Industrial and process control, distributed power, medical, ATE, communications,
defense and aerospace.
For details on proper operation please refer to the:
Design Guide & Applications Manual for Maxi, Mini, Micro Family.
Absolute Maximum Ratings
Product Overview
These DC-DC converter modules use advanced
power processing, control and packaging
technologies to provide the performance,
flexibility, reliability and cost effectiveness of a
mature power component.
High frequency ZCS/ZVS switching provides
high power density with low noise and
high efficiency.
Part Numbering
e.g. V375C12T150BL2
375C
Product Grade Temperatures (°C)
Grade
Operating
Storage
E
= - 10 to +100 - 20 to +125
C
= - 20 to +100 - 40 to +125
T
= - 40 to +100 - 40 to +125
H
= - 40 to +100 - 55 to +125
M
= - 55 to +100 - 65 to +125
B
Output Power
V
OUT
P
OUT
2V
50W
3.3V
50W, 75W
5V
50W, 100W
8V
100W
12V
75W, 150W
15V
75W, 150W
24V
75W, 150W
28V
75W, 150W
36V
75W, 150W
48V
75W, 150W
Pin Style
Finish
Blank:
Short
Tin/Lead
L:
Long
Tin/Lead
S:
Short ModuMate
Gold
N:
Long ModuMate
Gold
F:
Short RoHS
Gold
G:
Long RoHS
Gold
K:
Extra Long RoHS
Gold
Baseplate
Blank:
Slotted
2:
Threaded
3:
Through-hole
Product Type
V
= Standard
S
= Enhanced
efficiency
(avail.
≤12
V
OUT
only)
Output Voltage
2
= N/A
3V3
= 3.3V
5
= 5V
8
= 8V
12
= 12V
15
= 15V
24
= 24V
28
= 28V
36
= 36V
48
= 48V
375V Micro Family
Page 1 of 14
Rev 9.6
06/2017
vicorpower.com
800 927.9474
375V Input
Module Family Electrical Characteristics
Electrical characteristics apply over the full operating range of input voltage, output load (resistive) and baseplate temperature, unless otherwise specified.
All temperatures refer to the operating temperature at the center of the baseplate.
MODULE INPUT SPECIFICATIONS
Parameter
Operating input voltage
Input surge withstand
Undervoltage turn-on
Undervoltage turn-off
Overvoltage turn-off/on
Disabled input current
204.7
429.2
242.5
212.2
446.3
467.5
1.1
Min
250
Typ
375
Max
425
500
247.5
Unit
V
DC
V
DC
V
DC
V
DC
V
DC
mA
PC pin low
<100ms
Notes
MODULE OUTPUT SPECIFICATIONS
Parameter
Output voltage setpoint
Line regulation
Temperature regulation
Power sharing accuracy
Programming range
10
±0.02
±0.002
±2
Min
Typ
Max
±1
±0.20
±0.005
±5
110
Unit
%
%
% / °C
%
%
Notes
Of nominal output voltage. Nominal input; full load; 25°C
Low line to high line; full load
Over operating temperature range
10 to 100% of full load
Of nominal output voltage. For trimming below 90%
of nominal, a minimum load of 10% of maximum
rated power may be required.
Externally Applied
Externally Applied
Externally Applied
Externally Applied
Externally Applied
Externally Applied
Externally Applied
Externally Applied
Externally Applied
Externally Applied
+OUT to –OUT — Absolute Maximum Ratings
2V
3.3V
5V
8V
12V
15V
24V
28V
36V
48V
-0.5 to 3.1
-0.5 to 4.7
-0.5 to 7.0
-0.5 to 10.9
-0.5 to 16.1
-0.5 to 20.0
-0.5 to 31.7
-0.5 to 36.9
-0.5 to 47.1
-0.5 to 62.9
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
V
DC
Note:
The permissible load current must never be exceeded during normal, abnormal or test conditions. For additional output related application
information, please refer to output connections on page 9.
THERMAL RESISTANCE AND CAPACITY
Parameter
Baseplate to sink; flat, greased surface
Baseplate to sink; thermal pad (P/N 20265)
Baseplate to ambient
Baseplate to ambient; 1000LFM
Thermal capacity
Min
Typ
0.24
0.21
10.9
2.8
48
Max
Unit
°C/Watt
°C/Watt
°C/Watt
°C/Watt
Watt-sec/°C
375V Micro Family
Page 2 of 14
Rev 9.6
06/2017
vicorpower.com
800 927.9474
375V Input
Module Family Electrical Characteristics (Cont.)
MODULE CONTROL SPECIFICATIONS
Parameter
Min
Typ
Max
Unit
Notes
Primary Side (PC = Primary Control; PR = Parallel)
PC bias voltage
current limit
PC module disable
PC module enable delay
PC module alarm
PC resistance
PR emitter amplitude
PR emitter current
PR receiver impedance
PR receiver threshold
PR drive capability
Secondary Side (SC = Secondary Control)
SC bandgap voltage
SC resistance
SC capacitance
SC module alarm
1.21
990
1.23
1000
0.033
0
1.25
1010
V
DC
Ω
µF
V
DC
With open trim; referenced to –Sense. See Fig. 7
Referenced to –Sense
0.9
5.7
150
375
2.4
500
2.5
625
2.6
12
1.0
5.9
5.50
1.5
2.3
5.75
2.1
2.6
4
6.00
3.0
2.9
7
0.5
1.1
6.1
V
DC
mA
V
DC
ms
Vavg
MΩ
Volts
mA
Ω
Volts
modules
25°C
Minimum pulse width: 20ns
Without PR buffer amplifier
UV, OV, OT, module fault. See Figs. 3 and 5
See Fig. 3, converter off or fault mode
PR load >30Ω, <30pF
PC current = 1.0mA
PC voltage = 5.5V
Switch must be able to sink
≥4mA.
See Fig. 2
MODULE GENERAL SPECIFICATIONS
Parameter
Isolation test voltage (IN to OUT)*
Isolation test voltage (IN to base)*
Isolation test voltage (OUT to base)*
Isolation resistance
Weight (E, C, T grade)
Weight (H, M grade)
Temperature limiting
Agency approvals
1.9
(52.8)
2.1
(58.7)
100
Min
3000
1500
500
10
2.1
(59.3)
2.3
(65.2)
115
cURus, cTÜVus, CE
2.3
(65.8)
2.5
(71.7)
Typ
Max
Unit
V
RMS
V
RMS
V
RMS
MΩ
ounces
(grams)
ounces
(grams)
°C
See Figs. 3 and 5. Do not operate coverter >100°C.
UL60950-1, EN60950-1, CSA60950-1, IEC60950-1.
With appropriate fuse in series with the +Input
Notes
Complies with reinforced insulation requirements
Complies with basic insulation requirements
Complies with operational insulation requirements
IN to OUT, IN to baseplate, OUT to baseplate
* Isolation test voltage, 1 minute or less.
Note:
Specifications are subject to change without notice.
.
375V Micro Family
Page 3 of 14
Rev 9.6
06/2017
vicorpower.com
800 927.9474
375V Input
MODULE SPECIFIC OPERATING SPECIFICATIONS
2V
OUT
, 50W (e.g. S375C2C50BL, V375C2C50BL)
Parameter
Efficiency
S375C2C50BL (enhanced efficiency)
V375C2C50BL (standard efficiency)
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load current
Current limit
Short circuit current
Min
78.0
72
2.7
Typ
81.0
73.9
80
2.8
2.5
±0.02
28.8
28.8
Max
Unit
%
100
2.9
3.5
±0.2
25
33.8
33.8
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
25.5
17.5
3.3V
OUT
, 75W (e.g. S375C3V3C75BL, V375C3V3C75BL)
Parameter
Efficiency
S375C3V3C75BL (enhanced efficiency)
V375C3V3C75BL (standard efficiency)
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load current
Current limit
Short circuit current
Min
82.0
79.0
4.14
Typ
85.0
80.5
94
4.3
3.9
±0.02
24.6
24.6
Max
Unit
%
118
4.46
5.9
±0.4
22.7
30.6
30.6
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
23.1
15.8
3.3V
OUT
, 50W (e.g. S375C3V3C50BL, V375C3V3C50BL)
Parameter
Efficiency
S375C3V3C50BL (enhanced efficiency)
V375C3V3C50BL (standard efficiency)
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load current
Current limit
Short circuit current
Min
80.0
75.7
4.14
Typ
83.0
77
140
4.3
3.4
±0.02
17.5
17.5
Max
Unit
%
175
4.46
4
±0.2
15.15
20.6
20.6
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
15.5
10.6
5V
OUT
, 100W (e.g. S375C5C100BL, V375C5C100BL)
Parameter
Efficiency
S375C5C100BL (enhanced efficiency)
V375C5C100BL (standard efficiency)
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load current
Current limit
Short circuit current
Min
81.3
80
6.03
Typ
82.3
81.8
120
6.25
3.1
±0.02
23
23
Max
Unit
%
150
6.47
5.5
±0.2
20
26
26
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
20.4
14
375V Micro Family
Page 4 of 14
Rev 9.6
06/2017
vicorpower.com
800 927.9474
375V Input
MODULE SPECIFIC OPERATING SPECIFICATIONS (CONT.)
5V
OUT
, 50W (e.g. S375C5C50BL, V375C5C50BL)
Parameter
Efficiency
S375C5C50BL (enhanced efficiency)
V375C5C50BL (standard efficiency)
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load current
Current limit
Short circuit current
Min
83.5
79.5
6.03
Typ
85.0
80.9
120
6.25
2.7
±0.02
11.5
11.5
Max
Unit
%
150
6.47
3.4
±0.2
10
13.5
13.5
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
10.2
7
8V
OUT
, 100W (e.g. S375C8C100BL, V375C8C100BL)
Parameter
Efficiency
S375C8C100BL (enhanced efficiency)
V375C8C100BL (standard efficiency)
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load current
Current limit
Short circuit current
Min
84.0
82.5
9.36
Typ
87.0
83.7
180
9.7
3.6
±0.02
14.4
14.4
Max
Unit
%
225
10.1
4.2
±0.2
12.5
16.9
16.9
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
12.7
8.75
12V
OUT
, 150W (e.g. S375C12C150BL, V375C12C150BL)
Parameter
Efficiency
S375C12C150BL (enhanced efficiency)
V375C12C150BL (standard efficiency)
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load current
Current limit
Short circuit current
Min
85.0
85.0
13.7
Typ
86.0
86.0
220
14.3
5.4
±0.02
14.4
14.4
Max
Unit
%
275
14.9
7.4
±0.2
12.5
16.9
17.5
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
No load
No load to full load; nominal input
Output voltage 95% of nominal
Output voltage <250mV
0
12.7
8.75
12V
OUT
, 75W (e.g. S375C12C75BL, V375C12C75BL)
Parameter
Efficiency
S375C12C75BL (enhanced efficiency)
V375C12C75BL (standard efficiency)
Ripple and noise
Output OVP setpoint
Dissipation, standby
Load regulation
Load current
Current limit
Short circuit current
Min
85.0
84.0
13.7
Typ
88.0
85.5
100
14.3
3.5
±0.02
7.19
7.19
Max
Unit
%
125
14.9
4
±0.2
6.25
8.44
8.44
mV
Volts
Watts
%
Amps
Amps
Amps
Notes
Nominal input; full load; 25°C
p-p; Nominal input; full load; 20MHz bandwidth
25°C; recycle input voltage or PC to restart (>100ms off)
[align=left][b][size=3][color=#000000]Job Description:[/color][/size][/b][/align][align=left][size=3][color=#000000]- Develop and optimize advanced audio algorithm on TI C6X.[/color][/size][/align][al...
Did you know that GaN is a relatively new technology compared to other semiconductor materials such as silicon and GaAs? For high RF and high power applications such as long-distance signal transmissi...
I would like to ask if Samsung's s3c2500 or s3c4510 chips have a sleep function. I have searched the chip manual for a long time but can't seem to find the power management function. There is just a p...
I want to build a high-frequency microvolt signal amplifier circuit that amplifies 50UV sinusoidal signals within 10MHz. I hope to amplify the 50uV signal to about 10mV. I can consider the solution of...
PCB is a printed circuit board, which is the carrier of electronic circuits. PCB is used in almost all modern electronic products. PCB design is the last link of circuit design and also the redesign o...
0 Introduction
With the development of my country's economy, the number of motor vehicles continues to increase. The growth of existing roads and other hardware facilities can no longer meet t...[Details]
Power management solutions for today's portable application processors are becoming increasingly integrated. Total power consumption, standby and sleep current consumption affect battery size, bill...[Details]
At very low temperatures, certain metals and alloys lose their resistance to electric
current
and become
superconductors
. Two parameters that are often measured are the transition ...[Details]
To understand how and why OLED power supply affects display image quality, you must first understand OLED display technology and power supply requirements. This article will explain the latest OLED...[Details]
introduction
Incandescent bulbs can emit a variety of light, but in specific applications, only green, red, and yellow light are usually needed - such as traffic lights. If an incand...[Details]
The rectified DC voltage is then converted back to AC using power electronics such as insulated gate bipolar transistors.
The output voltage is switched on and off at a high frequency, control...[Details]
Currently, each country is developing its own USB interface
charging specifications
, which leads to a major problem that a USB interface
charging
device manufactured in one country...[Details]
Key Points
1. Now, in addition to high-end smartphones and tablets, users also expect to use touch screens in other applications, and they are gradually appearing in cars and instruments.
...[Details]
1 Development of LED Film and Television Lighting
1.1 The significance of developing film and television lighting
Lighting power consumption accounts for a large proportion of the total p...[Details]
Nowadays, more and more people have digital cameras. The convenience and speed of digital cameras have gradually replaced film cameras and become the main tool for people's daily photography. The n...[Details]
Mobile phones, MP3s, tablet computers, laptops, digital cameras, handheld game consoles, navigation devices, etc., all these mobile devices are powered by mobile batteries, and the battery life is ...[Details]
1 Introduction
Fieldbus is a serial, digital, multi-point communication data bus between field equipment/instruments installed in the production process area and automatic control devices/syst...[Details]
Fairchild's FAN6208 is a synchronous rectification (SR) controller for isolated LLC or LC resonant converters that can drive two individual SR MOSFETs emulating the behavior of rectifier diodes. FAN62...[Details]
Today, fleet management innovation has made great progress. Whether trucks, buses, taxis or other means of transportation, wireless satellite positioning systems are used to enable dispatchers to u...[Details]
"Multimeter" is the abbreviation of multimeter, which is an indispensable tool in our electronic production. The advantages of multimeter are that it has many uses, a wide range, an...[Details]