
max .079
53
2.09
25
.984
35
1.38
This is a metric design and millimeter dimensions take precedence ( mm )
inch
2
www.e-t-a.de
1833
Thermal Overcurrent Circuit Breaker 127-...
Accessories
Mounting sockets
10F-P10
(up to 16 A max. load)
68
2.68
12
21
11
22
8
.315
max. tightening torque
of mounting screw: 2.5 Nm
blade terminals
DIN 46244-A6.3-0.8 (QC .250)
1
10F-K10
(up to 20 A max. load)
wire corss sectional areas
2 x max. 2.5 mm
2
(AWG14) stranded
2 x max. 4 mm
2
(AWG12) solid
max. tightening torque of terminal screw: 1.2 Nm
12
1
.472
.039
12
.472
1
.039
5.6
.220
30
1.18
9.5
.374
75
15
.591
45
1.77
75
2.95
13
.512
6
.236
7
.276
50
1.97
12
7.5
.296
10F-A10
(up to 16 A max. load)
blade terminals DIN 46244-A6.3-0.8 (QC .250)
8
.315
59
2.32
12
11
11
21
22
21
22
wire corss sectional areas
2 x max. 2.5 mm
2
(AWG14) stranded
2 x max. 4 mm
2
(AWG12) solid
7
.276
Accessories for sockets
(
up to 20 A max. load)
2-way bus bar
Y 301 166 02
4-way bus bar
Y 301 166 01
4.2
.165
2.9
.114
8.5
.335
7.9
.311
12.5
.492
15
.591
22.9
.902
thickness = 0.8 mm
.031 in.
15
15
15
.591 .591 .591
52.9
2.08
Connector bus links -K10
X 210 589 01/2.5
mm
2
(AWG 14), black (up to 20 A max. load)
X 210 589 02/1.5
mm
2
(AWG 16), brown (up to 13 A max. load)
ø2.5
.099
50 pin lugs to DIN 46230
tinned copper
Connector bus links -P10
X 210 588 01/1.5
mm
2
(AWG 16), brown (up to 13 A max. load)
X 210 588 02/2.5
mm
2
(AWG 14), black (up to 20 A max. load)
X 210 588 03/2.5
mm
2
(AWG 14), red (up to 20 A max. load)
X 210 588 04/2.5
mm
2
(AWG 14), blue (up to 20 A max. load)
100 quick-connect tabs 6.3 (.250)
DIN 46247 tinned brass,
insulated
~70
~2.76
This is a metric design and millimeter dimensions take precedence ( mm )
inch
All dimensions without tolerances are for reference only. In the interest of improved design,
performance and cost effectiveness the right to make changes in these specifications
without notice is reserved.Product markings may not be exactly as the ordering codes.
Errors and omissions excepted.
~70
~2.76
1833
www.e-t-a.de
3