Compact size 2 Form A and
2 Form A 1 Form B 35A power
relays for energy management
and industrial equipment
New
HE-S RELAYS
TYPICAL APPLICATIONS
• Photovoltaic power generation systems (Solar inverter)
• Uninterruptible Power Supplies (UPS)
• Inverter
• Office air conditioner
• Industrial equipment
RoHS compliant
Protective construction: Flux-resistant type
FEATURES
1. High-capacity and long life 35A 277V AC 5×10
4
(long life
type)
2. Electrical life (resistive load)
Form A contact
35A 277V AC
30A 220V AC
20A 277V AC
Standard type
3×10
—
1×10
5
4
Long life type
5×10
4
1×10
5
2×10
5
7. Contact gap (initial)
• Form A contact: Min. 3.2 mm
.126 inch/each
contact
• Form B contact: Min. 0.7 mm
.028 inch
Min. 0.5 mm
.020 inch
(When Form A contact
welded)
8. Mirror contact mechanisms (Compliant with EN60947-4-1
mirror contact)
Detection of main contact welding makes it possible to
construct a safety circuit.
• Designed so that Form A contact and Form B contact will
not close at the same time.
• When Form A contact welded, Form B contact gap of at
least 0.5 mm
.020 inch
is maintained.
* Form B contact, when used to monitor the condition of Form A contact, can be
used exclusively as an auxiliary contact.
Condi-
tions
Normal operation
Non-excitation
Form A
contact
Form B
contact
3. Compact size and low operating power
W: 30
×
L: 36
×
H: 40 mm
W: 1.181
×
L: 1.417
×
H: 1.575 inch
Operating power: 1,880 mW (holding power: 170 mW)
4. Reduced coil holding voltage contributes to saving
energy of equipment
The coil holding voltage can be reduced up to 30%V of the
nominal coil voltage. This equals to operating power of
approximately 170 mW, which contributes equipment energy
savings.
* Coil holding voltage is the coil voltage after 100 ms from the applied nominal coil
voltage.
Excitation
Form A
contact
Form B
contact
When Form A
contact welded
Non-excitation
Form A
contact
Form B
contact
Min. 0.5 mm
Min. .020 inch
5. Contact gap: 3.2 mm
.126 inch
(VDE0126 compliant)
Compliant with European photovoltaic standard VDE0126
Compliant with EN61810-1 2.5 kV surge breakdown voltage
(between contacts)
6. Insulation distance (initial)
• Between Form A contact and coil: Min. 11.0 mm
.433 inch
(Clearance/Creepage)
• Between Form B contact and coil: Min. 3.2 mm
.126 inch
(Clearance/Creepage)
• Between Form A contact sets: Min. 8.2 mm
.323 inch
(Clearance/Creepage)
• Between Form A contact and Form B contact: Min. 12.8 mm
.504 inch
(Clearance/Creepage)
Mirror
contact
mecha-
nisms
Welding
–1–
ASCTB360E 201604-T
HE-S (AHES3, 4)
2. Specifications
Characteristics
Arrangement
Form A
contact
Form B
contact*
6
Contact resistance (Initial)
Contact material
Contact resistance (Initial)
Contact material
Nominal switching capacity
(Resistive load)
Max. switching voltage
Contact carring power
(Resistive load)
Max. switching current
Min. switching capacity
(Reference value)*
1
Nominal switching capacity
(Resistive load)
Max. switching voltage
Contact carring power
(Resistive load)
Max. switching current
Min. switching capacity
(Reference value)*
1
Item
Specifications
Standard type
2 Form A, 2 Form A 1 Form B
Long life type
2 Form A, 2 Form A 1 Form B
Contact
Max. 100mΩ (By voltage drop 6V DC 1A),
Max. 3mΩ (By voltage drop 6V DC 20A, Reference value)
AgSnO
2
type
Max. 100mΩ (By voltage drop 6V DC 1A)
Au flashed AgNi type
35A 277V AC
480V AC, 110V DC
9,695VA
35A
100mA 5V DC
1A 277V AC, 1A 30V DC
277V AC, 30V DC
277VA
1A
10mA 5V DC
1,880mW (after applying min.100ms coil nominal voltage)
170mW (30%V of coil holding voltage)
Min. 1,000MΩ (at 500 V DC) Measurement at same location as “Breakdown voltage” section.
Max. 1,000A 1 ms, 3 times (Reference value)
2,000 Vrms for 1 min. (Detection current: 10mA)
5,000 Vrms for 1 min. (Detection current: 10mA)
5,000 Vrms for 1 min. (Detection current: 10mA)
1,000 Vrms for 1 min. (Detection current: 10mA)
2,000 Vrms for 1 min. (Detection current: 10mA)
5,000 Vrms for 1 min. (Detection current: 10mA)
10,000V (Between Form A contact and coil) (Initial)
2,500V (Between Form B contact and coil) (Initial)
30 to 110%V (Form A contact carrying current: 35A, at –40 to +55°C
–40 to +131°F)
30 to 60%V (Form A contact carrying current: 35A, at –40 to +85°C
–40 to +185°F)
Max. 30 ms (at nominal coil voltage, excluding contact bounce time)
Max. 10 ms (at nominal coil voltage, excluding contact bounce time, without diode)
98 m/s
2
(Half-wave pulse of sine wave: 11 ms; detection time: 10
μs)
980 m/s
2
(Half-wave pulse of sine wave: 6 ms)
10 to 55 Hz at double amplitude of 1.0 mm
.039 inch
(Detection time: 10
μs)
10 to 55 Hz at double amplitude of 1.5 mm
.059 inch
Min. 5×10
6
(at 180 times/min.)
Min. 3×10
4
(35A 277V AC) (ON : OFF = 1s : 9s) Min. 5×10
4
(35A 277V AC) (ON : OFF = 1s : 9s)
—
Min. 1×10
5
(30A 220V AC) (ON : OFF = 1s : 9s)
Min. 1×10
5
(20A 277V AC) (ON : OFF = 1s : 9s) Min. 2×10
5
(20A 277V AC) (ON : OFF = 1s : 9s)
Min. 5×10
4
(35A 250V AC) (cos
φ
= 0.8)
Min. 3×10
4
(35A 250V AC) (cos
φ
= 0.8)
(ON : OFF = 0.1s : 10s)
(ON : OFF = 0.1s : 10s)
Min. 1×10
5
(1A 277V AC) (ON : OFF = 1s : 9s)
Form A
contact
Rating
Form B
contact*
6
Nominal operating power
Insulation resistance (Initial)
Short current (A contact, Initial)
Between open Form A contacts
Between Form A contact and coil
Breakdown Between Form A contact sets
voltage
Between open Form B contacts
(Initial)
Between Form B contact and coil
Between Form A contact and
Form B contact
Surge breakdown voltage*
2
(Between contact and coil)
Coil holding voltage*
3
Operate time (at 20°C
68°F)
(Initial)
Release time (at 20°C
68°F)*
4
(Initial)
Functional
Shock
resistance
Destructive
Functional
Vibration
resistance
Destructive
Mechanical
Electrical
(Form A
contact)
Electrical
(Form B
contact)*
6
Conditions
Unit weight
Resistive load
Electrical
characteristics
Mechanical
characteristics
Expected life
Inductive load
Resistive load
Min. 1×10
5
(1A 30V DC) (ON : OFF = 1s : 9s)
Temperature: –40 to +55°C
–40 to +131°F
(Coil holding voltage 30 to 110%V)
Temperature: –40 to +85°C
–40 to +185°F
(Coil holding voltage 30 to 60%V or storage)
Humidity: 5 to 85% R.H. (Not freezing and condensing at low temperature)
Air pressure: 86 to 106 kPa
Approx. 64 g
2.26 oz
Conditions for operation, transport and storage*
5
Notes: *1. This value can change due to the switching frequency, environmental conditions, and desired reliability level, therefore it is recommended to check this with the
actual load.
*2. Wave is standard shock voltage of
±1.2×50μs
according to JEC-212-1981
*3. Coil holding voltage is the coil voltage after 100 ms from the applied nominal coil voltage.
*4. Release time will lengthen if a diode, etc., is connected in parallel to the coil. Be sure to verify operation under actual conditions.
*5. The upper operation ambient temperature limit is the maximum temperature that can satisfy the coil temperature rise value. Refer to Usage, transport and storage
conditions in NOTES.
*6. Regarding Form B contact, only the 2 Form A 1 Form B type applies.
–3–
ASCTB360E 201604-T
HE-S (AHES3, 4)
2. 2 Form A 1 Form B type
CAD Data
30.0
1.181
36.0
1.417
Schematic (Bottom view)
3
4
5
6
40.0 (38.0)
1.575 (1.496)
2
7
1
8
4.0
.157
2.0
.079
27.0
1.063
22.9
7.6
.902
.299
2.4
.094
2-1.2
2-.047
24.4
.961
29.4
1.157
Recommended PC board pattern
(Bottom view)
22.9
.902
.
dia
ia.
1.6
63 d
.
2-
.0
dia
2-
2.2
dia.
2-
087
2-.
2-1.2
2-.047
21.3
.839
2-0
2-.
.8 d
03
ia.
1d
ia.
7.6
.299
21.3
.839
11.0
.433
4-3.3
4-.130
4-0.8
4-.031
19.0
.748
R0
R.
.8
03
1
11.0
.433
1.0
.039
General tolerance:
±0.3
±.012
4.0
.157
1.6
.063
19.0
.748
Tolerance:
±0.1
±.004
SAFETY STANDARDS
Item
2 Form A
Standard type
(AHES∗19∗)
2 Form A 1 Form B
2 Form A
2 Form A 1 Form B
Certification
File No.
N.O. contact (Form A contact)
Contact rating
Temp.
35A, 277VAC, Resistive
20A, 277VAC, Resistive
15A, 480VAC, Resistive
TV-8
AC-7a: 35A, 250VAC, cos
φ
= 0.8
AC-3: 12A, 230VAC, cos
φ
= 0.45
AC-3: 8A, 480VAC, cos
φ
= 0.45
85°C
185°F
85°C
185°F
85°C
185°F
40°C
104°F
85°C
185°F
85°C
185°F
85°C
185°F
Cycles
3×10
10
5
10
5
25×10
3
4
N.C. contact (Form B contact)
Contact rating
Temp.
—
1A, 30VDC, Resistive
1A, 277VAC, Resistive
—
DC-13: 1A, 24VDC, L/R = 48ms
—
85°C
185°F
85°C
185°F
—
85°C
185°F
Cycles
—
10
5
10
5
—
8×10
4
UL/C-UL
(Recognized)
E43149
VDE
(Certified)
40042442
3×10
4
3×10
4
3×10
4
Item
2 Form A
Long life type
(AHES∗29∗)
2 Form A 1 Form B
2 Form A
2 Form A 1 Form B
Certification
File No.
N.O. contact (Form A contact)
Contact rating
Temp.
35A, 277VAC, Resistive
20A, 277VAC, Resistive
15A, 480VAC, Resistive
TV-10
AC-7a: 35A, 250VAC, cos
φ
= 0.8
AC-3: 12A, 230VAC, cos
φ
= 0.45
AC-3: 8A, 480VAC, cos
φ
= 0.45
85°C
185°F
85°C
185°F
85°C
185°F
40°C
104°F
85°C
185°F
85°C
185°F
85°C
185°F
Cycles
5×10
4
2×10
5
10
5
25×10
3
3×10
4
3×10
4
3×10
4
N.C. contact (Form B contact)
Contact rating
Temp.
—
1A, 30VDC, Resistive
1A, 277VAC, Resistive
—
DC-13: 1A, 24VDC, L/R = 48ms
—
85°C
185°F
85°C
185°F
—
85°C
185°F
Cycles
—
10
5
10
5
—
8×10
4
UL/C-UL
(Recognized)
E43149
VDE
(Certified)
40042442
EN/IEC VDE Certified
INSULATION CHARACTERISTIC (IEC61810-1)
Item
Clearance/Creepage distance (IEC61810-1)
Category of protection (IEC61810-1)
Tracking resistance (IEC60112)
Insulation material group
Over voltage category
Rated voltage
Pollution degree
Type of insulation (Between contact and coil)
Type of insulation (Between open contacts)
Characteristic (Form A contact)
Min. 5.5mm
.217inch/8.0mm .315inch
RT II
PTI 175
III a
III
250V
3
Reinforced insulation
Full disconnection
–5–
ASCTB360E 201604-T