12 VDC, 40 mA max. with short-circuit protection circuit (E5AR-TQQE3MW-FLK: 21 mA max.)
Current output
Relay output
Auxiliary output
Potentiometer input
Event input
Other functions
Ambient operating temperature
Ambient operating humidity
Storage temperature
Note 1:
Do not use an inverter output as the power supply. (Refer to
Safety Precautions for All E5
@
R Models.)
2:
The supply voltage (i.e., 100 to 240 VAC or 24 VAC/VDC) depends on the model. Be sure to specify the required type when ordering.
3:
The Controller is equipped with multiple sensor input. Temperature input or analog input can be selected with the input type setting switch. There is basic
insulation between power supply and input terminals, power supply and output terminals, and input and output terminals.
■
Input Ranges
Platinum Resistance Thermometer, Thermocouple, Current, or Voltage Input
Input type
Platinum
resistance
thermometer
Thermocouple
Current
Voltage
Name
2300
1800
1300
900
800
700
600
400
200
100
0
−100
−200
Pt100
K
J
T
E
L
U
N
R
S
B
(
W/Re
)
5-26
2300.0
W
mA
V
1700.0
1300.0
850.0
850.0
850.0
1300.0
1700.0
1800.0
Tempera-
ture
range
(°C)
500.0
400.0
150.00
400.0
600.0
400.0
20 to
4
100.0
10 to
20 to
5 to 1 5 to 0
0
0
0.0
−200.0 −150.00 −200.0
−20.0
−100.0
−20.0
−200.0
−100.0
−200.0
−200.0
0.0
0.0
0.0
Setting
Minimum
setting unit
(SP and alarm)
Input type
setting switch
0
0.1°C
1
0.01
°C
2
3
4
5
6
7
8
0.1°C
TC.PT
9
10
11
12
13
14
15
16
17
18
19
(Depends on scaling and number
of decimal places.)
TC.PT
Set to TC.PT.
IN1
TYPE
ANALOG
Set to ANALOG
IN1
TYPE
ANALOG
Note:
The shaded area indicates the setting status at the time of purchase.
3
E5AR-T
■
Characteristics
Indication accuracy
Thermocouple input with cold junction compensation: (±0.1% of PV or
±1°C,
whichever is greater)
±1
digit max. (See note 1.)
Thermocouple input without cold junction compensation: (±0.1% FS or
±1°C,
whichever is smaller)
±1
digit (See note 2.)
Analog input:
±0.1%
FS
±1
digit max.
Platinum resistance thermometer input: (±0.1% of PV or
±0.5°C,
whichever is greater)
±1
digit max.
Position-proportional potentiometer input:
±5%
FS
±1
digit max.
Standard control (heating or cooling control), heating/cooling control, standard control with remote SP (2-input models only), heating/cool-
ing control with remote SP (2-input models only), cascade standard control (2-input models only), cascade heating/cooling control (2-input
models only), proportional control (2-input models only), position-proportional control (control-valve control models only)
Control mode
Influence of temperature
Thermocouple input (R, S, B, W): (±1% of PV or ±10°C, whichever is greater) ±1 digit max.
Other thermocouple input: (±1% of PV or ±4°C, whichever is greater) ±1 digit max.
Influence of voltage
*K thermocouple at -100°C max.: ±10°C max.
Platinum resistance thermometer: (±1% of PV or ±2°C, whichever is greater) ±1 digit max.
Analog input: (±1%FS) ±1 digit max.
Control period
Proportional band (P)
Integral time (I)
Derivative time (D)
Hysteresis
Manual reset value
Alarm setting range
Input sampling period
Insulation resistance
Dielectric strength
Vibration resistance
(malfunction)
Shock resistance
(malfunction)
Inrush current
Weight
Degree of protection
Memory protection
Applicable standards
0.2 to 99.0 s (in units of 0.1 s) for time-proportioning control output
0.00% to 999.99% FS (in units of 0.01% FS)
0.0 to 3,999.9 s (in units of 0.1 s)
0.0 to 3,999.9 s (in units of 0.1 s)
0.01% to 99.99% FS (in units of 0.01% FS)
0.0% to 100.0% (in units of 0.1% FS)
−19,999
to 99,999 EU (See note 3.)
(The decimal point position depends on the input type and the decimal point position setting.)
50 ms
20 MΩ min. (at 500 VDC)
2,000 VAC, 50/60 Hz for 1 min (between charged terminals of different polarities)