1/5
VPF-S600 Switching Power Supply
Rev. 12-2006
Features
·Built-in active PFC function
·Short Circuit, overload, over voltage,
over temperature protected
·Current Sharing (Available)
·Current Monitoring
·Power Good Signal
·Built-in Remote Inhibit
·Built-in Remote Sense
·Extended temperature range: -40 ~ +75 ºC
available
Model
1
VPF-S600-03R(I)
VPF-S600-05R(I)
VPF-S600-12R(I)
VPF-S600-16R(I)
VPF-S600-24R(I)
VPF-S600-36R(I)
VPF-S600-48R(I)
Preset
Voltage
3.3V
5V
12V
16V
24V
36V
48V
Output Current
Output
2, 3, 4
2 - 3.3 V
5
12
16
22
31
-
-
-
-
-
6 V
15 V
21 V
30 V
47 V
Minimum
0A
0
0
0
0
0
A
A
A
A
A
Maximum
90 A
90 A
50 A
37.5 A
27.27 A
19.35 A
12.5 A
Max. Power
5, 6
Regulation
7
297 W
+/- 1%
450
600
600
600
600
W
W
W
W
W
+/-
+/-
+/-
+/-
+/-
1%
1%
1%
1%
1%
Ripple & Noise
7, 8
(Vpp)
50 mV
50 mV
1%
1%
1%
1%
1%
48 - 56 V
0A
600 W
+/- 1%
Notes:
1 Adding “I” Indicates Current sharing model.
2 Customer must specify output voltage.
3 Output is fully isolated.
4 Output voltage is measured at output power connector.
5 Provides peak power of 900 W within 500 µS for all models. For longer duty duration please contact us.
6 Must use external forced airflow min. 30 CFM to achieve maximum power.
7 1% minimum load is required to maintain the ripple and regulation.
8 Ripple and noise is measured from 10 KHz to 20 MHz at output terminals with a 0.1 µF ceramic capacitor and
a 22 µF electrolytic capacitor in parallel.
V-Infinity, LLC, 20050 SW 112th Ave., Tualatin, OR 97062
www.v-infinity.com
1-866-372-1258
2/5
VPF-S600 Switching Power Supply
Rev. 12-2006
Input
Parameter
Input Frequency
Input Voltage
Input Current
Inrush Current
Power Factor
Conditions/Description
Min
47
90
Nom
Max
63
264
10
70
Units
Hz
VAC
A
A
At 90-264 VAC
Peak measured at 230 VAC at full load, cold start
Active power factor correction meets EN61000-3-2 class D
Output
Parameter
Transient response
Conditions/Description
Output voltage returns to within 1% in less than
2.5 mS for a 50% load change. Peak
transient does not exceed 5%.
Turn-on and turn-off overshoot shall not exceed
5% over nominal voltage.
Measured at 230 V and full load
12 V model:
Min
Nom
Max
Units
Overshoot
Efficiency
80%
Turn on delay
Hold up time
Adjustability
Remote sense
Remote Inhibit
LED display
(LED 1)
Power Good
All other models:
82%
At 120 VAC
1
second
At 120 VAC and 80% of rated maximim load
20
mS
Adjustable with built-in trim pot.
+/- 5%
Designated as RS+ and RS- on the CN3. Total voltage compensation for cable losses with
respect to the main output. (NOT available for current sharing models.)
Designated as RSW on the CN3. Requires a low signal to inhibit the output.
Green - the power supply is operating normally.
Orange - when any protection occurs or when Remote Inhibit is in effect.
Designated as PG on the CN3. This signal
goes high 100-500 mS after the output reaches regulation.
It goes low at least 1 mS before loss of regulation.
Designated as CSH on (CN3), use in parallel for forced current sharing function.
Accuracy of shared current with up to 4 parallel units is within 10% at full load.
Disignated as CMN on (CN3) for current sense purpose. CMN is a 0.5 to 3VDC output
voltage to represent a linear 0% to 100% output current.
Current Sharing
Current Monitor
Protection Circuit
Parameter
Input Fuse
Input under-voltage
Conditions/Description
Built-in ac fuse. A blown fuse usually indicates permanent
damage to the power supply serviceable by factory only.
Power supply shuts down when ac input is under
80 VAC. When ac line reappears over 86 +/- 5 VAC,
the power supply restarts automatically.
Current limiting starts at 110-140% of the rated output current and
recovers automatically.
Short circuit can be continuous. Recovers automatically upon removal of short.
Output is protected agaist overvoltage. Unit shuts down and latches
when voltage at output terminals exceeds 130%. AC input needs to be
reset to restart the power supply.
Power supply shuts down when temperature is in excess of 85 ºC. Auto recovery.
Overload
Short circuit
Output Over-voltage
Over temp.
V-Infinity, LLC, 20050 SW 112th Ave., Tualatin, OR 97062
www.v-infinity.com
1-866-372-1258
3/5
VPF-S600 Switching Power Supply
Rev. 12-2006
General and Safety
Parameter
Operating temp.
Optional operating
temp.
Storage temp.
Optional storage
temp.
Operating humid.
Storage humid.
EMI
Safety
Leakage Current
Isolation Voltage
(HI-POT)
Conditions/Description
Derates linearly from 100% load at 50 ºC to 50%
load at 70 ºC.
Derates linearly from 100% load at 50 ºC to 37.5%
load at 75 ºC.
Min
0
-40
-20
-40
Non-condensing
5%
Non-condensing
5%
Pass FCC Part 15 Subject J Class B, CISPR 22 class B, CE Mark
UL60950-1 (E222889), CSA C22.2 No. 950-95, TUV EN60950 and CB
at 264 VAC
Applied for 3 seconds
Primary to secondary:
3000
Primary to transformer core:
1500
Primary to earth ground:
1500
Allowable resistance measured when 25 A current is
applied from the ground pin of the three prong plug
to the farthest earthed connection point.
Standard warranty length
According to MIL-HDBK-217 at 30 ºC
150,000
1
Nom
Max
50
75
85
85
90%
95%
Units
ºC
ºC
ºC
ºC
RH
RH
3.5
mA
VAC
VAC
VAC
Grounding Test
0.1
Ohm
Warranty
MTBF
Burn-in
2
8
years
hours
hours
Full load, at 45 +/- 5 ºC, 230 VAC. Burn-in for
up to 8 hours in early productions. Time
reduced gradually as product matures.
Note
: Customer must specify extended temperature on PO.
Mechanical
Parameter
Weight
Enclosure
Mounting holes
Conditions/Description
8.00(L) x 4.33(W) x 2.56(H)
Two sets of 8 threaded mounting holes available on the enclosure
B: 6-32, maximum insertion depth of 0.2 inches.
C: M4, maximum insertion depth of 0.2 inches.
Min
Nom
Max
1450
Units
grams
inches
Input Connector - (CN1)
Parameter
AC input (Option 1)
AC Input (Option 2)
Conditions/Description
Molex Part No. 26-48-1201 or similar (5 pin).
Suggested mating plug: Molex Part No. 09-91-0500 or equivalent (5 pin, 3 used)
Howder Terminal block Part No. HD-121-3P (3 pin, M3 Screw) 9.5mm spacing
Suggested mating connector:
Molex 19198-0045 or similar
Note
: Input connector needs to be specified on the PO.
V-Infinity, LLC, 20050 SW 112th Ave., Tualatin, OR 97062
www.v-infinity.com
1-866-372-1258
4/5
VPF-S600 Switching Power Supply
Rev. 12-2006
Output Connector - (CN2)
Parameter
Output (Option 1)
Conditions/Description
Molex Part No. 26-48-1201 or similar.(20 pin)
Output pin assignment, VO+ (Pins 1-10), VO- (Pins 11-20)
Suggested mating connector:
Molex Part No. 09-91-2000, contact:08-50-0106 or similar.
Howder Terminal block Part No. HD-121-8P (8 pin, M3.5 Screw) 9.5mm spacing
Output (Option 2)
Note:
Output pin assignment, VO+ (Pins 1-4), VO- (Pins 5-8)
Suggested mating connector:
Molex 19198-0045 or similar.
Output connector needs to be specified on the PO.
Logic Connector - (CN3)
Parameter
Logic
Pin Assignments:
Conditions/Description
JS B7B-XH-A
Suggested mating connector:
JST XHP-7 or equivalent , Contact: SXH-001T-P0.6.
1. CMN - Current Monitoring
2. CSH - Current Sharing
3. RTN - Return / Output Ground
4. PG - Power Good Signal
5. RSW - (Remote On-Off / Remote Inhibit)
6. RS(-) - Remote Sense
7. RS(+) - Remote Sense
JST B2B-XH-A
Suggested mating connector:
JST XHP-2 or equivalent, Contact: SXH-001T-P0.6.
Fan
V-Infinity, LLC, 20050 SW 112th Ave., Tualatin, OR 97062
www.v-infinity.com
1-866-372-1258
Rev. 12-2006
5/5
VPF-S600 Switching Power Supply
Note:
Remove all edges and sharp corners
0.25R mm max.
Unit: mm
Undefined Tolerance: +/- 0.15
Material: Aluminum
Thickness: Case 3mm,
Finish: Black Anodized
V
AJR REV. 09-2005
V-Infinity, LLC, 20050 SW 112th Ave., Tualatin, OR 97062
www.v-infinity.com
1-866-372-1258