PSR-SCP- 24DC/URD3/4X1/2X2
PSR-SPP- 24DC/URD3/4X1/2X2
Safety Relay as a Contact Extension Block
With Off-Delay Contacts
INTERFACE
Data Sheet
Description
The
PSR-...- 24DC/URD3/4X1/2X2
safety relay can be
used as a contact extension block in safety circuits
according to DIN EN 60204-1/VDE 0113-1.
The device has an interface for the T-BUS DIN rail
connector. This interface can be used for single-channel
control and monitoring. Alternatively, the device can also be
operated in single-channel mode via a contact on the basic
device.
Depending on the external wiring, the maximum safety
category that can be achieved is safety category 3
according to EN 954-1.
The relay has four enable current paths, one signaling
current path, and one confirmation path. Depending on the
time set, the contacts drop with a 0.5 ... 38 second delay
according to stop category 1 (DIN EN 60204-1/VDE 0113-1).
The extension unit can be used as a contact multiplier for
emergency stop relays and two-hand controls.
© PHOENIX CONTACT - 05/2006
Observe the safety instructions on page 4.
Make sure you always use the latest documentation.
It can be downloaded at
www.download.phoenixcontact.com.
A conversion table is available on the Internet at
http://www.download.phoenixcontact.com/general/7000_en_00.pdf.
This data sheet is valid for all products listed on the following page:
102857_01_en
PHOENIX CONTACT GmbH & Co. KG • 32823 Blomberg • Germany
Phone: +49 - 52 35 - 30 0 • Fax: +49 - 52 35 - 34 12 00 • www.phoenixcontact.com
www.phoenixcontact.com/salesnetwork
1
PSR-...- 24DC/URD3/4X1/2X2
Ordering Data
Safety Relays
Description
Safety relay as a contact extension block with off-delay contacts, with screw
connection
Type
PSR-SCP- 24DC/URD3/4X1/2X2
Order No.
2981512
2981525
Pcs./Pkt.
1
1
Safety relay as a contact extension block with off-delay contacts, with spring- PSR-SPP- 24DC/URD3/4X1/2X2
cage connection
Accessories
Description
DIN rail connector, yellow, for PSR applications
Dummy plug
Type
PSR-TBUS
PSR-TBUS-TP
Order No.
2890425
2981716
Pcs./Pkt.
50
50
Documentation
Description
Application manual for PSR safety relays
Type
Order No.
Pcs./Pkt.
1
UM EN SAFETY RELAY APPLICATION 2888712
Technical Data
Input Data
Nominal input voltage U
N
Permissible range
Typical current consumption at U
N
Typical response time (K1, K2)
Release time (K1, K2)
BG approval up to a maximum of
Surge protection
Status indicators (K1, K2)
24 V DC
0.85 - 1.1 x U
N
94 mA
20 ms
0.5 ... 38 seconds (±20%)
30 seconds
Suppressor diode
Green LED
Output Data
Contact type: Positively driven contact assembly Class A according to
EN 50205
Contact material
Maximum switching voltage
Minimum switching voltage
Limiting continuous current
N/O contact
N/C contact (65-66)
I
TH2
= I
12
+ I
22
+ ... I
N2
Maximum inrush current
N/O contact
N/C contact (65-66)
Minimum switching current
Maximum shutdown power
1
4 enable current paths, 1 signaling current path, 1 confirmation path
Silver tin oxide (AgSnO
2
)
250 V AC/DC
15 V AC/DC
6A
3A
72 A
2
6A
3A
25 mA
Ohmic load
τ
= 0 ms
Inductive load
τ
= 40 ms
48 W
40 W
35 W
33 W
1
24 V DC 144 W (72 W)
1
48 V DC 288 W (144 W)
1
110 V DC 77 W
220 V DC 88 W
250 V AC 1500 VA (750 VA)
Minimum switching power
0.4 W
102857_01_en
PHOENIX CONTACT
2
PSR-...- 24DC/URD3/4X1/2X2
Output Data (Continued)
Mechanical service life
Switching capacity according to DIN EN 60947-5-1/VDE 0660-200
10
7
cycles, approximately
Cycles
360/h:
3600/h:
Short-circuit protection of the output circuits, external
Enable current paths
Signaling current path
1
DC13
24 V:
230 V:
24 V:
230 V:
6A
–
3A
–
AC15
–
5A
–
3A
NEOZED 10 A gL/gG
NEOZED 4 A gL/gG
The maximum values given in brackets apply to N/C contacts 65-66.
General Data
Permissible ambient operating temperature
Nominal operating mode
Degree of protection according to VDE 0470-1
Housing
Connection terminal blocks
Installation location
Mounting position
Air and creepage distances between circuits
Basic insulation
Impulse voltage withstand level
Pollution degree
Surge voltage category
Dimensions (W x H x D)
PSR-SCP- 24DC/URD3/4X1/2X2
PSR-SPP- 24DC/URD3/4X1/2X2
Conductor cross section
PSR-SCP- 24DC/URD3/4X1/2X2
PSR-SPP- 24DC/URD3/4X1/2X2
Housing material
1
-20°C to +55°C
100% operating factor
IP20
IP20
IP54, minimum
Any
According to DIN EN 50178:1998-04
1
4 kV
1
2
III
22.5 mm x 99 mm x 114.5 mm
22.5 mm x 112 mm x 114.5 mm
0.2 mm
2
... 2.5 mm
2
0.2 mm
2
... 1.5 mm
2
Polyamide PA, not reinforced
Safe isolation, reinforced insulation, and 6 kV between the input circuit/N/C contacts and the enable contact current paths.
Tests/Approvals
BG/GS
UL
applied for
102857_01_en
PHOENIX CONTACT
3
PSR-...- 24DC/URD3/4X1/2X2
Safety Instructions
–
–
–
During operation, parts of electrical switching devices carry hazardous voltages.
Before working on the device, disconnect the power.
Please observe the safety regulations of electrical engineering and industrial safety and liability
associations.
Disregarding these safety regulations may result in death, serious personal injury or damage to
equipment.
Startup, assembly, modifications, and upgrades may only be carried out by a skilled electrical
engineer.
For emergency stop applications, the machine must be prevented from restarting automatically by
a higher-level control system.
Protective covers must not be removed when operating electrical switching devices.
In the event of an error, replace the device immediately.
Repairs, especially if the housing must be opened, may only be carried out by the manufacturer or
authorized persons. Otherwise the warranty is invalidated.
–
–
–
–
–
When operating relay modules the operator must meet the requirements for noise emission for electrical and
electronic equipment (EN 61000-6-4) on the contact side and, if required, take appropriate measures.
102857_01_en
PHOENIX CONTACT
4
PSR-...- 24DC/URD3/4X1/2X2
Structure
6
5
2
7
1
A
7
8
9
2
8
4
0
4
3
7
6
5
7
8
9
1
A
7
2
1
A
4
0
66
28
37
38
2
A
65
4
R
PS
-U
K
2
2
A
8
2
A
7
3
RD
3
o
P
r
,
e
01
w
3
5
3
5
6
6
6
8
R
PS
K
-U
RD
3
w
o
P
r
,
e
01
3
5
6
6
6
8
27
1
K
2
4
7
5
2
K
50
1 0
2 0
3
(t
)
)
1
2
K
(t
3
50
1 0
2 0
3
(t
)
K
1
K
2
1
Y
4
8
7
5
5
8
1
6
5
1
(t
)
3
K
1
K
2
1
Y
8
4
5
7
1
6
1
5
5
7
4
K1
8
/
K
APPROVAL
1
2 Y1
K
2
APPROVAL
16
Y
1
15
16
15
PSR-SCP- 24DC/URD3/4X1/2X2
Order No.: 29 81 51 2
PSR-SPP- 24DC/URD3/4X1/2X2
Order No.: 29 81 52 5
47
47
48
48
57
58
23
57
24
58
Serial No.
Serial No.
15 27 37 47 57 65
15 27 37 47 57 65
PSR-SCP- 24DC/URD3/4X1/2X2
Figure 1
1
2
3
4
5
6
7
8
9
10
Structure
Metal lock for mounting on the DIN rail
Plug-in COMBICON screw terminal blocks
Plug-in COMBICON spring-cage terminal blocks
27-28, 37-38, 47-48, and 57-58: Enable current paths
K1, K2: Input
Y1: Connection to the DIN rail connector
15-16: Confirmation contacts
Off delay setting
A1, A2: Supply voltage connection
65-66: Alarm contacts
K1
/K2
T-BUS
Y1
T-BUS
15
T-BUS
27
37
57
58
K1
POWER
)
)
K2
A1
T-BUS
A2
T-BUS
16
T-BUS
28
38
48
47
Figure 2
Block diagram
66
65
16 28 38 48 58 66
16 28 38 48 58 66
1
1
PSR-SPP- 24DC/URD3/4X1/2X2
Block Diagram
102857_01_en
PHOENIX CONTACT