• 0/4-20mA, 0-10V DC, -10 to 10V DC, Type K, J, R, S, B,
E, T, N, C thermocouple and RTD
SPECIFICATIONS
Analog I/O Module Specifications
Part Number
Input Points
FC6A-J2C1
2
FC6A-J4A1
4
FC6A-J8A1
8
FC6A-L06A1
4
FC6A-L03CN1
2
FC6A-J4CN1
4
FC6A-J8CU1
8
Thermocouple
Thermistor
(NTC, PTC)
−
FC6A-K4A1
−
Input Signal Type
Voltage (0 to 10V) Voltage (-10 to +10V)
Current (0 to 20mA) Current (4 to 20mA)
Voltage (0 to 10V) Voltage (-10 to +10V)
Current (0 to 20mA) Current (4 to 20mA)
Thermocouple Resistance Thermometer
−
2
1
−
−
Output Points
−
−
4
Voltage (0 to 10V)
Voltage (−10 to +10V)
Current (0 to 20mA)
Current (4 to 20mA)
Output Signal Style
−
−
−
Voltage (0 to 10V) Voltage (-10 to +10V)
Current (0 to 20mA) Current (4 to 20mA)
−
−
External Power Supply
External Current Draw (24V DC) 1
Rated Power Voltage 24V DC, Allowable Voltage Range 20.4 to 28.8V DC
25mA
30mA
40mA
100mA
80mA
40mA
30mA
125mA
Connector Insertion/
Removal Durability
Applicable Ferrule
Internal Power Consumption
(5V DC)
100 times minimum
1-wire: AI 0.5-10 (Phoenix Contact), 2-wire: AI-TWIN 2×0.5-10 (Phoenix Contact)
40mA max.
45mA max.
40mA max.
55mA max.
55mA max.
50mA max.
45mA max.
50mA max.
Internal Power Consumption (at
24V DC while all I/Os are ON)
0.27W
0.30W
0.27W
0.37W
0.37W
0.34W
0.30W
0.34W
Weight (approx.)
115g
110g
110g
110g
115g
110g
110g
115g
Note 1: The external current draw is the value when all the analog inputs are used and the analog output value is at 100%.
1
Analog Input Specifications (1)
Part Number
Input Signal Type
Input Range
Input Impedance
Input Detection Current
Sampling Duration Time
Sampling Repetition Time
AD
Conversion
Total Input System Transfer Time
Type of Input
Operating Mode
Conversion Method
Maximum Error at 25°C
Input
Error
Cold Junction Compensation Error
Temperature Coefficient
Digital Resolution
Input per Resolution
Data
Data Type in Application Program
Monotonicity
Input Data Out of Range
Input Filter
Noise
Resistance
Recommended Cable for Noise
Immunity
Crosstalk
Isolation
Effect of Improper Input Connection
Maximum Permanent Allowed Overload (No
Damage)
Selection of Analog Input Signal Type
FC6A-J2C1
Voltage Input
0 to 10V
-10 to +10V
1MΩ maximum
−
Current Input
0 to 20mA
4 to 20mA
50Ω maximum
−
FC6A-J4A1/FC6A-J8A1/FC6A-L06A1
Voltage Input
Current Input
0 to 10V
0 to 20mA
-10 to +10V
4 to 20mA
1MΩ maximum
50Ω maximum
−
−
1ms
1ms or 10ms (selectable with application software)
Sampling time × valid input channels
Sampling time + sampling interval + 1 scan time
Single-ended input
Self-scan
∑ ∆ type ADC
±0.1% of full scale
±0.2% of full scale
−
−
−
−
±0.006% of full scale/°C
±0.01% of full scale/°C
65,536 increments (16 bits)
4,096 increments (12 bits)
0 to 10V: 0.15mV
0 to 20mA: 0.30μA
0 to 10V: 2.44mV
0 to 20mA: 4.88μA
-10 to +10V: 0.30mV
4 to 20mA: 0.244μA
-10 to +10V: 4.88mV
4 to 20mA: 3.91μA
Optional: -32,768 to 32,767 (selectable for each channel)
1
Yes
Detectable
2
Soft filter (0 to 10 s, selectable in increments of 0.1 s)
Twisted pair shielded cable
1LSB maximum
Between input and power circuit: Transformer-isolated
Between input and internal circuit: Photocoupler-isolated
No damage
13V DC
40mA
13V DC
Using programming software
40mA
Calibration or Verification to Maintain Rated
Accuracy
Not possible
Note 1: The data processed in the analog I/O module can be linear-converted to a value between -32,768 and 32,767. The optional range designation, and analog I/O data minimum and maximum values can be selected
using data registers allocated to analog I/O modules.
Note 2: When an error is detected, a corresponding error code is stored to a data register allocated to analog I/O operating status.
2
Analog Input Specifications (2)
Part Number
Input Signal Type
Voltage Input
FC6A-L03CN1/FC6A-J4CN1
Current Input
Resistance
Thermometer
Thermocouple
Thermocouple
FC6A-J8CU1
NTC Thermistor
PTC Thermistor
Type K (-200 to +1,300°C)
Type J (-200 to +1,000°C)
Pt100, Pt1000 3-wire
Type R (0 to 1,760°C)
type (-200 to 850°C)
Type S (0 to 1,760°C)
0 to 10V DC
0 to 20mA
Input Range
Ni100, Ni1000 3-wire
Type B (0 to 1,820°C)
-10 to +10V
4 to 20mA
type
Type E (-200 to +800°C)
(-60 to 180°C)
Type T (-200 to +400°C)
Type N (-200 to +1,300°C)
Type C (0 to 2,315°C)
Input Impedance
1 MΩ minimum 50Ω maximum
1 MΩ minimum
1 MΩ minimum
Input Detection Current
—
—
0.1mA maximum
0.1mA maximum
Sampling Duration Time
10ms, 100ms or 104ms (selectable using application software)
AD
Conversion
Sampling Repetition
Time
Total Input System
Transfer Time
Type of Input
Operating Mode
Conversion Method
Maximum Error at 25°C
Input
Error
Cold Junction
Compensation Error
Temperature Coefficient
Type K (-200 to +1,300°C)
Type J (-200 to +1,000°C)
Type R (0 to 1,760°C)
Type S (0 to 1,760°C)
Type B (0 to 1,820°C)
Type E (-200 to +800°C)
Type T (-200 to +400°C)
Type N (-200 to +1,300°C)
Type C (0 to 2,315°C)
1 MΩ minimum
0.1mA maximum
-90 to +150°C
100 to 10,000Ω
1 MΩ minimum
0.1mA maximum
104ms
Sampling time × valid input channels
Sampling time + sampling interval + 1 scan time
Single-ended input
Self-scan
∑ ∆ type ADC
FC6A-L03CN1: ±0.1% of full scale + cold junction
compensation error
FC6A-J4CN1: ±0.2% of full scale + cold junction
compensation error
3
±4°C maximum
±0.2% of full scale
—
—
±0.2% of full scale + cold junction compensation error
3
±4°C maximum
0.01%/°C of full scale
Digital Resolution
Data
Input Value of LSB
Data Type in Application
Program
Monotonicity
Input Data Out of Range
Input Filter
Recommended Cable
for Noise Immunity
Crosstalk
FC6A-L03CN1: 0.006%/°C of full scale
FC6A-J4CN1: 0.01%/°C of full scale
Type K: approx. 15,000
increments (14 bits)
Type J: approx. 12,000
increments (14 bits)
Type R: approx. 17,600
Pt100: approx. 10,500
increments (15 bits)
increments (14 bits)
Type S: approx. 17,600
Pt1,000: approx. 8,000 increments (15 bits)
increments (13 bits)
Type B: approx. 18,200
65,536 increments (16 bits)
Ni100: approx. 2,400
increments (15 bits)
increments (12 bits)
Type E: approx. 10,000
Ni1,000: approx. 2,400 increments (14 bits)
increments (12 bits)
Type T: approx. 6,000
increments (13 bits)
Type N: approx. 15,000
increments (14 bits)
Type C: approx. 23,150
increments (15 bits)
0 to 20mA:
0 to 10V: 0.15mV
0.30μA
-10 to +10V:
0.1°C
0.1°C
4 to 20mA:
0.30mV
0.244μA
Yes
Detectable
2
Software
Twisted pair shielded cable
Type K: approx. 15,000
increments (14 bits)
Type J: approx. 12,000
increments (14 bits)
Type R: approx. 17,600
increments (15 bits)
Type S: approx. 17,600
increments (15 bits)
Type B: approx. 18,200
increments (15 bits)
Type E: approx. 10,000
increments (14 bits)
Type T: approx. 6,000
increments (13 bits)
Type N: approx. 15,000
increments (14 bits)
Type C: approx. 23,150
increments (15 bits)
NTC: approx. 2,400 increments (12 bits)
PTC: approx. 9,900 increments (14 bits)
0.1°C
0.1°C
1Ω
Optional: selectable for each channel from -32,768 to 32,767
1
Noise
Resistance
Isolation
Twisted pair cable
1 LSB maximum
Between input and power circuit: Transformer-isolated
Between input and internal circuit: Photocoupler-isolated
No damage
13V DC
40mA
Using programming software
Not possible
Effect of Improper Input Connection
Maximum Permanent Allowed
Overload (No Damage)
Selection of Input Signal Type
and Input Range
Calibration or Verification to
Maintain Rated Accuracy
Note 1: The data processed in the analog I/O module can be linear-converted to a value between -32,768 and 32,767. The optional range designation, and analog I/O data minimum and maximum values can be selected
using data registers allocated to analog I/O modules.
Note 2: When an error is detected, a corresponding error code is stored to a data register allocated to analog I/O operating status.
Note 3: R, S: ±6 (0 to 200°C) B: no compensation K, J, E, T, N: ±0.4% of full scale (0°C maximum)
3
Analog Output Specifications
Part Number
Voltage
Output Signal Style/Output Range
Current
Impedance
Load Type
DA Conversion Time
DA
Conversion
Output Update Interval
Total Output System Transfer Time
Maximum Error at 25°C
Temperature Coefficient
Repeatability after Stabilization Time
Output Error
Output Voltage Drop
Non-lineality
Output Ripple
Overshoot
Total Error
Digital Resolution
Voltage
Output Value of LSB
Data
Current
Data Type in Application Program
Monotonicity
Current Loop Open
Noise
Resistance
Isolation
Recommended Cable for
Noise Immunity
Crosstalk
Between output and power circuit
Between output and internal circuit
FC6A-K4A1
FC6A-L06A1
0 to 10V DC
-10 to +10V DC
0 to 20mA
4 to 20mA
Voltage output: 1 kΩ minimum
Current output: 300Ω maximum
Resistive load
1ms
1ms
DA Conversion Time +Output Update Interval + 1 scan time
±0.1% of full scale
±0.006%/°C of full scale
±0.4% of full scale
No damage
±0.01%/°C of full scale
20mV maximum
0%
±1% of full scale
4,096 increments (12 bits)
0 to 10V DC: 2.44mV
-10 to +10V DC: 4.88mV
0 to 20mA: 4.88μA
4 to 20mA: 3.91μA
Optional: -32,768 to 32,767 (selected for each channel)