Energy Management
Modular Power Quality Analyzer
Type WM23-96
•
Accuracy ±0.5 F.S. (current/voltage)
•
Three-phase modular power analyzer
•
Backlighted LCD 4x3 1/2 DGT Display
•
Front size: 96x96 mm
•
Measurements of phase and system variables: W, W
dmd
, var,
VA, VA
dmd
, PF, V
L-N
, V
L-L
, A, An, Hz, THD-A, THD-V
•
TRMS measurement of distorted waves (voltages/currents)
•
Measurement of MAX values: W L1, W L2, W L3, W∑, W
dmd
(AL1-AL2-AL3 max on request)
•
Measurement of MIN values: PF L1, PF L2, PF L3, PF
∑
•
Harmonic analysis (FFT) up to the 16
th
harmonic (current
and voltage)
•
Instantaneous variables read-out: 4x3 1/2 digit
•
Up to 2 optional relay or open collector outputs
•
1 optional analogue output
•
MODBUS, JBUS Protocol
•
Protection degree (front): IP 65
•
Universal power supply: 18-60VAC/VDC, 90-260 VAC/VDC
•
Phases asymmetry control
•
Optional RS 232 serial port
•
Optional RS 422/485 serial port
Product Description
µP-based three-phase mod-
ular power quality analyzer
with built-in programming
key-pad.
Particularly recommended for
a detailed analysis of the
electrical variables and of the
power quality. Housing for
panel mounting and IP65
(front) protection degree.
Ordering Key
Model
Range Code
System
Power Supply
Slot A
Slot B
Slot C
Slot D
Options
WM23-96AV53H XX XX XX XX X
Type selection
Range code
208VLL/5(6)AAC
-20%
≤
Un
≤+20%
AV5:
400VLL/5(6)AAC
-20%
≤
Un
≤+15%
AV6:
100VLL/5(6)AAC
-20%
≤
Un
≤+15%
AV7:
660VLL/5(6)AAC
-30%
≤
Un
≤+15%
50-60 Hz for all input mod-
ules. Module not removable.
AV4:
System
3:
Three-phase,
unbalanced load,
with or without
neutral
Slot A (signal retransmission)
XX:
A1:
A2:
A3:
A4:
B1:
B2:
B3:
B4:
V1:
V2:
Power supply
A:
B:
C:
D:
L:
H:
24 VAC -15 +10%
50-60Hz
48 VAC -15 +10%
50-60Hz
115VAC -15 +10%
50-60Hz
230 VAC -15 +10%
50-60Hz
18 to 60VAC/VDC
90 to 260VAC/VDC
V3:
V4:
W1:
W2:
W3:
W4:
None
Single analogue output,
20mADC
Single analogue output,
±5mADC
Single analogue output,
±10mADC
Single analogue output,
±20mADC
Dual analogue output,
20mADC
Dual analogue output,
±5mADC
Dual analogue output,
±10mADC
Dual analogue output,
±20mADC
Single analogue output,
10VDC
Single analogue output,
±1VDC
Single analogue output,
±5VDC
Single analogue output,
±10VDC
Dual analogue output,
10VDC
Dual analogue output,
±1VDC
Dual analogue output,
±5VDC
Dual analogue output,
±10VDC
Slot B (communication)
XX:
S1:
None
Serial port,
RS485 multidrop,
bidirectional
Slot C (redundant output or
digital inputs)
XX:
R1:
R2:
O1:
NOTE: max. digital output
(alarms and/or pulses): 2,
any exceeding output is
redundant.
NOTE: the second ana-
logue output is intended
as redundant type only.
O2:
D1:
D2:
None
Single relay output
(AC1-8AAC, 250VAC)
Dual relay output
(AC1-8AAC, 250VAC)
Single open collector
output (30V/100mADC)
Dual open collector
output (30V/100mADC)
3 digital inputs
3 digital inputs +
aux output
Slot D (alarm output)
XX:
R1:
R2:
O1:
O2:
None
Single relay output,
(AC1-8AAC, 250VAC)
Dual relay output,
(AC1-8AAC, 250VAC)
Single open collector
output (30V/100mADC)
Dual open collector
output (30V/100mADC)
NOTE: with the A, B, C, D
types power supply, only
an open collector module
or a single relay output
module can be used.
The instrument can be ful-
ly equipped only with L
and H type power supply.
Options
X:
S:
A:
None
RS232 serial port
displaying and record-
ing of AL1-AL2-AL3
max instead of WL1-
WL2-WL3 max.
Options: S+A above.
Y:
Specifications are subject to change without notice
WM23-96DS 080806
1
WM23-96
Input Specifications
Number of analogue inputs
Current
Voltage
Digital Inputs
AQ1038
Use
3
4
On request
Number of inputs: 3 ( voltage
free)
Synchronization of the
W-VAdmd measurements
Input 1: lock of programming
Inputs 2 and 3: W-VA dmd
measurements synchronization
24VDC/1mA
Number of inputs: 3 +
inputs power supply
Max 20Hz, dutycycle 50%
16V<+Aux<24VDC
Max 15mA
Min 100kΩ
4000VRMS
In=5A; Pn= In* Un
Un: F.S. range AV4-5-6-7
±(0.5% In +2DGT)
±(0.5% Un +2DGT)
±(1% Un +2DGT)
±0.1Hz
Active power
(@ 25°C ± 5°C, R.H.
≤
60%)
Reactive Power
(@ 25°C ± 5°C, R.H.
≤
60%)
Apparent power
(@ 25°C ± 5°C, R.H.
≤
60%)
Harmonic distortion
(@ 25°C ± 5°C, R.H.
≤
60%)
Additional errors
Humidity
Temperature drift
Display
Display refresh time
Measurements
±(1% Pn +2DGT)
±(2% Pn +2DGT)
±(1% Pn +2DGT)
±3% F (up to 16
th
harmonic)
.S.
(F 100%)
.S.:
≤0.3%
F from 60% to 90% H.R.
.S.
≤
200ppm/°C
Back-lighted LCD 4x3
1
/
2
digit
70 x 38mm
700ms
Current, voltage, power, power
factor, frequency, harmonic
distortion. TRMS measure-
ment of a distorted wave.
Direct
>200 kΩ
>900 kΩ
>200 kΩ
>900 kΩ
Reading voltage
AQ1042
Input frequency
Output voltage
Output current
Open contact
resistance
Insulation
Accuracy
(display, RS232, RS485)
Current
Phase-neutral voltage
Phase-phase voltage
Frequency
Coupling type
Input impedance
208VLL 5(6)AAC (AV4):
400VLL 5(6)AAC (AV5):
100VLL 5(6)AAC (AV6):
660VLL 5(6)AAC (AV7):
Output Specifications
Analogue Outputs
Number of outputs
Accuracy
Range
(on request)
Up to 1 (+1 redundant)
±0.2% f.s.
(@ 25°C ±5°C, R.H.
≤60%)
0 to 20 mADC,
0 to ±20 mADC
0 to ±10 mADC,
0 to ±5 mADC
0 to 10 VDC,
0 to ±10 VDC
0 to ±5 VDC
0 to ±1 VDC
Programmable within the
whole range of retransmis-
sion; it allows the retrans-
mission management of all
values from: 0 and 20 mADC,
See relevant list
≤
900 ms typical
(filter excluded, FFT excluded)
≤
1%
acc. to IEC 60688-1, EN 60688-1
≤
500 ppm/°C (input+out-
≤
600
Ω
≤
550
Ω
≤
1100
Ω
≤
2200
Ω
≥
10 kΩ
≥
10 kΩ
≥
10 kΩ
≥
10 kΩ
Insulation
By means of optocouplers,
4000 V
RMS
output to
measuring input
4000 V
RMS
output to
supply input
(on request)
Multidrop
bidirectional (static and
dynamic variables)
2 or 4 wires, max. distance
1200m, termination directly
on the instrument
255, selectable by key-pad
MODBUS/JBUS (RTU)
System and phase variables:
see table “display pages”
All the configuration parameters,
activation of the static output.
1 start bit, 8 data bit,
no parity, 1 stop bit
9600 bauds
By means of optocouplers,
4000 V
RMS
output to
measuring input
4000 V
RMS
output to
supply input
(on request)
bidirectional (static and
dynamic variables)
3 wires, max. distance 15m,
1 start bit, 8 data bit
RS422/RS485
Connections
Addresses
Protocol
Data (bidirectional)
Dynamic (reading only)
Static (writing only)
Data format
Baud-rate
Insulation
Scaling factor:
Variables
Response time
Ripple
Total temperature drift
put)
Load:
20 mADC
±20 mADC
±10 mADC
± 5 mADC
10 VDC
±10 VDC
± 5 VDC
± 1 VDC
RS232
Connections
Data format
2
Specifications are subject to change without notice
WM23-96DS 080806
WM23-96
Output Specifications (cont.)
Baud-rate
Protocol
other data
Digital outputs
no parity, 1 stop bit
9600 bauds
MODBUS/JBUS (RTU)
as per RS422/485
(on request)
To be used as alarms or
remote control.
(on request)
up to 2, independent
Up alarm, down alarm
see the “List of the variables
that can be connected...”
from 0 to 100% of the
electrical scale
from 0 to 100% of the
electrical scale
0 to 255s
Selectable, normally
de-energized and normally
energized
Output type
Relay, SPDT type
AC 1-8A @ 250VAC
DC 12-5A @ 24VDC
AC 15-2.5A @ 250VAC
DC 13-2.5A @ 24VDC
≤
150 ms, filter excluded,
FFT excluded, setpoint
on-time delay: “0 s”
By means of optocouplers,
4000 V
RMS
output to
measuring input,
4000 V
RMS
output to
supply input.
The outputs can be either
relay type or open collector
type (V
ON
1.2VDC/Max.
100mA, V
OFF
30VDC Max.).
Insulation like relay outputs.
Min. response time
Insulation
Alarm outputs
Number of outputs
Alarm type
Variables to be controlled
Set-point adjustment
Hysteresis
On-time delay
Relay status
Note
Software Functions
Password
1st level
2nd level
Transformer ratio
Numeric code of max
4 digits; 2 protection levels
of the programming data
Password “0”, no protection
Password from 1 to 1000, all
data are protected.
CT from 1 to 5000
VT from 1.0 to 1999, where
CT x VT
≤
10000
Programmable from 1 to 30 min
From 0 to 100% of the
input electrical scale
1 to 16
Measurements, alarms, serial
port (fundamental variables:
V, A, W and their derived ones).
Up to 4 by page
Page 1: V L1, V L2, V L3,
V LN∑
Page 2: V L12, V L13, V L31,
V∑
Page 3: A L1, A L2, AL3, An
Page 4: PF L1, PF L2,
PF L3, PF∑
Page 5: PF L1(min),
PF L2 (min),
PF L3 (min)
Page 6: W L1, W L2, W L3
Page 7: W L1 (max),
W L2 (max),
W L3 (max)
Page 7: “A” option:
AL1 (max)
AL2 (max)
AL3 (max)
Page 8: var L1, var L2, var L3
Page 9: VA L1, VA L2, VA L3
Page 10: AL1 (alarm 1)
Page 11: AL2 (alarm 2)
Page 12: W∑, PF∑, var∑, Hz
Page 13: W∑, PF∑, VA∑, Hz
Page 14: W∑ (max), PF∑ (min)
Page 15: W dmd, VA dmd, r.t.
Page 16: W dmd (max),
VA dmd (max)
Page 17: THD VL1, THD VL2,
THD VL3
Page 17: THD AL1,
THD AL2, THD AL3
Power demand (dmd)
Integration time
Filter
Filter operating range
Filtering coefficient
Filter action
Page Variables
Three-phase system with neutral
Supply Specifications
AC voltage
90 to 260 VDC/VAC
18 to 60VDC/VAC
24 VAC -15+10% 50-60Hz
48 VAC -15+10% 50-60Hz
115VAC -15+10% 50-60Hz
230 VAC -15+10% 50-60Hz
≤
30VA/12W (90 to 260V)
≤
20VA/12W (18 to 60V)
Power consumption
Specifications are subject to change without notice
WM23-96DS 080806
3
WM23-96
General Specifications
Operating temperature
Storage temperature
Installation category
Pollution degree
Key-pad lock
0 to +50°C (32 to 122°F)
(R.H. < 90% non condensing)
Immunity
Other standards
Safety
Product
Approvals
Connections 5(6)A
-10 to +60°C (14 to 140°F)
(R.H. < 90% non condensing)
light industry environment
EN 61000-6-2 (class A)
industrial environment
IEC 61010-1, EN 61010-1
IEC 60688-1, EN 60688-1
CE, UL, CSA
Screw-type, max 2.5 mm
2
wires
(2 x 1.5mm
2
)
96x96x140 mm
ABS, NORYL, PC (front)
self-extinguishing: UL 94 V-0
Front: IP65, NEMA4x, NEMA12
Connections: IP20
Approx. 400 g (packing incl.)
Insulation
Dielectric strength
EMC
Emissions
Cat. III (IEC 60664)
2
by means of a rotary switch
placed behind the display or
by means of a contact (in
case of presence of the digital
Housing
inputs module)
Dimensions
Material
4000 V
RMS
between all
inputs/outputs to ground
Protection degree
4000 V
RMS
for 1 minute
EN 61000-6-3 (class A)
residential, commercial and
Weight
Function Description
Input/analogue output scaling capability
Working of the analogue output (Y) versus the input variable (X) - (input/output scaling capability)
Figure A
The sign of measured quantity
and output quantity remains
the same. The output quantity
is proportional to the mea-
sured quantity.
Figure D
The sign of measured quantity
and output quantity remains
the same. With the measured
quantity being zero, the output
quantity has the value
Y1 = 0.2 (live zero output).
0
0
50 A
10 mA
100 A
20 mA
0
4
50 A
12 mA
100 A
20 mA
Figure B
The sign of measured quantity
and output quantity changes
simultaneously. The output
quantity is proportional to the
measured quantity.
Figure E
The sign of the measured
quantity changes but that of
the output quantity remains
the same. The output quantity
steadily increases from the
value X1 to the value X2 of the
measured quantity.
-100 kW
-10 mA
0
0
100 kW
10 mA
-100 kW
0
0
10 mA
100 kW
20 mA
Figure C
The sign of measured quantity
and output quantity remains
the same. From X0 to X1, the
output variable is 0. The range
X1...X2 is delineated on the
entire output range.
Figure F
The sign of the measured
quantity remains the same, that
of the output quantity changes
as the measured quantity
leaves range X0...X1 and pass-
es to range X1...X2.
80 V
0
100 V
5 mA
120 V
10 mA
0
-1 V
50 A
0
100 A
1V
4
Specifications are subject to change without notice
WM23-96DS 080806
WM23-96
Mode of operation
Waveform of the signals that can be measured
Figure G
Sinewave, undistorted
Fundamental content
100%
Harmonic content
0%
1.1107 | A |
A
rms
=
Figure H
Sinewave, indented
10...100%
Fundamental content
Harmonic content
0...90%
Frequency spectrum: 3rd to 16th harmonic
Figure I
Sinewave, distorted
Fundamental content
70...90%
Harmonic content
10...30%
Frequency spectrum: 3rd to 16th harmonic
Harmonic Analysis
Analysis principle
Harmonic measurement
Current
Voltage
Type of harmonics
FFT
Up to 16th harmonic
Up to 16th harmonic
THD (V
L
1)
THD (V
L
2)
THD (V
L
3)
THD (A
L
1)
THD (A
L
2)
THD (A
L
3)
Display pages
Others
THD %
The harmonic distortion
can be measured in both
3-wire or 4-wire systems.
Display pages
Variables that can be displayed in case of a three-phase system, 4-wire connection.
No
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
1st variable
V L1
V L1-2
A L1
PF L1
PF L1 (min)
W L1
W L1 (max)
var L1
VA L1
AL 1
AL 2
W
Σ
W
Σ
W
Σ
(max)
W dmd
W dmd (max)
THD V L1
THD A L1
2nd variable
V L2
V L2-3
A L2
PF L2
PF L2 (min)
W L2
W L2 (max)
var L2
VA L2
3rd variable
V L3
V L3-1
A L3
PF L3
PF L3 (min)
W L3
W L3 (max)
var L3
VA L3
4th variable
V LN
Σ
V
Σ
An
PF
Σ
Notes
Σ
= system
Σ
= system
An= neutral current
Σ
= system
With “A” option: AL1-AL2-AL3 max
PF
Σ
PF
Σ
PF
Σ
(min)
VA dmd
VA dmd (max)
THD V L2
THD A L2
var
Σ
VA
Σ
r.t.
Hz
Hz
variable connected to alarm 1
variable connected to alarm 2
Σ
= system
Σ
= system
Σ
= system
r.t.= symbol of communication
Rx/Tx on the serial port
total harmonic distortion
total harmonic distortion
THD V L3
THD A L3
Specifications are subject to change without notice
WM23-96DS 080806