(Reference 800-XC6DT2 for Standby Rating Technical Data)
SYSTEM RATINGS
Prime
Voltage (L-L)
Phase
PF
Hz
kW
kVA
Amps
skVA@30%
Voltage Dip
Generator Model*
Temp Rise
Connection
208V**
3
0.8
60
725
906
2518
1800
741RSL4045
105 °C/40 °C
12 LEAD LOW WYE
240V**
3
0.8
60
725
906
2182
1800
741RSL4045
105 °C/40 °C
12 LEAD HI DELTA
380V
3
0.8
60
725
906
1379
1850
575RSL4044
105 °C/40 °C
4 BAR WYE
480V**
3
0.8
60
725
906
1091
2500
574RSL4038
105 °C/40 °C
4 LEAD WYE
600V**
3
0.8
60
725
906
873
2825
574RSS4280
105 °C/40 °C
4 LEAD WYE
4160V
3
0.8
60
725
906
125
2600
742FSM4364
105 °C/40 °C
6 LEAD WYE
* Consult the factory for alternate configuration.
** UL 2200 Offered
CERTIFICATIONS AND STANDARDS
//
//
Emissions –
EPA Tier 2 Certified
Generator set is designed and manufactured
in facilities certified to standards ISO 9001:2008 and
ISO 14001:2004
//
Performance Assurance Certification (PAC)
- Generator Set Tested to ISO 8528-5 for Transient Response
- Verified product design, quality and performance integrity
- All engine systems are prototype and factory tested
Power Rating
- Accepts Rated Load in One Step Per NFPA 110
- Permissible average power output during 24 hours of
operation is approved up to 75%.
//
//
UL 2200 / CSA – Optional
– UL 2200 Listed
– CSA Certified
2
/ /
/
/
725-XC6DT2
STANDARD FEATURES*
MTU Onsite Energy is a single source supplier
Global Product Support
2 Year Standard Warranty
12V 2000 Diesel Engine
- 23.9 Liter Displacement
- Electronic Unit Pump Injection
- 4-Cycle
//
Complete Range of Accessories
//
//
//
//
Generator
- Brushless, Rotating Field Generator
- 2/3 Pitch Windings
- PMG (Permanent Magnet Generator) supply to regulator
- 300% Short Circuit Capability
//
Digital Control Panel(s)
- UL Recognized, CSA Certified, NFPA 110
- Complete System Metering
- LCD Display
//
Cooling System
- Integral Set-Mounted
- Engine Driven Fan
//
STANDARD EQUIPMENT*
//
Engine
No Load to Full Load Regulation
Brushless Alternator with Brushless Pilot Exciter
4 Pole, Rotating Field
105 °C Maximum Prime Temperature Rise
1 Bearing, Sealed
Flexible Coupling
Full Amortisseur Windings
125% Rotor Balancing
3-Phase Voltage Sensing
±0.25% Voltage Regulation
100% of Rated Load - One Step
5% Maximum Total Harmonic Distortion
Air Cleaners
Oil Pump
Oil Drain Extension & S/O Valve
Full Flow Oil Filter
Closed Crankcase Ventilation
Jacket Water Pump
Inter Cooler Water Pump
Thermostats
Blower Fan & Fan Drive
Radiator - Unit Mounted
Electric Starting Motor - 24V
Governor – Electronic Isochronous
Base - Structural Steel
SAE Flywheel & Bell Housing
Charging Alternator - 24V
Battery Box & Cables
Flexible Fuel Connectors
Flexible Exhaust Connection
EPA Certified Engine
//
Digital Control Panel(s)
//
Generator
NEMA MG1, IEEE and ANSI standards compliance for temperature rise
and motor starting
Sustained short circuit current of up to 300% of the rated current for
up to 10 seconds
Self-Ventilated and Drip-Proof
Superior Voltage Waveform
Digital, Solid State, Volts-per-Hertz Regulator
Digital Metering
Engine Parameters
Generator Protection Functions
Engine Protection
CAN Bus ECU Communications
Windows
®
-Based Software
Multilingual Capability
Remote Communications to RDP-110 Remote Annunciator
16 Programmable Contact Inputs
Up to 11 Contact Outputs
UL Recognized, CSA Certified, CE Approved
Event Recording
IP 54 Front Panel Rating with Integrated Gasket
NFPA110 Compatible
* Represents standard product only. Consult Factory/MTU Onsite Energy Distributor for additional configurations.
3
/ /
/
/
725-XC6DT2
APPLICATION DATA
//
Engine
MTU
12V 2000 G85 TB
4-Cycle
12-V
23.9 (1,457)
13 (5.1)
15 (5.9)
16:1
1,800
Electronic Isochronous (ADEC)
810 (1,086)
±0.25%
Dry
//
Fuel Consumption
PRIME
199.1 (52.6)
149.9 (39.6)
101.4 (26.8)
Manufacturer
Model
Type
Arrangement
Displacement: L (in
3
)
Bore: cm (in)
Stroke: cm (in)
Compression Ratio
Rated RPM
Engine Governor
Maximum Power: kWm (bhp)
Speed Regulation
Air Cleaner
At 100% of Power Rating: L/hr (gal/hr)
At 75% of Power Rating: L/hr (gal/hr)
At 50% of Power Rating: L/hr (gal/hr)
//
Cooling - Radiator System
PRIME
50 (122)
0.12 (0.5)
833 (220)
257 (68)
280 (15,923)
245 (13,932)
76.5 (4,350)
38 (51)
//
Liquid Capacity (Lubrication)
77 (20.3)
110 (29.1)
20 (5.3)
316 (83.5)
Total Oil System: L (gal)
Engine Jacket Water Capacity: L (gal)
After Cooler Water Capacity: L (gal)
System Coolant Capacity: L (gal)
Ambient Capacity of Radiator: °C (°F)
Maximum Restriction of Cooling Air, Intake,
and Discharge Side of Rad.: kPa (in. H
2
0)
Water Pump Capacity: L/min (gpm)
After Cooler Pump Capacity: L/min (gpm)
Heat Rejection to Coolant: kW (BTUM)
Heat Rejection to After Cooler: kW (BTUM)
Heat Radiated to Ambient: kW (BTUM)
Fan Power: kW (hp)
//
Air Requirements
PRIME
63 (2,225)
1,120 (39,554)
//
Electrical
24
2,800
Electric Volts DC
Cold Cranking Amps Under -17.8 °C (0 °F)
//
Fuel System
#12 JIC 37° Female
3/4” NPT Adapter Provided
#4 JIC 37° Female
1/4” NPT Adapter Provided
3 (10)
Diesel #2
480.7 (127)
Aspirating: *m /min (SCFM)
Air Flow Required for Rad.
Cooled Unit: *m
3
/min (SCFM)
Remote Cooled Applications;
Air Flow Required for Dissipation
of Radiated Gen-set Heat for a
Max of 25 °F Rise: *m
3
/min (SCFM)
3
278 (9,811)
Fuel Supply Connection Size
Fuel Return Connection Size
Maximum Fuel Lift: m (ft)
Recommended Fuel
Total Fuel Flow: L/hr (gal/hr)
* Air density = 1.184 kg/m
3
(0.0739 lbm/ft
3
)
//
Exhaust System
PRIME
560 (1,040)
160 (5,721)
8.5 (34.1)
Gas Temp. (Stack): °C (°F)
Gas Volume at Stack
Temp: m
3
/min (CFM)
Maximum Allowable
Back Pressure: kPa (in. H
2
0)
4
/ /
/
/
725-XC6DT2
WEIGHTS AND DIMENSIONS
Drawing above for illustration purposes only, based on standard open power 480 volt generator set. Lengths may vary with other voltages. Do not use for installation design. See website
for unit specific template drawings.
System
OPU
Dimensions (L x W x H)
4,320 x 1,600 x 2,200 mm (170 x 63 x 86.5 in)
Weight (less tank)
5, 737 kg (12,648 lb)
Weights and dimensions are based on open power units and are estimates only. Consult the factory for accurate weights and dimensions for your specific generator set.
[size=2]The American NVE brand uses cutting-edge giant magnetoresistance technology to develop ultra-high-speed digital isolators. Compared with traditional optocouplers, American NVE products have ma...
I have been looking for information on this topic recently and want to study it seriously, but unfortunately I have not found any relevant introduction. I wonder if any kind-hearted person can help me...
SMIC ushers in the dawn of “five years of profitability” 2006-8-7 With the arrival of the "five years of profitability" period, can SMIC deliver a report card that will excite investors? On June 28...
At first glance, a DC motor seems simple. You apply voltage to its terminals, and it turns. What if you want to control the direction of the motor's rotation? The correct way is to change the directio...
The exception is as follows: Exception 'Data Abort' (4): Thread-Id=077e0172(pth=8436d6c0), Proc-Id=074e008a(pprc=83c5f7b4) 'iesample.exe', VM-active=074e008a(pprc=83c5f7b4) 'iesample.exe' PC=424072b4(...
Abstract:
With the increasing complexity of smart vehicle electrical and electronic architectures, the full lifecycle management of vehicle electronic control components faces multiple challe...[Details]
Nios II is a configurable 16-/32-bit RISC processor. Combined with a rich set of peripheral-specific instructions and hardware acceleration units, it provides a highly flexible and powerful SOPC sy...[Details]
Ever since the Tesla fire incident, electric cars, already known for their poor reputation, have been subjected to even more scathing criticism. Despite this, many people are still willing to buy t...[Details]
In recent years, the government has increasingly supported electric vehicles, and the number of electric vehicles has increased. Observant drivers will notice that there are many more green license...[Details]
Today's security industry has entered the era of massive networking. Many enterprises, especially financial institutions, have established multi-level video surveillance networking platforms. Lever...[Details]
The automotive industry in 2025 is undergoing a thorough intelligent reshuffle.
Geely wants to make changes in the field of AI cockpits: in the future, there will be no traditional smart...[Details]
Electric vehicles are becoming increasingly popular, with increasingly longer ranges. There are two ways to charge electric vehicles: slow charging and fast charging. Which is the most suitable? Sl...[Details]
The complexity of the integrated circuits (ICs) used in electronic systems in vehicles is increasing. They aim to execute artificial intelligence (AI) algorithms to control autonomous driving funct...[Details]
Learned the following information.
Customer product: industrial computer motherboard
Glue application area: CPU/BGA filling
Glue color requirements: black or t...[Details]
"We have successfully launched the first version of our dedicated chip for EMB brake-by-wire. Second-generation samples have also been successfully completed, and we are actively planning a third-g...[Details]
A tubular motor is an electric motor that is typically used to control the movement of machines and equipment. Tubular motors are generally divided into two categories: linear tubular motors and ro...[Details]
Inverter power supplies on the market can generally be divided into two categories: sine wave inverters and square wave inverters. Some engineers also like to categorize pure sine wave inverters as...[Details]
A scale, a large, ground-mounted scale, is typically used to measure the tonnage of truck cargo. It's the primary weighing device used in factories, mines, and businesses for bulk cargo measurement...[Details]
There are more and more electric vehicles. Recently, I have heard some news about electric vehicles performing poorly in winter. I would like to briefly introduce whether heat pump technology is mo...[Details]
With the gradual popularization of new energy vehicles in recent years, more and more people have been able to access and purchase electric vehicles. The structure of electric vehicles is composed ...[Details]