Vega Series
450-900W Multiple Output Modular Power Supply
Features
1-10 Wide Range Outputs With Adjustment
Forward/Reverse/Low Noise/System Air Cooling
Output Voltages From 0.5V - 62V
48VDC Input Option
Medical Approval Options
MIL-STD-810 Shock and Vibration
PFC compliant to EN61000-3-2
Safety Agency Approvals EN, cULus, BSI, CE
Key Market Segments & Applications
Specifications
Model
Input Voltage Range
(47-440Hz with reduced PFC)
Input Current (Typ. at 90VAC)
Efficiency (Typ.)
Nominal Output Voltages
Output Voltage Adjustment
Minimum Load
Max Output Power
Max Ripple & Noise (pk-pk)
Regulation (load, line, cross)
Hold Up Time
Over Voltage Protection
Overload/Short Circuit
Remote ON/OFF Control
Remote Sense
Isolation
(3)
VEGA 450
VEGA 650
VEGA 900
(1)
(1)
-
90 - 264VAC 47-63Hz
90-264VAC 47-63Hz
150-264VAC 47-63Hz
or 34-75VDC
A
7.7A
11A
9.2A at 150VAC
%
75% at 230VAC (or 48VDC) and full load, configuration dependent
VDC
0.5 - 62 (See configuration guide)
-
Wide range, via potentiometer or remote adjust pin, module dependent
A
0A
(2)
W
450
650
900
mV
<1% (or 50mV which ever is greater) using EIAJ test method & 20MHz bandwidth
%
Less than 0.5%
ms
16ms min at 90VAC (150VAC for 900W, 10ms for 450WDC input)
%
120 - 150% (See website for more details)
%
105-125%, constant current characteristic, 150% max short circuit current.
-
A TTL compatible signal will turn ON/OFF all output modules (optional)
V
Compensates for total of 0.75V total line drop (optional on dual output modules)
-
Input-Output 4.3kVDC
(3)
; (2 x MOPPs (3rd edition 60601)),
Input-Ground 2.3kVDC; Output-Ground 200VDC
Conducted EMI
-
EN55022 Class B, (as per CISPR .22), Class A for 48V input
Radiated EMI
-
EN55022 Class B, (as per CISPR .22)
Operating Temperature
°C
0°C to 50°C, derate ea. output @ 2.5%/°C from 50°C to 65°C.
(4)
Consult factory for
70°C operation. -20°C startup requires a 30 min. warm-up period.
Cooling
-
Forced Air Cooled
Dynamic Load Response
-
<6% or 300mV of set voltage for 50% load change (above 25% load),
recovery to within 1% of nominal within 500
μs
Safety Agency Approvals
-
UL/CSA/IEC/EN 60950-1, UL/CSA/IEC/EN 60601-1, ANSI/AAMI ES60601-1, IEC/EN 61010-1,
(601-1 not available on 48V input)
CE Mark
Vibration
G
MIL-STD-810E, Method 514.4,Pro I, Cat 1, 9
2G, 10-200Hz sweep for 1hr to search for resonant. 6G random, 6-Axis to IEC68-2-64
Shock
G
MIL-STD-810F, Method 516.5, Pro I, IV, VI; 20G per IEC68-2-27
Switching Frequency
kHz
200
Weight (Typ.)
lbs
3.0 lbs. + 0.25 lbs. / used slot; maximum # of slots =5
Size (L×W×H)
in(mm)
10.6” x 5” x 2.5” (268.4mm x 127mm x 63.5mm)
Warranty
yrs
3 Years
Consult datasheet and application notes for detailed specifications and test methods.
(1) Will operate with 130-330VDC, CE Mark safety approval only applies.
(2) DC Input <44V input 370W
(3) 4kVAC Type tested (non-production test). Refer to CB Report
(4) 450WDC 1.5%/°C
1-800-526-2324 • www.us.tdk-lambda.com/lp/
53
Disclaimer: us.tdk-lambda.com/lp/legal.htm
Vega Series
Configuring Guide
Choose your options for boxes A through E. Select output voltage,
single or dual output module code from the tables below, and options
(if required) A maximum of 5 module slots may be used. List actual
output voltages required to have them pre-set by the factory.
V
A
B
C
D
E
Choose the following power supply options.
Primary Options
(Leave empty if not required)
F
AC Fail, Global/fan Inhibit, 5V/100mA standby
FV
AC Fail, Global/fan Inhibit, 5V/300mA standby
5,7
AC Fail, Global/fan Inhibit, 5-15V/1A standby
xFW
E
AC Fail, Global/fan Enable, 5V/100mA standby
EV
AC Fail, Global/fan Enable, 5V/300mA standby
5,7
xEW AC Fail, Global/fan Enable, 5-15V/1A standby
(5) Specify value of x from 5-15V.
(Increase leakage current by 90μA.).
Input Filter Choice*
120VAC, 60Hz 240VAC, 60Hz 264VAC, 63Hz (9)
S
564μA
1270μA
1.5mA
M
244μA
550μA
650μA
L
109μA
246μA
290μA
R
66μA
148μA
175μA
T
23μA
51μA
60μA
Input Connection
F
Fast on terminals (7)
S
Screw terminals
I
Switched IEC 320 Connector (7)
Cooling
F
Standard forward air fan
Q
Quiet fan, forward air (7)
R
Standard reverse air fan (6)
P
Quiet fan, reverse air (6) (7)
C**
Customer air (30 CFM req’d)
Output Power
0
450W DC Input
4
450W
6
650W
9
900W
Single Output Module Selection
†
Output Options
(Leave empty if not required)
Inhibit, module good,
and current share
N
Output Connection
Fast on terminals
Screw terminals
F
S
Vout
Module
Conn. Opt.
Example
12B3SN: 12V @ 12A single output module, screw terminal outputs, inhibit option
† Remote sense is standard on single output modules, optional on duals.
Dual Output Module Selection
V1
/
Output Connection
Fast on terminals
Screw terminals
F
S
V2
Module
Conn. Opt.
Output Options
Inhibit, module good,
and remote sense
N
Remote sense
R
(Leave empty if not required)
Example
3.3/12H1L/3FR: 3.3V @ 12A and 12V @ 6A output, fast on output terminals
and remote sense option.
Full Description Example:
V4FSSFV 5L1S 3.3E1SN 15/15H3/3SR
450W power supply with standard forward air fan, screw terminal input connections,
1.5mA leakage input
fi
lter, AC fail with Global/fan inhibit & 5V @ 300mA
aux. supply option with the following outputs:
5V @ 35A Screw terminal connections with remote sense standard
3.3V @ 60A Screw terminal connection with output inhibit, module good,
and current share options, remote sense standard
15V @ 10A Screw terminal connection with remote sense option (1st half of dual)
15V @ 6A Screw terminal connection with remote sense option (2nd half of dual)
Note the module descriptions are to be used as listed in the module tables.
* Max Leakage calculated at 264VAC, 63Hz. Note: Contact Lambda
Technical Support for non-standard leakage options emissions compliance.
** Thermocoupled evaluation unit recommended. Consult sales office.
(6) Not available on 900W Model (7) Not available on 450WDC Model
(8) Only available on 900W Model (9) Type testing result
Model Selector
Module V Range Amp
Single Output
B1L
1.8-3.8V 20A
C1
1.8-4.1V 35A
C1Y
1.8-4.1V 40A
D1L
1.8-3.8V 50A
E1
1.8-3.8V 60A
1.8-3.8V 80A
F1
(6)
Z2
1.8-3.8V 95A
Z3
1.8-3.8V 114A
B1H
3.9-5.5V 20A
L1
4.2-5.5V 35A
D2
3.8-9V
45A
D1H
3.9-5.5V 50A
E2
3.8-8V
60A
Z18
4.2-5.5V 66A
F2
(6)
3.8-8V
75A
Z4
3.9-5.5V 95A
Z6
3.9-5.5V 104A
B2
5-9V
25A
B3
9.1-16.2V 12A
C3
9.1-16.2V 18A
D3
8-16.5V
24A
E3L
8-13.9V
40A
Z7
8-16.5V
45A
EE2
7.6-16V
45A
D4
14-21.5V 18A
Slots Module
1
1
1
1.5
2
2
3
4
1
1
1.5
1.5
2
2
2
3
3.5
1
1
1
1.5
2
3
4
1.5
V Range
Amp Slots
30A
36A
14A
18A
27A
6A
10A
15A
25A
36A
5A
18A
22.5
4.5A
10A
18
10A
18
10A
15A
2
2
1
2
2
1
1
1.5
2
3.5
1
3
4
1
2
4
2
4
2
3
1
1
E4
14-19.9V
E3H
14-15V
C4
16.2-21.5V
CC3
18.2-32.4V
E5L
20-24V
B5
21.6-31V
C5
21.6-31V
D5
21-28V
E5H
24-28V
Z19
(8)
24-28V
HH5/3 25.3-44.2V
DD4
28-43V
EE4
(8)
28-38
HH5/4
32.5-53V
BB4
32.6-43V
EE5L
(8)
40-48
C5B4
43-48V
EE5H
(8)
48-56
CC5
48.1-62V
DD5
42-56V
Model Selector
Module V1 Min - V1 Max
Dual Output
H1L/1L
1.8V - 3.8V
H1L/1H
1.8V - 3.8V
H1L/2
1.8V - 3.8V
H1L/3
1.8V - 3.8V
H1L/4
1.8V - 3.8V
H1H/1L
3.9V - 5.5V
H1H/1H
3.9V - 5.5V
H1H/2
3.9V - 5.5V
H1H/3
3.9V - 5.5V
H1H/4
3.9V - 5.5V
H2/1L
5.6V - 9V
H2/1H
5.6V - 9V
H2/2
5.6V - 9V
H2/3
5.6V - 9V
H2/4
5.6V - 9V
H3/1L
9.1V - 16.2V
H3/1H
9.1V - 16.2V
H3/2
9.1V - 16.2V
H3/3
9.1V - 16.2V
H3/4
9.1V - 16.2V
H5/1L
16.2V - 28V
H5/1H
16.2V - 28V
H5/2
16.2V - 28V
H5/3
16.2V - 28V
H5/4
16.2V - 28V
V1 Amp
12A
12A
12A
12A
12A
12A
12A
12A
12A
12A
10A
10A
10A
10A
10A
10A
10A
10A
10A
10A
5A
5A
5A
5A
5A
V2 Min - V2 Max V2 Amp Slots
1.8V - 3.8V
3.9V - 5.5V
5.6V - 9V
9.1V - 16.2V
16.3V - 25V
1.8V - 3.8V
3.9V - 5.5V
5.6V - 9V
9.1V - 16.2V
16.3V - 25V
1.8V - 3.8V
3.9V - 5.5V
5.6V - 9V
9.1V - 16.2V
16.3V - 25V
1.8V - 3.8V
3.9V - 5.5V
5.6V - 9V
9.1V - 16.2V
16.3V - 25V
1.8V - 3.8V
3.9V - 5.5V
5.6V - 9V
9.1V - 16.2V
16.3V - 25V
8A
8A
6A
6A
4.5A
8A
8A
6A
6A
4.5A
8A
8A
6A
6A
4.5A
8A
8A
6A
6A
4.5A
8A
8A
6A
6A
4.5A
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
Wide Range Programmable*
W2
(6)
1-7.5V
30A
W5
0.5-32V
8.5A
* Refer to Vega Datasheet
For Additional Information, please visit
us.tdk-lambda.com/lp/products/vega-series.htm
1-800-526-2324 • www.us.tdk-lambda.com/lp/
54
Revision C4: Apr 2015