The Smart Power Relay E-1048-8I.- is a remotely controllable electronic
load disconnecting relay with three functions in a single unit:
l
electronic relay
l
electronic overcurrent protection
l
status indication
The 7 pin INLINE version is designed for use with various E-T-A
terminal blocks, e. g. 17-P10-Si. A choice of current ratings is available
from 1 A through 20 A. An operating voltage range of DC 9...32 V
allows the connection of DC 12 V and DC 24 V loads.
In order to switch and protect loads remotely, it has until now been
necessary to connect several discreet components together:
- an electro-mechanic relay, control cable and integral contact
to close the load circuit
- an additional protective element (circuit breaker or fuse) for
cable or equipment protection
- a device for current measurement (shunt)
Now type E-1048-8I. combines all these functions in a single unit,
thus minimising the number of connections in the circuit and
thereby reducing the risk of failures.
E-1048-8I... INLINE version
Technical Data
(TU = 25 °C, US = DC 24 V) (TU =
Power supply LINE +
Type
Voltage ratings U
N
Operating voltage U
S
:
Load circuit LOAD
Load output
Max. current rating I
N
Types of loads
Current rating range I
N
Power MOSFET, high side switching
20 A
resistive, inductive, capacitive, lamp
loads, motors (depending on duration
of inrush current)
1 A...15 A (fixed ratings)
up to 85 °C ambient without load
reduction, 20 A up to 70 °C.
Two basic versions with factory pre-
set ratings:
version 1: 1 A/2 A/3 A/5 A/7.5 A/10 A
version 2: 15 A/20 A
DC power supply with small R
i
battery and generator etc.
DC 12 V/DC 24 V
DC 9...32 V
ambient temperature at UN)
Applications
Type E-1048-8I. is suited to all applications with DC 12 V or DC 24
V circuits, where magnetic valves, motors or lamp loads have to be
switched, protected or monitored:
- road vehicles (utility vehicles, buses, special vehicles)
- rail vehicles
- marine industry (ships, boats, yachts etc.)
The Power Relay is also suitable for industrial use (process control,
machine-building, engineering) as an electronic coupling relay
between PLC and DC 12 V or DC 24 V load
Features
l
l
l
l
l
l
l
l
Integral power electronics provide a wear-resistant switching
function, insensitive to shock and vibration.
Only a fraction of the control power needed by electro-mechanical
relays is required for switching loads. This is important for battery
buffered load circuits which have to remain controlled even with
the generator off line.
The extremely low induced current consumption of less than 1 mA
is absolutely necessary for battery buffered applications.
The load circuit is disconnected in the event of an overload or
short circuit, the trip curve is also suitable for smaller motor loads.
The load circuit is permanently monitored for wire breakage.
Two status outputs for control signal AS and group signal SF
provide status indication. For processing the actual value of the
current flow in a power management system an analogue output
from 0 to 5 V is provided. This voltage signal may also be used as
an input to a control circuit or to switch off the unit by means of
external control in the event of low load current value.
For switching and monitoring loads of 20 A plus it is possible to
connect several units in parallel. Uniform power distribution between
units must be ensured by symmetrical design of the supply cables
(length and cross section).
Coloured label, e. g. red = 10 A, see ordering information.
Induced current consumption
I
0
of the unit (OFF condition) < 1 mA
Typical voltage drop U
ON
at rated current I
N
(at 25 °C)
I
N
1
2
3
5
A
A
A
A
50
55
60
80
U
ON
mV
mV
mV
mV
I
N
7.5 A
10 A
15 A
20 A
typically 1.3 x I
N
U
ON
90 mV
110 mV
60 mV
60 mV
Switching point
Trip time
(standard curve)
(-40 °C...+85 °C: 1.1...1.5 x I
N
)
typically 200 ms with switch-on onto
overload and/or load increase on duty
Current limitation
version 1: typically 75 A
version 2: typically 350 A
Temperature disconnection power transistor > 150 °C
After trip
- resettable via external control signal
(low-high) at control input IN+
- reset of supply voltage
Parallel connection of channels for loads of 20 A plus, several units of
identical current ratings may be
connected in parallel. To ensure equal
distribution of current between units,
symmetrical design of the supply feed
is necessary (length and cross section).
Leakage current in OFF
condition
version 1: max. 100 µA
version 2: max. 500 µA
Free-wheeling diode
for connected load
integral
version 1: max. 40 A
version 2: max. 100 A
7
2015/16
www.e-t-a.de
7
- 21
Smart Power Relay E-1048-8I...
Technical Data
(TU = 25 °C, US = DC 24 V) (TU = ambient temperature at UN)
Delay time t
on
/t
off
(resistive load)
typically 5 ms / typically 1.5 ms
(EMC filter in control input)
Technical Data
(TU = 25 °C, US = DC 24 V) (TU = ambient temperatureat UN)
Temperature range
ambient temperature
- standard: -40...+85 °C
without load reduction (70 °C at 20 A)
- for other temperature ranges please
see ordering key
combined test, 9 cycles with
functional test
test to DIN EN 60068-2-30, Z/AD
min. temperature -40 °C,
max. temperature +90 °C
test to DIN IEC 60068-2-14, Nb
in operation, with temperature change
6 g eff. (10 Hz...2,000 Hz)
test to DIN EN 60068-2-64
25 g/11 ms, 10 shocks
test to DIN EN 60068-2-27
test to DIN EN 60068-2-52, severity 3
housing IP30 to DIN 40050
higher protection class upon request
EMC directive:
emitted interference EN 50081-1
noise immunity EN 61000-6-2
Automotive directive:
emitted interference, noise immunity:
72/245/EW6 und 95/54/E6
Wire breakage monitoring in wire breakage thresholds:
ON and OFF
in OFF-condition (version 1):
condition of load
R
load
> typically 100 kΩ
in OFF-condition (version 2):
R
load
> typically 10 kΩ
in ON-condition: I
load
< typically 0.2 x I
N
indication via group fault signalisation
SF (switching output)
Fault indication will not be stored, i.e.
after remedy of wire breakage fault
indication will disappear
possible options:
- wire breakage indication only in ON
condition
- wire breakage indication only in OFF
condition
- no wire breakage indication)
Short circuit, overload
- disconnection of load, indication via
in load circuit
group signal SF
- no automatic re-start
- after remedy of the fault unit has to
be reset via control input IN+
Control input IN+
Control voltage IN+
0...5 V = “OFF”, 8.5...32 V =
“ON”
Control current I
E
1...10 mA (8.5...DC 32 V)
Reset in the event of a failure - reset via external control signal (low
- high) at control input IN+
- via reset of supply voltage
Dimmer operation
possible, see max. switching frequency
(e.g. PWM signal)
Switching frequency
at resistive or inductive load max. 100 Hz
Status and diagnostic function
Control signal AS
transistor output minus switching (LSS),
open collector, short circuit and overload
proof, max. load: DC 32 V/2 A
0 V-level: when unit is set
(at IN+ = 8.4...32 V)
transistor output minus switching (LSS),
open collector, short circuit and overload
proof, load max. DC 32 V/2 A
0 V-level with overload and short circuit
disconnection, wire breakage indication
voltage output 0-5 V proportional
to load current:
1 V = 0.2 x I
N
5 V = 1.0 x I
N
5 V... typically 6.5 V = overload range
tolerance: (for I
load
> 0.2 x I
N
)
± 8 % of I
N
max. output current 5 mA
load resistance > 1 kΩ against GND
response time when switching on a load:
t
90
= typically 20 ms
response time of load change on duty:
t
90
= typically 1 ms
LED yellow
LED red
Tests
Humid heat
Temperature change
Vibration (random)
Shock
Corrosion
Protection class
EMC requirements
Terminals of INLINE version
(7 pin, standard)
7 blade terminals 6.3 mm x 0.8 mm
to DIN 46244-A6.3-0.8
contact material CuZn37F37
copper-plated and tin-plated
Mounting:
- E-T-A socket type 17-P10-Si
(max. load 16 A)
- on a pc board with 6.3 mm
receptacles
Housing INLINE version
max. dimensions
Materials
Mass
Approvals
CE, e1 logo
INLINE:
11.5 x 50 x 56 mm when plugged in
11.5 x 50 x 66 mm including terminals
INLINE: PA66
approx. 23 g...33 g, depending on
version
according to EU, EMC and automotive
directives
Group signal SF
Analogue output U(I)
7
Trip times
definition of t
90
reached 90% of final value
Visual status indication
Control signal AS
Group fault signal SF
General data
Reverse polarity protection
Control circuit
yes
Load circuit
no (due to integral free-wheeling diode)
Status outputs
interference voltage resistance
max. DC 32 V
7
- 22
www.e-t-a.de
2015/16
Smart Power Relay E-1048-8I...
Ordering Information
Type
E-1048-8I
Smart Power Relay DC 12 V/24 V - 1 A...20 A
in INLINE version
Housing / temperature range
3
with housing / 70 °C (without moisture condensation)
4
with housing / -40 °C...+85 °C (70 °C at I
N
= 20 A)
C
with control input (+ control 8.5...32 V)
LEDs
0
without LEDs
3
2 LEDs: AS yellow, SF red
Status output minus-switching
A
without
D
with AS and SF
Contents of group fault signal SF/
LED indication SF
0
without
1
short circuit / overload
3
short circuit / overload + wire breakage on
4
short circuit / overload + wire breakage
off + wire breakage on
Analogue output
V0
without
V1
0...5 V
Characteristic curve
4
200 ms
(switch-off delay with overload)
Voltage rating
U3
DC 12/24 V
Current ratings /
colour of label
1 A /
black
2 A /
grey
3 A /
purple
5 A /
light-brown
7.5 A /
brown
10 A /
red
15 A /
blue
20 A /
yellow
Dimensions INLINE version (all options = “DELUXE”)
66
2.60
56
2.21
1
4
6
3
7
5
2
LED red
11.5
.453
LED yellow
50
1.97
This is a metric design and millimeter dimensions take precedence ( mm )
inch
Connection diagram INLINE version
(all options = “DELUXE”)
LINE (+)
DC 12 V/24 V
AS
yellow
SF
red
Available configurations:
E-1048-8I
E-1048-8I
E-1048-8I
E-1048-8I
E-1048-8I
E-1048-8I
E-1048-8I
E-1048-8I
3
4
4
4
4
4
4
4
- C 0
- C 0
- C 3
- C 3
- C 3
- C 3
- C 3
- C 3
A
A
A
D
D
D
D
D
control input
part number (without options = “BASIC”)
0
0
1
1
1
3
4
4
V0 - 4 U3 - ... A
V0 - 4 U3 - ... A
V0 - 4 U3 - ... A
V0 - 4 U3 - ... A
V1 - 4 U3 - ... A
V0 - 4 U3 - ... A
V0 - 4 U3 - ... A
V1 - 4 U3 - ... A
LOAD (+)
GND
max. 6,5 V
IN+
1…10 mA
group fault signal
part number (various options)
control signal
analogue output 0 … 5 V
=
SF *
AS *
max. 2 A
max. 2 A
U(I) *
max. 5 mA
part number (all options = “DELUXE”)
* Optionally available:
- signal outputs AS / SF
- analogue output U(I)
Preferred types
Preferred types
E-1048-8I4-C3D1V1-4U3-
E-1048-8I3-C3D1V0-4U3-
E-1048-8I4-C3A1V0-4U3-
Standard current ratings (A)
1
x
x
x
2
x
x
x
3
x
x
x
5
x
x
x
7.5 10
x
x
x
x
x
x
15
x
x
x
20
x
x
x
Pin selection INLINE version
7
E-1048-8I.
LINE +
GND
SF
U(I)
AS
IN+
LOAD
(2)
(5)
(7)
(3)
(6)
(4)
(1)
17-P10-Si
(2)
(5)
(7)
(3)
(6)
(4)
(1)
[2(k)]
[12]
[24]
[2(i)]
[23]
[11]
[1]
2015/16
www.e-t-a.de
7
- 23
Smart Power Relay E-1048-8I...
Typical time/current characteristics (T
A
= 25 °C)
Version 1:
1 A, 2 A, 3 A, 5 A, 7.5 A and 10 A (standard 200 ms)
1000
100
Trip time in ms
10
1
current limitation
n
0.1
0
2
1
typ. 1.3 x I
N
... times rated current I
N
(typ. 75 A)
I (A)
Version 2:
15 A and 20 A (standard 200 ms)
1000
100
Trip time in ms
10
1
current limitation
0.1
0
1
2
typ. 1.3 x I
N
... times rated current I
N
(typ. 350 A)
I (A)
7
7
- 24
www.e-t-a.de
2015/16
E-1048-8I...
- Accessories E-1048-8I...
Accessories for E-1048-8I.
Single mounting sockets
(with adapter)
(up to
16 A
max. load)
17-P10-Si
17-P10-Si-20025
17-P70-Si
17-P70-Si-20025
(retaining clip Y 300 581 11 available on request)
polarized blade terminal
DIN 46244-A6.3-0.8 (QC .250)
-P10
10
.394
slot for fitting labels from
Phoenix, Weidmüller
blade terminal DIN 46244 part 2
C profile (2xA2.8-0.8) (QC 2x.110)
-P70
10
.394
2-way mounting socket
6-way mounting socket
23-P10-Si
63-P10-Si
(retaining clip Y 300 581 03 available on request)
6.3
.248
2.8
.110
retaining clip
depth
10 mm
(.394 in.)
1
11
23
2(k)
12
24
2(i)
8.5
.335
10
.394
1
2(k)
12
2(i)
12.5
.492
25
.984
polarized
recess
12.5
.492
50
1.97
75
2.95
50
1.97
57.4
2.26
6 x 6.8 = 40.8
6 x .268 = 1.61
6.8
.268
7.4
.291
4.4
.173
22.2
polarized blade terminals
DIN 46244-A6.3-0.8 (QC .250) .874
7.4
.291
6.25
12.5
.246
.492
21
.827
retaining
clip
10
.394
64
2.52
50
1.97
57.4
2.26
64
2.52
4.4
.173
6
.236
2
.079
max. 30
max. 1.18
25.8
1.02
33.3
1.31
5
.197
41.3
1.63
11
23
1.4
.055
45.8
1.80
24
6.5
.256
80
3.15
12.5
.492
symmetrical rail
EN 50022-35x7.5
adapter X20040901
G-profile
EN 50035-G32
polarization recess
Connector bus links -P10
X 210 588 01/
1.5 mm
2
, (AWG 16), brown (up to 13 A max. load)
X 210 588 02/
2.5 mm
2
, (AWG 14), black (up to 20 A max. load)
X 210 588 03/
2.5 mm
2
, (AWG 14), red (up to 20 A max. load)
X 210 588 04/
2.5 mm
2
, (AWG 14), blue (up to 20 A max. load)
100 quick-connect tabs 6.3 (.250)
DIN 46247 tinned brass,
insulated
~70
~2.76
Busbar (10-way)
(supplied as a complete package)
for type 17 socket
(for max. 100 A continuous load),
more positions available on request
X 211 157 01
with terminal
X 211 157 02
without terminal
Phoenix terminal AKG 35
max. cross section 35 mm
2
(AWG 2)
cylinder head screw washer
M4x4 ISO1207
A 4.3 DIN 125
nickel plated
nickel plated
2 mounting clips
Y 300 504 02
(2 pcs needed per unit)
2
.079
7.5
.295
female
connector
1.9
.075
1
.039
Installation drawing with
mounting clips Y 300 504 02
3.5
.138
M4 Cu rail, tin-plated
10
.394
7
.276
12.8
.504
2
.079
0.5
.020
12.5
.492
154.8
6.09
pressure-relief joint
(1.1 mm (.043 in.)
thick constriction)
Insulating sleeving for busbar (10-way)
Y 303 824 01
5.4
.213
8
.315
9
.354
17
.669
125
4.92
7.3
.287
60.4
2.38
50
1.97
8.5
.335
M4
16.5
.650
20
.787
2
.079
7
This is a metric design and millimeter dimensions take precedence ( mm )
inch
All dimensions without tolerances are for reference only. In the interest of improved design,
performance and cost effectiveness the right to make changes in these specifications without
notice is reserved. Product markings may not be exactly as the ordering codes. Errors and
omissions excepted.
2015/16
www.e-t-a.de
7
- 25