POWER
Data Sheet
Total Power:
Up to 24 KW
Input Voltage:
180-264 Vac
342-528 Vac
Single Phase or
3-Phase
# of Outputs:
Up to 8
Special featureS
5 years manufacturer’s warranty
Multi output intelligent and modular
high power system
Standard 19” rack
Outputs parallel up to 1600 A
Outputs series up to 1000 V
100% digital control
Outputs program as voltage or current
source
Versatile input configurable to:
• Low line 180-264 Vac single phase
and 3-phase
• High line 342-528 Vac 3-phase
Medical safety approved – NO
ISOLATION XFMR NEEDED
Flexible control interfaces (Note 1)
Air cooled
Semi F47 compliance
Field upgradeable firmware
Programmable slew rate
Fast current slew rate up to 200 Hz
Active power factor correction
User defined command profiles
Modular High Power System
Up to 24000 Watts
iHP12
iHP24
iHP24 Electrical Specifications
Input Parameter
Font: Minion Bold for VS
Minion italic for i ; size for each is the same
Created on Mac
Color: "i" 100% Blue, 50% Magenta,
0% Yellow, 0% Black
"VS" - 100% Black
19” Rack 24 KW strapped as
3-phase 380/480 Vac Nominal
(iHP24H3A/L)
342 Vac to 528 Vac
(Nominal rating 380/480 Vac)
47-63 Hz
19” Rack 24 KW strapped as
3-phase 208/240 Vac Nominal
(iHP24L3A/L)
187.5 Vac to 264 Vac
(Nominal rating 208/240 Vac)
Input range
Number of phases
Frequency
Phase detection
Max current/phase
Undervoltage
detection
Current inrush
Power factor
Harmonic distortion
Line interruption
Input leakage current
Power switch
Input protection
Input overvoltage
protection
Phase imbalance
Rack parallel
Efficiency
Standby voltage
Standby regulation
Standby max current
3-phase (Wye or Delta) 4 wire total (3-phase and 1 protective earth ground)
Loss of phase will inhibit unit off.
Housekeeping/comms must continue with phase loss.
51 A @ 342 Vac
40 A @ 432 Vac
84 A @ 187.5 Vac
Nominal input locked on at turn-on. Undervoltage shutdown at 15% below nominal.
Turn-on at 12% below nominal. Not to interfere with SEMI F47 specs.
2.5 x Max input current
> 0.98 @ full load and nominal line
THD < 13%, PWHD < 22% (refer to EN 61000-3-12)
Designed to meet SEMI F47-0706, 53, 58, S14 at nominal input voltages
< 2.5 mA (Note for fixed condition 3rd edition leakage = 5 mA)
Front panel power switch provided
Internal fuse (not user serviceable)
Up to 115% of nominal input shall not damage unit
≤ 5%
Up to 6 racks (144 KW)
> 90% @ 3P 380 Vac full load
> 91% @ 3P 480 Vac full load
5V
4.75 - 5.25 V
1A
> 91% @ 3P 240 Vac full load
> 90% @ 3P 208 Vac 3P full load
SafetY
UL 60950-1 2
nd
Edition; EN60950-1;
IEC60950-1/EN60950
CSA C22.2 No. 60950-1-07, 2
nd
Edition
EN60601-1; IEC60601-1; IEC60601
UL 60601-1 1st Edition; ANSI/AAMI
ES60601-1 (2005 + C1:09 + A2:10) 3
rd
Ed
CAN/CSA-C22.2 No. 60601-1 (2008)
CB Certificate and Report
CE (LVD+RoHS), EN60950-1
Note 1: Analog 0-5 V or 0-10 V separate for voltage or current; Digital Ethernet UDP, RS485, CAN or Ethernet TC/IP with PowerPro
Connect Module option. Command protocol is patterned to PMBus specification using a proprietary transaction protocol.
i
HP Data Sheet
iHP12 Electrical Specifications
Input Parameter
19” Rack 12 KW strapped as
1-phase 200/220/230/240 Vac
Nominal (iHP12L1A)
180 Vac to 264 Vac
(Nominal rating 200/220/230/240 Vac)
1-phase 3-wire total (2-phase and 1
protective earth ground)
Type: 19” Rack 12 KW strapped as
3-phase 200/208/240 Vac Nominal
(iHP12L3A)
180 Vac to 264 Vac
(Nominal rating 200/208/240 Vac)
Type: 19” Rack 12 KW strapped
as 3-phase 380/480 Vac Nominal
(iHP12H3A)
342 Vac to 528 Vac
(Nominal rating 380/480 Vac)
Input range
Number of phases
Frequency
Phase detection
Max current/phase
Undervoltage detection
Current inrush
Power factor
Harmonic distortion
Line interruption
Input leakage current
Power switch
Input protection
Input overvoltage protection
Phase imbalance
Rack parallel
Efficiency
Standby voltage
Standby regulation
Standby max current
3-phase (Wye or Delta) 4-wire total (3-phase and 1 protective earth ground)
47-63 Hz
NA
75 A @ 180 Vac
Loss of phase will inhibit unit off.
Housekeeping/comms must continue with phase loss.
44 A @ 180 Vac
23 A @ 342 Vac
19 A @ 432 Vac
Nominal input locked on at turn-on. Undervoltage shutdown at 15% below nominal. Turn-on at 12% below nominal.
Not to interfere with SEMI F47 specs.
2.5 x Max input current
> 0.99 @ full load and nominal line
> 0.98 @ full load and nominal line
THD < 13%, PWHD < 22% (refer to EN 61000-3-12)
Designed to meet SEMI F47-0706, 53, 58, S14 at nominal input voltages
< 1.25 mA
Front panel power switch provided
Internal fuse (not user serviceable)
Up to 115% of nominal input shall not damage unit
NA
< 5%
Up to 6 racks (72 KW)
> 91% @ 1P 240 Vac full load
> 90% @ 1P 208 Vac/200 Vac full load
> 91% @ 3P 240 Vac full load
> 90% @ 3P 208 Vac/200 Vac full load
5V
4.75 - 5.25 V
1A
> 90% @ 3P 380 Vac full load
> 91% @ 3P 480 Vac full load
< 5%
<2.5 mA
EMC/Immunity
Parameter
ESD
Fast Transients
Surge Immunity
Conducted Immunity
Radiated Immunity
Power Frequency Magnetic Field
Voltage Dips, Short Interruptions and Voltage Variations
Conducted Emission
Radiated Emission
All Models (Unless otherwise specified)
EN61000-4-2 (IEC1000-4-2)
EN61000-4-4 (IEC1000-4-4)
EN61000-4-5 (IEC1000-4-5)
EN61000-4-6 (IEC1000-4-6)
EN61000-4-3 (IEC1000-4-3)
EN61000-4-8
EN 61000-4-34
EN55011, FCC CFR 47, Part 15, Subpart B
EN55011, FCC CFR 47, Part 15, Subpart B
i
HP Data Sheet
Electromagnetic Compatibility/Input Transient
Category
Radiated Emissions
3
Standard
EN 55011/CISPR11
FCC CFR 47, Part 15,
Subpart B
Frequency
30 M - 1 GHz
30 M - 1 GHz
>1 GHz (see standard)
150 k - 30 MHz
See standard
See standard
80 M - 2 GHz
Level/Limits
Class A
Class A
Class A
See standard
See standard
10 V/meter
8 KV contact,
15 KV Air
+/- 4 KV
2 KV DM, 2 KV CM
2 KV DM, 2 KV CM
6 KV, CM & DM
PSU Performance
Criteria
1
5 dB Margin
5 dB Margin
5 dB Margin
Conducted Emissions
3
Power Line Harmonics
2
Voltage Fluctuations
2
Radiated Immunity
ESD
Electrical Fast Transient
Surge AC
EN 55011/CISPR11
EN 61000-3-12
EN 61000-3-11
EN 61000-4-3
EN 61000-4-2
EN 61000-4-4
EN 61000-4-5
IEEE C62.41
A
A
A
A
A
Fail Safe
A
A
A
C
A
A
A
B
Conducted Susceptibility
Voltage Dips and Sags
2
EN 61000-4-6
EN 61000-4-34
SEMI F47
150 KHz – 80 MHz
>95% reduction for
>30% reduction for
>95% reduction for
20% reduction for
30% reduction for
50% reduction for
60% reduction for
10 Vrms
10 mS
500 mS
500 mS
5000 mS
500 mS
200 mS
200 mS
Notes:
1
Performance Criteria as defined by EN 300 386 V1.3.3
2
Applies to AC power supplies only.
3
Conducted and radiated emissions are measured using a typical set-up. In an actual end system, additional EMI filters may be required.
OUTPUT – General Specs
Parameter
MODULE CODE
# Outputs
Nominal O/P (V)
Max Power (W)
O/P Current Range (A)
Power Density (W/cu-in)
Efficiency (%)
Module Input Voltage
Module Operating Temp
Series Operation
Parallel Operation
SL
1
12.0 V
2400 W
0.0 A - 200 A
32.5
93.5
SQ
1
24.0 V
2880 W
0.0 A - 120 A
39.0
93.5
SW
1
48.0 V
3000 W
0.0 A - 62.5 A
40.6
93.5
400 V
-0 °C to +65 °C; Baseplate Temp TBD
250 V modules can be connected in series up to 800 V for Medical and 1000 V for ITE
Up to 8 modules can be paralleled in 1 rack, with up to 6 racks connected in parallel.
Single Wire Parallel connection will be provided as part of configuration
S8
1
80.0 V
3000 W
0.0 A - 37.5 A
40.6
93.5
S1
1
125.0 V
3000 W
0.0 A -24 A
40.6
93.5
S2
1
250.0 V
3000 W
0.0 A -12 A
40.6
93.5
i
HP Data Sheet
OUTPUT – Module in Voltage Source Mode
Voltage Source
MODULE CODE
Nominal Output (V)
Setting Range (V)
Low Frequency RMS Ripple (mV)
Line Regulation (mV)
Load Regulation (mV)
P-P Ripple (mV)
Drift (Temp Stability)
Temp Coefficient
(PPM/°C)
Pgm Accuracy (mV)
Pgm Resolution (mV)
Meas Accuracy (mV)
Meas Resolution
Transient Response
Current Sense Method
SL
12
0.6 V - 14.4 V
24
12
24
60
SQ
24
1.2 V - 28.8 V
48
24
48
120
SW
48
2.4 V - 57.6 V
96
48
96
240
S8
80
4.0 V - 96.0 V
160
80
160
400
S1
125
6.25 V - 150.0 V
250
125
250
625
S2
250
12.5 V - 300.0 V
500
250
500
1250
±0.05% of Iout Rated over 8 hours, after 30 minute warm up, constant Line, Load and Temp
200
Digital: 0.1% of Nominal Output Voltage; Analog: 1.0% of Nominal Output Voltage
SL=TBD; SQ=1; SW=2; S8=8; S1=6; S2=21
0.2% + 0.2% of Nominal Output Voltage
SL=TBD; SQ=1; SW=2; S8=8; S1=6; S2=21
Max 5.0% deviation from current set point must recover within 1mS for a 50% step load.
Internal Shunt; External Shunt can be used for better temperature stability.
OUTPUT – Module in Current Source Mode
Current Source - Programmable load compensation available for resistive and inductive loads; capacitive load applications; and
LED drive applications
MODULE CODE
Nominal Output (V)
Setting Range (A)
RMS Ripple (mA)
Line Regulation (mA)
Load Regulation (mA)
P-P Ripple (mA)
Drift (Temp Stability)
Temp Co-efficient
(PPM/°C)
SL
12
0.0 A - 200 A
200
200
800
SQ
24
0.0 A - 120 A
120
120
480
SW
48
0.0 A - 62.5 A
62.5
125
250
N/A
S8
80
0.0 A - 37.5 A
37.5
93.75
150
S1
125
0.0 A - 24 A
24
48
96
S2
250
0.0 A - 12 A
12
24
48
±0.05% of I
out
Rated over 8 hours, after 30 minute warm up, constant Line, Load and Temp
SL, SQ = 300 PPM; All other modules are 200 PPM.
Temp Co-efficient at rack level is [Temp Co-efficient (module level)] + [4500 PPM of Iout-max]
0.7% digital, 1.3% analog of rated output max
79.2
26.4
13.2
10
5.2
2.6
Pgm Accuracy (A)
Pgm Resolution (mA)
Meas Accuracy
Meas Resolution
Transient Response
Current Sense Method
79.2
26.4
0.7% + 0.7% of Rated Output Max
13.2
10
5.2
2.6
0-63% output current change in 7.5 mSec, residual value 1%, settling time 35 mSec
Internal Shunt / External Shunt
i
HP Data Sheet
Environmental Specifications
Operating Condi
tions
Operating Temperature
Storage Temperature
Operating Humidity
Storage Humidity
Operating Altitude
Storage Altitude
Vibration
ALL MODELS (Unless Otherwise Specified)
0 °C to +50 °C at 100% rated load.
-40 °C to +85 °C. For Liquid Cooled models, liquid must be drained before storage
20% - 90% non condensing
10% - 95% non condensing
Up to 9,842 feet above sea level (3,000 meters)
Up to 30,000 feet above sea level (9,144 meters)
Operating Sinusoidal Vibration MIL-STD-810G Method 528 Procedure I (Type 1):
NEBS Office Vibration Environment, Alternate Procedure
Operating Random Vibration: IPC-9592B Class 1
Non-Operating Vibration (Packaged): IPC-9592B Class 1; MIL-STD-810G, Method 514.6, Procedure 1, Category 7,
Table 514.6C-VII General Exposure
MIL-STD-810G Method 516.6 Procedures I, II, IV, VI
NSTA for <100 lbs; MIL-STD-2073-1 >100 lbs
<65 dBA with 80% load @ 30 °C at nominal input voltage with Smart Fan algorithm to be optimized based on module
and rack thermal sensors. When modules are inhibited via software control, the fan speed is reduced to idle and acoustic
noise is <46 dBA. With modules off via front panel switch fans are at idle for 1 min, and off for 9 min.
Fan Cooled = IP20
2
Yes
Standard Markings
Module and Marking Detail
SW
Shock
Shipping and Handling
Cooling and Audible Noise
Ingress Protection
Pollution Degree
RoHS Compliance
Module Code
Label