INSTALLATION AND MAINTENANCE INSTRUCTIONS
2400AT and 2400AIT Direct Wire
Photoelectronic with Fixed Heat
Smoke Detectors
Specifications
Size: Diameter:
Height:
Weight:
Air Velocity:
Operating Temperature:
Operating Humidity:
Visual Indicator:
Latching Alarm:
Audible Signal:
Fixed Temperature Thermal:
Electrical Ratings
System Voltage:
Maximum Ripple Voltage:
Start-up Capacitance:
Start-up Time:
Voltage Limits:
Current Limits
Standby:
Alarm Current:
Reversed Supply:
Alarm Impedance:
Alarm Signal:
A Division of Pittway
3825 Ohio Avenue, St. Charles, Illinois 60174
1-800-SENSOR2, FAX: 630-377-6495
5.5 inches (140 mm)
3.19 inches (81 mm); add 0.5 inches (13 mm) for thermal units
0.7 lb. (310 g)
3000 ft/min (15 M/s)
0° C to 38° C (0° to 100° F)
10% to 93% Relative Humidity, noncondensing
Solid State LED
Reset by Momentary Power Interruption
85dBA minimum interrupted tone when in alarm or supply voltage polarity is reversed
135°F (57° C)
24 VDC
4 Volts peak-to-peak
.02
µ
F Maximum
36 Sec. Maximum
10 – 32 VDC
120
µ
A Maximum; 100
µ
A Nominal
15mA at 10V; 67mA at 32V; 48mA at 24V
5mA at 10V; 19mA at 32V; 15mA at 24V (Detector not in Alarm)
666 ohms Maximum; 478 ohms Minimum
15mA Minimum in Alarm
an interrupted, 85 dBA tone when the individual detector
alarms or when the supply voltage polarity is reversed.
An LED on each detector lights to provide a local alarm in-
dication and will remain on until the supply polarity is re-
versed. A screw terminal is provided for a remote LED
annunciator optional accessory (RA400Z). These detectors
also have the latching feature. The alarm can be reset only
by momentary power interruption.
Mounting
Each 2400 Series detector is supplied with a mounting
bracket kit to permit mounting in either of two ways:
1. Directly to a 3- or 4-inch octagonal, 1
1
/
2
-inch deep elec-
trical box (See Figures 1 and 2).
2. To a 4-inch square electrical box by using a plaster ring
with the mounting bracket kit supplied.
Spacing
NFPA 72E defines the spacing requirements for smoke de-
tectors. Typically, this is 30 feet when the detectors are in-
stalled on a smooth ceiling. However, ALL installations
must comply with NFPA 72E and/or special requirements
of the authority having jurisdiction.
1
I56-287-02
Before Installing
Please thoroughly read the System Sensor manual I56-407-
XX,
Guide for Proper Use of System Smoke Detectors.
This
manual provides detailed information on detector spacing,
placement, zoning, wiring, and special applications. It is
available at no charge from System Sensor. (For installa-
tions in Canada refer to CAN/ULC4-S524,
Standard for the
Installation of Fire Alarm Systems
and CEC Part 1, Sec. 32.)
General Description
System Sensor 2400AT and 2400AIT photoelectronic smoke
detectors, listed to UL 268, provide open area protection
and are intended for use with UL-listed, compatible, 2-wire
control panels. The sensor in this detector operates on the
light scattering principle and features a unique photo-optic
sensing chamber that optimizes smoke entry while mini-
mizing the effects of ambient light.
These detectors also provide restorable, 135° F fixed-tem-
perature heat detection. The 2400AT heat detection unit is
integrated with the photoelectronic sensor while the
2400AIT’s heat detection unit is isolated from the photo-
electronic smoke sensor and can be monitored separately.
In addition, a piezoelectric horn in each detector produces
D400-03-00
Figure 1. Flush mounting of detector on 4-inch
octagonal box:
Figure 2. Detector mounting bracket:
TAMPER
RESISTANT
TAB
A78-1394-00
TO MAKE DETECTOR TAMPER RESISTANT,
BREAK OFF TAB EXTENSION
AT SCRIBED LINE
A78-534-00
Installation Wiring Guidelines
All wiring must comply with the National Electrical Code
and the applicable local codes, and any special require-
ments of the authority having jurisdiction, using the proper
wire gauges. The conductors used to connect smoke detec-
tors to control panels and accessory devices should be
color-coded to reduce the likelihood of wiring errors. Im-
proper connections can prevent a system from responding
properly in the event of a fire.
For signal wiring (wiring between interconnected detec-
tors), wiring no smaller than AWG 18 is recommended. The
clamping plates in the base can accept wire sizes up to
AWG 12. For best system performance, the power (+and –)
loop wires should be twisted pair and installed in separate
grounded conduit or shielded cable to protect the loop from
extraneous electrical interference. If a cable shield is pro-
vided, the shield connection to and from the detector must
be made continuous by using wire nuts, crimping, or sol-
dering, as appropriate for a reliable connection.
Wire connections are made by stripping about 3/8” insula-
tion from the end of the wire, sliding the bare end of the
wire under the clamping plate, and tightening the clamping
plate screw. Do NOT loop the wire under the terminals.
System Sensor smoke detectors are marked with a compat-
ibility identifier located as the last digit of a five-digit code
stamped on the back of the product. Connect detectors only
to compatible control units as indicated in System Sensor’s
compatibility chart. This chart contains a current list of UL-
listed control units and detector combinations and is avail-
able from System Sensor upon request.
CAUTION
Dust covers provide limited protection against airborne
dust particles during shipping. Dust covers MUST be re-
moved before the smoke detectors can sense smoke. Re-
move sensors before beginning remodeling or heavy
construction.
Tamper-resistance Feature
The Tamper Resistant Tab, in the detector mounting
bracket, can make the detector tamper-resistant by making
it necessary to use a pocket screwdriver, or similar tool, to
detach the detector from the bracket.
To make the detector tamper-resistant, use needle-nose pli-
ers to break the smaller tab at the scribed line on the
Tamper Resistant Tab. Figure 2 shows the location of this
tab on the detector mounting bracket.
To remove a detector from the bracket after it has been
made tamper-resistant, use a pocket screwdriver, or other
similar tool, to depress the Tamper Resistant Tab, in the slot
on the mounting bracket, and rotate the detector counter-
clockwise.
Testing
NOTE:
Before testing, notify the proper authorities that the
smoke detector system is undergoing maintenance
and, therefore, the system will be temporarily out
of service. Disable the zone or system undergoing
maintenance to prevent unwanted alarms.
Figure 3. Wiring diagram for 2400AT detector with two-wire control panel:
D400-03-00
2
I56-287-02
Figure 4. Wiring diagram for 2400AIT detector with isolated thermal and two-wire panels:
Detectors must be tested after installation and periodic
maintenance. System Sensor 2400AT and 2400AIT Smoke
Detectors can be tested in the following five ways:
NOTE:
Before testing the detector, check for the presence
of the flashing LED. If it does not flash, power has
been lost (check the wiring), or it is defective (re-
turn for repair – refer to the Warranty).
A. Recessed Test Switch
1. Push and hold the recessed test switch with a 0.1 inch
maximum diameter tool, such as a pocket screw-
driver.
2. The LED on the detector should light within 5 sec-
onds. The p-horn should also sound.
B. Calibrated Test Card (R59-18-00)
1. Remove the detector cover by placing a small bladed
screwdriver in the side slot of the detector cover,
twisting it slightly until the cover can be turned coun-
terclockwise for removal.
2. Insert the NO ALARM end of the test card fully into
the test slot (see Figure 6) and slide it counterclock-
wise until it stops.
3. The detector should not alarm (wait at least 20
seconds).
4. Remove the test card by sliding it clockwise before re-
moving, then repeat with the ALARM end of the test
card.
5. The LED should latch on within 20 seconds, indicat-
Figure 5. Bottom and side views, showing position
of test switch:
LED
RECESSED TEST
SWITCH
ing alarm and annunciating the panel.
6. Replace the cover by gently rotating it clockwise until
it locks in place.
C. Test Module (System Sensor Model No. MOD400R)
The MOD400R is used with an analog or digital voltme-
ter to check the detector sensitivity as described in the
test module’s manual.
D. Aerosol Generator (Gemini 501)
Set the generator to represent 4%/Ft. to 5%/Ft. obscura-
tion as described in the aerosol generator manual. Using
the bowl shaped applicator, apply aerosol until the unit
alarms.
E. Direct Heat Method (Hair dryer of 1000-1500 watts)
Direct the heat toward the bimetallic collector. Hold the
heat source about 12 inches from the detector in order to
avoid damage to the plastic. When the heat rises to
greater than 135°F the detector will latch in alarm.
The detector will reset only after it has had sufficient time
to cool and the power source has been temporarily inter-
rupted. Both smoke and heat detection testing are recom-
mended for verifying system protection capability.
Detectors that fail these tests should be cleaned as de-
scribed under MAINTENANCE and retested. If the detec-
tors still fail these tests, they should be returned for repair.
Notify the proper authorities the system is back on line.
Maintenance
NOTE:
Before cleaning, notify the proper authorities that
the smoke detector system is undergoing mainte-
nance and, therefore, will be temporarily out of
service. Disable the system undergoing mainte-
nance to prevent unwanted alarms.
1. Remove the detector cover by placing a small-bladed
screwdriver in the side slot of the detector cover, twist-
ing it until the cover can be turned counterclockwise for
removal.
2. Vacuum the screen carefully without removing it. If fur-
ther cleaning is required, continue with step 3, other-
3
I56-287-02
TEST MODULE
SOCKET
PUSH RECESSED SWITCH WITH
A .1" MAX. DIAMETER TOOL
A78-1393-00
D400-03-00
3.
4.
5.
6.
wise skip to step 6.
Remove the screen by pulling it straight out. Vacuum the
inside.
Clean the vaned chamber piece by vacuuming out dust
and particles.
To replace the screen, orient it so that the arrow on top
aligns with the field test socket on the base of the detec-
tor. Carefully push the screen onto the base making sure
it fits tightly to the chamber.
Replace the cover by gently rotating it clockwise until it
locks in place.
Figure 6:
REMOVABLE COVER
TEST SLOT
CLEANABLE SCREEN
(P/N RS24T)
REMOVAL
SLOT
A78-1409-00
WARNING
The Limitations of Property Protection Smoke Detectors and Sounders
cannot quickly detect, or sense at all, a fire developing on another level of
The sounder in this detector will not operate if the power is cut off for any
a building. For this reason,
detectors shall be located on every level and
reason.
in every bedroom within a building.
The sounder may not be heard.
The loudness of the sounder meets or
Smoke detectors have sensing limitations, too.
Ionization detectors and
exceeds the current standards. However, the sounder may not alert a
photoelectronic detectors are required to pass fire tests of the flaming and
sound sleeper or one who has recently used drugs or has been drinking
smoldering types. This is to ensure that both can detect a wide range of
alcoholic beverages. This sounder may not be heard if it is placed in an
fires. Ionization detectors offer a broad range of fire-sensing capability, but
area which is separated by a closed door, or if it is located on a different
they are somewhat better at detecting fast-flaming fires than slow-smol-
floor from the person in a hazardous situation, or if it is placed too far
dering fires. Photoelectronic detectors sense smoldering fires better than
away to be heard over the ambient noise such as traffic, air conditioners,
flaming fires, which have little, if any, visible smoke. Because fires develop
machinery, or musical appliances that may prevent alert persons from
in different ways, and are often unpredictable in their growth, neither type
hearing the alarm.
of detector is always best, and a given detector may not always provide
The sounder may not be heard by persons who are hearing impaired.
early warning of a specific type of fire.
In this case, a visual indicator shall also be used.
In general, detectors cannot be expected to provide warnings for fires re-
This smoke detector used with this base is designed to
activate and ini-
sulting from inadequate fire protection practices, violent explosions, es-
tiate
emergency action, but will do so only when used in conjunction with
caping gases that ignite, improper storage of flammable liquids like
an authorized fire alarm system. This detector must be installed in accor-
cleaning solvents that ignite, other similar safety hazards, arson, smoking
dance with NFPA standard 72.
in bed, children playing with matches or lighters, etc. Smoke detectors
Smoke detectors will not work without power.
AC or DC powered
used in high air velocity conditions may have a delay in alarm due to dilu-
smoke detectors will not work if the power supply is cut off .
tion of smoke densities created by frequent and rapid air exchanges. Addi-
Smoke detectors will not sense fires which start where smoke does not
tionally, high air velocity environments may create increased dust
reach the detectors.
Smoldering fires typically do not generate a lot of
contamination, demanding more frequent detector maintenance.
heat which is needed to drive smoke up to the ceiling where the smoke
Smoke detectors cannot last forever.
Smoke detectors contain electronic
detector is usually located. For this reason, there may be large delays in
parts. Even though detectors are made to last over 10 years, any part can
detecting a smoldering fire with either an ionization-type detector or a
fail at any time. Therefore, smoke detectors shall be replaced after being in
photoelectronic-type detector. Either one of them may alarm only after
service for 10 years. The smoke detector system that this detector is used
flaming has initiated, which will generate the heat needed to drive the
in must be tested regularly per NFPA 72. This smoke detector should be
smoke to the ceiling.
cleaned regularly per NFPA 72 or at least once a year.
Smoke from fires in chimneys, in walls, on roofs, or on the other side of a
closed door may not reach the smoke detector and alarm it. A detector
Three-Year Limited Warranty
System Sensor warrants its enclosed smoke detector to be free from de-
fects in materials and workmanship under normal use and service for a
period of three years from date of manufacture. System Sensor makes no
other express warranty for this smoke detector. No agent, representative,
dealer, or employee of the Company has the authority to increase or alter
the obligations or limitations of this Warranty. The Company’s obligation
of this Warranty shall be limited to the repair or replacement of any part of
the smoke detector which is found to be defective in materials or work-
manship under normal use and service during the three year period com-
mencing with the date of manufacture. After phoning System Sensor’s toll
free number 800-SENSOR2 (736-7672) for a Return Authorization number,
send defective units postage prepaid to: System Sensor, Repair Depart-
D400-03-00
4
ment, RA #__________, 3825 Ohio Avenue, St. Charles, IL 60174. Please
include a note describing the malfunction and suspected cause of failure.
The Company shall not be obligated to repair or replace units which are
found to be defective because of damage, unreasonable use, modifica-
tions, or alterations occurring after the date of manufacture. In no case
shall the Company be liable for any consequential or incidental damages
for breach of this or any other Warranty, expressed or implied whatsoever,
even if the loss or damage is caused by the Company’s negligence or fault.
Some states do not allow the exclusion or limitation of incidental or conse-
quential damages, so the above limitation or exclusion may not apply to
you. This Warranty gives you specific legal rights, and you may also have
other rights which vary from state to state.
I56-287-02