U36L SERIES
U36L
Series
Large Can
Screw Terminals
Longest Life
U36 Grade
High Ripple
350 to 500VDC
Ratings
RoHS Compliant
85 C
Maximum
Temperature
Engineering Bulletin Mar 07
The U36L series is the longest life version of the industry standard U36D specifically designed to
provide the ripple current capability and long life required for high reliability inverter applications. The
U36L has an endurance rating of 10,000 hours at 85 C with the rated ripple current applied. These
capacitors are available with a variety of high current English or Metric thread terminals. Mounting
options include a three-footed clamp or a bottom stud. Custom designs are available upon request.
L ARGE CAN 85 C
U36L
Summary of Specifications
Screw terminals: high and low post, English and Metric thread.
Capacitance range: 1,500 to 15,000µF.
Voltage range: 350 to 500VDC.
Category temperature range: 40 C to 85 C.
Leakage current: 0.02CV(µA) or 5mA, whichever is smaller, after 5 minutes at 25 C.
Standard capacitance tolerance: 20%
Nominal case size (D L): D = 50mm (2.000”) to 89mm (3.500”); L = 79mm (3.125”) to
220mm (8.625”).
Rated lifetime: 10,000 hours at 85 C with rated ripple current applied.
United Chemi-Con, Inc. 9801 W. Higgins Road, Rosemont, IL 60018 Tel 847-696-2000 Fax 847-696-9278 www.chemi-con.com
1/ 9
U36L Series
U36L Specifications - Screw Terminals
Item
Category Temperature Range
Rated Voltage Range
Capacitance Range
Capacitance Tolerance
Leakage Current
I
40 to
85 C
Characteristics
Engineering Bulletin Mar 07
350 to 500VDC
1,500 to 15,000 F at
20% ( M ) at
25 C, 120Hz
25 C, 120Hz
25 C.
0.02CV ( A ) or 5mA, whichever is smaller, after 5 minutes at
Where I = Max. leakage current ( A ), C = Nominal capacitance ( F ) and V = Rated voltage ( V )
Rated Ripple Current Multipliers
Ambient Temperature ( C )
45 C
2.82
65 C
1.73
85 C
1.00
Endurance
(Load Life)
The following specifications shall be satisfied when the capacitors are restored to 25 C after
subjecting them to DC voltage for 10,000 hours at 85 C with the rated ripple current applied.
The sum of the DC voltage and peak AC voltage must not exceed the full rated voltage of
the capacitors.
Capacitance change:
≤
20% from initial measurement
ESR change
:
≤
200% of initial specified limit
Leakage current
:
≤
initial specified limit
Shelf Life
The following specifications shall be satisfied when the capacitors are restored to 25 C after
exposing them for 500 hours at 85 C without voltage applied. The rated voltage shall be
applied to the capacitors for a minimum of 30 minutes, at least 24 hours and not more than
48 hours before the measurements.
Capacitance change:
≤
20% from initial measurement
ESR change
:
≤
200% of initial specified limit
Leakage current
:
≤
initial specified limit
Vibration Rating
Maximum Tightening Torque
10 -55Hz, 10g sinusoidal in three axis, 2 hours per axis.
Terminal
Code
HP
HL
CD
CP
CH
CA
CS
Thread
Size
10 - 32 NF- 2B
M5x0.8 - 6H
M5x0.8 - 6H
1
/
4
- 28
1
/ - 28
4
3 Threads Engaged
in
·
lb
18.0
18.0
18.0
35.0
35.0
35.0
35.0
N
·
m
2.0
2.0
2.0
4.0
4.0
4.0
4.0
6 Threads Engaged
in
·
lb
25.0
25.0
25.0
55.0
55.0
55.0
55.0
N
·
m
2.8
2.8
2.8
6.2
6.2
6.2
6.2
NF- 2B
NF- 2B
M6x1- 6H
M6x1- 6H
L ARGE CAN 85 C
Typical Inductance (nH)
at 1MHz
Terminal
Code
HP
HL
CD
CP
CH
CA
CS
Case Diameter
Ø
50
Ø
63.5
Ø
76
Ø
89
U36L
20
20
NA
NA
NA
NA
NA
22
22
18
14
16
14
16
25
25
22
18
20
18
20
NA
NA
NA
18
20
18
20
Custom Designs
Custom CV values per case size and termination type may be available upon request.
Contact appropriate representative with specific requirements.
2/9
United Chemi-Con, Inc. 9801 W. Higgins Road, Rosemont, IL 60018 Tel 847-696-2000 Fax 847-696-9278 www.chemi-con.com
U36L Series
Diagram of Dimensions - Screw Terminals
Large Can / Screw Terminals
Case Dimensions
Case Size
Code
CA5
CB7
CD0
CE3
D92
DA5
DB7
DD0
DE3
DN0
E79
E92
EA5
EB7
ED0
EE3
EJ0
EN0
F92
FA5
FB7
FD0
FE3
FF5
FK0
FN0
Ø
D
2.0 (0.080)
Engineering Bulletin Mar 07
Unit: mm (inches)
L
1.0 (0.040)
105 (4.125)
117 (4.625)
130 (5.125)
143 (5.625)
92 (3.625)
105 (4.125)
117 (4.625)
130 (5.125)
143 (5.625)
220 (8.625)
079
(3.125)
092
(3.625)
105 (4.125)
117 (4.625)
130 (5.125)
143 (5.625)
180 (7.125)
220 (8.625)
92 (3.625)
105 (4.125)
117 (4.625)
130 (5.125)
143 (5.625)
155 (6.125)
190 (7.500)
220 (8.625)
F
0.25 (0.010)
50.8 (2.000)
22.2 (0.875)
63.5 (2.500)
28.6 (1.125)
F
Vent
S
T
76.2 (3.000)
31.8 (1.250)
J
Insulating
Sleeve
L
H
89.0 (3.500)
31.8 (1.250)
Insulating
End Disk
D
Terminal Specifications
Terminal
Code
HP
HL
CD
CP
CH
CA
CS
Available Case Diameter
Ø
D
Ø
D
Code
C
C
D-E
D-F
D-F
D-F
D-F
mm (inches)
50.8 (2.000)
50.8 (2.000)
63.5 – 76.2 (2.500 – 3.000)
63.5 – 89.0 (2.500 – 3.500)
63.5 – 89.0 (2.500 – 3.500)
63.5 – 89.0 (2.500 – 3.500)
63.5 – 89.0 (2.500 – 3.500)
Thread
Size
10 - 32 NF- 2B
M5x0.8 - 6H
M5x0.8 - 6H
1
/
4
- 28 NF- 2B
1
/ - 28 NF- 2B
4
M6x1- 6H
M6x1- 6H
Minimum
Thread
Depth
09.5
(0.375)
09.5
(0.375)
08.5
(0.335)
08.7
(0.344)
11.9 (0.468)
08.7
(0.344)
11.9 (0.468)
J
0.5 (0.020)
6.4 (0.250)
6.4 (0.250)
5.0 (0.200)
2.4 (0.093)
6.4 (0.250)
2.4 (0.093)
6.4 (0.250)
H
2.0 (0.080)
L
L
L
L
L
L
L
J
J
J
J
J
J
J
Ø
S
0.25 (0.010)
Ø
T
0.25 (0.010)
08.0
(0.313)
8.0 (0.313)
13.0 (0.512)
17.5 (0.689)
17.5 (0.689)
17.5 (0.689)
17.5 (0.689)
11.1 (0.438)
11.1 (0.438)
18.8 (0.740)
—
—
—
—
L ARGE CAN 85 C
U36L
United Chemi-Con, Inc. 9801 W. Higgins Road, Rosemont, IL 60018 Tel 847-696-2000 Fax 847-696-9278 www.chemi-con.com
3/9
U36L Series
Mounting Hardware - Screw Terminals
Type C: Three-Footed Clamp
360
3
Engineering Bulletin Mar 07
Unit: mm (inches)
30
45
D
5
15
A
T
J
G
K
5.1 0.5 (2 holes)
(0.201 0.020)
R
S
B
Clamp: Zinc with silver trivalent
chromate post treatment.
Hardware: Screw, washer and hexagon
nut included with each clamp.
Type C: Clamp Dimensions
Mounting
Code
C
C
C
C
Case
Ø
D
50.8 (2.000)
63.5 (2.500)
76.2 (3.000)
89.0 (3.500)
A
1.0 (0.040)
31.8 (1.250)
38.1 (1.500)
44.5 (1.750)
50.8 (2.000)
B
1.0 (0.040)
36.5 (1.437)
42.9 (1.689)
49.2 (1.937)
56.5 (2.224)
G
1.0 (0.040)
13.3 (0.524)
13.3 (0.524)
13.3 (0.524)
16.0 (0.630)
J
0.5 (0.020)
4.5 (0.177)
4.5 (0.177)
4.5 (0.177)
4.5 (0.177)
K
0.5 (0.020)
7.1 (0.280)
7.1 (0.280)
7.1 (0.280)
8.0 (0.313)
R
1.0 (0.040)
19.1 (0.751)
19.1 (0.751)
19.1 (0.751)
21.0 (0.827)
S
1.0 (0.040)
9.5 (0.374)
9.5 (0.374)
9.5 (0.374)
9.0 (0.354)
T
0.5 (0.020)
0.8 (0.032)
0.8 (0.032)
1.0 (0.040)
1.0 (0.040)
Note: Type B two-footed clamp available upon request for
Ø
50.8,
Ø
63.5 and
Ø
76.2. Consult UCC for specifications.
Type S: Stud Mounting
L ARGE CAN 85 C
U36L
Q
M
P
K
T
D
N
R
Type S: Stud Mounting Dimensions
Mounting
Code
S
P
1.0 (0.040)
16.0 (0.630)
T
Thread Size
M12
M
1.0 (0.040)
19.0 (0.748)
N
1.0 (0.040)
18.0 (0.709)
Ø
K
2.0 (0.080)
Ø
Q
1.0 (0.040)
R
1.0 (0.040)
1.40 (0.055)
30.0 (1.181)
22.0 (0.866)
4/9
United Chemi-Con, Inc. 9801 W. Higgins Road, Rosemont, IL 60018 Tel 847-696-2000 Fax 847-696-9278 www.chemi-con.com
U36L Series
Part Numbering System for U36L Series
18 Fields
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17 18
Engineering Bulletin Mar 07
When ordering, always specify complete 18-field global part number.
E 3 6 L 4 0 1 C P S 3 3 2 M E A 5 M
9
8
7
6
Supplement Code.
Field 18.
C = PET insulation with end disk.
F = Coated can.
M = Pb-free PVC insulation with end disk.
Case Size.
Fields 15, 16 and 17.
The single letter diameter code is inserted in field 15.
C =
Ø
50.8mm (
Ø
2.000”)
D =
Ø
63.5mm (
Ø
2.500”)
E =
Ø
76.2mm (
Ø
3.000”)
F =
Ø
89mm (
Ø
3.500”)
The double character length code is inserted in fields 16 and 17.
For lengths
≤
99mm, insert the actual length rounded to nearest
millimeter. For lengths of 100mm or more, insert the appropriate
alpha numeric code as indicated below.
79 = 79mm (3.125”)
92 = 92mm (3.625”)
A5 = 105mm (4.125”)
B7 = 117mm (4.625”)
D0 = 130mm (5.125”)
E3 = 143mm (5.625”)
F5 = 155mm (6.125”)
J0 = 180mm (7.125”)
K0 = 190mm (7.500”)
N0= 220mm (8.625”)
Capacitance Tolerance.
Field 14.
M = 20%
Capacitance.
Fields 11, 12 and 13.
Expressed in Microfarads. The first two digits are significant
figures inserted in fields 11 and 12, and the third digit inserted
in field 13 indicates the number of zeros for capacitance of
10 F or more. R indicates the decimal point for capacitance
less than 10 F (e.g. 3R3 = 3.3 F; 330 = 33 F; 331 = 330 F;
332 = 3,300 F; 333 = 33,000 F ).
Mounting Hardware.
Field 10.
N = None.
B = Two-footed clamp.
C = Three-footed clamp.
S = Stud mount.
Terminal Type.
Fields 8 and 9.
HP = High post 10-32 NF- 2B screw thread.
HL = High post M5x0.8 screw thread.
CD = UTE M5x0.8 screw thread.
CP = Low post
1
/
4
-28 NF-2B screw thread.
CH = High post
1
/
4
-28 NF-2B screw thread.
CA = Low post M6x1 screw thread.
CS = High post M6x1 screw thread.
DC Rated Voltage.
Fields 5, 6 and 7.
Expressed in Volts. The first two digits are significant figures
inserted in fields 5 and 6, and the third digit inserted in field 7
indicates the number of zeros for rated voltage of 10VDC or
more. R indicates the decimal point for rated voltage less than
10VDC (e.g. 4R0 = 4.0VDC; 400 = 40VDC; 401 = 400VDC).
Series Name.
Fields 2, 3 and 4.
Enter the 3-letter/digit series name in fields 2, 3 and 4. If the
series name is only 2 letters/digits, place a dash in field 4.
For a series name with more than 3 letters/digits, refer to the
individual series for the appropriate 3-field series name.
Capacitor Type.
Field 1.
Aluminum Electrolytic Capacitor (Polar).
5
4
L ARGE CAN 85 C
U36L
3
2
1
United Chemi-Con, Inc. 9801 W. Higgins Road, Rosemont, IL 60018 Tel 847-696-2000 Fax 847-696-9278 www.chemi-con.com
5/9