WESTCODE
An
IXYS Company
German Standard DIN 110 690V
Date:- 18 Mar, 2005
Data Sheet Issue:- 1
Ultra Rapid
Semiconductor Protection Fuse
European Square Body Fuses
German Standard DIN 110 Blade Contact
Voltage Ratings 600V to 690V
Current Ratings 63A to 1600A
Sizes 0, 1, 2, 3
Key Features:
Extremely high interrupting rating fuses for the protection of power semiconductors in accordance
with IEC Standard 60269.1 and 4.
Exceptionally low I
2
t, power losses
Highly reliable low voltage trip indicator system which conforms to UL, IEC, DIN and VDE standards
Non Magnetic construction
Increased technical performance gives higher ratings and a reduction in volume and weight
Microswitch system reference : MS 3V 1-5
Fuse holder types : SI DIN80 630A or SI DIN80 1250A
Data Sheet: 069URxDxxxxB Issue 1
Page 1 of 8
March, 2005
WESTCODE
An
IXYS Company
German Standard DIN 110 690V
Main Characteristics:
Current
rating
I
N
(A)
63
80
100
125
160
200
250
315
350
400
450
500
-
550
Pre-arcing
I
2
t @ 1 ms
I
2
t
p
(kA
2
s)
0.2
0.33
0.47
0.85
1.6
3.
5.8
12
15.5
23
26
41
52
Tested
Interrupting
rating
Size
Voltage
Ref:
069UR0D0063B
069UR0D0080B
069UR0D0100B
069UR0D0125B
Total Clearing
I
2
t @ U
N
(kA
2
s)
1.1
1.8
2.50
4.50
8.5
15.5
30
62
80
120
150
240
300
Watt Losses
0.8I
N
I
N
7.5
9.5
13.0
15.0
18.5
21.5
25
22.5
30
32.5
44
44
45
14
19
26
30
37
43
50
55
60
65
88
88
90
690V
0
069UR0D0160B
069UR0D0200B
069UR0D0250B
069UR0D0315B
069UR0D0350B
069UR0D0400B
200kA @690V
690V
+6%
069UR0D0450B
069UR0D0500B
069UR0D0550B
Notes: Minimum operating voltage for integrated trip indicator = 20V
Microswitch Reference : MS 3V 1-5
Size
Voltage
Ref:
069UR1D0160B
069UR1D0200B
069UR1D0315B
069UR1D0315B
069UR1D0350B
Current
rating
I
N
(A)
160
200
250
315
350
400
450
500
550
630
700
Pre-arcing
I
2
t @ 1 ms
I
2
t
p
(kA
2
s)
1.3
2.6
4.7
7.5
10.5
19
26.5
37
52
75
95
Total Clearing
I
2
t @ U
N
(kA
2
s)
7
13.5
25
40
55
100
140
195
280
390
490
Watt Losses
0.8I
N
I
N
27.5
22.5
25.5
32.5
33.5
34
35
36
37.5
42.5
42.5
35
45
52
65
67
68
70
72
75
85
95
Tested
Interrupting
rating
1
690V
069UR1D0400B
069UR1D0450B
069UR1D0500B
069UR1D0550B
069UR1D0630B
069UR1D0700B
200kA @690V
Notes: Minimum operating voltage for integrated trip indicator = 20V
Microswitch Reference : MS 3V 1-5
Data Sheet: 069URxDxxxxB Issue 1
Page 2 of 8
March, 2005
WESTCODE
An
IXYS Company
German Standard DIN 110 690V
Size
Voltage
Ref:
069UR2D0400B
069UR2D0450B
069UR2D0500B
Current
rating
I
N
(A)
400
450
500
550
630
700
800
900
1000
-
1100
Pre-arcing
I
2
t @ 1 ms
I
2
t
p
(kA
2
s)
15
20
28
37
54
76
115
170
240
270
Total Clearing
I
2
t @ U
N
(kA
2
s)
80
115
145
195
280
400
600
900
1250
1450
Watt Losses
0.8I
N
I
N
32.5
40
45
47.5
52.5
55
60
62.5
67.5
82.5
75
80
90
95
105
110
120
125
135
165
Tested
Interrupting
rating
690V
2
069UR2D0550B
069UR2D0630B
069UR2D0700B
069UR2D0800B
200kA @660V
690V
+6%
600V
069UR2D0900B
069UR2D1000B
060UR2D1100B
200kA @600V
Notes: Minimum operating voltage for integrated trip indicator = 20V
Microswitch Reference : MS 3V 1-5
Size
Voltage
Ref:
069UR3D0500B
069UR3D0550B
069UR3D0630B
Current
rating
I
N
(A)
500
550
630
700
800
900
1000
1100
1250
1400
-
1600
Pre-arcing
I
2
t @ 1 ms
I
2
t
p
(kA
2
s)
19
27
40
55
95
135
170
240
350
480
555
Total Clearing
I
2
t @ U
N
(kA
2
s)
100
140
210
300
490
700
900
1260
1850
2500
3300
Watt Losses
0.8I
N
I
N
52.5
55
60
62.5
65
67.5
77.5
80
90
100
120
105
110
120
125
130
135
155
160
180
200
240
Tested
Interrupting
rating
690V
3
069UR3D0700B
069UR3D0800B
069UR3D0900B
069UR3D1000B
069UR3D1100B
200kA @660V
170kA @700V
690V
+6%
600V
069UR3D1250B
069UR3D1400B
060UR3D1600B
Notes: Minimum operating voltage for integrated trip indicator = 20V
Microswitch Reference : MS 3V 1-5
Electrical Characteristics:
Times vs current characteristics
The following curves indicate the pre-arcing time for each rated current as a function of RMS value of
pre-arcing current I:
-
Tolerances on this current ± 8%
-
Beyond 30 sec or 10 sec, small overloads must be eliminated by another device.
-
Curve CC’ represents the maximum times taken by the associated device to clear small overloads; only its
horizontal line is represented.
Its oblique line must be plotted according to sketch in top right corner:
-
The intersection of the fuse and CC’ curves indicates the minimum breaking current I
pm
of the fuse.
Page 3 of 8
March, 2005
Data Sheet: 069URxDxxxxB Issue 1
WESTCODE
An
IXYS Company
German Standard DIN 110 690V
Times vs current characteristics
Size 0
Size 1
Size 2
Size 3
Data Sheet: 069URxDxxxxB Issue 1
Page 4 of 8
March, 2005
WESTCODE
An
IXYS Company
German Standard DIN 110 690V
Total clearing I²T:
The horizontal curves given belowindicated the maximum values of total operating I
2
t (I
2
t
t
) as a function
of prospective current Ip @ 660V, cosϕ = 0.15. Oblique lines indicate the corresponding total operating
time T
t
, with pre-arcing time in brackets.
Size 0
Size 1
Size 2
Size 3
Data Sheet: 069URxDxxxxB Issue 1
Page 5 of 8
March, 2005