Digital Daily Time Switch
H5F
CSM_H5F_DS_E_3_4
Daily Time Control with Simple Operations
• Specify the operation days.
(However, you can set only one pattern of operation days
and specified days.)
• Up to 12 ON/OFF operations (24 for pulse-output operation).
• Special holidays can be handled easily with the holiday
setting function.
• Adjustments for sudden schedule changes can be made eas-
ily using output override and automatic return operation.
• The operation program can be checked easily with the pro-
gram check function.
• Enables pulse output operation and summer time setting.
• Incorporates finger-safe terminals.
• Conforms to UL, CSA, and CE marking.
• Meets a variety of mounting requirements: flush mounting,
surface mounting, and DIN track mounting.
PS
E
For the most recent information on models that have been certified for
safety standards, refer to your OMRON website.
Model Number Structure
■
Model Number Legend
H5F-@B
1 2
1. Mounting method
None:
Flush mounting
F:
Surface mounting
K:
Surface mounting/track mounting
2. Language
B:
English
Ordering Information
■
List of Models
Wiring
Screw terminals
Mounting method
Flush mounting
Surface mounting
Surface mounting/track mounting
H5F-B
H5F-FB
H5F-KB
Model
■
Accessories (Order Separately)
Name
Soft cover
Hard cover
Flush Mounting Adapter (See note 2.)
Mounting Track
50 cm (l)
×
7.3 mm (t)
1 m (l)
×
7.3 mm (t)
1 m (l)
×
16 mm (t)
End Plate
Spacer
Note: 1.
Supplied with H5F-KB model.
2.
Supplied with H5F-B (flush-mounting) model.
For H5F-B
For H5F-FB/-KB
Y92A-48F1
Y92A-48
Y92A-48E (See note 1.)
Y92F-30
PFP-50N
PFP-100N
PFP-100N2
PFP-M
PFP-S
Models
1
H5F
Specifications
■
Ratings
Rated supply voltage
Operating voltage range
Power consumption
Control outputs
100 to 240 VAC (50/60 Hz)
85% to 110% of rated supply voltage
Approx. 2.4 VA at 264 VAC
Contact output: SPST-NO, 15 A at 250 VAC, resistive load, 10 A at 24 VDC, resistive load
Minimum applied load: 100 mA at 5 VDC (failure level: P, reference value)
NEMA A300 Pilot Duty, 1/3 HP at 120 VAC
External connections
Terminal screw tightening torque
Screw terminals (M3.5 screw)
0.98 to 1.17 N · m
■
Characteristics
Accuracy of operating time
Setting error
Influence of voltage
Influence of temperature
Influence of EMS. (at EN61326-1)
Time accuracy
Memory protection
Insulation resistance
Dielectric strength
Noise immunity
Vibration resistance
Shock resistance
Ambient temperature
Ambient humidity
Life expectancy
±15
s per month
(at 25°C)
Continuous use: 5 years min. (at 25°C); Power-interruption rate of 50%: 10 years min. (at 25°C) (see note 2)
(lithium battery)
100 MΩ min. (between current-carrying terminals and exposed non-current-carrying metal parts, between operating
power supply circuit and control output circuit and between non-continuous contacts)
2,000 VAC, 50/60 Hz for 1 min (between current-carrying terminals and exposed non-current-carrying metal parts and
between operating power supply circuit and control output circuit)
1,000 VAC, 50/60 Hz for 1 min (between non-continuous contacts)
1.5 kV (between power terminals)
Square-wave noise by noise simulator (pulse width: 100 ns/1
μs,
1-ns rise)
Destruction:10 to 55 Hz with 0.375-mm single amplitude, four cycles each in three directions (8 minutes per cycle)
Malfunction:10 to 55 Hz with 0.25-mm single amplitude for 10 minutes each in three directions
Destruction:300 m/s
2
3 times each in 6 directions
Malfunction:100 m/s
2
3 times each in 6 directions
Operating:–10°C to 55°C (with no icing)
Storage: –25°C to 65°C (with no icing)
Operating: 35% to 85%
Mechanical (at 20°C):
100,000 operations min.
Electrical (at 20°C):
50,000 operations min. (15 A, 250 VAC, resistive load)
50,000 operations min. (1 HP, 250 VAC, motor load)
50,000 operations min. (10 A, 250 VAC, inductive load (cosφ = 0.7))
50,000 operations min. (100 W, 100 VAC, lamp load)
10,000 operations min. (300 W, 100 VAC, lamp load)
UL508/Listing, CSA C22.2 No. 14, conforms to EN61010-1 (Pollution degree 2/overvoltage category II)
Conforms to VDE0106/P100 (finger protection).
Conforms to Electrical Appliance and Material Safety Law (for Japan)
(EMI)
Emission Enclosure:
Emission AC mains:
(EMS)
Immunity ESD:
Immunity RF-interference:
Immunity Conducted
Disturbance:
Immunity Burst:
Immunity Surge:
Immunity Voltage Dip/Interruption:
Immunity Magnetic Power Field:
Case color
Weight
Light gray (Munsell 5Y7/1)
H5F-B: approx. 115 g; H5F-KB: approx. 160 g; H5F-FB: approx. 130 g
EN61326-1 (See note 3.)
EN55011 Group 1 class A
EN55011 Group 1 class A
EN61326-1 (See note 3.)
EN61000-4-2: 4 kV contact discharge (level 2)
8 kV air discharge (level 3)
EN61000-4-3: 10 V/m (Amplitude-modulated, 80 MHz to 1 GHz,
1.4 to 2 GHz) (level 3)
10 V (0.15 to 80 MHz) (according to EN61000-6-2)
2 kV power-line (level 3)
1 kV I/O signal-line (level 4)
EN61000-4-5: 1 kV line to lines (power and output lines) (level 2);
2 kV line to ground (power and output lines) (level 3)
EN61000-4-11: 0.5 cycle, 100% (rated voltage)
EN61000-4-8: 30 A/m
EN61000-4-6:
EN61000-4-4:
±0.01% ±0.05
s max. (see note 1)
Approved safety standards
EMC
Note: 1.
The total error including the repeat accuracy, setting error, variation due to voltage change, and variation due to temperature change is
±0.01%±0.05
s max.
±0.01%
also indicates an error in the time interval of a set time.
2.
The total time when power is not being supplied.
3.
Industrial electromagnetic environment (EN/IEC 61326-1 Table 2)
2
H5F
Connections
■
Terminal Arrangement
Flush Mounting Models
H5F-B
(Rear View)
Surface Mounting Models Surface Mounting/Track Mounting Models
H5F-FB
(Front View)
H5F-KB
(Front View)
Power source
100 to 240 VAC
H5F
TIME SWITCH
SU MO TU WE TH
FR
SA
PM
OUT
POWER
OUT
ON
AUTO
OFF
+1h
CLR
ON
PW
TMR/
P
3 00
PM
MODE
h
SELECT
d
HOLIDAY
TEST
5 00
m
/
P
WD
WRITE
OUT
POWER
OUT
ON
AUTO
OFF
H5F
TIME SWITCH
SU MO TU WE TH
FR
SA
PM
ON
PW
TMR/
P
3 00
PM
MODE
h
SELECT
d
HOLIDAY
TEST
5 00
m
/
P
WD
WRITE
CLR
+1h
Load
Power supply
of load
Load
Power source
100 to 240 VAC
Power supply
of load
Load
Power source
100 to 240 VAC
Power supply
of load
Note: 1.
2.
3.
4.
5.
The Time Switch uses M3.5 terminals.
The Time Switch output is no-voltage contact output. An external power supply is required to drive the load.
Applicable wire: 600-V vinyl-insulated wire (solid wire or twisted wire, copper), 14 to 24 AWG, 2 wires max. per terminal.
Applicable tightening torque: 0.98 to 1.17 N·m.
Recommended fuse: T2A, 250 VAC, time delay, low breaking capacity.
Operation
■
Operation
Operation method
Time range
Operation
Digital quartz
24 h
×
7 days (Operation days can be specified.)
1. Daily operation (Multiple-day operation possible.)
2. Pulse-output operation (Pulse width can be set in units of 1 s from 1 to 59 s and in units of 1 min
from 1 to 60 min.)
3. Partial operation on specified day (One or some of the operations for certain days can also be
executed on other days.)
4. Forced ON/OFF operation
5. Holiday operation
6. Output override and automatic return operation
1. Day, hours (12-hour (am/pm) or 24-hour clock), minutes (0:00 to 11:59 a.m./ 0:00 to 11:59 p.m.,
0:00 to 23:59)
2. Digital display by LCD. Character height: 8 mm
3. Digital display of present time and time schedules for operation
4. Timing chart display of present time and time schedules for operation
Program check function, summer time function
1 independent circuit
1 min
1 min
24 (see note)
Display
Other functions
Number of circuits
Minimum setting unit
Minimum set interval
Number of operations that can be set
Note:
Up to 12 ON/OFF operations are possible per day. (For pulse-output operation, the number is 24.)
3
H5F
■
Operation Functions
Timer operation (ON/OFF operation)
Controls the output according to preset of ON and OFF times
•
Minimum setting unit: 1 min
•
Up to 12 ON/OFF operations are possible per day.
Multiple-day operation example ON time : 20:00
OFF time: 10:30 (following day)
Output turns ON for a fixed period (pulse width) at the set time.
•
Pulse width: 1 to 59 s, or 1 to 60 min. (The same pulse width setting is used for all types of
output operation.)
•
The pulse width can be set in units of 1 s or 1 min.
•
Up to 24 pulse-output operations are possible per day.
Forcibly turns ON/OFF the output by the output ON/OFF switch.
Using the output ON/OFF switch and the Write Key, control output is held in the ON state until
the next OFF time.
•
It is also possible to hold the control output in the OFF state until the next ON time.
•
Operation after the output turns OFF (or ON) will be based on the regular program.
•
This function can be used with pulse-output operation.
Select the day of the week to execute some or all of the operations set for the operation day.
(Convenient, for example, for executing a half-day operation on Saturday.)
•
All programs run on operation days.
•
Only programs specified to run on a specified day will run.
•
Only one pattern of specified days can be set.
ON time
OFF time
Pulse-output operation
Pulse
width
ON time
Forced ON/OFF operation
Override and automatic return operation
Regular
program
Output
operation
Start of override and
automatic return operation
Partial operation on specified day
Program 1 Program 2
(special)
Regular
program
Operation on
operation day
Operation on
specified day
Example
with
Program 1
only for specified day
Holiday setting
Operation on Operation
operation day on holiday
Regular
program
Operation in
present
week
Operation from
next
week
It is possible to set a day in the present week as a holiday (i.e., a non-operation day: output
OFF regardless of the settings). When that day has passed, operation will continue according
to the regular program, and operation will be executed as normal on that day from the follow-
ing week
•
This function can be used with pulse-output operation.
Note:
Both the timer operation and the pulse-output operation cannot be programmed together.
■
Operation When Power Turns OFF
1.
The time and settings are backed up using a lithium battery.
2.
The display stays ON but the output turns OFF.
3.
Settings for all types of operation except override and automatic
return operation are possible.
4
H5F
Nomenclature
Front Panel
(Actual Size)
H5F
TIME SWITCH
SU MO TU WE TH FR SA
A
Mode Key
OUT
I
TMR/
P
Key
H
Output ON/OFF
Switch
G
CLR/+1h Key
No.
A
B
C
D
E
F
G
H
Mode Key
h (Hour) Key
POWER
OUT
ON
AUTO
OFF
+1h
HOLIDAY
TEST
CLR
SELECT
d
WRITE
TMR/
P
MODE
h
B
h Key
m
/
P
WD
C
m/
P
WD Key
D
Write Key
E
d/Test Key
F
Select/Holiday Key
Name
Function
Switches between time adjustment mode, the operation setting modes, and run mode.
Sets hours or switches between 12-hour (am/pm) and 24-hour display.
Sets minutes or a pulse time width.
Writes the set data to memory or confirms settings with the program check function.
Moves the cursor to specify a day or starts the program check function.
Specifies or cancels a specified day or switches to holiday setting mode.
Erases the set data and initializes the day of operation or sets/clears summer time.
ON:
Turns on the output regardless of the setting.
AUTO: Turns on/off the output according to the setting.
OFF: Turns off the output regardless of the setting.
Override and automatic return operation can be executed by using this key in combina-
tion with the Write Key.
Selects timer operation or pulse-output operation.
m/
P
WD (Minute/Pulse Time Width) Key
Write Key
d/Test (Day Shift/Program Test) Key
Select/Holiday Key
CLR/+1h (Clear/Summer Time) Key
Output ON/OFF switch
I
TMR/
P
(Timer/Pulse output) Key
Display
Time Adjustment Mode Indicator
SU MO TU WE TH FR SA
Displays the Present Time,
Operation Time, and Time Width
Output Indicator
Lit when control output is ON.
Power Indicator
Lit when power is supplied
to the Time Switch.
Pulse Operation Indicator
Lit: Pulse-output operation
Not lit: Timer operation
Present Day Indicator
Operation Day Indicator
Lit: Operation day
Not lit: Non-operation day
Flashing: Specified operation day
S
AM
PM
ON
PW
P
Partial Operation on Specified Day Indicator
Pulse Width Unit Indicator
Summer Time Indicator
Lit when set to summer time.
Operation Setting Mode Indicator
s
m
+1h
AM
PM
P
Next Operation Indicators
Run mode:
Displays the direction (i.e., ON or
OFF) and time of the next output
operation.
Operation time setting mode: Displays the program number for
the setting.
Holiday setting mode:
Displays
hday
(hday) when the
Time Switch is in holiday setting
mode.
Program check:
Displays
test
(test) during
program check.
5