Data are valid at +25°C, unless otherwise specified.
Parameter
Input
Nominal input voltage
Permanent input
voltage range (Ui)
Extended permanent
input voltage range
Transient input voltage
Start up input voltage
Undervoltage lock-out
Start up time
Reflected ripple current
Input current in short
circuit mode (Average)
No load input current
Output
Output voltage *
Full temperature range
Ui min. to max.
75% load
Ambient temperature : 25°c
Ui nominal, 75% load
Full temperature range
Ui min. to max.
Full temperature range
Ui min. to max.
Nominal
Nominal
Nominal
Nominal
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Typical
Typical
Typical
VDC
VDC
VDC
VDC
%
W
A
A
A
A
mVpp
mVpp
mVpp
%
%
%
3,3
5
12
15
+/- 2
8
1,6
1,6
0,65
0,55
50
100
150
+/- 1
+/- 2,5
81
3,3
5
12
15
+/- 2
10
2
2
0,80
0,65
50
100
150
+/- 1
+/- 2,5
82
3,3
5
12
15
+/- 2
10
2
2
0,80
0,65
50
100
150
+/- 1
+/- 2,5
83
Conditions
Limit or
typical
Nominal
Min. - Max.
Min. - Max.
Maximum
Maximum
Minimum
Min. - Max.
Maximum
Typical
Maximum
Maximum
Units
Single Output MGDSI-10
10-D
9
4,7-16
/
/
/
/
4-4,5
50
50
50
100
10 - H
20
9-36
/
40/0,1
/
/
7-8,5
50
50
30
30
10 - J
24
16-40
16-45
45/0,1
/
/
12-15
50
30
30
30
Industrial
Grade
10 - Q
72
36-140
36-154
175/0,1
165/1
33
/
50
30
20
10
Full temperature range
Full temperature range
Full temperature range
(Consult factory)
Full load
No undervoltage lock-out
turn-on/turn-off threshold
Ui nominal
Nominal output
Full load : resistive
Ui nominal, full load at
switching freq. BW = 20MHz
Ui nominal
Short-circuit
Ui nominal
No load
VDC
VDC
VDC
VDC/S
VDC/S
VDC
VDC
ms
mApp
mA
mA
3,3
5
12
15
+/- 2
10
2
2
0,80
0,65
50
100
150
+/- 1
+/- 2,5
83
Set Point accuracy
Output power
Output current **
3,3V output
5V output
12V output
15V output
Ripple output voltage ***
3,3V and 5V output
12V output
15V output
Line regulation
Load regulation ****
Efficiency
Maximum admissible
Capacitive load
3,3V and 5V output
12V and 15V output
5
Ui nominal
Full load
BW = 20MHz
Ui min. to max.
Full load
Ui nominal
25% to full load
Ui nominal
Full load
Ui nominal
Full load
Per output
Maximum
Maximum
µF
µF
1 000
330
1 000
330
1 000
330
1 000
330
Note * : For proper operation the MGDI-10 module requires to install a 22µF chemical or tantalum capacitance accross output terminals.
Note ** : For 9-36V input range, the current is derated at 80% at 9V and increases linearly to full current at 12V.
Note *** : The ripple output voltage is the periodic AC component imposed on the output voltage, an aperiodic and random component (noise) has also to be considered.
This noise can be reduced by adding an external capacitor (typically 10nF/ rated voltage depending on isolation requirement) connected between the pin Gin and the pin
Gout of the converter. This capacitor should be layed-out as close as possible from the converter.
Note **** : For load regulation characteristics from 0% to full load, please contact factory.
Data are valid at +25°C, unless otherwise specified.
Industrial
Grade
Parameter
Input
Nominal input voltage
Permanent input
voltage range (Ui)
Extended permanent
input voltage range
Transient input voltage
Start up input voltage
Undervoltage lock-out
Start up time
Reflected ripple current
Input current in short
circuit mode (Average)
No load input current
Output
Output voltage *
Set Point accuracy
Output power
Output current **
5V output
12V output
15V output
Ripple output voltage ***
5V output
12V output
15V output
Line regulation
Load regulation ****
Cross load output
regulation
Efficiency
Maximum admissible
Capacitive load
5V output
12V and 15V output
Conditions
Limit or
typical
Nominal
Min. - Max.
Min. - Max.
Maximum
Maximum
Minimum
Min. - Max.
Maximum
Typical
Maximum
Maximum
Units
Bi Output MGDBI-10
10-D
9
4,7-16
/
/
/
/
4-4,5
50
50
50
100
10 - H
20
9-36
9-36
40/0,1
/
/
7-8,5
50
50
30
30
10 - J
24
16-40
16-45
45/0,1
/
/
12-15
50
30
30
30
10 - Q
72
36-140
36-154
175/0,1
165/1
33
/
50
30
20
10
Full temperature range
Full temperature range
Full temperature range
(Consult factory)
Full load
No undervoltage lock-out
turn-on/turn-off threshold
Ui nominal
Nominal output
Full load : resistive
Ui nominal, full load at
switching freq. BW = 20MHz
Ui nominal
Short-circuit
Ui nominal
No load
Full temperature range
Ui min. to max.
75% load
Ambient temperature : 25°c
Ui nominal, 75% load
Full temperature range
Ui min. to max.
Full temperature range
Ui min. to max.
Ui nominal
Full load
BW = 20MHz
Ui min. to max.
Full load
Ui nominal
25% to full load
Ui nominal
+ Vout nominal load
- Vout from 25% to full load
Ui nominal
Full load
Ui nominal
Full load
Per output
VDC
VDC
VDC
VDC/S
VDC/S
VDC
VDC
ms
mApp
mA
mA
Nominal
Nominal
Nominal
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Maximum
Typical
Typical
Typical
Typical
VDC
VDC
VDC
%
W
A
A
A
mVpp
mVpp
mVpp
%
%
%
%
+/- 5
+/- 12
+/- 15
+/- 2
+/- 4
+/- 0,800
+/- 0,325
+/- 0,265
50
100
150
+/- 1
+/- 2,5
+/- 0,5
81
+/- 5
+/- 12
+/- 15
+/- 2
+/- 5
+/- 1
+/- 0,40
+/- 0,33
50
100
150
+/- 1
+/- 2,5
+/- 0,5
82
+/- 5
+/- 12
+/- 15
+/- 2
+/- 5
+/- 1
+/- 0,40
+/- 0,33
50
100
150
+/- 1
+/- 2,5
+/- 0,5
83
+/- 5
+/- 12
+/- 15
+/- 2
+/- 5
+/- 1
+/- 0,40
+/- 0,33
50
100
150
+/- 1
+/- 2,5
+/- 0,5
83
5
Maximum
Maximum
µF
µF
470
100
470
100
470
100
470
100
Note * : For proper operation the MGDI-10 module requires to install a 22µF chemical or tantalum capacitance accross output terminals.
Note ** : For 9-36V input range, the current is derated at 80% at 9V and increases linearly to full current at 12V.
Note *** : The ripple output voltage is the periodic AC component imposed on the output voltage, an aperiodic and random component (noise) has also to be considered.
This noise can be reduced by adding an external capacitor (typically 10nF/ rated voltage depending on isolation requirement) connected between the pin Gin and the pin
Gout of the converter. This capacitor should be layed-out as close as possible from the converter.
Note **** : For load regulation characteristics from 0% to full load, please contact factory.
Data are valid at +25°C, unless otherwise specified.
Parameter
Input
Nominal input voltage
Permanent input
voltage range (Ui)
Extended permanent
input voltage range
Transient input voltage
Start up input voltage
Undervoltage lock-out
Start up time
Reflected ripple current
Input current in short
circuit mode (Average)
No load input current
Output
Output voltage *
Set Point accuracy
Output power
Output current **
5V & +/- 12V output
5V & +/- 15V output
Ripple output voltage***
5V output
12V output
15V output
Line regulation
Load regulation ****
Cross load output
regulation
Efficiency
Maximum admissible
Capacitive load
3,3V and 5V output
12V and 15V output
Full temperature range
Nominal
Ui min. to max.
Nominal
75% load
Ambient temperature : +25°c
Maximum
Ui nominal, 75% load
Full temperature range
Maximum
Ui min. to max.
Full temperature range
Ui min. to max.
Ui nominal
Full load
BW = 20MHz
Ui min. to max.
Full load
Ui nominal
25% to full load
Ui nominal
+ Vout nominal load
- Vout from 25% to full load
Ui nominal
Full load
Ui nominal
Full load
Per output
Maximum
Maximum
Maximum
Maximum
Maximum
Typical
Typical
Typical
Typical
VDC
VDC
%
W
A
A
mVpp
mVpp
mVpp
%
%
%
%
5 & +/- 12
5 & +/- 15
+/- 2
5 & +/- 2,5
1 & +/- 0,20
1 & +/- 0,15
50
100
150
+/- 1
+/- 2,5
+/- 0,5
83
Conditions
Limit or
typical
Nominal
Min. - Max.
Min. - Max.
Maximum
Maximum
Minimum
Min. - Max.
Maximum
Typical
Maximum
Maximum
Units
Industrial
Grade
Tri Output MGDTI-10
10 - H
20
9-36
/
40/0,1
/
/
7-8,5
50
50
30
30
10 - J
24
16-40
16-45
45/0,1
/
/
12-15
50
30
30
30
Full temperature range
Full temperature range
Full temperature range
(Consult factory)
Full load
No undervoltage lock-out
turn-on/turn-off threshold
Ui nominal
Nominal output
Full load : resistive
Ui nominal, full load at
switching freq. BW = 20MHz
Ui nominal
Short-circuit
Ui nominal
No load
VDC
VDC
VDC
VDC/S
VDC/S
VDC
VDC
ms
mApp
mA
mA
5 & +/- 12
5 & +/- 15
+/- 2
5 & +/- 2,5
1 & +/- 0,20
1 & +/- 0,15
50
100
150
+/- 1
+/- 2,5
+/- 0,5
83
5
Maximum
Maximum
µF
µF
470
100
470
100
Note * : For proper operation the MGDI-10 module requires to install a 22µF chemical or tantalum capacitance accross output terminals.
Note ** : For 9-36V input range, the current is derated at 80% at 9V and increases linearly to full current at 12V.
Note *** : The ripple output voltage is the periodic AC component imposed on the output voltage, an aperiodic and random component (noise) has also to be considered.
This noise can be reduced by adding an external capacitor (typically 10nF/ rated voltage depending on isolation requirement) connected between the pin Gin and the pin
Gout of the converter. This capacitor should be layed-out as close as possible from the converter.
Note **** : For load regulation characteristics from 0% to full load, please contact factory.