DEMO CIRCUIT 818
LTC2924
QUICK START GUIDE
LTC2924
Quad Power Supply
Sequencer
DESCRIPTION
Demonstration circuit 818 is a Quad Power Supply Se-
quencer featuring the LTC2924.
Demonstration circuit 818 can configure the LTC2924 to
sequence up to 4 power supplies via any combination of
pass FETS or power supply enable control inputs. The
0.61V reference of the LTC2924 permits the DC818 to be
easily modified by simple resistor changes to work with
any voltage level from 5V down to 0.8V. The schematic
provides a table of resistor values for common supply
voltages: 5V, 3.3V, 3.0V, 2.8V, 2.5V, 1.8V, 1.6V, 1.2V and
1.0V. Refer to the data sheet for equations to calculate
other voltages and hysteresis levels. Convenient test
points are provided to facilitate evaluation of the power
up and power down sequencing. Additional jumper op-
tions are provided to permit cascading multiple DC818s
for additional channels.
The circuit board is assembled with four IRL3714ZS N-
channel DD packaged MOSFETs capable of controlling up
to 10A loads for connecting each of four rails with the an
associated load. The board is designed to also accept
SO-8 packaged MOSFETs for lower current operation.
In addition to the output voltage dividers, the circuit
board also has two capacitors for sequence and Power
Good signal timing adjustments, one resistor for setting
the hysteresis current injected into each output voltage
divider and two configuration jumpers for cascading
boards for additional channels.
LTC is a trademark of Linear Technology Corporation
PERFORMANCE SUMMARY
Specification s are at T
A
= 25°C
SYMBOL
V
CC
I
CC
V
ON(TH)
V
OFF(TH)
V
INON(TH)
V
INOFF(TH)
V
OUT(EN)
I
OUT(EN)
PARAMETER
Input Supply Range
Input Supply Current
ON, Low to High Threshold
ON, High to Low Threshold
IN1-IN4 Low to High Threshold
IN1-IN4 High to Low Threshold
OUT1-OUT4 Gate Drive Voltage
OUT1-OUT4 On Current
CONDITIONS
V
IN
= 3.6V, I
LOAD
= 100mA
0.6000
0.6013
0.6020
0,6026
MIN
3.0
TYP
1.5
0.6060
0.6074
0.6081
0.6087
10
V
CC
+4.5
8.6
MAX
6.0
3.0
0.6121
0.6135
0.6142
0.6148
V
CC
+6
11.2
UNITS
V
mA
V
V
V
V
V
µA
OPERATING PRINCIPLES
The active high ON pin initiates the power on sequence
when the applied voltage exceeds 0.61V. Upon sequence
initiation, the Sequencer TIMER capacitor C
TMR
is charged
by a 5uA current, generating a sequencing time pulse of
C
TMR
(uF)/5. At the end of each sequence timeout, the
LTC2924 enables a successive power supply. Each sup-
ply is enabled by driving a 10uA current out of the appro-
priate OUTn pin. This current is derived from a charge
pump capable of enhancing the gate of a NMOS pass FET
or driving a power supply enable pin. A capacitor can be
1
LTC2924
connected to the OUTn pins to control the slew rate of
each MOSFET controlled supply.
As the power supply turns on, the resistive divider con-
nected to the IN1 pin starts to drive up the voltage at the
IN1 pin. When the voltage at this pin exceeds 0.61V, a
comparator signals the logic that the supply is on. The
timer circuit is enabled again and the cycle repeats until
the last power supply has turned on. The power off se-
quence is initiated by pulling the ON pin voltage below
0.61V after a power on sequence has completed. The
power off sequence turns off the power supply in the re-
verse order of the power on sequence. OUT4 is turned off
first. The timer function is used between each supply be-
ing sequenced down.
QUICK START PROCEDURE
Demonstration circuit 818 is easy to set up to evaluate
the performance of the LTC2924.
Install all four jumpers in position 1.
Connect an ON signal source to the ON pin circuit (TP7
or TP8, the latter provides a voltage divider which can be
configured as an under voltage lockout.) The voltage on
TP7 should be less than 0.55V.
Connect four external power supply outputs (3.3V, 2.5V,
1.8V, and 1.2V) to appropriate INPUT pins (TP3, TP4,
TP5, and TP6). Refer to the table on the schematic or
the data sheet to change the dividers to support other
voltages.
Attach optional loads to TP11, TP12, TP13 and TP14 (up
to 10 amps depending on acceptable voltage drop).
Initiate the turn on sequence by raising the ON signal
source so that TP7 is above 0.62V and observe the load
voltage transitions on the four channel scope (see figure
1).
Drop the ON pin voltage below 0.55V (or to ground) to
observe the turn off sequence (see Figure 2). NOTE:
Output voltage decay will vary with load and capacitance.
Figure 1. Power up mode
2