The D1U4-W-1600-54-HBxC is a 1600W power factor corrected (PFC) front end power module intended for hot swap
redundant systems. There is a main output of 54VDC (floating with respect to chassis ground) and a 12VDC Standby/
bias output (that is present whenever the incoming AC source is applied.
The form factor is suitable for 1RU chassis enclosures and is designed to deliver reliable bulk DC power to servers,
workstations, storage systems, PoE switches or any 54VDC distributed power architecture requiring high power
density.
The high efficiency design supports speed controlled dual DC fans in a thermally optimized package that is self-pro-
tecting and able to auto recover from over-current and over-temperature events. Visual status information is provided
via front panel mounted LED indicators in addition to hardware logic signals and a PMBus™ management interface.
ORDERING GUIDE
Model Number
Power Output High Power Output Low
Main Output
Line AC
Line AC
1600W
1200W
54V
Standby
Output
12V
Airflow
Back to front
Front to back
FEATURES
1600W Output Power
1.6"(1U) x 14.0" x 4.0"
(41.0mm x 355.6mm x 101.6mm)
54VDC Main; PoE compatible
12V SB Output
To Be Discontinued *
D1U4-W-1600-54-HB4C
D1U4-W-1600-54-HB3C
PMBus™ Power Management Bus supported by
dual redundant I2C interfaces.
N+1 Redundancy Capable; hot swap (up to 8
modules in parallel)
Active current sharing on 54VDC Main output;
integral bidirectional MOSFET output isolation
device
Over-Voltage, Over-Current; Over-Temperature
Protection
Internal variable speed cooling fans
20ms full cycle hold up
RoHS Compliant
Two-year warranty
INPUT CHARACTERISTICS
Parameter
Input Voltage Operating Range
Input Frequency
Turn-on Input Voltage
Turn-off Input Voltage
Maximum Current @ VIN = 200Vac
Maximum Current @ VIN = 90Vac
Inrush Current
Power Factor
OUTPUT VOLTAGE CHARACTERISTICS
Output
Voltage
Parameter
Conditions
Ramp Up
Ramp Down
1600W
1200W
Cold start between 0 to 1ms
At 230Vac; FL
Min.
90
47
81
70.5
Typ.
115/230
50/60
Max.
264
63
89
78.0
10
15
100
Units
Vac
Hz
Vac
Arms
Apk
0.95
Conditions
Min.
Typ.
Max.
Units
Voltage Set Point
54V
Vdc
Line & Load Regulation
52.38
55.62
54V
Output Current
0
30
A
1
20MHz Bandwidth
540
mVp-p
Ripple Voltage & Noise
Load Capacitance
3800
24,000
µF
Voltage Set Point
12
Vdc
Line & Load Regulation
11.64
12.36
12V
Output Current
0
2
A
1
Ripple Voltage & Noise
20MHz Bandwidth
33
mVp-p
Load Capacitance
1530
µF
1
Ripple and noise are measured with a parallel combination of a 0.1µF ceramic capacitor and 2 x 270µF OSCON
capacitors on each of the power module outputs measurement nodes. See test set up diagram below.
www.murata-ps.com/en/3d/acdc.html
www.murata-ps.com/en/3d/acdc.html
www.murata-ps.com/en/3d/acdc.html
www.murata-ps.com/en/3d/acdc.html
www.murata-ps.com/en/3d/acdc.html
www.murata-ps.com/en/3d/acdc.html
Available now at
www.murata-ps.com/en/3d/acdc.html
For full details go to
www.murata-ps.com/rohs
CB
Test Certificate
and Test Report
PM
www.murata-ps.com/support
CPS_D1U4-W-1600-54-HBxC.B04
Page 1 of 6
* Last Time Buy date is 3/31/2019. Please click here to view the Discontinuance Notification.
D1U4-W-1600-54-HBxC
AC-DC Power Supply
RIPPLE MEASUREMENT
2x270uF OSCON
Power Supply
AC Phase
0.1uF Ceramic
Load Box
AC Ground
BNC to BNC Shielded Cable
General Notes:
1. Load the outputs at specified minimum
output current.
2. Connect the probe as shown with the
input tip and ground as short as possible.
3. Take all measurements
4. Repeat the measurements with the
outputs at specified maximum output
current.
Oscilloscope
20MHz BW
OUTPUT CHARACTERISTICS
Parameter
Remote Sense
Efficiency
Output Rise (Monotonic)
Startup Time
Transient Response
Current Sharing Accuracy (up to 8 in parallel)
Hot Swap Transients
Hold Up Time
ENVIRONMENTAL CHARACTERISTICS
Parameter
Storage Temperature Range
Operating Temperature Range
Operating Humidity
Storage Humidity
Altitude
Shock
Operational Vibration
MTBF
Safety Approvals
Input Fusing
Weight
Conditions
Min.
Typ.
Max.
Units
Remote sense is not enabled on these variants due to the System Control feature and the relatively wide line &
load regulation window.
230Vac (excluding fan)
90
%
Overshoot less than 10% for all outputs; no negative transition at
10% to 95% rise time
turn off.
AC Ramp Up
3
s
PS_ON activation
250
ms
54VDC 50% step (50-100%; 100%-50%)
±2700
load; 1A/µs
mV
12VSB 1A/µs
±250
At 100% load
±10
%
5
%
100% load 230Vac nominal
20
ms
Conditions
Non-Condensing
Non-Condensing
Min.
-40
0
10
5
3000
Typ.
Max.
70
50
90
90
Units
°C
%
M
G
K Hours
Non-Operating
30
Operational, 0.5G; 5-500Hz
Telcordia SR-332 40°C
630
CAN/CSA-C22.2 No.60950-1-07 Am 1:2011
ANSI/UL 60950-1-2011
IEC60950-1:2005 (2nd Ed)+A1:2009 and EN60950-1:2006/A11:2009/A1:2010/A12:2011
CQC GB4943,1-2011
Internal 20A/250V rated fast blow in AC line
4.63/2.1
lbs/kg
www.murata-ps.com/support
CPS_D1U4-W-1600-54-HBxC.B04
Page 2 of 6
D1U4-W-1600-54-HBxC
AC-DC Power Supply
PROTECTION CHARACTERISTICS
Output
Voltage
54V
Parameter
Over-Temperature
Over-Voltage
Over-Current
12VSB
Over-Voltage
Over-Current
Conditions
Auto re-start
Latching
Constant Current for 200ms
followed by latch
Latching
Latching
Min.
55
57
33
13.5
2.2
Typ.
Max.
65
60
39
14.4
2.6
Units
°C
V
A
V
A
ISOLATION CHARACTERISTICS
Parameter
Insulation Safety Rating / Test Voltage
Isolation
Conditions
Input to Output - Reinforced
Input to Chassis - Basic
Output to Chassis (Ground)
Min.
3000
1500
2250
Typ.
Max.
Units
Vrms
Vrms
Vdc
Grounding
The Main 54VDC output shall be provided with isolation between the output and chassis ground. It shall be able
to withstand the following tests:
a) 1500VRMS at 50Hz to 60Hz for 60s.
b) 2250 VDC for 60s.
There shall be no insulation breakdown during the test as defined in sub clause 5.2.2 of IEC 60950-1:2001. The
resistance after the test should be at least 2M ohms when measured at 500VDC.
The VRTN should be isolated from the 12VSB Return and the power module shall support PoE Electrical Isolation
Requirements.
STATUS INDICATORS AND CONTROL SIGNALS
Status
LED Indicators
Conditions
Off
Off
Blinking Green
Green
Blinking Amber
Amber
Description
No AC applied to any power module in host system
No AC applied to this power module only
AC Present & VSTANDBY “on”
54VDC and VSTANDBY “on” and “OK”
Power Module Warning
Power Module Failure
I
2
C and PMBus
SYS_CONTR
EMISSIONS AND IMMUNITY
Characteristic
Input Current Harmonics
Voltage Fluctuation & Flicker
Conducted Emissions
Radiated Emissions
ESD Immunity
Radiated Field Immunity
Electrical Fast Transients/Burst Immunity
Surge Immunity
RF Conducted Immunity
Magnetic Field Immunity
Voltage Dips & Interruptions
There is provision for the connection of dual I2C buses for redundancy.
This enables two master devices to connect to single slave device(s) within the power module.
The power module is provided with a PMBus Management Interface that provides status, measurement and
control data.
Host system control input that can be used to turn on/off the Main 54VDC Output.
Standard
IEC/EN 61000-3-2
IEC/EN 61000-3-3
FCC 47 CFR Part 15; CISPR 22; EN55022
IEC/EN 61000-4-2;
IEC/EN 61000-4-3
IEC/EN 61000-4-4
IEC/EN 61000-4-5
IEC/EN 61000-4-6
IEC/EN 61000-4-8
IEC/EN 61000-4-11
Compliance
Complies with Class A Limits
Complies
Complies to Class A with 6dB margin
Complies to Class A with 6dB margin
4KV Contact discharge; Criteria A
8KV Operational air discharge; Criteria A
15KV non-operational air discharge, Criteria A
Complies
Complies
1KV/2KV; Criteria A performance
3VAC, 80% AM, 1KHz; Criteria A performance
3A/m
Complies
www.murata-ps.com/support
CPS_D1U4-W-1600-54-HBxC.B04
Page 3 of 6
D1U4-W-1600-54-HBxC
AC-DC Power Supply
OUTPUT CONNECTOR AND SIGNAL SPECIFICATION
DC and Signal Connector: FCI # 51732-028-LF
P1
P2
P3
P4
P5
P6
x1
AC_OK
PS_ON
V
OUT
V
OUT
V
OUT
V
RTN
V
RTN
V
RTN
I_SHARE
PS_KILL
SYS_CONTR
Vout SENSE+
I
2
C DATA2
Vout SENSE-
I
2
C CLOCK2
I
2
C DATA1
PS_PRESENT
I
2
C CLOCK1
B
A
x2
P_GOOD
V_STBY
x3
V_STBY
V_STBY
x4
No User
Connection
V_STBY
RETURN
x5
V_STBY
RETURN
V_STBY
RETURN
D
C
Blade/ Pin Assignment
P1, P2, P3
P4, P5, P6
A2
A3
C2, C3, D3
C4, C5, D5
B1
D1
Signal Name
VOUT
VRTN
VOUT_SENSE +
VOUT_SENSE -
VSTBY
VSTBY Return
I_SHARE
AC_OK
Description
Main 54V Output Voltage
Main 54V Output Voltage, Return
Main 54V Output Voltage Sense +
Main 54V Output Voltage Sense -
Standby Voltage Output
Standby Voltage Output, Return
Analogue active current share bus
AC Source Voltage OK Signal
(Internally pull up to VSTANDBY by 10KΩ (3.3V & 5V
VSTANDBY).
10KΩ (to 5V) for 12 VSTANDBY
Power Good Signal
(Internally pull up to VSTANDBY by 10KΩ (3.3V & 5V
VSTANDBY).
10KΩ (to 5V) for 12 VSTANDBY
Floating pin; will turn off main output
Logic Level
Current
0V to 8V
>2.4V (Active, OK)
<0.4V (not OK)
-4mA/+5mA
+4mA
-2mA
D2
A1
B5
C1
A4
A5
B3
B4
B2
P_GOOD
PS_KILL
PS_PRESENT
PS_ON_L
I
2
C_SDA0 (SDA)
I
2
C_SCL0 (SCL)
I
2
C_SDA1 (SDA)
I
2
C_SCL1 (SCL)
SYS_CONTR
>2.4V (Active, GOOD)
<0.4V (not GOOD)
>2.4V “high”
<0.4V “low”
0V
>2.4V “high”
<0.4V “low”
+4mA
-2mA
Tied internally to VSTANDBY Return
Internally pull up to VSTANDBY by 1KΩ; can be driven with
open drain/collector switches
I
2
C compatible Data Bus
I
2
C compatible Data Bus
I
2
C compatible Data Bus
>2.4V “high”
I
2
C compatible Data Bus
<0.4V “low”
Host system control that can be used to turn on/off the Main
54V DC Output via an internal output switch within power
module. Low turns “on” output switch
MATING CONNECTOR
Supplier
FCI
Press Fit, Straight
--
Press Fit, Right Angle
--
Solder Straight
--
Solder Right Angle
51762-1060-2000-ABLF
www.murata-ps.com/support
CPS_D1U4-W-1600-54-HBxC.B04
Page 4 of 6
D1U4-W-1600-54-HBxC
AC-DC Power Supply
WIRING DIAGRAM FOR OUTPUT
-
Dotted lines show optional remote sense connections.
Optional remote sense lines can be attached to a load that is a distance
away from the power supply to improve regulation at the load.
Sense + (Main Output Remote Sense)
A2
P1, P2, P3
VOUT
Sense + (Main Output Remote Sense)
VOUT
A2
P1, P2, P3
D1U4
P4, P5, P6
A3
B1
VRTN
Sense -
I_Share
54V Load
VRTN
Sense -
I_Share
P4, P5, P6
A3
B1
D1U4
C2, C3, D3
C1
Vstby
PS_On_L
Close Switch (or FET, BJT or wire)
to turn on +54V OUT
12V Standby Load
Vstby
PS_On_L
C2, C3, D3
C1
C4, C5, D5
A1
Vsb Return
Vsb Return
C4, C5, D5
PS_Kill
PS_Kill
A1
CURRENT SHARING NOTES
1. Main 54VDC Output: Analogue active share bus. The ISHARE bus (Pin B1) must be connected on all sharing modules.
It is not required that the SENSE signals are connected to the remote load for current share to operate correctly.
2. Up to eight (8) power modules can be connected in parallel (non-redundant) or N+1 configuration. The current share bus is analogue bi-directional (can source or sink
current from the ISHARE bus).
The voltage of the bus would measure 8VDC for a single power module at 100% load; for two (2) modules sharing a common load the ISHARE bus voltage would be 4V for
a perfect 50/50 current share scenario.
3. VSTANDBY output power modules can also be connected in parallel; however the combined available power is limited to that available from a single power module (12V;
2A; 24W) irrespective of the number of modules connected in parallel.
The value of a resistor can be displayed in the schematic diagram, such as 200 ohms, but after importing it into the PCB diagram, how can its value be displayed?...
[i=s]This post was last edited by Quantum Well on 2016-12-21 11:03[/i]A zero-based AVR microcontroller learning tutorial produced by Huijing Electronics, including operation and test chapters. Welcome...
Received an email from TI today saying it has been shipped. [table=98%,#ffffff] [tr][td=25%][align=left][b]Order Number:[/b][/align][/td][td=75%] [/td][/tr] [tr][td][b]Ordered on:[/b] [/td][td][align=...
Hey, I got an inspiration when I attended the party that day. Can you guess what it is?The first person to guess it will be rewarded with 20 core coins. :)...