Control voltages: 3-32 VDC, 20-275 VAC (24-190 VDC)
Design according to EN/IEC60947-4-2, EN/IEC60947-4-3,
EN/IEC62314, UL508, CSA 22-2 No. 14-13
• Integrated voltage transient protection with varistor
• 100 kA short circuit current rating according to UL508
1
2
Product Description
This new range of solid state
contactors presents a unique
opportunity to maximize effi-
ciency in panel space and
is an evolution of solid state
switches for which Carlo
Gavazzi is very well known.
The nominal current ratings
are at 40˚C. The smallest
width is 17.5mm and is rated
at 37 AAC. Power and control
teminals allow for safe loop-
ing of cables.
Voltage transient protection
is standard across the output
with a varistor. Specifications
are stated at 25°C unless
otherwise noted.
Ordering Key
RGC 1 A 60 A 30 K K E _
Solid state relay
Number of poles
Switching mode
Rated operational voltage
Control voltage
Rated operational current
Connection type for control
Connection type for power
Connection configuration
Option
1. RGC..32 models are not VDE approved
2. Germanischer Lloyd approval applicable only to models RGC1....15.KE,
RGC1...20.KE, RGC1..25..KE and RGC1....30.KE
Ordering Key
(Refer to page 2 and 3 for available part numbers)
1 Phase SSR
with heatsink
RGC1A: ZC
4
RGC1B: IO
4
Rated voltage,
Blocking voltage
23: 230V +10% - 15%, 800Vp
60: 600V +10% -15%, 1200Vp
Control voltage
D: 3 or 4-32VDC
A: 20 - 275VAC,
24-190 VDC
Rated
current at 40˚C
3
15: 20AAC, 525A²s
20: 23AAC, 525A²s
25: 25AAC, 1800A²s
30: 30AAC, 1800A²s
32: 30 AAC, 18000A
2
s
32: 37 AAC, 18000A
2
s
40: 40AAC, 3200A²s
42: 43AAC, 18000A²s
60: 60AAC, 3200A²s
62: 65AAC, 18000A²s
90: 85AAC, 6600A²s
92: 85AAC, 18000A²s
Connection
control
Connection
power
Connection
configuration
Option
P: Overtemperature
protection
(OTP)
5
K: Screw
K: Screw
E: Contactor
G: Box clamp G: Box clamp
M: Pluggable
spring-loaded
3. Refer to Derating Curves
4. ZC = Zero cross switching, IO= Instant ON switching
5. Default control connection for RGC...P is Box Clamp. See Connections Specifications
Specifications are subject to change without notice (22.05.2018)
1
RGC...E
Selection Guide
Rated voltage,
Blocking voltage,
Switching mode
Control voltage
Connection
control/power
Rated operational current @ 40
o
C (I
2
t value)
Product width
20 AAC (525A²s)
23 AAC (525A²s)
17.5mm, low depth
17.5mm
25 AAC (1800A²s)
17.5mm, low depth
30 AAC (1800A²s)
22.5mm
230V, 800Vp
ZC
3-32VDC
20-275VAC, 24-190VDC
Screw/Screw
Spring/Screw
Screw/Screw
Spring/Screw
RGC1A23D15KKE
RGC1A23D15MKE
RGC1A23A15KKE
RGC1A23A15MKE
40 AAC (3200A²s)
35mm
RGC1A23D20KKE
RGC1A23D20MKE
RGC1A23A20KKE
RGC1A23A20MKE
43 AAC (18000A²s)
35mm
RGC1A23D25KKE
RGC1A23D25MKE
RGC1A23A25KKE
RGC1A23A25MKE
60 AAC (3200A²s)
70mm
RGC1A23D30KKE
RGC1A23D30MKE
RGC1A23A30KKE
RGC1A23A30MKE
65 AAC (18000A²s)
70mm
3-32VDC
20-275VAC, 24-190VDC
Screw/Box
Screw/Box
RGC1A23D40KGE
RGC1A23A40KGE
20 AAC (525A²s)
17.5mm, low depth
RGC1A23D42KGE
RGC1A23A42KGE
23 AAC (525A²s)
17.5mm
RGC1A23D60KGE
RGC1A23A60KGE
25 AAC (1800A²s)
17.5mm, low depth
RGC1A23D62KGE
RGC1A23A62KGE
30 AAC (1800A²s)
22.5mm
600V, 1200Vp
ZC
4-32VDC
20-275VAC, 24-190VDC
Screw/Screw
Spring/Screw
Screw/Screw
Spring/Screw
RGC1A60D15KKE
RGC1A60D15MKE
RGC1A60A15KKE
RGC1A60A15MKE
30 AAC (18000A²s)
17.5mm, low depth
RGC1A60D20KKE
RGC1A60D20MKE
RGC1A60A20KKE
RGC1A60A20MKE
37 AAC (18000A²s)
17.5mm, low depth
RGC1A60D25KKE
RGC1A60D25MKE
RGC1A60A25KKE
RGC1A60A25MKE
RGC1A60D30KKE
RGC1A60D30MKE
RGC1A60A30KKE
RGC1A60A30MKE
4-32VDC
Screw/Screw
Spring/Screw
Screw/Box
Spring/Box
RGC1A60D32KKE
RGC1A60D32MKE
-
-
40 AAC (3200A²s)
35mm
-
-
RGC1A60D32KGE
RGC1A60D32MGE
43 AAC (18000A²s)
35mm
60 AAC (3200A²s)
70mm
65 AAC (18000A²s)
70mm
4-32VDC
20-275VAC, 24-190VDC
Screw/Box
Spring/Box
Screw/Box
Spring/Box
RGC1A60D40KGE
RGC1A60D40MGE
RGC1A60A40KGE
RGC1A60A40MGE
20 AAC (525A²s)
17.5mm, low depth
RGC1A60D42KGE
RGC1A60D42MGE
RGC1A60A42KGE
RGC1A60A42MGE
23 AAC (525A²s)
17.5mm
RGC1A60D60KGE
-
RGC1A60A60KGE
-
25 AAC (1800A²s)
17.5mm, low depth
RGC1A60D62KGE
RGC1A60D62MGE
RGC1A60A62KGE
RGC1A60A62MGE
30 AAC (1800A²s)
22.5mm
600V, 1200Vp
IO
4-32VDC
Screw/Screw
RGC1B60D15KKE
RGC1B60D20KKE
RGC1B60D25KKE
RGC1B60D30KKE
40 AAC (3200A²s)
35mm
43 AAC (18000A²s)
35mm
60 AAC (3200A²s)
70mm
65 AAC (18000A²s)
70mm
4-32VDC
Screw/Box
RGC1B60D40KGE
RGC1B60D42KGE
RGC1B60D60KGE
RGC1B60D62KGE
2
Specifications are subject to change without notice (22.05.2018)
RGC...E
Selection Guide - RGC..P
Rated voltage,
Blocking voltage,
Switching mode
600V, 1200Vp
ZC
Control voltage
(Integrated Overtemperature Protection)
Rated operational current @ 40
o
C (I
2
t value)
Product width
30 AAC (1800A²s)
22.5mm
Connection
control / power
5-32VDC
20-275VAC, 24-190VDC
Box/Screw
Box/Screw
RGC1A60D30GKEP
RGC1A60A30GKEP
43 AAC (18000A²s)
35mm
65AAC (18000A²s)
70mm
85AAC (6600A²s)
70mm + fan
85AAC (18000A²s)
70mm + fan
5-32VDC
20-275VAC, 24-190VDC
Box/Box
Box/Box
RGC1A60D42GGEP
RGC1A60A42GGEP
RGC1A60D62GGEP
RGC1A60A62GGEP
RGC1A60D90GGEP
RGC1A60A90GGEP
RGC1A60D92GGEP
RGC1A60A92GGEP
Output Voltage Specifications
RGC..23..
Operational voltage range
Blocking voltage
Internal varistor
24-240 VAC,
+10%, -15% on max
800Vp
275V
RGC..60..
42-600 VAC,
+10% -15% on max
1200 Vp
625V
General Specifications
Latching voltage
(across L1-T1)
Operational frequency
range
Power factor
Touch Protection
Control input status
Pollution degree
20V
45 to 65Hz
> 0.5 @ Vrated
IP20
continuously ON Green LED,
when control input is applied
2
(non-conductive pollution with
possibilities of condensation)
Rated impulse withstand
Over-voltage category
Isolation
Input to Output
6 kV (1.2/50μs) for voltage,
Uimp
III
(fixed installations)
RGC... 4000 Vrms
RGC...D..P 2500 Vrms
RGC...A..P 4000 Vrms
Input and Output RGC... 4000 Vrms
to case
RGC...D..P 4000 Vrms
RGC...A..P 4000 Vrms
Input to Fan/ Alarm Output
RGC...A..P 2500 Vrms
Specifications are subject to change without notice (22.05.2018)
3
RGC...E
Output Specifications
Rated operational current
6
AC-51 rating @ Ta=25°C
AC-51 rating @ Ta=40°C
AC-53a rating @ Ta=40°C
Number of motor starts per hour
(x:6, Tx:6s, F:50%) at 40˚C
7
Min. operational current
Rep. overload current -
(Motor Rating) PF = 0.4 - 0.5
UL508: T
AMB
=40°C, t
ON
=1s, t
OFF
=9s,
50 cycles
RGC..15..
20 AAC
20 AAC
5 AAC
30
150 mAAC
RGC..20..
25.5 AAC
23 AAC
5 AAC
30
150 mAAC
RGC..25..
30 AAC
25 AAC
5 AAC
30
250 mAAC
RGC..30..
30 AAC
30 AAC
8 AAC
30
250 mAAC
RGC..32..KE
30 AAC
30 AAC
5 AAC
30
500 mAAC
RGC..32..GE
43 AAC
37 AAC
5 AAC
30
500 mAAC
51 AAC
Maximum transient surge current (I
TSM
), t=10ms
325 Ap
Maximum off-state leakage current
at rated voltage
3 mAAC
525 A²s
I²t for fusing (
t=10ms
), Minimum
Crititcal dv/dt (@ Tj init = 40°C)
1000 V/μs
60 AAC
325 Ap
3 mAAC
525 A²s
1000 V/μs
51 AAC
600 Ap
3 mAAC
1800 A²s
1000 V/μs
84 AAC
600 Ap
3 mAAC
1800 A²s
1000 V/μs
51 AAC
1900 Ap
3 mAAC
18000 A²s
1000 V/μs
51 AAC
1900 Ap
3 mAAC
18000 A²s
1000 V/μs
Rated operational current
6
AC-51 rating @ Ta=25°C
AC-51 rating @ Ta=40°C
AC-53a rating @ Ta=40°C
Number of motor starts per hour
(x:6, Tx:6s, F:50%) at 40˚C
7
Min. operational current
Rep. overload current -
(Motor Rating) PF = 0.4 - 0.5
UL508: T
AMB
=40°C, t
ON
=1s, t
OFF
=9s,
50cycles
RGC..40..
47 AAC
40 AAC
13 AAC
30
400 mAAC
RGC..42..
50 AAC
43 AAC
16 AAC
30
500 mAAC
RGC..60..
70 AAC
60 AAC
14.8 AAC
30
400 mAAC
RGC..62..
75 AAC
65 AAC
20 AAC
30
500 mAAC
RGC..90..
85 AAC
85 AAC
18 AAC
30
400 mAAC
RGC..92..
85 AAC
85 AAC
20 AAC
30
500 mAAC
126 AAC
Maximum transient surge current (I
TSM
), t=10ms
800 Ap
Maximum off-state leakage current
at rated voltage
3 mAAC
3200 A²s
I²t for fusing (
t=10ms
), Minimum
Crititcal dv/dt (@ Tj init = 40°C)
1000 V/μs
126 AAC
1900 Ap
3 mAAC
18000 A²s
1000 V/μs
126 AAC
800 Ap
3 mAAC
3200 A²s
1000 V/μs
168 AAC
1900 Ap
3 mAAC
18000 A²s
1000 V/μs
168 ACC
1150 Ap
3 mAAC
6600 A²s
1000 V/μs
168 AAC
1900 Ap
3 mAAC
18000 A²s
1000 V/μs
6. See Derating Curves
7. Overload profile for AC-53a;
Ie: AC-53a: x-Tx: F-S, where Ie = nominal current (AC-53a AAC), x = overload current factor, Tx = duration of overload current (s), F = duty cycle (%), S = number
of starts per hour. Example; 5A: AC-53a: 6 - 6 : 50 - 30 = max. 30 starts for the RGC..15 with an overload profile of 30A for 6 seconds with a duty cycle of 50%
Overtemperature Alarm Specifications for RGC...P
Output type
Normal state
Maximum current rating
Rated voltage (EN61131-2: 2003)
Rated voltage, Us
Fan rating, U
f
Alarm voltage drop
Visual Indication
Reverse polarity protection
RGC..D..P
PNP open collector
Closed
50 mADC
24VDC -15%, +20%
RGC...D9xGGEP 24VDC ± 10%
RGC...A9xGGEP N/A
Typical
2.8VDC
Maximum
4VDC
Continous Red LED
24VDC
RGC..A..P
Potential Free
Closed
50 mADC
24VDC -15%, +20%
N/A
24VDC ±10%, 50mA nominal
8, 9
, Ua
1.8VDC
3.5VDC
Continous Red LED
24VDC
8. DC supply for alarm signal should be supplied from a Class 2 power source
9. Maximum voltage to be applied between 11+ and 12- (Ua) terminals should be 35VDC maximum with reference to A2-
4
Specifications are subject to change without notice (22.05.2018)
RGC...E
Input Specifications
RGC..D..
Control voltage range
10, 11
RGC..A..
20 - 275 VAC,
24 (-10%) - 190 VDC
20-275 VAC,
24 (-10%) - 190 VDC
20-275 VAC,
24 (-10%) - 190 VDC
20 VAC/DC
20 VAC/ 24VDC
5 VAC/DC
-
2 cycles
@ 230VAC/110VDC
RGC..23..
RGC..60..
RGC...P (Uc)
3 - 32 VDC
4 - 32 VDC
5 - 32 VDC
3.0 VDC
3.8 VDC
5 VDC
1 VDC
32 VDC
0.5 cycle + 500µs @ 24VDC
Pick-up voltage
Drop-out voltage
Maximum Reverse voltage
Response time pick-up (RGC1A..)
Response time pick-up (RGC1B..)
Response time drop-out
Input current @ 40°C
RGC..23..
RGC..60..
RGC...P
350µs @ 24 VDC
0.5 cycle
+ 500µs @ 24VDC
See diagrams below
N/A
0.5 cycle + 40ms @ 230VAC/110VDC
See diagrams below
10. DC control to be supplied by class 2 power source according to UL1310
11. For GL approved models control range for RGC1.23... is 4-32VDC and for RGC1.60... 5-32VDC
RG..A..
RGC1 .. A : input current vs input voltage
40mA
35mA
30mA
25mA
RGC .. A
20mA
15mA
RGC..A..P
(Normal Operation)
10mA
RGC..A..P
(Active Protection)
5mA
0mA
0VAC
50VAC
100VAC
150VAC
200VAC
250VAC
300VAC
RGC1 .. A : input current vs input voltage
40mA
35mA
30mA
25mA
20mA
15mA
10mA
RGC..A..P
(Normal Operation)
RGC..A..P
(Active Protection)
RGC .. A
5mA
0mA
0VDC
50VDC
100VDC
150VDC
200VDC
250VDC
Specifications are subject to change without notice (22.05.2018)