Protection Relays
Voltage Monitoring Relays
TVM SERIES
Description
The TVM Series Provides protection for motors and other
sensitive loads. Continuously measures the voltage of each
of the three phases using a microcomputer circuit design
that senses under and overvoltage, voltage unbalance, phase
loss, and phase reversal. Protection is provided even when
regenerated voltages are present. Includes a trip delay to
prevent nuisance tripping and a restart delay to prevent short
cycling after a momentary power outage.
Operation
Upon application of line voltage, the restart delay begins.
The output relay is de-energized during restart delay. Under
normal conditions, the output energizes after restart delay.
Undervoltage, overvoltage, and voltage unbalance must be
sensed for continuous trip delay period before the output is
de-energized. The output will not de-energize if a fault is
corrected during the trip delay. The restart delay begins as
soon as the output relay de-energizes. If the restart delay is
completed when the fault is corrected, the output relay will
energize immediately.
The output relay will not energize if a fault or phase reversal is
sensed as 3-phase input voltage is applied.
Reset:
Reset is automatic upon correction of a fault.
LED Operation
The LED flashes green during the restart delay, then glows
green when the output energizes. It flashes red during the trip
delay then glows red when the output de-energizes. It flashes
red/green if phase reversal is sensed.
Wiring Diagram
L1 = Phase A
L2 = Phase B
L3 = Phase C
NO = Normally Open
NC = Normally Closed
C = Common, Transfer Contact
Relay contacts are isolated.
F = 2A Fast acting fuses are
recommended, but not required
Features & Benefits
FEATURES
Proprietary
microcontroller based
circuitry
VOLTAGE
UNBALANCE
TRIP
DELAY
RESTART
DELAY
BENEFITS
Constant monitoring to protect against phase loss,
phase reversal; over, under, and unbalanced voltage;
short cycling
Perfect for OEM applications where cost, size and
ease of installation are important
Provides diagnostics of relay, fault and time
delay status
Protects against shock, vibration and humidity
Ordering Information
MODEL
LINE
VOLTAGE
Compact design
measures 2 in.
(50.8mm) square
LED indication
Encapsulated
TVM208A100.5S3S
TVM230A101S1S
TVM460A41S5M
TVM460A75S2M
TVM480A45S5S
TVM480A100.5S3S
208VAC
230VAC
460VAC
460VAC
480VAC
480VAC
10%
10%
4%
7%
4%
10%
0.5s
1s
1s
5s
5s
0.5s
3s
1s
5m
2m
5s
3s
If you don’t find the part you need, call us for a custom product 800-843-8848
© 2016 Littelfuse Protection Relays & Controls
www.littelfuse.com/tvm
www.littelfuse.com/
Rev: 1-A-062716
Protection Relays
Voltage Monitoring Relays
TVM SERIES
Accessories
LPSM003ZXID (Indicating),
LPSM003Z (Non-indicating) Fuse Holders
Littelfuse POWR-SAFE Dead Front holders
provide optimum protection to personnel for
Class CC and Midget-Style fuses. 600 VAC/DC
0KLK002.T Midget Fuse (2 Amp)
10 x 38 fast acting, high-interrupting capacity,
current-limiting type fuse. 600 Vac/500 Vdc
P1015-13
(AWG 10/12),
P1015-64
(AWG 14/16),
P1015-14
(AWG 18/22)
Female Quick Connect
These 0.25 in. (6.35 mm) female terminals are
constructed with an insulator barrel to provide
strain relief.
P1023-20 DIN Rail Adapter
Allows module to be mounted on a 35 mm DIN
type rail with two #10 screws.
VRM6048 Voltage Reduction Module
Allows the voltage monitor to monitor a 3-phase
550 to 600VAC Line.
Specifications
Line Voltage
Type
Input Voltage
AC Line Frequency
Phase Sequence
Power Consumption
3-phase delta or wye with no connection
to neutral
208 to 480VAC
50 - 100 Hz
ABC
Approx. 2W for 240V units
Approx. 3W for 480V units
Overvoltage, Undervoltage,
& Voltage Unbalance
Overvoltage & Undervoltage
Voltage detection with delay trip &
automatic reset
Undervoltage Trip Point
88 - 92% of the selected line voltage
Reset Voltage
≅
+3% of trip voltage
Overvoltage Trip Point
109 - 113% of the selected line voltage
Reset Voltage
≅
-3% of trip voltage
Trip Variation vs Temperature
≤ ±2%
Voltage Unbalance
Factory fixed from 4 - 10%
Reset On Balance
≅
-0.7% unbalance
Trip Delay Range
Fixed from 0.2 - 100s ±15% or ±0.1s,
whichever is greater
Restart Delay Range
Fixed from 0.5s - 999m ±15% or ±0.2s,
whichever is greater
Phase Reversal & Phase
Loss Response
≤ 200ms; automatic reset
Phase Loss
≥ 25% unbalance
Output
Type
Isolated SPDT relay contacts
Rating
208 to 240VAC (55°C)
10A resistive @ 125VAC, 5A @ 250VAC,
1/4 hp @ 125VAC
380 to 480VAC
10A resistive @ 240VAC, 1/4 hp @ 125VAC,
1/3 hp @ 250VAC, max. voltage 277VAC
Life
Mechanical - 1 x 10
6
; Electrical - 1 x 10
5
Protection
Phase Reversal/Failure
ASME A17.1 Rule 210.6
Motors and Generators
NEMA MG1 14:30, 14:35
Surge
IEEE C62.41-1991 Level B
Dielectric Breakdown
208 to 240VAC
≥ 1500V RMS input to output terminals
380 to 480VAC
≥ 2500V RMS input to output terminals
Mechanical
Mounting
Surface mount with one #8 (M5 x 0.8) screw
Dimensions
H
50.8 mm (2.0”);
W
50.8 mm (2.0”);
D
31.75 mm (1.25”)
Termination
0.25 in. (6.35 mm) male quick connect terminals
Environmental
Operating/Storage
Temperature
-40° to 55°C / -40° to 85°C
Humidity
95% relative, non-condensing
Weight
≅
2.8 oz (79 g)
© 2016 Littelfuse Protection Relays & Controls
www.littelfuse.com/tvm
www.littelfuse.com/
Rev: 1-A-062716
Mouser Electronics
Authorized Distributor
Click to View Pricing, Inventory, Delivery & Lifecycle Information:
Littelfuse
:
TVM480A45S5S TVM460A75S2M TVM230A101S1S TVM480A100.5S3S TVM460A41S5M TVM208A100.5S3S