Data sheet
5SJ4216-8HG41
CIRCUIT BREAKER 240V 14KA, 2-POLE, D, 16A,
D=70MM ACC. TO UL 489
General technical data
Number of poles
Number of poles / Note
Tripping characteristic class
Installation environment regarding EMC
circuit-breaker / Design
Mechanical service life (switching cycles) / typical
Equipment marking / acc. to DIN 40719 extended
according to IEC 204-2 / acc. to IEC 750
Overvoltage category
2
2P
D
Suitable for environment B (immunity to interference
not applicable)
5SJ4
20 000
F
3
Voltage
Type of voltage
Insulation voltage / at AC / rated value
V
AC/DC
440
Supply voltage
Supply voltage / at AC / rated value
Supply voltage frequency / rated value
V
Hz
400
50
Protection class
5SJ4216-8HG41
Page 1/4
01.12.2015
Changes preserved
© Copyright Siemens AG
Protection class IP
IP20, with connected conductors, IP 40 in the handle
range
Switching capacity
Switching capacity current
● acc. to EN 60898 / rated value
● acc. to IEC 60947-2 / rated value
kA
kA
10
15
Dissipation
Power loss [W]
● for rated value of the current / at AC / in hot
operating state / per pole
W
2
Electricity
rated current In / IEC, DIN/VDE / at 40 Cel
Current / at AC / rated value
A
A
16
16
Main circuit
Operating voltage
● minimum
● at AC / acc. to UL 489 and CSA C22.2 No. 5-02
/ maximum
● at DC / 1-channel / acc. to UL 489 and CSA
C22.2 No. 5-02 / maximum
● at DC / 2-channel / acc. to UL 489 and CSA
C22.2 No. 5-02 / maximum
● at DC / rated value / maximum
V
V
V
V
V
24
240
60
125
60
Product details
Product feature / Touch protection
Product component
● Tunnel terminals top
● Tunnel terminals bottom
● combined terminal top
● combined terminal bottom
Product feature
● halogen-free
● sealable
● silicon-free
Product expansion / can be installed / supplementary
devices
Yes
Yes
Yes
Yes
No
No
Yes
Yes
Yes
Product function
Product function
● Note
● neutral conductor switching
Terminal tightening torque for Cu, 60/75°C;
3.5Nm/31lb.in
No
5SJ4216-8HG41
Page 2/4
01.12.2015
Changes preserved
© Copyright Siemens AG
Short circuit
Breaking capacity short-circuit current (Icn) / at AC /
acc. to UL 1077 and CSA C22.2 No.235
kA
14
Number
Number of test cycles / for environmental testing /
acc. to IEC 60068-2-30
6
Connections
Connectable conductor cross-section / finely
stranded / with core end processing
● minimum
● maximum
Position / of power supply cord
mm²
mm²
0.75
25
Any
Mechanical Design
Height
Width
Depth
Mounting position
Installation depth
Number of width units
Mounting type
mm
mm
mm
mm
90
36
70
any
70
2
on standard mounting rail
Environmental conditions
Degree of pollution
Influence of the surrounding temperature
Vibration resistance
Vibration resistance / acc. to IEC 60068-2-6
Ambient temperature
● minimum
● maximum
● during storage / minimum
● during storage / maximum
°C
°C
°C
°C
-25
55
-40
75
3
max. 95% humidity
50 m/s² at 25 to 150Hz and 60m/s² at 35Hz (4sec)
50 m/s² at 25 to 150Hz and 60m/s² at 35Hz (4sec)
Certificates
Equipment marking
● acc. to DIN EN 61346-2
● acc. to DIN EN 81346-2
F
F
General Product Approval
Declaration of
Conformity
Test
Certificates
sonstig
5SJ4216-8HG41
Page 3/4
01.12.2015
Changes preserved
© Copyright Siemens AG
Further information
Information- and Downloadcenter (Catalogs, Brochures,…)
http://www.siemens.com/lowvoltage/catalogs
Industry Mall (Online ordering system)
https://eb.automation.siemens.com/mall/en/WW/Catalog/Product/5SJ42168HG41
Service&Support (Manuals, Certificates, Characteristics, FAQs,...)
http://support.automation.siemens.com/WW/view/en/5SJ42168HG41/all
Image database (product images, 2D dimension drawings, 3D models, device circuit diagrams, ...)
http://www.automation.siemens.com/bilddb/cax_en.aspx?mlfb=5SJ42168HG41
CAx-Online-Generator
http://www.siemens.com/cax
Tender specifications
http://ausschreibungstexte.siemens.com/tiplv
35,2
6,2
70,2
108,8
last modified:
27.11.2015
5SJ4216-8HG41
Page 4/4
01.12.2015
Changes preserved