Solid State Relays (600 VAC Models)
G3NA-6
New Models Available at 600 VAC Load
Voltage Line with 10 A, 25 A and 50 A
Output Current
• Load voltage range: 180 to 660 VAC
• Lower input current: 7 mA max at 24 VDC
• All models are same dimensions as G3NA series.
• Built-in varistor effectively absorbs external surges.
• Operation indicator enables monitoring operation.
• Protective cover for greater safety.
• Certified by UL, CSA.
Ordering Information
■
List of Models
Isolation
Photocoupler
Zero cross
function
Yes
Indicator
Yes
Applicable output load
(See note 1.)
10 A at 400 to 600 VAC
25 A at 400 to 600 VAC
50 A at 400 to 600 VAC
Rated input voltage
5 to 24 VDC
100 to 240 VAC
5 to 24 VDC
100 to 240 VAC
5 to 24 VDC
100 to 240 VAC
Model
G3NA-610B DC5-24
G3NA-610B AC100-240
G3NA-625B DC5-24
G3NA-625B AC100-240
G3NA-650B DC5-24
G3NA-650B AC100-240
Note: 1.
The applicable output load depends on the ambient temperature. Refer to
Load Current vs. Ambient Temperature
in
Engineering Data.
2.
Loss time increases under 400 VAC. (Refer to
Precautions for Correct Use.)
Confirm operation with the actual load.
■
Accessories (Order Separately)
One-touch Mounting Plates
Model
R99-12 FOR G3NA
Heat Sinks
Slim Models Enabling DIN-track Mounting
Model
Y92B-N50
Y92B-N100
Y92B-N150
Y92B-P250N
10 A
20 A
40 A
50 A
Applicable maximum load current
Low-cost Models
Model
Y92B-A100
Y92B-A150N
Y92B-A250
20 A
40 A
40 A
Applicable maximum load current
Solid State Relays (600 VAC Models)
G3NA-6
467
Specifications
■
Ratings
Input (at an Ambient Temperature of 25°C)
Model
G3NA-6@@B
Rated voltage
5 to 24 VDC
100 to 240 VAC
Operating voltage
4 to 32 VDC
75 to 264 VAC
Impedance
(See note 1.)
7 mA max.
72 kΩ±20%
Voltage level
Must operate voltage
4 VDC max.
75 VAC max.
Must release voltage
1 VDC min.
20 VAC min.
Note: 1.
The input impedance is measured at the maximum value of the rated supply voltage (for example, with the model rated at 100 to 240 VAC,
the input impedance is measured at 240 VAC).
2.
Refer to
Temperature Characteristics (for Must Operate Voltage and Must Release Voltage)
in
Engineering Data
for further details.
Output
Model
Rated load voltage
Load voltage range
Applicable load
Load current (See note 1.)
With heat sink
(See note 2.)
G3NA-610B
G3NA-625B
G3NA-650B
400 to 600 VAC
360 to 660 VAC
0.5 to 10 A (at 40°C)
0.5 to 25 A (at 40°C)
0.5 to 50 A (at 40°C)
Without heat sink
0.5 to 4 A (at 40°C)
0.5 to 4 A (at 40°C)
0.5 to 6 A (at 40°C)
150 A (60 Hz, 1 cycle)
220 A (60 Hz, 1 cycle)
440 A (60 Hz, 1 cycle)
Inrush current
Note: 1.
The load current varies depending on the ambient temperature. Refer to
Load Current vs. Ambient Temperature
under
Engineering Data.
2.
When an OMRON Heat Sink (refer to
Options)
or a heat sink of the specified size is used.
■
Characteristics
Item
Operate time
Release time
Output ON voltage drop
Leakage current
Insulation resistance
Dielectric strength
Vibration resistance
Shock resistance
Ambient temperature
Ambient humidity
Weight
G3NA-610B-UTU
G3NA-625B-UTU
G3NA-650B-UTU
1/2 of load power source cycle + 1 ms max. (DC input)
3/2 of load power source cycle + 1 ms max. (AC input)
1/2 of load power source cycle + 1 ms max. (DC input)
3/2 of load power source cycle + 1 ms max. (AC input)
1.8 V (RMS) max.
10 mA max. (at 400 VAC)
20 mA max. (at 600 VAC)
100 MΩ min. (at 500 VDC)
4,000 VAC, 50/60 Hz for 1 min
Destruction: 10 to 55 to 10 Hz, 0.75-mm single amplitude (1.5-mm double amplitude)
Destruction: 1,000 m/s
2
Operating:−30°C to 80°C (with no icing or condensation)
Storage:
−30°C
to 100°C (with no icing or condensation)
Operating: 45% to 85%
Approx. 120 g
468
Solid State Relays (600 VAC Models)
G3NA-6
Engineering Data
Load Current vs. Ambient Temperature
G3NA-610B
Load current (A)
G3NA-625B
Load current (A)
30
G3NA-650B
Load current(A)
20
16
10
With standard heat sink
(Y92B-A100 or Y92B-N50)
or aluminum plate measuring
150 mm x 150 mm x t3.2 mm
(W x H x t)
60
With standard heat sink
(Y92B-P250 N)
25
With standard heat sink
(Y92B-N150or Y92B-A150N)
50
With standard heat sink
(Y92B-A250)
20
With standard heat sink
(Y92B-N100 or Y92B-A100)
or aluminum plate measuring
200 mm x 200 mm x t3.2 mm
(W x H x t)
With iron plate measuring
100 mm x 100 mm x t0.8 (W x H x t)
40
With standard heat sink
(Y92B-A150 N)
8
6
5
4
15
With iron plate measuring
100 x 100 x t0.8 (W x H x t)
Without heat sink
30
10
8
5
4
20
2
0
-30 -20
0
20
40
60
80
100
Without heat sink
10
6
Without heat sink
0
–
30
–
20
–
10 0
10 20 30 40 50 60 70 80 90 100
Ambient temperature (˚C)
0
–30 –20 –10 0
10 20 30 40 50 60 70 80 90 100
Ambient temperature (°C)
Ambient temperature (˚C)
One Cycle Surge Current
The values shown by the solid line are for non-repetitive inrush currents.
Keep the inrush current below the values shown by the dotted line if it occurs repetitively.
G3NA-610B
Inrush current (A peak)
G3NA-625B
Inrush current (A peak)
G3NA-650B
Inrush current (A peak)
150
200
400
100
150
300
100
50
50
200
100
0
10
30 50
100 200
500 1,000
5,000
Energized time (ms)
0
0
10
30 50
100 200
500 1,000
5,000
Energized time (ms)
10
30 50
100 200
500
1,000
5,000
Energized time (ms)
Thermal Resistance Rth (Back of
Junction SSR) (Examples)
Model
G3NA-6@@B
Rth (°C/W)
0.37
Thermal Resistance Rth of Heat Sinks
(Examples)
Model
Y92B-N50
Y92B-N100
Y92B-N150
Y92B-P250N
Y92B-A100
Y92B-A150N
Y92B-A250
Rth (°C/W)
2.8
1.63
1.38
1.12
1.63
1.37
1.25
Note:
When using a commercially available heat sink, use one with a
thermal resistance equal to or less that the OMRON Heat Sink.
Solid State Relays (600 VAC Models)
G3NA-6
469
Dimensions
■
Relays
Note:
All units are in millimeters unless otherwise indicated.
G3NA-610B, G3NA-625B
Two, M5 x 12 screws
Mounting Holes
Terminal Arrangement/
Internal Connections
(Top View)
Load
Two, 4.3-dia.
or M4 holes
58 max.
47.5 44
4.5 dia.
1
Output
2
47.6
±
0.2
Operating
indicator
Two, M4 x 2
screws
12±0.4
25
43 max.
4.5
8.2
16.8
26 max.
28 max.
Load
power
supply
(−)
4
Input
(+)
3
G3NA-650B
Two, M5 x 12 screws
Mounting Holes
Terminal Arrangement/
Internal Connections
(Top View)
Load
Two, 4.3-dia.
or M4 holes
58 max.
47.5 44
4.5 dia.
1
Output
2
47.6
±
0.2
Operating
indicator
Two, M4 x 2
screws
12±0.4
25
43 max.
4.5
8.2
16.8
26 max.
28 max.
Load
power
supply
(−)
4
Input
(+)
3
■
Optional Accessories (Order Separately)
One-touch Mounting Plate
The One-touch Mounting Plate is used to mount the G3NA to a DIN
Track.
R99-12 FOR G3NA (for the G3NA and G3NE)
Two, M4 mounting
holes for the G3NA
To mount the Relay to DIN
Track, first mount it to the
One-touch Mounting Plate
and then attach it to the DIN
Track as shown in the
diagram.
Two, M4 mounting
holes for the G3NE
30
44
To remove the Relay from
the DIN Track, pull down on
the tab with a screwdriver in
the direction of the arrow.
•
When a Relay is mounted to DIN Track, use it within the rating for a
Relay without a heat sink.
•
Use the following DIN Tracks: PFP-100N or PFP-100N2.
470
Solid State Relays (600 VAC Models)
G3NA-6
Heat Sinks
Y92B-N50 Heat Sink (for max. 10 A load
current)
Type G3NA-610B is recommended for max. 10 A with this heat sink.
For upright standing to the
ground,
a 30% derating of the load current is required (from the
Load Current vs. Ambient Temperature
graphs).
The orientation indicated by the external dimensions is not the correct mounting orientation. When opening mounting holes, refer to the
mounting hole dimensions.
Mounting Holes
4.6 dia.
Two, M3 holes
Two, 3.2-dia. holes
Two, M4 holes
44 max. 30
47.6
77 max.
90±0.3
100 max.
47 max.
90±0.4
Two, 4.4-dia.
or M4 holes
35
30.5±0.3
5.6
5
6
51 max.
4.5
35±0.2
Weight: approx. 200
g
Y92B-N100 Heat Sink (for max. 20 A load
current)
Type G3NA-625B is recommended for 20 A with this heat sink.
For upright standing to the
ground,
a 30% derating of the load current is required (from the
Load Current vs. Ambient Temperature
graphs).
The orientation indicated by the external dimensions is not the correct mounting orientation. When opening mounting holes, refer to the
mounting hole dimensions.
Mounting Holes
Two, M4
4.6 dia.
Two, M3 holes
holes
Two, 3.2-dia. holes
Two, 4.4-dia.
or M4 holes
35
30.5±0.3
71 max. 30
75 max.
90±0.4
47.6
77 max.
90±0.3
100 max.
5.6
28
13
5
100 max.
4.5
35±0.2
Weight: approx. 400
g
Y92B-N150 Heat Sink (for max. 40 A load
current)
Type G3NA-625B is recommended for max. 25 A and G3NA-650B for max. 40 A with this heat sink.
For upright standing to the
ground,
a 30% derating of the load current is required (from the
Load Current vs. Ambient Temperature
graphs).
The orientation indicated by the external dimensions is not the correct mounting orientation. When opening mounting holes, refer to the
mounting hole dimensions.
47.6
4.6 dia.
Three,
M4 holes
Two, 3.2-dia. holes
Mounting Holes
Two, 4.4-dia.
or M4 holes
35
100 max. 30
104 max.
56±0.3
77 max.
90±0.3
100 max.
5.6
28
5
100 max.
13
4.5
Weight: approx. 560
g
Solid State Relays (600 VAC Models)
G3NA-6
471