Surge arrester
Stacked surge arresters in casing
Series/Type:
Ordering code:
Version/Date:
LN30M1-A1800AC-3C
B88069X2963B161
Issue 04 / 2015-03-04
Content of header bars 1 and 2 of data sheet will be automatically entered in headers and footers! Please fill in the
table and then change the color to "white". This ensures that the table disappears (invisible) for the customer PDF.
Don't change formatting when entering or pasting text in the table and don't add any cell or line in and to it!
Identification/Classification 1
(header 1 + top left bar):
Identification/Classification 2
(header 2 + bottom left header bar):
Ordering code: (top right header bar)
Series/Type: (bottom right header bar)
Surge arrester
Stacked surge arresters in casing
B88069X2963B161
LN30M1-A1800AC-3C
EPCOS AG 2015. Reproduction, publication and dissemination of this publication, enclosures hereto and the information
contained therein without EPCOS' prior express consent is prohibited.
EPCOS AG is a TDK Group Company.
Surge arrester
Stacked surge arresters in casing
B88069X2963B161
LN30M1-A1800AC-3C
Features
High self-extinguishing capability
High follow current limitation capability
Stable performance over life
High insulation resistance
RoHS-compatible
Applications
AC power lines, phase-neutral
Class I – surge protection
Electrical specifications
DC spark-over voltage
1)
Front of wave spark-over voltage
- at 1.2/50 µs, 6 kV
Breakdown time
- typical values
- for 99% of measured values
Insulation resistance at 100 V
DC
Class I according to EN 61343-11
Nominal operating voltage
2)
Max. continuous operating voltage
2)
Nominal discharge current 8/20 µs
Max. discharge current 8/20 µs
Impulse current 10/350 µs
Follow current extinguishing capability
3)
Max. temporary overvoltage (max. 5 s)
2)
Connection cable cross section
Weight
Operation and storage
- temperature
- humidity
Climatic category (IEC 60068-1)
Label, black negative
U
N
U
c
I
n
I
max
I
imp
I
f
U
T
> 600
< 2500
< 100
< 20
> 10
230
275
20
40
20
6
440
> 10
~ 70
−40
... +125
5 … 95
40/ 125/ 21
V
V
ns
ns
G
V
V
kA
kA
kA
kA
V
mm²
g
°C
%
Certifications
1)
2)
3)
UL 1449 (E319264)
At delivery AQL 0.65 level II, DIN ISO 2859
At 48...62 Hz
Cut-off selectivity for 40 A NH-gG/gL circuit breakers is given.
Issue 04 / 2015-03-04
Page 2 of 5
PPD AB PD / PPD AB PM
Please read
Cautions and warnings
and
Important notes
at the end of this document.
Surge arrester
Stacked surge arresters in casing
B88069X2963B161
LN30M1-A1800AC-3C
Cautions and warnings
The surge arrester can be used if the maximum expected follow current can be securely
extinguished.
The follow current must be limited (see values on page 2) so that the arrester can be properly
extinguished when the surge has decayed. The arrester might otherwise heat up and ignite
adjacent components.
If the contacts of the surge arresters are defective, current load can cause sparks and loud
noises.
Surge arresters may become hot in the event of longer periods of current stress (burn risk). In the
event of overload the connectors may fail or the component may be destroyed.
Surge arresters must be handled with care and must not be dropped.
Do not continue to use damaged surge arresters.
Display of ordering codes for EPCOS products
The ordering code for one and the same EPCOS product can be represented differently in data
sheets, data books, other publications, on the EPCOS website, or in order-related documents such as
shipping notes, order confirmations and product labels.
The varying representations of the
ordering codes are due to different processes employed and do not affect the specifications of
the respective products.
Detailed information can be found on the Internet under
www.epcos.com/orderingcodes
PPD AB PD / PPD AB PM
Please read
Cautions and warnings
and
Important notes
at the end of this document.
Page 4 of 5
Issue 04 / 2015-03-04
Important notes
The following applies to all products named in this publication:
1. Some parts of this publication contain
statements about the suitability of our products for
certain areas of application.
These statements are based on our knowledge of typical
requirements that are often placed on our products in the areas of application concerned. We
nevertheless expressly point out
that such statements cannot be regarded as binding
statements about the suitability of our products for a particular customer application.
As a
rule, EPCOS is either unfamiliar with individual customer applications or less familiar with them
than the customers themselves. For these reasons, it is always ultimately incumbent on the
customer to check and decide whether an EPCOS product with the properties described in the
product specification is suitable for use in a particular customer application.
2. We also point out that
in individual cases, a malfunction of electronic components or failure
before the end of their usual service life cannot be completely ruled out in the current state
of the art, even if they are operated as specified.
In customer applications requiring a very high
level of operational safety and especially in customer applications in which the malfunction or
failure of an electronic component could endanger human life or health (e.g. in accident
prevention or life-saving systems), it must therefore be ensured by means of suitable design of the
customer application or other action taken by the customer (e.g. installation of protective circuitry
or redundancy) that no injury or damage is sustained by third parties in the event of malfunction or
failure of an electronic component.
3.
The warnings, cautions and product-specific notes must be observed.
4. In order to satisfy certain technical requirements,
some of the products described in this
publication may contain substances subject to restrictions in certain jurisdictions (e.g.
because they are classed as hazardous).
Useful information on this will be found in our Material
Data Sheets on the Internet (www.epcos.com/material). Should you have any more detailed
questions, please contact our sales offices.
5. We constantly strive to improve our products. Consequently,
the products described in this
publication may change from time to time.
The same is true of the corresponding product
specifications. Please check therefore to what extent product descriptions and specifications
contained in this publication are still applicable before or when you place an order.
We also
reserve the right to discontinue production and delivery of products.
Consequently,
we cannot guarantee that all products named in this publication will always be available.
The aforementioned does not apply in the case of individual agreements deviating from the
foregoing for customer-specific products.
6. Unless otherwise agreed in individual contracts,
all orders are subject to the current version of
the “General Terms of Delivery for Products and Services in the Electrical Industry”
published by the German Electrical and Electronics Industry Association (ZVEI).
7. The trade names EPCOS, Alu-X, CeraDiode, CeraLink, CeraPad, CeraPlas, CSMP, CSSP,
CTVS, DeltaCap, DigiSiMic, DSSP, ExoCore, FilterCap, FormFit, LeaXield, MiniBlue, MiniCell,
MKD, MKK, MotorCap, PCC, PhaseCap, PhaseCube, PhaseMod, PhiCap, PQSine, SIFERRIT,
SIFI, SIKOREL, SilverCap, SIMDAD, SiMic, SIMID, SineFormer, SIOV, SIP5D, SIP5K, TFAP,
ThermoFuse, WindCap are
trademarks registered or pending
in Europe and in other countries.
Further information will be found on the Internet at www.epcos.com/trademarks.
Page 5 of 5