Class of Operation gL/gG, 690V ac 440V dc 6 to 630 Amps
Sizes 00 to 3
Technical Data:
Rated Voltage:
Rated Breaking Capacity:
Approvals: IEC269,VDE 0636
Description:
A square bodied range of industrial fuse links
Rated Frequency:
for wide variety of applications where 690V is needed.
Operating Frequency:
Packaging:
All fuse links are packed in 3’s.
Selectivity:
Standards:
DIN43620 Part 1
Ordering Code:
Rating/Type/Body Size/Category
Design - Insulator:
e.g. 100NH2G-690
- Metal Parts:
Contact Blades:
Protection Type:
Dimensions:
Tests:
Constancy of
Characteristics:
On/Off Indicator:
Mechanical Stress:
Catalog Symbol: NH_G-690
NH
690V ac / 440V dc
50kA
50 Hz
45 - 62 Hz
1 : 1.6 up to 690V ac
1 : 1.25 up to 380V ac
Ceramic
Corrosion-proof (top plate also
galvanic plated)
Full contact blades,
silver plated copper.
IP 00 according to DIN40050
DIN 43620
VDE 0636/21 (RS 5126-75)
Resistant to ageing.
Spring indicator, minimum
operating voltage 10V
Vibrations 7 up to 50 Hz
with 1 g, shocks with 5 g
Specifications (Dimensions all in mm)
SIZE
C00
00
0
1(small)
1
2
3
4a
A
49 ± 1.5
49 ± 1.5
68 ±
+1.5
–3.0
68 ± 2.5
68 ± 2.5
68 ± 2.5
68 ± 2.5
90 ± 30
B
78.5 ± 1.5
78.5 ± 1.5
125 ± 1.5
135 ± 2.5
135 ± 2.5
150 ± 2.5
150 ± 2.5
200 ± 3.0
C min.
15
15
15
15
20
25
32
50
D
21
30
30
30
41
51
72
100
E ± 0.8 F max.
35
35
35
40
40
48
60
85
41
48
48
48
53
61
76
85
G
60 ± 2.0
60 ± 2.0
60 ± 2.0
60 ± 2.0
60 ± 2.0
60 ± 2.0
60 ± 2.0
60 ± 2.0
5-2-00
SB99216
Rev. A
Form No. NH
Page 1of 4
BIF Doc# 9003
Bussmann
®
HRC Fuse Links
Class of Operation gL/gG, 690V ac 440V dc 6 to 630 Amps
Sizes 00 to 3
NH
Technical Data
Size
Rated operational current l
e
Rated uninterupted current with
connecting knives l
u
Rated operational voltage Ul
e
AC
Rated insulating voltage U
i
AC
Insulating class
Rated frequency
Protection catagory
Rated inpulse withstand voltage
UtilisationCatagory:
AC23B / 380V, cos
j
=0.35
AC22B / 500V, cos
j
=0.65
AC21B / 660V, cos
j
=0.95
AC23B / 660V, cos
j
=0.35*
Dynamic short-circuit strength
with fuse links according to VDE
0636 Part 21
Rated short time withstand
current l
cw
(with connecting
knives) (1s)
Power disipation of the fuse links
Standard terminal
For bus bars with max. width
For cable lug: with 1 cable lug
with 2 cable lugs
Ambient air temperature
120kA
120kA
120kA
120kA
00
160A
200A
690V
1000V
C
45-62 Hz
IP20
12kV
1280/960A
480A
240A
-
250A
400A
690V
1000V
C
45-62 Hz
IP20
12kV
2000/1500A
750A
375A
2000/1500A*
1
400A
630A
690V
1000V
C
45-62 Hz
IP20
12kV
3200/2400A
1200A
600A
3200/2400A*
2
3
630A
1000A
690V
1000V
C
45-62 Hz
IP20
12kV
5040/3780A
1890A
945A
5040/3780*
>3.0kA
12W
M8
20mm
2.5-70mm
2
-
-25 to +55 deg
>10kA
23W
M10
30mm
6-150mm
2
70-150mm
2
-25 to +55 deg
>20kA
34W
M10
40mm
6-240mm
2
150-240mm
2
-25 to +55 deg
>20kA
48W
M12
50mm
10-240mm
2
150-240mm
2
-25 to +55 deg
*designed with arc chambers and break roller.
5-2-00
SB99216
Rev. A
Form No. NH
Page 2 of 4
BIF Doc# 9003
Bussmann
®
HRC Fuse Links
Class of Operation gL/gG 690V ac 440V dc 6 to 630 Amps
Sizes 00 to 3
Time Current Characteristics for Size 00
Time Current Characteristics for Size 1
NH
Size 00 Details:
Approvals:
Rated Currents:
Weight:
Catalog
1
Number
VDE, ÖVE, KEMA, IEC, SEV
6, 10, 16, 20, 25, 32, 35, 40, 50, 63,
80, 100, 125, and 160 A
0.16 kg.
Total at
690V
Nom.
Watts Rated
Loss Voltage
Size 1 Details:
Approvals:
Rated Currents:
Weight:
Catalog
1
Number
Amp
Ratings
VDE, ÖVE, KEMA, IEC, SEV
40, 50, 63, 80, 100,125,160, 200,
224, 250 Amps
0.38 kg.
I
2
t (Ampere
2
Seconds)
Pre-
Total at
Total at
Arcing
380V
500V
Total at
690V
Nom.
Watts Rated
Loss Voltage
I
1
t (Ampere
1
Seconds)
Amp
Pre-
Total at Total at
Ratings Arcing
380V
500V
6NH00G-690
10NH00G-690
16NH00G-690
20NH00G-690
25NH00G-690
32NH00G-690
35NH00G-690
40NH00G-690
50NH00G-690
63NH00G-690
80NH00G-690
100NH00G-690
125NH00G-690
160NH00G-690
6
33
100
10
75
180
16
350
830
20
780
1,800
25
1,450
3,400
32
2,400
5,700
35
3,600
8,500
40
5,000 11,500
50
8,000 18,500
63 13,000 31,000
80 18,200 43,000
100 26,800 63,500
125 40,500 96,000
160 78,000 178,000
210
405
1,900
4,200
7,800
12,800
19,300
26,300
43,000
72,000
100,000
140,000
215,000
410,000
450 1.3
705 1.6
3,250 2.0
7,200 2.1
12,500 2.4
21,000 3.7
31,500 3.8
44,000 4.7
69,100 6.3
113,000 7.8
160,000 8.5
230,000 9.4
350,000 12.6
650,000 17.7
690
ac
40NH1G-690
50NH1G-690
63NH1G-690
80NH1G-690
100NH1G-690
125NH1G-690
160NH1G-690
200NH1G-690
224NH1G-690
250NH1G-690
40
50
63
80
100
125
160
200
224
250
5,000
8,000
13,000
18,200
26,800
40,500
76,500
120,500
160,500
197,000
11,500
26,300
44,000 4.7
18,500
43,000
69,100 6.3
31,000
72,000 113,000 7.8
43,000 100,000 160,000 8.5
63,500 140,000 230,000 9.4
96,000 215,000 350,000 12.6
178,000 410,000 650,000 17.7
285,500 650,000 1,050,000 20.0
380,500 866,000 1,360,000 23.0
462,000 1,100,000 1,700,000 25.2
690
ac
5-2-00
SB99216
Rev. A
Form No. NH
Page 3 of 4
BIF Doc# 9003
Bussmann
®
HRC Fuse Links
Class of Operation gL/gG 690V ac 440V dc 6 to 630 Amps
Sizes 00 to 3
Time Current Characteristics for Size 2
Time Current Characteristics for Size 3
NH
Size 2 Details:
Approvals:
Rated Currents:
Weight:
Catalog
1
Number
Amp
Ratings
VDE, ÖVE, KEMA, IEC, SEV
40, 50, 63, 80, 100,125,160, 200,
224, 250, 315, 355, 400 Amps
0.59 kg.
I
2
t
Pre-
Arcing
(Ampere
2
Seconds)
Total at
Total at
380V
500V
Total at
690V
Nom.
Watts Rated
Loss Voltage
Size 3 Details:
Approvals:
Rated Currents:
Weight:
Catalog
1
Number
Am
Ratings
CEBEC
315, 355, 400, 425, 500, and 630 Amps
1.0 kg.
I
2
t (Ampere
2
Seconds)
Pre-
Total at
Total at
Arcing
380V
500V
Total at
690V
Nom.
Watts Rated
Loss Voltage
40NH2G-690
50NH2G-690
63NH2G-690
80NH2G-690
100NH2G-690
125NH2G-690
160NH2G-690
200NH2G-690
224NH2G-690
250NH2G-690
315NH2G-690
355NH2G-690
400NH2G-690
40
50
63
80
100
125
160
200
224
250
315
355
400
5,000
8,000
13,000
18,200
26,800
40,500
76,500
120,500
160,500
197,000
330,000
405,000
600,000
11,500
18,500
31,000
43,000
63,500
96,000
178,000
285,500
380,500
462,000
800,000
960,000
1,400,000
26,300
43,000
72,000
100,000
140,000
215,000
410,000
650,000
866,000
1,100,000
1,780,000
2,230,000
3,300,000
44,000
69,100
113,000
160,000
230,000
350,000
650,000
1,050,000
1,360,000
1,700,000
2,800,000
3,500,000
5,000,000
4.7
6.3
7.8
8.5
9.4
12.6
17.7
20.0
23.0
25.2
30.0
35.8
41.5
315NH3G-690
355NH3G-690
400NH3G-690
500NH3G-690
630NH3G-690
315
355
400
500
630
330,000 800,000 1,780,000 2,800,000
405,000 960,000 2,230,000 3,500,000
600,000 1,400,000 3,300,000 5,000,000
1,000,000 2,400,000 5,400,000 8,310,000
1,700,000 4,100,000 9,200,000 15,000,000
30.0
35.8 690
41.5 ac
43.0
47.4
690
ac
The only controlled copy of this BIF document is the electronic read-only version located on the Bussmann Network Drive. All other copies of this BIF document are by definition uncontrolled.This
bulletin is intended to clearly present comprehensive product data and provide technical information that will help the end user with design applications. Bussmann reserves the right, without notice,
to change design or construction of any products and to discontinue or limit distribution of any products. Bussmann also reserves the right to change or update, without notice, any technical infor-
mation contained in this bulletin. Once a product has been selected, it should be tested by the user in all possible applications.
The compiler environment used is cosmic STM8. The sprintf entry parameter does not support the input of U8 type. It needs to be changed to U16 to pass. Otherwise, the output print will be garbled. Is ...
I use the following method on wince to get mux and sinkfilter hr = m_pCaptureGraphBuilder->SetOutputFileName( &MEDIASUBTYPE_Avi, L"test.avi", &m_pMuxFilter, &m_pVideoFileSink ); Why does an error occu...
Live broadcast time: March 31 (Thursday) 10:00-11:30 amLive broadcast topic: RSL15 - ON Semiconductor's more efficient, smarter and safer BLE 5.2 Bluetooth chipLive broadcast content:
Starting with BL...
First log in to the website [url=http://www.ti.com.cn/lsds/ti_zh/analog/webench/overview.page]http://www.ti.com.cn/lsds/ti_zh/analog/webench/overview.page[/url] Fill in some design conditions you need...
[align=left]Reasons for using chip beads and chip inductors: Whether to use chip beads or chip inductors depends mainly on the application. Chip inductors are needed in resonant circuits. When it is n...
High efficiency and low standby power consumption are two major challenges in today's switching power supply design. Resonant topology or LLC topology is becoming increasingly popular because it ca...[Details]
Today, with the increasing integration of functions, mobile phones can also be used as portable media players (PMP), digital cameras, handheld computers (PDAs), and even global positioning systems ...[Details]
introduction
Throughout the history of automotive lighting, power has always played an important role. Initially, cars only needed headlights to see the road in the dark. Later, other light so...[Details]
As LEDs continue to improve in almost every aspect of performance and cost, LED lighting is being used in an increasingly wide range of applications, among which LED street lights are a focus of in...[Details]
With the development and widespread application of computer technology, especially in the field of industrial control, computer communication is particularly important. Although serial communication g...[Details]
1 Introduction
PROFIBUS is an international, open, and manufacturer-independent fieldbus standard. It is widely used in manufacturing automation, process industry automation, and automatio...[Details]
I've been studying dot matrix recently. It looks simple, but it takes a while to master it completely! The 8*8 dot matrix hardware circuit I'm making now is like this. The row is driven by 74HC138 + t...[Details]
Among the many members of the single-chip microcomputer family, the MCS-51 series of single-chip microcomputers has occupied the main market of industrial measurement and control and automation eng...[Details]
From the previous section, we have learned that the timer/counter in the microcontroller can have multiple uses, so how can I make them work for the purpose I need? This requires setting the timer/...[Details]
introduction
MEMS is a high-tech that has flourished on the basis of integrated circuit production technology and dedicated micro-electromechanical processing methods. Pressure sensors develop...[Details]
LED guardrail lights use fluorescent tubes or LEDs as light sources and continuous guardrails as carriers to form an approximately linear guardrail light strip. This article mainly introduces...[Details]
D5026A is a driver IC designed by Shanghai Debei Electronics for energy-saving LED display screens. Its design concept is energy-saving and compatible with existing solutions, that is, it can be ...[Details]
Since AC mains power may experience power outages, voltage sags and surges, continuous undervoltage and overvoltage, and frequency fluctuations during supply, these factors will affect the continuous ...[Details]
0 Introduction
Under normal circumstances, the three-phase power in the power system is symmetrical, and they meet certain amplitude and phase conditions; but when the load changes, the syst...[Details]
Introduction
Today, as IC (integrated circuit) has developed to a super-large scale, IC design based on IP (Intellectual Property) cores and their reuse are important means to ensure the ef...[Details]