70~100W Constant Voltage + Constant Current LED Driver
ELG-100
series
IS 15885(Part 2/Sec13)
110
(for DA-Type only)
M
M
SELV
IP65 IP67
THOMAS SAMUEL
THOMAS SAMUEL
Type HL
R-41027766
(for 24/24B/36/36A/42/42A/48/48B/54/54A only)
■
Features
Constant Voltage + Constant Current mode output
Metal housing design with functional Ground
Built-in active PFC function
■
Applications
LED street lighting
LED architectural lighting
LED bay lighting
LED floodlighting
Type HL for use in Class I, Division 2
hazardous (Classified) location.
Class 2 power unit
No load / Standby power consumption
<0.5W
IP67 / IP65 rating for indoor or outdoor installations
Function options: output adjustable via potentiometer;
3 in 1 dimming (dim-to-off); Smart timer dimming; DAL
I
Typical lifetime>50000 hours
5 years warranty
■
Description
ELG-100 series is a 100W AC/DC LED driver featuring the dual mode constant voltage
and constant current output. ELG-100 operates from 100
½
360VAC and offers models with
different rated voltage ranging between 24V and 54V. Thanks to the high efficiency up to 91%,
with the fanless design, the entire series is able to operate for -40
℃
~ +90
℃
case temperature under
free air convection. The design of metal housing and IP67/IP65 ingress protection level allows this
series to fit both indoor and outdoor applications. ELG-100 is equipped with various function options,
such as dimming methodologies, so as to provide the optimal design flexibility for LED lighting system
■
Model Encoding
ELG - 100 - 36
A
-
Blank:2-wire input for standard model
Input wiring type
3Y:3-wire input for standard model
Function mode option
Rated output
voltage(24/36/42/48/54V)
Rated
wattage
Series name
Function
Note
In Stock
In Stock
In Stock
In Stock
In Stock
By request
In Stock
{
Type
Blank
A
B
AB
DA
Dx
D2
IP Level
IP67
IP65
IP67
IP65
IP67
IP67
IP67
Io and Vo fixed.
Io
and Vo
adjustable through built-in potentiometer.
3 in 1 dimming function (0~10Vdc, 10V PWM signal and resistance)
Io and Vo adjustable through built-in potentiometer &
3 in 1 dimming function (0~10Vdc, 10V PWM signal and resistance)
DALI control technology.
Built-in Smart timer dimming function by user request.
Built-in Smart timer dimming and programmable function.
File Name:ELG-100-SPEC 2018-08-16
70~100W Constant Voltage + Constant Current LED Driver
SPECIFICATION
MODEL
DC VOLTAGE
ELG-100-24
24V
CONSTANT CURRENT REGION
Note.2
12 ~ 24V
RATED CURRENT
4.0A
200VAC ~ 305VAC
RATED POWER
96W
100VAC ~ 180VAC
70W
RIPPLE & NOISE (max.)
Note.3
200mVp-p
VOLTAGE ADJ. RANGE
OUTPUT
CURRENT ADJ. RANGE
21.6 ~ 26.4V
2 ~ 4A
±0.5%
±1.0%
1000ms, 80ms/115VAC
15ms/115VAC
Note.5
ELG-100
54V
27 ~ 54V
1.78A
96.12W
70W
350mVp-p
series
ELG-100-36
36V
18 ~ 36V
2.66A
95.76W
70W
250mVp-p
32.4 ~ 39.6V
1.33 ~ 2.66A
±2.5%
±0.5%
±1.0%
10ms/230VAC
ELG-100-42
42V
21 ~ 42V
2.28A
95.76W
70W
250mVp-p
37.8 ~ 46.2V
1.14 ~ 2.28A
±2.5%
±0.5%
±0.5%
ELG-100-48
48V
24 ~ 48V
2A
96W
70W
300mVp-p
43.2 ~ 52.8V
1 ~ 2A
±2.0%
±0.5%
±0.5%
ELG-100-54
Adjustable for A/AB-Type only (via the built-in potentiometer)
48.6 ~ 59.4V
0.89 ~ 1.78A
±2.0%
±0.5%
±0.5%
Adjustable for A/AB-Type only (via the built-in potentiometer)
VOLTAGE TOLERANCE
Note.4
±3.0%
LINE REGULATION
LOAD REGULATION
SETUP, RISE TIME
Note.6
HOLD UP TIME (Typ.)
VOLTAGE RANGE
FREQUENCY RANGE
POWER FACTOR
500ms, 100ms/230VAC
100 ~ 305VAC
47 ~ 63Hz
142 ~ 431VDC continue,320VAC for 24Hrs; 360VAC for 1Hr
(Please refer to "STATIC CHARACTERISTIC" section)
PF
≧
0.97/115VAC, PF
≧
0.95/230VAC, PF
≧
0.92/277VAC@full load
(Please refer to "POWER FACTOR (PF) CHARACTERISTIC" section)
THD< 20%(@load
≧
50%/115VC; @load
≧
60%/230VAC; @load
≧
75%/277VAC)
(Please refer to “TOTAL HARMONIC DISTORTION(THD)” section)
88%
1.1A / 115VAC
89%
0.6A / 230VAC
90%
0.5A/277VAC
90%
91%
TOTAL HARMONIC DISTORTION
INPUT
EFFICIENCY (Typ.)
AC CURRENT
INRUSH CURRENT(Typ.)
COLD START 60A(twidth=850
μ
s measured at 50% Ipeak) at 230VAC
;
Per NEMA 410
3 units (circuit breaker of type B) / 6 units (circuit breaker of type C) at 230VAC
<0.75mA / 277VAC
MAX. No. of PSUs on 16A
CIRCUIT BREAKER
LEAKAGE CURRENT
NO LOAD / STANDBY
POWER CONSUMPTION
OVER CURRENT
No load power consumption <0.5W for Blank / A / Dx / D2-Type
Standby power consumption <0.5W for B / AB / DA-Type
95 ~ 108%
Constant current limiting, recovers automatically after fault condition is removed
SHORT CIRCUIT
PROTECTION
OVER VOLTAGE
OVER TEMPERATURE
WORKING TEMP.
MAX. CASE TEMP.
WORKING HUMIDITY
ENVIRONMENT STORAGE TEMP., HUMIDITY
TEMP. COEFFICIENT
VIBRATION
SAFETY STANDARDS
DALI STANDARDS
SAFETY & WITHSTAND VOLTAGE
ISOLATION RESISTANCE
EMC
EMC EMISSION
EMC IMMUNITY
MTBF
OTHERS
DIMENSION
PACKING
NOTE
Hiccup mode, recovers automatically after fault condition is removed
47 ~ 54V
28 ~ 34V
41 ~ 48V
Shut down output voltage, re-power on to recover
54 ~ 62V
62 ~ 72V
Shut down output voltage, re-power on to recover
Tcase=-40 ~ +90
℃
(Please refer to “ OUTPUT LOAD vs TEMPERATURE” section)
Tcase=+90℃
20 ~ 95% RH non-condensing
-40 ~ +80
℃
, 10 ~ 95% RH
±
0.03%/
℃
(0 ~ 60
℃
)
10 ~ 500Hz, 5G 12min./1cycle, period for 72min. each along X, Y, Z axes
UL8750
(type”HL”)
,
CSA C22.2 No. 250.13-12;
IEC/EN/AS/NZS 61347-1, IEC/EN/AS/NZS 61347-2-13
independent, EN62384;
EAC TP TC 004;BIS IS15885(for 24/24B/36/36A/42/42A/48/48B/54/54A only);
GB19510.1, GB19510.14 ; IP65 or IP67;
KC KN61347
-
1
,
KN61347
-
2
-
13
approved
Compliance to IEC62386-101, 102, 207 for DA-Type only
I/P-O/P:3.75KVAC
I/P-FG:2.0KVAC
O/P-FG:1.5KVAC
I/P-O/P, I/P-FG, O/P-FG:100M Ohms / 500VDC / 25
℃
/ 70% RH
Compliance to EN55015,EN61000-3-2 Class C (@load
≧
60%); EN61000-3-3;GB17743, GB17625.1
;EAC TP TC 020; K
C KN15,KN61547
Compliance to EN61000-4-2,3,4,5,6,8,11; EN61547, light industry level (surge immunity Line-Earth 6KV, Line-Line 4KV)
;EAC TP TC 020; KC KN15
,
KN61547
978.2K hrs min. Telcordia SR-332 (Bellcore)
199*63*35.5mm (L*W*H)
282.9Khrs min.
MIL-HDBK-217F (25
℃
)
0.85kg; 16pcs/14.2kg/0.72CUFT
1. All parameters NOT specially mentioned are measured at 230VAC input, rated current and 25
℃
of ambient temperature.
2. Please refer to "DRIVING METHODS OF LED MODULE". For DA-Type, Constant Current region is 60%~100% of maximum voltage
under rated power delivery.
3. Ripple & noise are measured at 20MHz of bandwidth by using a 12" twisted pair-wire terminated with a 0.1uf & 47uf parallel capacitor.
4. Tolerance : includes set up tolerance, line regulation and load regulation.
5. De-rating may be needed under low input voltages. Please refer to STATIC CHARACTERISTIC sections for details.
6. Length of set up time is measured at first cold start. Turning ON/OFF the driver may lead to increase of the set up time.
7. The driver is considered as a component that will be operated in combination with final equipment. Since EMC performance will be affected by the
complete installation, the final equipment manufacturers must re-qualify EMC Directive on the complete installation again.
8. This series meets the typical life expectancy of >50,000 hours of operation when Tcase, particularly tc point (or TMP, per DLC), is about 80
℃
or less.
9. Please refer to the warranty statement on MEAN WELL's website at http://www.meanwell.com
10.The ambient temperature derating of 3.5
℃
/1000m with fanless models and of 5
℃
/1000m with fan models for operating altitude higher than 2000m(6500ft).
File Name:ELG-100-SPEC 2018-08-16
70~100W Constant Voltage + Constant Current LED Driver
Block Diagram
ELG-100
series
PFC fosc : 50~120KHz
PWM fosc : 60~130KHz
I/P
EMI FILTER
&
RECTIFIERS
PFC
CIRCUIT
POWER
SWITCHING
RECTIFIERS
&
FILTER
O.L.P.
Vo+
Vo-
O.T.P.
O.L.P.
PWM & PFC
CONTROL
DETECTION
CIRCUIT
O.V.P.
CASE :Protective Earth
DRIVING METHODS OF LED MODULE
※
This series is able to work in either Constant Current mode (a direct drive way) or
Constant Voltage mode (usually through additional DC/DC driver) to drive the LEDs.
100
(A)
Constant
V
oltage
area
(B)
Constant
Current area
In the constant current region, the highest voltage at the output of the driver
depends on the configuration of the end systems.
Should there be any compatibility issues, please contact MEAN WELL.
50
(min.)
(C)
Hiccup
Protection
50
100
Io(%)
Vo(%)
Typical output current normalized by rated current (%)
◎
This characteristic applies to Blank/A/B/AB/DX/D2-Type,
For DA-Type, the Constant Current area is 60%~100% Vo.
File Name:ELG-100-SPEC 2018-08-16
70~100W Constant Voltage + Constant Current LED Driver
DIMMING OPERATION
ELG-100
series
AC/N(Blue)
AC/L(Brown)
ELG-100
DIM+(
Blue
)*
DIM-(White)**
Vo-(Black)
Vo+(Red)
* DIM+ for B/AB-Type
DA+ for DA-Type
PROG+ for D2-Type
* *DIM- for B/AB-Type
DA- for DA-Type
PROG- for D2-Type
※
3 in 1 dimming function (for B/AB-Type)
Output constant current level can be adjusted by applying one of the three methodologies between DIM+ and DIM-:
0 ~ 10VDC, or 10V PWM signal or resistance.
Direct connecting to LEDs is suggested. It is not suitable to be used with additional drivers.
Dimming source current from power supply: 100
μ
A (typ.)
◎
Applying additive 0 ~ 10VDC
100%
90%
80%
Output current (%)
Vo+
Vo-
DIM+
+
-
+
Additive Voltage
-
+
-
70%
60%
50%
40%
30%
20%
10%
0%
0V 1V
2V 3V 4V 5V 6V 7V 8V 9V 10V
Dimming input: Additive voltage
DIM-
“DO
NOT connect "DIM- to Vo-"
◎
Applying additive 10V PWM signal (frequency range 100Hz ~ 3KHz):
100%
90%
80%
Output current (%)
Vo+
Vo-
DIM+
+
-
+
-
70%
60%
50%
40%
30%
20%
Additive PWM signal
DIM-
“DO
NOT connect "DIM- to Vo-"
10%
0%
0% 10% 20% 30% 40% 50% 60% 70% 80% 90% 100%
Duty cycle of additive 10V PWM signal dimming input
◎
Applying additive resistance:
+
-
100%
90%
Vo+
Vo-
DIM+
+
Output current (%)
80%
70%
60%
50%
40%
30%
-
Additive Resistance
DIM-
“DO
NOT connect "DIM- to Vo-"
20%
10%
0%
Short
10K/N 20K/N 30K/N 40K/N 50K/N 60K/N 70K/N 80K/N 90K/N 100K/N
(N=driver quantity for
synchronized
dimming operation
)
Dimming input: Additive resistance
Note : 1. Min. dimming level is about 8% and the output current is not defined when 0%<
I
out<8%.
2. The output current could drop down to 0% when dimming input is about 0k
Ω
or 0Vdc, or 10V PWM signal with 0% duty cycle.
File Name:ELG-100-SPEC 2018-08-16
70~100W Constant Voltage + Constant Current LED Driver
※
DAL
I
Interface (primary side; for DA-Type)
Apply DALI signal between DA+ and DA-.
DAL
I
protocol comprises 16 groups and 64 addresses.
First step is fixed at 8% of output.
ELG-100
series
※
Smart timer dimming function (for Dxx-Type by User definition)
MEAN WELL Smart timer dimming primarily provides the adaptive proportion dimming profile for the output constant current level to perform up to 14
consecutive hours. 3 dimming profiles hereunder are defined accounting for the most frequently seen applications. If other options may be needed,
please contact MEAN WELL for details.
Ex :
◎
D01-Type: the profile recommended for residential lighting
Set up for D01-Type in Smart timer dimming software program:
Dimming Level(%)
T1
TIME**
LEVEL**
06:00
100%
T2
07:00
70%
T3
11:00
50%
T4
---
70%
Operating Time(HH:MM)
**: TIME matches Operating Time in the diagram whereas LEVEL matches Dimming Level.
Example: If a residential lighting application adopts D01-Type, when turning on the power supply at 6:00pm, for instance:
[1] The power supply will switch to the constant current level at 100% starting from 6:00pm.
[2] The power supply will switch to the constant current level at 70% in turn, starting from 0:00am, which is 06:00 after the power supply turns on.
[3] The power supply will switch to the constant current level at 50% in turn, starting from 1:00am, which is 07:00 after the power supply turns on.
[4] The power supply will switch to the constant current level at 70% in turn, starting from 5:00am, which is 11:00 after the power supply turns on.
The constant current level remains till 8:00am, which is 14:00 after the power supply turns on.
Ex:
◎
D02-Type: the profile recommended for street lighting
Set up for D02-Type in Smart timer dimming software program:
Dimming Level(%)
T1
TIME**
LEVEL**
01:00
50%
T2
03:00
80%
T3
8:00
100%
T4
11:00
60%
T5
---
80%
Operating Time(HH:MM)
**: TIME matches Operating Time in the diagram whereas LEVEL matches Dimming Level.
Example: If a street lighting application adopts D02-Type, when turning on the power supply at 5:00pm, for instance:
[1] The power supply will switch to the constant current level at 50% starting from 5:00pm.
[2] The power supply will switch to the constant current level at 80% in turn, starting from 6:00pm, which is 01:00 after the power supply turns on.
[3] The power supply will switch to the constant current level at 100% in turn, starting from 8:00pm, which is 03:00 after the power supply turns on.
[4] The power supply will switch to the constant current level at 60% in turn, starting from 1:00am, which is 08:00 after the power supply turns on.
[5] The power supply will switch to the constant current level at 80% in turn, starting from 4:00am, which is 11:00 after the power supply turns on. The
constant current level remains till 6:30am, which is 14:00 after the power supply turns on.
File Name:ELG-100-SPEC 2018-08-16