Step 11. Enter to the Thermocouple Type Input Submenu
Press
d
to display flashing, previously selected Thermocouple
type.
Step 12. Scroll through available selection of TC types
Press
b
to sequence thru flashing Thermocouple types,
(select k -for type "K" CHROMEGA
®
/ALOMEGA
®
)
J K T E N DIN J
J k t E N dN J
R S B C - TC types
R S b C - Display
Step 30. Select the Deviation Control Type Submenu
Press
d
. If flashing
_DEV
Deviation is displayed press
a
,
otherwise press
b
until flashing
_DEV
is shown. Now
press
d
to store and go to next menu item.
Step 31. Select the Latched Type Submenu
Press
d
. If flashing
UNLT
Unlatched is displayed press
a
,
otherwise press
b
until
UNLT
is displayed.
Press
d
to store and advance to next menu item.
Step 32. Select the Normally Open Type of Contact
Closure Submenu
Press
d
. If flashing
N.o.
Normally Open is displayed,
press
a
, otherwise press
b
until
N.o.
is displayed. Press
d
to store and advance to next menu item.
Step 33. Select the Above Type of Active Submenu
Press
d
. If flashing
ABoV
Above is displayed, press
a
,
otherwise press
b
until
ABoV
is displayed. Press
d
to store
and advance to next menu item.
Step 34. Enable Alarm 1 at Power On (
A.P.oN
)
Press
d
. If flashing
ENBL
is displayed, press
a
, otherwise
press
b
until
ENBL
is displayed. Press
d
to store and
advance to next menu item.
Step 35. Enter Alarm 1 High Submenu
Press
a
twice to skip
ALR.L
Alarm 1 Low value.
ALR.L
is
for below &
ALR.H
for above.
Step 36. Set the Alarm 1 High value (
ALR.H
)
Press
d
. Press
b
or
c
until value to set the display to
002.0
. Press
d
to save.
Step 37. Enter the Alarm 2 Menu
The display will show
ALR2
the top menu for Alarm 2.
Repeat steps from 28 to 36 to set for Alarm 2 the same
conditions as for Alarm 1.
Step 38. Configuration of Display Color Selection
Press
a
until the
COLR
Display Color Selection Menu
appears on the Display. Configure
COLR
as
N.CLR
/
GRN
(green),
1.CLR
/
RED
(red),
2.CLR
/
AMBR
(amber). Please
refer to the operator’s manual if needed.
Step 39. Run a Test
Press
a
until reset the controller and return to
RUN
Mode
to display
075.0
(Ambient Temperature). Now you are
ready to observe temperature as it rises 10°F higher than
displayed. Touch the tip of the Thermocouple to raise the
temperature above the Alarm 2 High value
082.0
, and AL2
will turn on, and Display Color will change from Green to
Amber. Continue touching the tip to raise the temperature
above the Alarm 1 High value
087.0
and Display Color will
change from Amber to Red.
SPECIFICATION
Accuracy:
+0.5°C temp;
0.03% rdg. process typical
Resolution:
1°/0.1°; 10 µV process
Temperature Stability:
0.04°C/°C RTD;
0.05°C/°C TC @ 25°C (77°F);
50 ppm/°C process
Display:
4-digits, 9-segments LED,
21 mm (0.83") with red, green and
amber programmable colors
Input Types:
Thermocouple, RTD, Analog Voltage
and Current
TC: (ITS 90)
J, K, T, E, R, S, B, C, N, L
RTD: (ITS 68)
100/500/1000 ohm Pt sensor
2-, 3-, or 4-wire; 0.00385 or 0.00392
curve
Voltage:
0 to 100 mV, 0 to 1 V, 0 to 10 Vdc
Current:
0 to 20 mA (4 to 20 mA)
Output 1
†
:
Relay 250 Vac @ 3 A Resistive Load,
SSR, Pulse
Output 2
†
:
Relay 250 Vac @ 3 A Resistive Load,
SSR, Pulse
†
Only with -AL option
Options: Communication
RS-232 / RS-485
or
10BaseT
or
Excitation: 24 Vdc @ 25 mA
EXC. not available for Low Power Option
Step 13. Store TC type
After you have selected the Thermocouple type press
d
to
store your selection, the instrument automatically advances
to the next menu item.
Step 14. Enter to Reading Configuration Menu
The display shows
RDG
Reading Configuration, which is the
top menu for 4 submenus: Decimal Point, Degree Units,
Filter Constant and Input/Reading Submenus.
Step 15. Enter to Decimal Point Submenu
Press
d
to show
DEC
Decimal Point.
Step 16. Display the Decimal Point position
Press
d
again to display the flashing Decimal Point position.
Step 17. Select the Decimal Point position
Press
b
to select
FFF.F
Decimal Point position.
Step 18. Store selected Decimal Point position
By pressing
d
momentarily the Decimal Point position will
be stored and the instrument will go to the next menu item.
Step 19. Enter to Temperature Unit Submenu
Display shows
TEMP
Temperature Unit.
Step 20. Display available Temperature Units
Press
d
to display the flashing Degree
°F
or
°C
.
Step 21. Scroll through Temperature Units selection
Press
b
to select
°F
Degree.
Step 22. Store the Temperature Unit
Press
d
to display momentarily that the Degree Unit has
been stored and the instrument will go automatically to the
next menu item.
Step 23. Enter the Filter Constant Submenu
Display shows
FLTR
Filter Constant Submenu.
Step 24. Display the Filter Constant Value Submenu
Press
d
to display the flashing, previously selected Filter
Constant.
Step 25. Scroll through available Filter Constants
Press
b
to sequence thru Filter Constants
0001
,
0002
,
0004
,
0008
,
0016
,
0032
,
0064
and
0128
.
Step 26. Store the Filter Constant
Press
d
momentarily to store
0004
Filter Constant and the
instrument will automatically go to the next menu item.
Step 27. Enter Alarm 1 Menu
The display will show
ALR1
the top menu for Alarm 1. In the
following steps we are going to enable Alarm 1, Deviation,
Unlatch, Normally Open, Active Above, Enable at power on
and +2°F High Alarm i.e. Process Value > Setpoint 1 Value
+2°F will activate Alarm 1.
Step 28. Enter Alarm 1 Enable/Disable Submenu
Press
d
to display flashing
DSBL
/
ENBL
.
Step 29. Enable Alarm 1 Submenu
If flashing
ENBL
is displayed, press
a
, if
DSBL
is displayed,
press
b
until
ENBL
is displayed, then press
d
to store and
go to the next menu item.
Line Voltage/Power:
90 - 240 Vac ±10%, 50 - 400 Hz*,
or 110-375 Vdc,
4W
for Single Display;
5W
for Dual Display
* No CE compliance above 60 Hz
Low Voltage Power Option:
12 - 36 Vdc,
3 W**
for Single Display;
20 - 36 Vdc,
4 W**
for Dual Display
** Units can be powered safely with 24 Vac
but No Certification for CE/UL are claimed.
Dimensions:
48 H x 96 W x 127 D mm
(1.89 x 3.78 x 5")
Weight:
295 g (0.65 lb)
Approvals:
FM, UL, C-UL, CE per EN 61010-1:2001
WARNING:
These products are not designed for use in, and should not be used for, patient-
connected applications.
This device is marked with the international caution symbol. It is important to read the
Setup Guide before installing or commissioning this device, as the guide contains important
information relating to safety and EMC.
It is the policy of NEWPORT to comply with all worldwide safety and EMC/EMI regulations that apply.
NEWPORT is constantly pursuing certification of its products to the European New Approach Directives.
NEWPORT will add the CE mark to every appropriate device upon certification.
The information contained in this document is believed to be correct, but NEWPORT Electronics, Inc.
accepts no liability for any errors it contains, and reserves the right to alter specifications without notice.
i/8 Temperature & Process
Monitor / Alarm (-AL)
For immediate technical or application assistance please call:
TRADEMARK NOTICE:
,
NEWPORT
,
NEWPORT
,
®
®
newportUS.com
,
and
the “Meter Bezel Design” are Trademarks of NEWPORT ELECTRONICS, INC.
WARRANTY/DISCLAIMER
NEWPORT Electronics, Inc. warrants this unit to be free of defects in materials and workmanship for a period of
one (1) year
from the date of purchase. In addition to NEWPORT’s standard warranty period, NEWPORT
Electronics will extend the warranty period for
four (4) additional years
if the warranty card enclosed with each
instrument is returned to NEWPORT.
If the unit malfunctions, it must be returned to the factory for evaluation. NEWPORT’s Customer Service
Department will issue an Authorized Return (AR) number immediately upon phone or written request. Upon
examination by NEWPORT, if the unit is found to be defective, it will be repaired or replaced at no charge.
NEWPORT’s WARRANTY does not apply to defects resulting from any action of the purchaser, including but not
limited to mishandling, improper interfacing, operation outside of design limits, improper repair, or unauthorized
modification. This WARRANTY is VOID if the unit shows evidence of having been tampered with or shows
evidence of having been damaged as a result of excessive corrosion; or current, heat, moisture or vibration;
improper specification; misapplication; misuse or other operating conditions outside of NEWPORT’s control.
Components which wear are not warranted, including but not limited to contact points, fuses, and triacs.
NEWPORT is pleased to offer suggestions on the use of its various products. However, NEWPORT neither
assumes responsibility for any omissions or errors nor assumes liability for any damages that result from
the use of its products in accordance with information provided by NEWPORT, either verbal or written.
NEWPORT warrants only that the parts manufactured by it will be as specified and free of defects.
NEWPORT MAKES NO OTHER WARRANTIES OR REPRESENTATIONS OF ANY KIND WHATSOEVER,
EXPRESS OR IMPLIED, EXCEPT THAT OF TITLE, AND ALL IMPLIED WARRANTIES INCLUDING ANY
WARRANTY OF MERCHANTABILITY AND FITNESS FOR A PARTICULAR PURPOSE ARE HEREBY
DISCLAIMED.
LIMITATION OF LIABILITY: The remedies of purchaser set forth herein are exclusive, and the total liability
of NEWPORT with respect to this order, whether based on contract, warranty, negligence, indemnification,
strict liability or otherwise, shall not exceed the purchase price of the component upon which liability is
based. In no event shall NEWPORT be liable for consequential, incidental or special damages.
CONDITIONS: Equipment sold by NEWPORT is not intended to be used, nor shall it be used: (1) as a "Basic
Component" under 10 CFR 21 (NRC), used in or with any nuclear installation or activity; or (2) in medical
applications or used on humans. Should any Product(s) be used in or with any nuclear installation or activity,
medical application, or used on humans, or misused in any way, NEWPORT assumes no responsibility as set forth
in our basic WARRANTY/DISCLAIMER language, and, additionally purchaser will indemnify NEWPORT and hold
NEWPORT harmless from any liability or damage whatsoever arising out of the use of the Product(s) in such a
manner.
RETURN REQUEST/INQUIRIES
Direct all warranty and repair requests/inquiries to the NEWPORT Customer Service Department. BEFORE
RETURNING ANY PRODUCT(S) TO NEWPORT, PURCHASER MUST OBTAIN AN AUTHORIZED RETURN
(AR) NUMBER FROM NEWPORT’S CUSTOMER SERVICE DEPARTMENT (IN ORDER TO AVOID
PROCESSING DELAYS). The assigned AR number should then be marked on the outside of the return package
and on any correspondence.
The purchaser is responsible for shipping charges, freight, insurance and proper packaging to prevent breakage
in transit.
FOR
WARRANTY
RETURNS,
please consult NEWPORT for current
repair BEFORE contacting NEWPORT:
1. Purchase Order number under which
the product was PURCHASED,
2. Model and serial number of the
product under warranty, and
3. Repair instructions and/or specific
problems relative to the product.
FOR
NON-WARRANTY
REPAIRS,
have the following information available
charges. Have the following information
available BEFORE contacting NEWPORT:
1. Purchase Order number to cover the
COST the repair,
2. Model and serial number of product,
and
3. Repair instructions and/or specific
problems relative to the product.
Newport Electronics, Inc.
2229 South Yale Street • Santa Ana, CA • 92704 • U.S.A.
TEL: (714) 540-4914 • FAX: (203) 968-7311
Toll Free: 1-800-639-7678 • www.newportUS.com • e-mail:info@newportUS.com
ISO 9001 Certified
Newport Technologies, Inc.
976 Bergar • Laval (Quebec) • H7L 5A1 • Canada
TEL: (514) 335-3183 • FAX: (514) 856-6886
Toll Free: 1-800-639-7678 • www.newport.ca • e-mail:info@newport.ca
Newport Electronics, Ltd.
One Omega Drive • River Bend Technology Centre
Northbank, Irlam • Manchester M44 5BD • United Kingdom
Tel: +44 161 777 6611 • FAX: +44 161 777 6622
Toll Free: 0800 488 488 • www.newportuk.co.uk • e-mail:sales@newportuk.co.uk
Newport Electronics B.V.
Postbus 8034 • 1180 LA Amstelveen • The Netherlands
TEL: +31 20 3472121 • FAX: +31 20 6434643
Toll Free: 0800 0993344 • www.newport.nl • e-mail: info@newport.nl
Newport Electronics spol s.r.o.
Frystatska 184, 733 01 Karviná • Czech Republic
TEL: +420 59 6311899 • FAX: +420 59 6311114
Toll Free: 0800-1-66342 • www.newport.cz • e-mail: info@newport.cz
Newport Electronics GmbH
Daimlerstrasse 26 • D-75392 Deckenpfronn • Germany
TEL: 49 7056 9398-0 • FAX: 49 7056 9398-29
Toll Free: 0800 / 6397678 • www.newport.de • e-mail: sales@newport.de
Newport Electronique S.A.R.L.
11, rue Jacques Cartier • 78280 Guyancourt • France
TEL: +33 1 61 37 29 00 • FAX: +33 1 30 57 54 27
Toll Free: 0800 466 342 • www.newport.fr • e-mail: sales@newport.fr
Mexico and Latin America
FAX: 001 (203) 359-7807
En Español: 001 (203) 359-7803
NEWPORT’s policy is to make running changes, not model changes, whenever an improvement is possible. This
affords our customers the latest in technology and engineering.
NEWPORT is a registered trademark of NEWPORT Electronics, Inc.
© Copyright 2005 NEWPORT Electronics, Inc. All rights reserved.
This document may not be copied, photocopied, reproduced, translated, or reduced to any electronic medium or
machine-readable form, in whole or in part, without the prior written consent of NEWPORT Electronics, Inc.
PATENT NOTICE:
This product is covered by one or more of the following patents: U.S. Pat. No. Des. 336,895;
5,274,577; 6,243,021 / Canada 2052599; 2052600 / Italy 1249456; 1250938 / France Brevet No. 91 12756 / Spain
2039150; 2048066 / UK Patent No. GB2 249 837; GB2 248 954 / Germany DE 41 34398 C2. The
®
is a Trademark
of OMEGA Engineering, Inc. USED UNDER LICENSE. Other U.S. and International patents pending or applied for.
MQS3446/N/0505
START HERE
This Quick Start Reference provides information
on setting up your instrument for basic operation.
The latest complete Communication and Operational
Manual as well as free Software and ActiveX Controls
are available at
www.newportUS.com/i
or on the
CD-ROM enclosed with your shipment.
Disassembly Instruction:
If necessary, the board assembly may be removed from the
front of the case housing.
Warning: Disconnect all ac power from the unit
before proceeding.
1.
Remove the
board assembly
from the case by
pulling at the
sides of the bezel.
2.
The bezel along
with the board
assembly will
unlatch from the
case housing.
WIRING
Wire the instrument according to the figure shown below.
Warning: Do not connect ac power to your
device until you have completed all input and
output connections. This device must only be
installed by a specially trained electrician with
corresponding qualifications. Failure to follow
all instructions and warnings may result in injury!
CONFIGURATION
MENU
Mode:
Flashing display in MENU Mode means you can make your
selection by pressing
b
button. If the flashing display is not
a four digit value, pressing
c
button will always direct the
instrument one step backward of the top menu item. The
second push on the
c
button will reset the instrument
except after the setpoint and the alarms, that will go to the
RUN Mode without resetting the instrument. The
a
button
will always sequence the instrument thru the menu items.
The
d
button has two functions:
1.
To save a selected flashing display
2.
To direct the instrument to the next submenu level
RUN
Mode:
b
causes the display to flash the PEAK with the
OPERATION - (For Thermocouple Input)
Step 1. Apply Power to the Instrument
When your device is first powered up it will display the
ambient temperature (assume 75°F).
Step 2. Enter Setpoint 1 Menu
Press
a
one time from run mode to get to
SP1
Setpoint 1.
Step 3. Enter the Setpoint 1 Value Submenu
Press
d
. Display shows the previous selection of Setpoint 1.
Step 4. Change the Setpoint 1 Value
Press
b
or
c
until desired value is displayed.
Step 5. Store the Setpoint 1 Value
Set the Setpoint 1 to 10 degree higher than Process value
(SP1 = 85) and press
d
to store, display flashes
STRD
message and advances to
SP2
Setpoint 2 Menu.
Step 6. Store the Setpoint 2 Value
Repeat steps 3 and 4. Set the Setpoint 2 to 5 degree higher
than Process value (SP2 = 80) and press
d
to store,
display flashes
STRD
message and advances to
CNFG
Configuration Menu.
Step 7. Enter the Input Type Menu
Press
d
to enter
INPT
Input Type Menu.
Step 8. Enter to the submenu items of Input Menu
Press
d
to display Input: Process, RTD or Thermocouple.
If flashing
T.ç
is displayed press
a
and proceed to Step 11.
SAFETY CONSIDERATION
This device is marked with the international
Caution symbol.
The instrument is a panel mount device protected in
accordance with EN 61010-1:2001, electrical safety
requirements for electrical equipment for measurement, control
and laboratory. Remember that the unit has no power-on
switch. Building installation should include a switch or circuit-
breaker that must be compliant to IEC 947-1 and 947-3.
SAFETY:
• Do not exceed voltage rating on the label located on
the top of the instrument housing.
• Always disconnect power before changing signal and
power connections.
• Do not use this instrument on a work bench without
its case for safety reasons.
• Do not operate this instrument in flammable or
explosive atmospheres.
• Do not expose this instrument to rain or moisture.
EMC:
• Whenever EMC is an issue, always use shielded cables.
• Never run signal and power wires in the same conduit.
• Use signal wire connections with twisted-pair cables.
• Install Ferrite Bead(s) on signal wire close to the
instrument if EMC problems persist.
MOUNTING
corresponding value. Press again to go back to RUN
Mode.
c
causes the display to flash VALLEY with the
corresponding value. Press again to go back to RUN
Mode.
d
causes flashing PEAK or VALLEY to reset corresponding
values. Press
d
one more time to go back to RUN Mode.
FLOW CHART
Step 9. Scroll through available selection of Input Menu
Press
b
until a flashing
T.ç
for Thermocouple is displayed.
Step 10. Enter to the Thermocouple Input Submenu
Press
d
to store Thermocouple Input. The display will stop
flashing and show the top menu for Thermocouple types. If
you press
a
controller will step to next menu item (Skip to Step 14).
Connect the main power connections as shown in the figure below.
Panel Mounting Instruction:
1.
Using the dimensions from the panel cutout diagram
shown above, cut an opening in the panel.
2.
Remove sleeve from the rear of the case by removing
thumbnuts.
3.
Insert the unit into the opening from the front of the panel, so
the gasket seals between the bezel and the front of the panel.
4.
Slip the sleeve over the rear of the case.
5.
Tighten the thumbnuts to hold the unit firmly in the panel.
FUSE
FUSE
FUSE
FUSE
FUSE
1
2
3
4
Connector Output Type For 115Vac For 230Vac
DC
Output 1
Relay
3 A(T)
3 A(T)
-
Output 2
Relay
3 A(T)
3 A(T)
-
Power
N/A
100 mA(T) 100 mA(T) 100 mA(T)
Power
N/A
N/A
N/A
400 mA(T)
_____
Underline denotes factory default setup
Output 1 and 2 are for -AL Alarm Option only.