© Siemens AG 2011
Overload Relays
SIRIUS 3RU1 Thermal Overload Relays
3RU11 for standard applications
■
Overview
"Increased safety" type of protection EEx e according to
ATEX directive 94/9/EC
The 3RU11 thermal overload relays are suitable for the overload
protection of explosion-proof motors with "increased safety" type
of protection EEx e. The relays meet the requirements of
EN 60079-7 (Electrical apparatus for areas subject to explosion
hazards – Increased safety "e");
see Catalog IC 10.
3
5
4
7
6
1
2
EC type test certificate for Category (2) G/D exists. It has the
number DMT 98 ATEX G 001.
■
Benefits
The most important features and benefits of the 3RU11 thermal
overload relays are listed in the overview table
(see
"General Data" on page 5/42).
■
Application
Industries
$
Connection for mounting onto contactors:
%
&
(
)
*
+
Optimally adapted in electrical, mechanical and design terms to the
contactors. Connecting pins can be used for direct mounting of the
overload relays. Stand-alone installation is possible as an alternative
(in some cases in conjunction with a stand-alone installation module).
Selector switch for manual/automatic RESET and RESET button:
With this switch you can choose between manual and automatic RE-
SET. A device set to manual RESET can be reset locally by pressing
the RESET button. A remote RESET is possible using the RESET mod-
ules (accessories), which are independent of size.
Switch position indicator and TEST function of the wiring:
Indicates a trip and enables the wiring test.
Motor current setting:
Setting the device to the rated motor current is easy with the large ro-
tary knob.
STOP button:
If the STOP button is pressed, the NC contact is opened. This switches
off the contactor downstream. The NC contact is closed again when
the button is released.
Transparent, sealable cover:
Secures the motor current setting and the TEST function against ad-
justment.
Supply terminals:
The generously sized terminals permit connection of two conductors
with different cross-sections for the main and auxiliary circuits. The
auxiliary circuit can be connected with screw terminals and alterna-
tively with spring-type terminals.
The 3RU11 thermal overload relays are suitable for customers
from all industries who want to guarantee optimum inverse-time
delayed protection of their electrical loads (e. g. motors) under
normal starting conditions (CLASS 10).
Application
The 3RU11 thermal overload relays have been designed for the
protection of three-phase and single-phase AC and DC motors.
If single-phase AC or DC loads are to be protected by the 3RU11
thermal overload relays, all three bimetal strips must be heated.
For this purpose, all main current paths of the relay must be con-
nected in series.
Ambient conditions
The 3RU11 thermal overload relays have temperature compen-
sation in accordance with IEC 60947-4-1 for the temperature
range of –20 °C to +60 °C. For temperatures from +60 °C to
+80 °C the upper set value of the setting range must be reduced
by the factor listed in the table below.
Ambient temperature in °C
+60
+65
+70
+75
+80
5
Derating factor for the upper set
value
1.0
0.94
0.87
0.81
0.73
The 3RU11 thermal overload relays up to 100 A have been de-
signed for inverse-time delayed protection of loads with normal
starting
(for "Function" see note on Technical Information on
page 5/1)
against excessive temperature rises due to overload
or phase failure.
An overload or phase failure results in an increase of the motor
current beyond the set rated motor current. Via heating ele-
ments, this current rise heats up the bimetal strips inside the de-
vice which then bend and as a result trigger the auxiliary con-
tacts by means of a tripping mechanism. The auxiliary contacts
then switch off the load by means of a contactor. The break time
depends on the ratio between the tripping current and set cur-
rent
I
e
and is stored in the form of a long-term stable tripping
characteristic
(for "Characteristic Curves" see the note on Tech-
nical Information on page 5/1).
The "tripped" status is signaled by means of a switch position in-
dicator. Resetting takes place either manually or automatically
after a recovery time has elapsed
(for "Function" see note on
Technical Information on page 5/1).
The devices are manufactured in accordance with environmen-
tal guidelines and contain environmentally friendly and reusable
materials.
They comply with all important worldwide standards and ap-
provals.
■
Accessories
The following optional accessories are available for the 3RU11
thermal overload relays:
• For the four overload relay sizes S00 to S3 one terminal
bracket each for stand-alone installation
• One mechanical RESET module for all sizes
• One cable release for resetting devices which are difficult to
access (for all sizes)
• One electrical remote RESET module in three voltage variants
for all sizes
• Terminal covers
5/46
Siemens LV 1 AO · 2011
© Siemens AG 2011
Overload Relays
SIRIUS 3RU1 Thermal Overload Relays
3RU11 for standard applications
■
Selection and ordering data
3RU11 thermal overload relays with screw terminals on the auxiliary current side for direct mounting
1)
, CLASS 10
Features and technical specifications:
• Overload and phase failure protection
• Auxiliary contacts 1 NO + 1 NC
• Manual and automatic RESET
Size of Rating
con-
for induction
tactor
2)
motor
rated value
3)
Current setting of
the inverse-time
delayed overload
release
•
•
•
•
Short-circuit DT
protection
with fuse,
type of coor-
dination 2,
gL/gG opera-
tional class
4)
A
0.5
1
1
1.6
2
2
2
4
4
4
6
6
10
10
16
20
20
25
35
35
10
10
16
20
20
25
35
35
40
50
63
63
25
35
35
40
50
63
80
80
100
100
63
80
80
125
125
160
160
200
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
4)
Switch position indicator
TEST function
STOP button
Integrated, sealable cover
Screw terminals
(on auxiliary current
side)
Order No.
Price
per PU
kg
3RU11 16-0AB0
3RU11 16-0BB0
3RU11 16-0CB0
3RU11 16-0DB0
3RU11 16-0EB0
3RU11 16-0FB0
3RU11 16-0GB0
3RU11 16-0HB0
3RU11 16-0JB0
3RU11 16-0KB0
3RU11 16-1AB0
3RU11 16-1BB0
3RU11 16-1CB0
3RU11 16-1DB0
3RU11 16-1EB0
3RU11 16-1FB0
3RU11 16-1GB0
3RU11 16-1HB0
3RU11 16-1JB0
3RU11 16-1KB0
3RU11 26-1CB0
3RU11 26-1DB0
3RU11 26-1EB0
3RU11 26-1FB0
3RU11 26-1GB0
3RU11 26-1HB0
3RU11 26-1JB0
3RU11 26-1KB0
3RU11 26-4AB0
3RU11 26-4BB0
3RU11 26-4CB0
3RU11 26-4DB0
3RU11 36-1HB0
3RU11 36-1JB0
3RU11 36-1KB0
3RU11 36-4AB0
3RU11 36-4BB0
3RU11 36-4DB0
3RU11 36-4EB0
3RU11 36-4FB0
3RU11 36-4GB0
3RU11 36-4HB0
3RU11 46-4DB0
3RU11 46-4EB0
3RU11 46-4FB0
3RU11 46-4HB0
3RU11 46-4JB0
3RU11 46-4KB0
3RU11 46-4LB0
3RU11 46-4MB0
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.150
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.320
0.320
0.320
0.320
0.320
0.320
0.320
0.320
0.320
0.320
0.550
0.550
0.550
0.550
0.550
0.550
0.550
0.550
PU
(UNIT,
SET, M)
PS*
PG
Weight
per PU
approx.
kW
A
0.11 ... 0.16
0.14 ... 0.2
0.18 ... 0.25
0.22 ... 0.32
0.28 ... 0.4
0.35 ... 0.5
0.45 ... 0.63
0.55 ... 0.8
0.7 ... 1
0.9 ... 1.25
1.1 ... 1.6
1.4 ... 2
1.8 ... 2.5
2.2 ... 3.2
2.8 ... 4
3.5 ... 5
4.5 ... 6.3
5.5 ... 8
7 ... 10
9 ... 12
1.8 ... 2.5
2.2 ... 3.2
2.8 ... 4
3.5 ... 5
4.5 ... 6.3
5.5 ... 8
7 ... 10
9 ... 12.5
11 ... 16
14 ... 20
17 ... 22
20 ... 25
5.5 ... 8
7 ... 10
9 ... 12.5
11 ... 16
14 ... 20
18 ... 25
22 ... 32
28 ... 40
36 ... 45
40 ... 50
18 ... 25
22 ... 32
28 ... 40
36 ... 50
45 ... 63
57 ... 75
70 ... 90
80 ... 100
5)
Size S00
S00
0.04
0.06
0.06
0.09
0.09
0.12
0.18
0.18
3RU11 16-..B0
0.25
0.37
0.55
0.75
0.75
1.1
1.5
1.5
2.2
3
4
5.5
Size S0
S0
0.75
1.1
1.5
1.5
2.2
3
4
5.5
3RU11 26-..B0
7.5
7.5
11
11
S2
3
4
5.5
7.5
7.5
11
15
3RU11 36-..B0
18.5
22
22
S3
11
15
18.5
22
30
37
45
45
3RU11 46-..B0
1)
Size S2
Size S3
With the suitable terminal brackets
(see "Accessories", page 5/50),
the
3RU11 overload relays for direct mounting can also be installed as stand-
alone units.
Observe maximum rated operational current of the devices.
Guide value for 4-pole standard motors at AC 50 Hz 400 V. The actual
starting and rated data of the motor to be protected must be considered
when selecting the units.
2)
3)
Maximum protection by fuse for overload relay, type of coordination 2.
For fuse values in conjunction with contactors, see "Technical
specifications" --> "Short-circuit protection with fuses/motor starter pro-
tectors for motor feeders", see note on Technical Information on page 5/1.
For overload relays > 100 A, see 3RB2.
5)
* You can order this quantity or a multiple thereof.
Siemens LV 1 AO · 2011
5/47
5
© Siemens AG 2011
Overload Relays
SIRIUS 3RU1 Thermal Overload Relays
3RU11 for standard applications
3RU11 thermal overload relays with screw terminals on the auxiliary current side for stand-alone installation
1)
, CLASS 10
Features and technical specifications:
• Overload and phase failure protection
• Auxiliary contacts 1 NO + 1 NC
• Manual and automatic RESET
Size of Rating
con-
for induction
tactor
2)
motor
rated value
3)
Current setting
of the inverse-
time delayed
overload release
•
•
•
•
Short-circuit DT
protection
with fuse,
type of coor-
dination 2,
gL/gG opera-
tional class
4)
A
0.5
1
1
1.6
2
2
2
4
4
4
6
6
10
10
16
20
20
25
35
35
40
50
63
63
B
B
B
B
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
}
Switch position indicator
TEST function
STOP button
Integrated, sealable cover
Screw terminals
(on auxiliary current
side)
Order No.
Price
per PU
kg
3RU11 16-0AB1
3RU11 16-0BB1
3RU11 16-0CB1
3RU11 16-0DB1
3RU11 16-0EB1
3RU11 16-0FB1
3RU11 16-0GB1
3RU11 16-0HB1
3RU11 16-0JB1
3RU11 16-0KB1
3RU11 16-1AB1
3RU11 16-1BB1
3RU11 16-1CB1
3RU11 16-1DB1
3RU11 16-1EB1
3RU11 16-1FB1
3RU11 16-1GB1
3RU11 16-1HB1
3RU11 16-1JB1
3RU11 16-1KB1
3RU11 26-4AB1
3RU11 26-4BB1
3RU11 26-4CB1
3RU11 26-4DB1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.180
0.240
0.240
0.240
0.240
PU
(UNIT,
SET, M)
PS*
PG
Weight
per PU
approx.
kW
A
0.11 ... 0.16
0.14 ... 0.2
0.18 ... 0.25
0.22 ... 0.32
0.28 ... 0.4
0.35 ... 0.5
0.45 ... 0.63
0.55 ... 0.8
0.7 ... 1
0.9 ... 1.25
1.1 ... 1.6
1.4 ... 2
1.8 ... 2.5
2.2 ... 3.2
2.8 ... 4
3.5 ... 5
4.5 ... 6.3
5.5 ... 8
7 ... 10
9 ... 12
11 ... 16
14 ... 20
17 ... 22
20 ... 25
Size S00
S00
0.04
0.06
0.06
0.09
0.09
0.12
0.18
0.18
3RU11 16-0AB1
0.25
0.37
0.55
0.75
0.75
1.1
1.5
1.5
5
2.2
3
4
5.5
Size S0
S0
7.5
7.5
11
11
3RU11 16-4AB1
Size S2
S2
15
18.5
22
22
22 ... 32
28 ... 40
36 ... 45
40 ... 50
80
80
100
100
}
}
}
}
3RU11 36-4EB1
3RU11 36-4FB1
3RU11 36-4GB1
3RU11 36-4HB1
1
1
1
1
1 unit
1 unit
1 unit
1 unit
101
101
101
101
0.480
0.480
0.480
0.480
3RU11 16-4EB1
Size S3
S3
30
37
45
45
45 ... 63
57 ... 75
70 ... 90
80 ... 100
5)
125
160
160
200
}
}
}
}
3RU11 46-4JB1
3RU11 46-4KB1
3RU11 46-4LB1
3RU11 46-4MB1
1
1
1
1
1 unit
1 unit
1 unit
1 unit
101
101
101
101
0.810
0.810
0.810
0.810
3RU11 16-4JB1
1)
2)
3)
Sizes S00 to S3 for screw and snap-on mounting onto TH 35 standard
mounting rails, size S3 also for TH 75 standard mounting rails.
Observe maximum rated operational current of the devices.
Guide value for 4-pole standard motors at AC 50 Hz 400 V. The actual
starting and rated data of the motor to be protected must be considered
when selecting the units.
4)
Maximum protection by fuse for overload relay, type of coordination 2.
For fuse values in conjunction with contactors, see "Technical
specifications" --> "Short-circuit protection with fuses/motor starter pro-
tectors for motor feeders", see note on Technical Information on page 5/1.
For overload relays > 100 A, see 3RB2.
5)
* You can order this quantity or a multiple thereof.
5/48
Siemens LV 1 AO · 2011
© Siemens AG 2011
Overload Relays
SIRIUS 3RU1 Thermal Overload Relays
3RU11 for standard applications
3RU11 thermal overload relays with Cage Clamp terminals for direct mounting
1)
and stand-alone installation
2)
, CLASS 10
Features and technical specifications:
• Overload and phase failure protection
• Auxiliary contacts 1 NO + 1 NC
• Manual and automatic RESET
Size of Rating
con-
for induction
tactor
3)
motor
rated value
4)
Current setting
of the inverse-
time delayed
overload release
•
•
•
•
Short-circuit DT
protection
with fuse,
type of coor-
dination 2,
gL/gG opera-
tional class
5)
A
0.5
1
1
1.6
2
2
2
4
4
4
6
6
10
10
16
20
20
25
35
35
10
10
16
20
20
25
35
35
40
50
63
63
25
35
35
40
50
63
80
80
100
100
63
80
80
125
125
160
160
200
B
B
B
B
B
B
}
}
}
}
}
}
B
}
B
}
}
}
}
}
B
B
B
B
B
B
B
B
}
}
}
}
B
B
B
B
B
B
}
}
}
}
B
B
B
B
}
}
}
}
5)
Switch position indicator
TEST function
STOP button
Integrated, sealable cover
Cage Clamp
terminals
(on auxiliary current
side)
Order No.
Price
per PU
kg
3RU11 16-0AC1
3RU11 16-0BC1
3RU11 16-0CC1
3RU11 16-0DC1
3RU11 16-0EC1
3RU11 16-0FC1
3RU11 16-0GC1
3RU11 16-0HC1
3RU11 16-0JC1
3RU11 16-0KC1
3RU11 16-1AC1
3RU11 16-1BC1
3RU11 16-1CC1
3RU11 16-1DC1
3RU11 16-1EC1
3RU11 16-1FC1
3RU11 16-1GC1
3RU11 16-1HC1
3RU11 16-1JC1
3RU11 16-1KC1
3RU11 26-1CD0
3RU11 26-1DD0
3RU11 26-1ED0
3RU11 26-1FD0
3RU11 26-1GD0
3RU11 26-1HD0
3RU11 26-1JD0
3RU11 26-1KD0
3RU11 26-4AD0
3RU11 26-4BD0
3RU11 26-4CD0
3RU11 26-4DD0
3RU11 36-1HD0
3RU11 36-1JD0
3RU11 36-1KD0
3RU11 36-4AD0
3RU11 36-4BD0
3RU11 36-4DD0
3RU11 36-4ED0
3RU11 36-4FD0
3RU11 36-4GD0
3RU11 36-4HD0
3RU11 46-4DD0
3RU11 46-4ED0
3RU11 46-4FD0
3RU11 46-4HD0
3RU11 46-4JD0
3RU11 46-4KD0
3RU11 46-4LD0
3RU11 46-4MD0
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
1 unit
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
101
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.190
0.320
0.320
0.320
0.320
0.320
0.320
0.320
0.320
0.320
0.320
0.550
0.550
0.550
0.550
0.550
0.550
0.550
0.550
PU
(UNIT,
SET, M)
PS*
PG
Weight
per PU
approx.
kW
A
0.11 ... 0.16
0.14 ... 0.2
0.18 ... 0.25
0.22 ... 0.32
0.28 ... 0.4
0.35 ... 0.5
0.45 ... 0.63
0.55 ... 0.8
0.7 ... 1
0.9 ... 1.25
1.1 ... 1.6
1.4 ... 2
1.8 ... 2.5
2.2 ... 3.2
2.8 ... 4
3.5 ... 5
4.5 ... 6.3
5.5 ... 8
7 ... 10
9 ... 12
1.8 ... 2.5
2.2 ... 3.2
2.8 ... 4
3.5 ... 5
4.5 ... 6.3
5.5 ... 8
7 ... 10
9 ... 12.5
11 ... 16
14 ... 20
17 ... 22
20 ... 25
5.5 ... 8
7 ... 10
9 ... 12.5
11 ... 16
14 ... 20
18 ... 25
22 ... 32
28 ... 40
36 ... 45
40 ... 50
18 ... 25
22 ... 32
28 ... 40
36 ... 50
45 ... 63
57 ... 75
70 ... 90
80 ... 100
Size S00 for stand-alone
S00
installation
6)
0.04
0.06
0.06
0.09
0.09
0.12
0.18
0.18
0.25
0.37
0.55
0.75
0.75
1.1
1.5
1.5
2.2
3
4
5.5
3RU11 16-..C1
Size S0 for direct mounting
1)7)
S0
0.75
1.1
1.5
1.5
2.2
3
4
5.5
3RU11 16-..D0
7.5
7.5
11
11
S2
3
4
5.5
7.5
7.5
11
15
3RU11 36-..D0
18.5
22
22
S3
11
15
18.5
22
30
37
45
45
3RU11 46-..D0
1)
Size S2 for direct mounting
1)7)
Size S3 for direct mounting
1)7)
With the suitable terminal brackets
(see "Accessories", page 5/50),
the
3RU11 overload relays for direct mounting can also be installed as stand-
alone units.
Size S00 for screw and snap-on mounting onto TH 35 standard mounting
rail.
Observe maximum rated operational current of the devices.
Guide value for 4-pole standard motors at AC 50 Hz 400 V. The actual
starting and rated data of the motor to be protected must be considered
when selecting the units.
2)
3)
4)
Maximum protection by fuse for overload relay, type of coordination 2.
For fuse values in conjunction with contactors, see "Technical
specifications" --> "Short-circuit protection with fuses/motor starter pro-
tectors for motor feeders", see note on Technical Information on page 5/1.
Auxiliary and main conductor connections with Cage Clamp terminal.
Auxiliary conductor connections with Cage Clamp terminals and main con-
ductor connections with screw terminals.
6)
7)
* You can order this quantity or a multiple thereof.
Siemens LV 1 AO · 2011
5/49
5
© Siemens AG 2011
Overload Relays
SIRIUS 3RU1 Thermal Overload Relays
Accessories
■
Overview
The following optional accessories are available for the 3RU11
thermal overload relays:
• For the four overload relay sizes S00 to S3 one terminal
bracket each for stand-alone installation
• One mechanical RESET module for all sizes
• One cable release for resetting devices which are difficult to
access (for all sizes)
• One electrical remote RESET module in three voltage variants
for all sizes
• Terminal covers
■
Selection and ordering data
Version
Size
DT
Order No.
Price
per PU
PU
(UNIT,
SET, M)
PS*
PG
Weight
per PU
approx.
kg
Terminal brackets for stand-alone installation
For separate mounting of overload relays;
screw and snap-on mounting onto TH 35
standard mounting rail; size S3 also for
TH 75 standard mounting rail
S00
S0
S2
S3
}
}
}
}
3RU19 16-3AA01
3RU19 26-3AA01
3RU19 36-3AA01
3RU19 46-3AA01
1
1
1
1
1 unit
1 unit
1 unit
1 unit
101
101
101
101
0.060
0.080
0.180
0.280
3RU19 .6-3AA01
Mechanical RESET
1)
Resetting plungers, holders and formers
S00 ... S3
}
B
A
3RU19 00-1A
3SB30 00-0EA11
3SX1 335
1
1
1
1 unit
1 unit
1 unit
101
102
102
0.038
0.020
0.004
Pushbuttons with extended stroke
(12 mm), IP65, Ø 22 mm
Extension plungers
For compensation of the distance between
the pushbutton and the unlatching button of
the relay
3RU19 00-1A
with pushbutton and
extension plunger
5
Cable releases with holder for RESET
1)
For Ø 6.5 mm holes in the control panel;
max. control panel thickness 8 mm
• Length 400 mm
• Length 600 mm
S00 ... S3
}
}
3RU19 00-1B
3RU19 00-1C
1
1
1 unit
1 unit
101
101
0.063
0.073
3RU19 00-1.
Modules for remote RESET, electrical
Operating range
0.85 ... 1.1 x
U
s
,
power consumption
AC 80 VA, DC 70 W,
ON period
0.2 ... 4 s,
switching frequency
60/h
3RU19 00-2A.71
24 ... 30 V
110 ... 127 V
220 ... 250 V
S00 ... S3
}
}
}
3RU19 00-2AB71
3RU19 00-2AF71
3RU19 00-2AM71
1
1
1
1 unit
1 unit
1 unit
101
101
101
0.066
0.067
0.066
Terminal covers
1)
Covers for cable lugs and busbar con-
nections
• Length 55 mm
Covers for box terminals
• Length 20.6 mm
• Length 20.8 mm
S2
S3
}
}
3RT19 36-4EA2
3RT19 46-4EA2
1
1
1 unit
1 unit
101
101
0.020
0.025
S3
}
3RT19 46-4EA1
1
1 unit
101
0.040
For more accessories (screwdrivers and labeling plates), see
page 5/62.
1)
The accessories are identical to those of the 3RB2 solid-state overload
relays.
* You can order this quantity or a multiple thereof.
5/50
Siemens LV 1 AO · 2011