LightHAWK
®
2 Wall Switch Occupancy Sensors
INSTALLATION INSTRUCTIONS
DESCRIPTION
The
LightHAWK2
Wall Switch is an intelligent self-adapting occupancy sensor that is designed to replace existing wall switches.
SPECIFICATIONS
• 1000 sq. ft. coverage area (Models: LHIR and LHMT)
• 400 sq. ft. coverage area (Models: LHUS)
• Single or Dual Circuit 120/277VAC, 50/60Hz operation
• Single or Dual Circuit 347VAC, 50/60Hz operation (Canadian version)
• Electrical Ratings: (Each Output Separately)
120VAC – 800W Incandescent, 1000W Ballast, 1/4 HP
277 VAC – 1800W Ballast, 1/4 HP
347VAC – 1500W Ballast
• Adjustable Time Delay: 4-30 minutes, self-adapts based on occupancy
• Light Level Adjustment (Circuit B output on Dual Circuit versions): 10 to 500FC
• UL, cUL Listed
PRECAUTIONS
• CAUTION: RISK OF ELECTRICAL SHOCK.
Turn power off at service panel before beginning installation. Never wire energized
electrical components.
• Read and understand all instructions before beginning installation.
• NOTICE:
For installation by a licensed electrician in accordance with National and/or local Electrical Codes and the following
instructions.
• NOTICE:
For indoor use only.
• CAUTION: USE COPPER CONDUCTOR ONLY
• Confirm device ratings are suitable for application prior to installation. Use of device in applications beyond its specified ratings or
in applications other than its intended use may cause an unsafe condition and will void manufacturer’s warranty.
• NOTICE:
Do not install if product appears to be damaged.
• NOTICE:
Connect to field wiring rated for 60°C or greater.
SAVE THESE INSTRUCTIONS!
INSTALLATION
1.
2.
3.
Turn power OFF at the service panel.
Remove the old switch(es) if applicable.
Wire as shown in the WIRING DIAGRAMS section.
Figures 1 and 2 denote wiring method for Leakage to Ground Sensors.
(NOTE: A secure ground is required for proper operation).
Figures 3 and 4 denote wiring method for Neutral Wiring Sensors.
(NOTE:
If using only a single voltage, connect BOTH the black and violet input wires to the power source.)
Figure 5 shows wiring for Low Voltage models. (NOTE:
Low Voltage models require one UVPP Power Pack per output.)
4.
5.
6.
7.
8.
Install sensor in wall box using mounting screws provided.
Restore power to the sensor and allow it to initialize (up to 2 minutes).
Sensor is factory configured to provide the most energy savings. If additional adjustments are required, see the
ADJUSTMENTS
section.
If daylight harvesting is desired, calibrate the sensor’s photocell as described in the
PHOTOCELL CONTROL
section.
Install a decorator style wall plate (not included).
9601 Dessau Road, Building One
|
Austin, TX 78754 Toll Free: 888-698-3242
|
Fax: 512-450-1215
|
www.hubbell-automation.com
1113B 6.9.2016
WIRING DIAGRAMS
FIGURE 1 - MULTI-TECH, DUAL CIRCUIT,
GROUND CONNECTION
FIGURE 2 - MULTI-TECH, SINGLE CIRCUIT,
GROUND CONNECTION
FIGURE 3 - ULTRASONIC, DUAL CIRCUIT,
NEUTRAL CONNECTION
FIGURE 4 - MULTI-TECH, SINGLE CIRCUIT,
NO BUTTON, NEUTRAL CONNECTION
FIGURE 5 - LOW VOLTAGE LIGHTHAWK2, MULTI-TECHNOLOGY SENSOR,
CONTROLLING TWO CIRCUITS USING UVPP POWER PACKS
Page 2
TEST MODE
1.
2.
Make sure lights are ON.
Press and hold the ON/OFF button. Lights will cycle OFF then back ON. Release the ON/OFF button.
•
For dual circuit sensors, press and hold the ON/OFF button for Circuit A.
•
For sensors without buttons, remove the cover (see
ADJUSTMENTS
section) and press and hold the Test Button.
Sensor is now in Test Mode
(NOTE: While in Test Mode the sensor will operate in Automatic ON/Automatic OFF mode).
Vacate
room; lights should turn OFF after 5 seconds. Wait 5 seconds after turn OFF before re-entering space. Step back into room, lights
will turn back ON. Repeat walk test as necessary to confirm sensor is operating and detecting in the area as desired. Sensor will
flash red LED while moving to indicate Passive Infrared (PIR) or Ultrasonic occupancy detection respectively.
(NOTE: Sensors with
ultrasonic technology can be very sensitive and may require more than 5 seconds of no movement before turning lights off.)
To exit Test Mode, press any button.
(NOTE:
Sensor will automatically exit Test Mode after sixty (60) minutes.)
MANUAL OVERRIDE
Press button(s) to toggle lights ON or OFF. Lights will remain in the last state determined by the buttons while occupancy is detected.
Sensor will return to the programmed mode of operation when the sensor times out.
NOTE: Sensors with no buttons always operate
in the Automatic ON/Automatic OFF mode and cannot be manually turned off.
PHOTOCELL CONTROL
The photocell is used to detect if other light sources such as sunlight, are sufficient to illuminate the space without turning on the
controlled lights. For Dual Circuit sensors, only Circuit B is controlled by the photocell. The sensor is shipped from the factory with the
photocell control disabled. If use of the photocell is desired, calibrate the photocell set point as follows:
1.
2.
3.
With the light level at the desired level where the controlled lights should be off, PRESS and RELEASE the photocell set button
using the end of a paper clip or small bladed screwdriver.
Step back from the sensor to avoid changing ambient light levels in the room. During calibration the sensor will turn the lights
OFF then back ON.
After the calibration process, the sensor will return to its programmed mode of operation. During occupancy, the sensor will
turn lighting OFF sixty (60) seconds after reaching or exceeding the set point level. When the lighting level drops below the set
point level the sensor will turn the lights ON.
3.
4.
ADJUSTMENTS
The following switch adjustments require that the sensor’s cover be removed. Remove the cover by inserting a small blade screwdriver
into the catch at the top of the sensor and gently pry the cover off. Set the adjustment switches as desired (see
CONFIGURATION
SWITCH SETTINGS
section). Factory default is all switches OFF. To re-install cover, place cover directly over the sensor and align the
cover’s four (4) catches with the recesses in the sensor housing. Snap cover onto housing making sure that all catches are securely in
place.
CONFIGURATION SWITCH SETTINGS – BANK A
Switch 1 – Relay 1 Sensor Operation
Programs the sensor for either Manual ON/Automatic OFF operation or Automatic ON/Automatic OFF operation. When set to Manual
ON/Automatic OFF mode, lights are turned ON by manually pressing the ON/OFF button. If the sensor times out and turns the
lights OFF in the Manual ON/Automatic OFF mode while the space is still occupied, any motion detected within thirty (30) seconds
will automatically turn the lights back ON, without requiring the user to press the ON button.
NOTE: Switch 1 has no function on
vacancy only model (Cat. No. Suffix “M”)
Switch 2 –
Used on 2 Relay models only. Sets sensor operation for second relay. Similar to swicth 1 above.
Switch 3 – Adaptive or Fixed Timer
Controls selection between Adaptive Timer Mode and Fixed Timer Mode. In Adaptive Timer Mode, the sensor automatically self-
adjusts its timeout delay to optimize energy savings. The sensor will initialize its timer value to eight (8) minutes. If the Bank B Timer
Select 0 and Timer Select 1 switches have been set to four (4) minutes, this will be the smallest timer value used. In Fixed Timer Mode,
the sensor’s self-adapting timer functions are disabled and the sensor’s timeout delay is set according to the Bank B Timer Select 0
and Timer Select 1 switch settings.
Page 3
Switch 4 – Adaptive Reset
The sensor is equipped with Hubbell Building Automation’s patented self-adaptive IntelliDAPT® technology which automatically adjusts
the sensor’s sensitivity and timer settings to optimize performance based on occupancy patterns. The sensor constantly learns and
adjusts appropriately. If the learned settings need to be reset (e.g. when relocating sensor to another area), toggle the switch ON then
OFF. The adaptive timer is reset according to the Bank B Timer Select 0 and Timer Select 1 switches. The adaptive sensitivity (both PIR and
Ultrasonic as applicable) are reset to factory default. The photocell sensor settings are also reset to factory default (disabled) such that the
sensor will turn on the light(s) in response to occupancy regardless of ambient light levels in the lighted space.
(NOTE: Adaptive reset can
also be achieved by pressing and holding the photocell set button for ten (10) seconds.)
Switch 5 – Relay Bypass
If it is necessary to service the controlled circuits without de-energizing them at the breaker panel
(NOTE: this is not recommended as a
standard procedure),
perform the following steps:
1.
2.
3.
With the lights ON, set the relay bypass switch to the ON position.
Push the button(s) to turn the lights OFF.
Push the button(s) again to verify override (lights should not come back on).
The relay bypass switch will now interrupt sensor operation, preventing output(s) from turning ON again, regardless of occupancy or
pushbutton conditions. To return the sensor to normal operation, flip the relay bypass switch to the OFF position. To confirm sensor is
operating normally, lights should now turn ON and OFF when the button(s) are pressed.
CONFIGURATION SWITCH SETTINGS – BANK B
Switches 1 and 2 – Timer Settings
Sets the length of time lights will remain ON after last motion is detected. The timeout value can be set to 4, 8, 16 or 30 minutes.
See
Bank A – Switch 3 - Adaptive or Fixed Timer
section for additional information.
Switches 3 and 4 – Sensing Technology Enable/Disable
Enables or disables the occupancy sensing technologies used by the sensor. If all sensing technologies are disabled, sensor operates as a
manual ON/OFF switch.
Switch 5 – Sensitivity
Sets the sensor’s initial Passive Infrared (PIR) and/or Ultrasonic sensitivity level. Sensitivity can be set to either High or Low.
Switch Bank A
1
2
3
4
5
Swicth Bank B
1
2
3
4
5
Function
Relay 1 Operation
Relay 2 Operation
Timer Mode
Adaptive Reset
Relay Bypass
Function
Timer Select 0
Timer Select 1
Time
Passive Infrared
Ultrasonic
Sensitivity
OFF
Manual ON/ Automatic OFF
Manual ON/ Automatic OFF
Adaptive
Enable Adaptation
Normal Operation
OFF
ON
Automatic ON/ Automatic OFF
Automatic ON/ Automatic OFF
Fixed
Restore Factory Default
Relay Override
ON
4 Min
Enabled
Enabled
High
8 Min
16 Min
Disabled
Disabled
Low
30 Min
Page 4
72-00565 Rev B