The FXP1500/1800 front-ends are power-factor-corrected (PFC) and
provide a 48 VDC (1500 or 1800 watt) output, and can be used in hot-swap
redundant systems. Their very small dimensions allow configuration of up
to three units in a 1U rack. The FXP front-ends have a rear-mounted AC
connector. The highly efficient thermal design with internal-fan cooling
permits their use over wide temperature ranges and provides very high
reliability.
Status information is provided with front panel LEDs, logic signals, and via
an I
2
C management interface. In addition, the I
2
C bus can enable the power
supply, set high fan speed, adjust the output voltage, and set the output
current limit. The FXP1500/1800's meet international safety standards and
display the CE-Mark for the European Low Voltage FXR-3-48G power-
shelf solutions provide rectification, system management, and power
distribution, while maintaining high reliability and offering flexibility for
future expansion. The power shelves can be configured with up to three
hot-swappable 1500 or 1800-watt AC-DC front-ends.
RoHS compliant for all six substances
High density front-ends 15.2 to 18.3 W/in
3
Wide input voltage range 85 to 264 VAC
12 V standby voltage, 1 A per front-end
Highly efficient topology reduces operating costs
I
2
C interface status and control
I
2
C voltage and current limit setting
Analog output voltage setting
Overtemperature, output overvoltage, and output
overcurrent protection
ORing circuits for true redundant operation:
V
o1
: ORing FETs; V
o2
: ORing Diodes
Status LEDs: AC OK, DC OK, and
Fan Fail/Overtemperature Fail
Telecommunications
Data Communications
Servers
Distributed Power
2
FXP1500/1800; FXR-3-48G
INPUT VOLTAGE
VAC
AUTO SELECTED
1
105 – 264
85 – 105
180 – 264
105 – 180
85 – 105
OUTPUT 1
OUTPUT 2
RATED POWER
W
1512
1212
1812
1512
1212
COMPATIBLE
SHELF
2
FXR-3-48G
FXR-3-48G
MODEL
FXP1500-48G
FXP1800-48G
1
2
V
o1 nom
VDC
48
48
48
48
48
I
o1 max
ADC
32.2
25.4
39.2
32.2
25.4
V
o2 nom
VDC
12
12
12
12
12
I
o2 max
ADC
1
1
1
1
1
The available output power is automatically adjusted depending on the input voltage.
1U standard racks are available from Bel Power Solutions. See the Rack (Power Shelf) section of this data sheet for configurations
and details.
Stress in excess of the absolute maximum ratings may cause performance degradation, adversely affect long-term
reliability, or cause permanent damage to the converter.
PARAMETER
Input Voltage
Operating Ambient Temperature
Storage Temperature
Non-Operating
CONDITIONS / DESCRIPTION
Continuous
Transient, 60 ms max.
V
i min
-
V
i max
,
I
o nom
, cooling by internal fan
@ 100 % load
@ 50 % load
MIN
MAX
264
300
50
70
85
UNIT
VAC
0
0
-40
°C
°C
Specification is valid for input voltage, load, and temperature ranges, unless otherwise stated.
PARAMETER
Input Voltage
Input Frequency
Turn-On Input Voltage
Turn-Off Input Voltage
Inrush Current Limitation
Hold-Up Time
Power Factor
Efficiency
Max Input Current
Input Connector
16 A – 20 A / 250 VAC; according to IEC320 C19
Ramping up
Ramping down
115/230 VAC acc. ETS 300 132-1
< 100 ms
After last AC line peak ,
V
i
= 230 VAC,
P
o nom
CONDITIONS / DESCRIPTION
MIN
85
47
79
70
NOM
230
50/60
MAX
264
63
85
78
50
20
0.95
89
90
20
UNIT
VAC
Hz
VAC
VAC
A
pk
ms
W/VA
%
A
rms
V
i nom
,
I
o nom
V
i
= 230 VAC,
I
o nom
,
T
C
= 25 °C
tech.support@psbel.com
FXP1500/1800; FXR-3-48G
Specification is valid for input voltage, load, and temperature ranges, unless otherwise stated.
PARAMETER
Nominal Output Voltage Vo1
Nominal Output Voltage Vo2
Output Voltage Set Point Accuracy
Output Voltage Trimming
(via I
2
C or with external resistor)
FXP1500-48G
Nominal Current Output 1
CONDITIONS / DESCRIPTION
MIN
NOM
48
12
-0.5
-8
+0.5
+8
32.2
25.4
39.2
32.2
25.4
36.8
30
43.8
36.8
30
1.0
1.5
-0.5
46.65
46.07
83.5
48
83.5
48
0.4
0.5
49.34
49.34
MAX
3
UNITS
VDC
VDC
%
V
o1 nom
%
V
o1 nom
ADC
ADC
ADC
ADC
ADC
ADC
ADC
ADC
ADC
ADC
ADC
ADC
%
V
o nom
mV/A
VDC
mV/A
VDC
VDC
I
o
= 16.1 A
I
o
= 0.5 A
V
i
= 230 VAC,
I
o1
=16.1 A,
T
C
= 25 °C
(47.8 - 48.2 VDC)
Adjustable (44.16 to 51.84 VDC)
@
V
i
=105 VAC – 264 VAC,
@
V
i
= 85 VAC – 105 VAC,
@
V
i
=180 VAC – 264 VAC,
FXP1800-48G
@
V
i
=105 VAC – 180 VAC,
@
V
i
= 85 VAC – 105 VAC,
@
V
i
= 105 VAC – 264 VAC
FXP1500-48G
@
V
i
= 85 VAC – 105 VAC
I
o1 max
@
V
i
= 180 VAC – 264 VAC
FXP1800-48G
I
o1 max
@
V
i
= 105 VAC – 180 VAC
I
o1 max
@
V
i
= 85 VAC – 105 VAC
I
o2 nom
@ Vi = 85 VAC – 264 VAC,
I
o1 nom
I
o1 nom
I
o1 nom
I
o1 nom
I
o1 nom
I
o1 max
I
o1 max
P
o
1.5 kW
P
o
1.2 kW
P
o
1.8 kW
P
o
1.5 kW
P
o
1.2 kW
droop hiccup
droop hiccup
droop hiccup
droop hiccup
droop hiccup
P
o
12 W
39.2
Current Limit Output 1
Nominal Current Output 2
Current Limit Output 2
Static Line Regulation Output 1
1.0
I
o2 max
@
V
i
= 85 VAC – 264 VAC
V
i min
-
V
i max
, 50 %
I
o nom
V
i
= 230 V, 5-100 %
I
o nom
FXP1500-48G
Static Load Regulation
V
o
: full load (32.2 ADC) to no load
Output 1
V
i
= 230 V, 5-100 %
I
o nom
(Droop Characteristic)
FXP1800-48G
V
o
: full load (32.2 ADC) to no load
Static Load Regulation Output 2
V
i
= 230 V, 5-100 %
I
o nom
(Droop Characteristic)
V
o
: full load (32.2 ADC) to no load
Load change 50 % <-> 100 %
I
o nom
, dI
o
/dt =1 A/s
Voltage deviation (droop + over- or undershoot)
FXP1500-48G
Dynamic Load Regulation
FXP1800-48G
All models
Max. recovery time to within 1 % of
V
o1 nom
Difference in current between two units for
V
o1
above
10 % load.
-5
-5.7
5
5.7
400
%
V
o nom
%
V
o nom
s
Current Share
FXP1500-48G
FXP1800-48G
Time required for output within regulation
after initial application of AC-input (
V
i nom
,
I
o nom
)
after removal of inhibit
(
V
i nom
,
I
o nom
)
V
i nom
,
I
o nom
, 20 MHz bandwidth
3.2
3.9
1.5
100
480
120
500
ADC
ADC
s
ms
mV
pp
mV
pp
mV
Start-Up Time
Output Voltage Ripple and Noise
(Filter 10 nF/10 µF)
Remote Sense
V
o1
V
o2
Total compensation for cable losses
PARAMETER
Input Fuse
Inrush Current Limitation
Output
Overvoltage Protection Latching
3
Overtemperature Protection
3
CONDITIONS/DESCRIPTION
Not user accessible
MIN
NOM
MAX
UNIT
25 A, fast blow
With NTCs
No-load -, short circuit - and overload proof
115
122
%
V
o nom
59.5
V
95
°C
Tracking
Absolute
Automatic power shutdown at
T
C
Remove input voltage to reset.
Asia-Pacific
+86 755 298 85888
Europe, Middle East
+353 61 225 977
North America
+1 408 785 5200
BCD.00023_AD
© 2016 Bel Power Solutions & Protection
4
FXP1500/1800; FXR-3-48G
Specification is valid for input voltage, load, and temperature ranges, unless otherwise stated.
PARAMETER
Visual Status Indication
I
2
C Communication Bus
I
2
C Communication Bus
Addressing
PS Present Pin
PS Main Output Remote
Shutdown
Power Supply OK
DC Current Fail
TYPE
4
FP
OC[S1, S2]
OC[T1-T5]
OC[U3]
OC[R1]
FP
I
2
C
I
2
C
CONDITIONS / DESCRIPTION
•
DC OK (green)
LED indicators
5
:
•
AC OK (green)
•
Fan fail & Over-temperature (amber)
•
Monitors alarm functions and allows control of specific parameters.
•
Uses standard Philips two wire bus (SCL and SDA signal lines)
Five lines provide up to 32 separate PSU I
2
C addresses
•
Used by system to indicate a PSU is installed in a system shelf
•
Contact closure to logic ground ( internal pull-down resistor of 1 kΩ)
•
TTL compatible signal, inhibited when open contact, high or at TTL logic “1”
•
Signal referenced to logic return (LRTN)
Two position switch in series with OC signal (logical AND) allows local enable/disable; “0” Position
=> PS disabled; “1” Position => PS Enabled
AC OK & DC OK & no overcurrent & no over-temperature & fans working
Reports over-current condition on main output, I
O1
Provides a warning that the input power has failed at least 5 ms before the output falls out of
regulation (<90% V
O1
set).
•
Open collector signal with 20 mA pull-down capability, referenced to logic return (LRTN).
•
AC fail will go high or open during power fail condition and will go low when input is within
the operating range.
•
A Power Fail warning will turn off the front panel green AC OK LED.
Internal under-voltage and overvoltage supervision of V
O1
.
•
Open collector signal with 20 mA pull-down capability, referenced to logic return (LRTN).
•
DC fail will go high or open if
V
o1 < 90% or V
O1
> 110% of V
O1
set, measured in front of the
ORing FETs.
•
Green LED on the front panel indicates normal operation; LED will flash if in parallel
operation V
O1
is OK, but the unit is disabled.
Indicates the PSU operating temperature has reached [T
shut-down
– 10K] Indicates if the unit is in
over-temperature shutdown.
•
Open collector signal with 20 mA pull-down capability, referenced to logic return (LRTN).
•
The OC-output will go low 100 ms before an over-temperature condition shuts down the
unit.
•
An amber LED on the front panel indicates over-temperature or fan fail.
Monitors the main output voltage, V
O1
, seen at the output connector.
Accuracy is ±0.45V over setting range and temperature.
Monitors the output current I
O1
: Accuracy ± 0.4A over the load range.
Output voltage trimming V
O1
: ±8% of V
O
set using external resistor
Setting accuracy over I2C: ± 50mV at V
o1
nom, ± 150mV over setting range
Two fan speed levels automatically set depending on the internal temperature. The fan speed can
be set to full speed or automatic control via I
2
C command.
Indicates if the cooling fans are operating or have failed.
Overcurrent signal which can be used for synchronous startup of units in parallel or to recover
from an overload condition.
AC Fail / Power Down
Warning
OC[U2]
& I
2
C
DC Fail / Output Voltage
Fault
OC[U4]
& I
2
C
Critical Temperature
Warning/Fan Fail
OC[U1]
& I
2
C
DC Voltage Monitoring
DC Current Monitoring
DC Voltage Trimming
(Margining)
Fan Speed Control
Fan OK/FAIL
Synchronized Startup Pin
4
I
2
C
I
2
C
OC[R4]
I
2
C
I
2
C
OC[U1]
& I
2
C
OC[R5]
5
Abbreviations used:
OC[#]
=> Hardwired signal accessible at PSU output connector, with pin number reference
FP
=> Provided by devices located on PSU Front panel
2
IC
=> Signal provided over I
2
C communication system; detailed I
2
C information is available from the specific
model’s I
2
C Manual found on the Bel Power Solutions web site.
See LED Function table for further details
tech.support@psbel.com
FXP1500/1800; FXR-3-48G
PARAMETER
Altitude
Relative Humidity, Non-Condensing
Temperature Coefficient
Shock
Sinusoidal Vibration
Random Vibration
MTBF
CONDITIONS / DESCRIPTION
Operating
Non-Operating
Operating
Storage
0 °C to 70 °C (after 15 min warm-up)
IEC/EN 60068-2-27, 11 ms
IEC/EN 60068-2-6
2-8 Hz
8-200 Hz
200-500 Hz
10-2000 Hz
Calculated per Bellcore (SR-332, Issue 1):
GB 25 °C
GB 25 °C (FNP1500-12G)
Demonstrated
MIN
NOM
MAX
10 k
40 k
90
95
0.02
40
7.5
2
4
6.15
230
TBD
250
5
UNIT
ASL Ft.
% RH
% RH
%/K
g
pk
mil
g
pk
g
pk
g
rms
10
5
kh
Maximum electric strength testing is performed in the factory according to EN50514, IEC/EN60950-1 2
nd
ed. and
UL/CSA60950-1 2
nd
ed. Input-to-output electric strength tests should not be repeated in the field. Bel Power Solutions will
not honor any warranty claims resulting from electric strength field tests.
PARAMETER
Agency Approvals
CONDITIONS / DESCRIPTION
Approved to latest edition of the following standards:
UL/CSA60950-1, IEC60950-1 and EN60950-1.
CE Mark for LVD
Input to case
Input to output
Output to case
Input to case
Input to output
Output to case
Output 1 to output 2
MIN
NOM
MAX
UNIT
Insulation Safety Rating
Basic
Reinforced
Functional
2.12
4.2
6
0.5
0.1
kVDC
kVDC
kVDC
kVDC
Electric Strength Test Voltage
6
Subassemblies are pre-tested with 4.2 kVDC in accordance with EN50514 and IEC/EN60950-1 2
nd
ed.
PARAMETER
Electrostatic Discharge
Electromagnetic Field
Electrical Fast Transients/Burst
Surge
Voltage Dips and Interruptions
RF Conducted Immunity
Emissions Conducted
Emissions Radiated
Harmonics
Voltage Fluctuation and Flicker
Voltage Sag
DESCRIPTION
IEC/EN 61000-4-2, level 4
IEC/EN 61000-4-3, level 3
IEC/EN 61000-4-4, level 3
IEC/EN 61000-4-5, level 3
IEC/EN 61000-4-11
IEC/EN 61000-4-6
CISPR 22/EN 55022/EN 61204
CISPR 22/EN 55022/EN 61204
IEC/EN 61000-3-2
IEC/EN 61000-3-3
SEMI F47-0200 (High Line 230 V)
CRITERION
Performance criterion B
Performance criterion A
Performance criterion B
Performance criterion B
Performance criterion B or better
10 VAC, AM 80 %, 1 kHz
Performance criterion A
Class B
Class A
Class B
Pass
Pass
Asia-Pacific
+86 755 298 85888
Europe, Middle East
+353 61 225 977
North America
+1 408 785 5200
BCD.00023_AD
© 2016 Bel Power Solutions & Protection