DC-DC Converters PCB Mount type
Ordering information
ZUS1R5
R
ZU
1
2
S
1R5
3
4
12
5
05
1Series
name
2Single
output
3Output
wattage
4Input
voltage
5Output
voltage
MODEL
MAX OUTPUT WATTAGE[W]
DC OUTPUT
ZUS1R50505
1.50
VOLTAGE[V] 5
CURRENT[A] 0.30
ZUS1R50512
1.56
12
0.13
ZUS1R50515
1.50
15
0.10
ZUS1R51205
1.50
5
0.30
ZUS1R51212
1.56
12
0.13
ZUS1R51215
1.50
15
0.10
ZUS1R52405
1.50
5
0.30
ZUS1R52412
1.56
12
0.13
ZUS1R52415
1.50
15
0.10
ZUS1R54805
1.50
5
0.30
ZUS1R54812
1.56
12
0.13
ZUS1R54815
1.50
15
0.10
SPECIFICATIONS
MODEL
VOLTAGE[V]
*
1
CURRENT[A]
INPUT
*
1
EFFICIENCY[%]
VOLTAGE[V]
CURRENT[A]
LINE REGULATION[mV]
LOAD REGULATION[mV]
*
2
RIPPLE[mVp-p]
OUTPUT
RIPPLE NOISE[mVp-p]
*
2
TEMPERATURE REGULATION[mV] -20 to +55
C
*
3
DRIFT[mV]
START-UP TIME[ms]
OUTPUT VOLTAGE ADJUSTMENT RANGE[V]
OUTPUT VOLTAGE SETTING[V]
PROTECTION
OVERCURRENT PROTECTION
CIRCUIT
INPUT-OUTPUT
ISOLATION INPUT-CASE
OUTPUT-CASE
OPERATING TEMP.,HUMID.AND ALTITUDE
STORAGE TEMP.,HUMID.AND ALTITUDE
ENVIRONMENT
VIBRATION
IMPACT
SAFETY
AGENCY APPROVALS
CASE SIZE/WEIGHT
OTHERS
COOLING METHOD
*1
*2
*3
*
ZU/ZT
ZUS1R50505 ZUS1R50512 ZUS1R50515 ZUS1R51205 ZUS1R51212 ZUS1R51215 ZUS1R52405 ZUS1R52412 ZUS1R52415 ZUS1R54805 ZUS1R54812
DC4.5 - 9
DC9 - 18
DC18 - 36
DC36 - 72
0.441typ 0.459typ 0.441typ 0.176typ 0.183typ 0.176typ 0.088typ 0.092typ 0.088typ 0.043typ 0.045typ
68typ
68typ
68typ
71typ
71typ
71typ
71typ
71typ
71typ
73typ
73typ
5
12
15
5
12
15
5
12
15
5
12
0.30
0.13
0.10
0.30
0.13
0.10
0.30
0.13
0.10
0.30
0.13
20max 48max 60max 20max 48max 60max 20max 48max 60max 20max 48max
40max 100max 120max 40max 100max 120max 40max 100max 120max 40max 100max
80max 120max 120max 80max 120max 120max 80max 120max 120max 80max 120max
120max 150max 150max 120max 150max 150max 120max 150max 150max 120max 150max
50max 150max 180max 50max 150max 180max 50max 150max 180max 50max 150max
20max 48max 60max 20max 48max 60max 20max 48max 60max 20max 48max
20max (Minimum input, Io=100%)
Fixed
4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 4.85 - 5.25 11.40 - 12.60
Works over 105% of rating and recovers automatically
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
-20 to +71
C
, 20 - 95%RH (Non condensing) (Refer to DERATING CURVE), 3,000m (10,000feet)
-40 to +85
C
, 20 - 95%RH (Non condensing), 9,000m (30,000feet) max
10 - 55Hz, 98.0m/s
2
(10G), 3minutes period, 60minutes each along X, Y and Z axis
490.3m/s
2
(50G), 11ms, once each X, Y and Z axis
UL60950-1, EN60950-1, EN50178, CSA C22.2 No.60950-1 Complies with IEC60950-1
27.5
X
7
X
18mm (W
X
H
X
D) / 10g max
Convection
ZUS1R54815
0.043typ
73typ
15
0.10
60max
120max
120max
150max
180max
60max
14.25 - 15.75
max
Rated input 5V, 12V, 24V or 48V DC Io=100%.
Measured by 20MHz oscilloscope.
The drift is a change at 25C of ambient temperature and 30 minutes - 8 hours after the input voltage applied at rated input/output.
Series/Parallel operation with other model is not possible.
ZU/ZT-2
ZUS1R5
External view
¶Recomended
size for
processing PCB
Name plate
27.5
+V
(0.5)
(TOP VIEW)
(19.465)
Outline
(1.25)
(1.25) 2-º1.6
Size between
case pins
12.7
18
17.78
+V
-V
IN
OUT
6.35
17.78
12.7
6.35
[0.25]
[0.5]
-V
2-A part
2-B part
±0.3
¶Specification
at A part
(2.54)
¶Specification
at B part
[0.25]
6.35
8.89
[0.35]
(8.035)
7
0.4
4
0.4
4-º1.5
4-º1
±0.1
11.43
21.59
(8.035)
(2.955)
2.5
1
±0.1
2.7
8.89
(9.305)
2.5
¶Weight: 10g or less.
¶Tolerance:
±
0.5
¶Case material: Brass
(1.25)
21.59
[0.85]
(1.25)
The converter is in contact with the
slanted area of the P.C.B. To keep
mm
isolation, adequate wiring on the
¶Dimensions
in
[inch]
¶Div.:
0.1inch
mounted side is required.
Performance data
¡
STATIC CHARACTERISTICS (ZUS1R52405)
¡
RISE TIME & FALL TIME (ZUS1R52405)
[0.7]
ZU/ZT
¡
OVERCURRENT CHARACTERISTICS (ZUS1R52405)
¡
DERATING CURVE
ZU/ZT-3
DC-DC Converters PCB Mount type
Ordering information
ZUS3
R
ZU
1
2
S
3
3
4
12
5
05
1Series
name
2Single
output
3Output
wattage
4Input
voltage
5Output
voltage
MODEL
MAX OUTPUT WATTAGE[W]
DC OUTPUT
ZUS30505
3
VOLTAGE[V] 5
CURRENT[A] 0.60
ZUS30512
3
12
0.25
ZUS30515
3
15
0.20
ZUS31205
3
5
0.60
ZUS31212
3
12
0.25
ZUS31215
3
15
0.20
ZUS32405
3
5
0.60
ZUS32412
3
12
0.25
ZUS32415
3
15
0.20
ZUS34805
3
5
0.60
ZUS34812
3
12
0.25
ZUS34815
3
15
0.20
SPECIFICATIONS
MODEL
VOLTAGE[V]
*
1
CURRENT[A]
INPUT
*
1
EFFICIENCY[%]
VOLTAGE[V]
CURRENT[A]
LINE REGULATION[mV]
LOAD REGULATION[mV]
*
2
RIPPLE[mVp-p]
OUTPUT
RIPPLE NOISE[mVp-p]
*
2
TEMPERATURE REGULATION[mV] -20 to +55
C
*
3
DRIFT[mV]
START-UP TIME[ms]
OUTPUT VOLTAGE ADJUSTMENT RANGE[V]
OUTPUT VOLTAGE SETTING[V]
PROTECTION
OVERCURRENT PROTECTION
CIRCUIT
INPUT-OUTPUT
ISOLATION INPUT-CASE
OUTPUT-CASE
OPERATING TEMP.,HUMID.AND ALTITUDE
STORAGE TEMP.,HUMID.AND ALTITUDE
ENVIRONMENT
VIBRATION
IMPACT
SAFETY
AGENCY APPROVALS
CASE SIZE/WEIGHT
OTHERS
COOLING METHOD
*1
*2
*3
*
ZU/ZT
ZUS30505 ZUS30512 ZUS30515 ZUS31205 ZUS31212 ZUS31215 ZUS32405 ZUS32412 ZUS32415 ZUS34805 ZUS34812
DC4.5 - 9
DC9 - 18
DC18 - 36
DC36 - 72
0.896typ 0.857typ 0.857typ 0.357typ 0.338typ 0.338typ 0.176typ 0.167typ 0.167typ 0.088typ 0.082typ
67typ
70typ
70typ
70typ
74typ
74typ
71typ
75typ
75typ
71typ
76typ
5
12
15
5
12
15
5
12
15
5
12
0.60
0.25
0.20
0.60
0.25
0.20
0.60
0.25
0.20
0.60
0.25
20max 48max 60max 20max 48max 60max 20max 48max 60max 20max 48max
40max 100max 120max 40max 100max 120max 40max 100max 120max 40max 100max
80max 120max 120max 80max 120max 120max 80max 120max 120max 80max 120max
120max 150max 150max 120max 150max 150max 120max 150max 150max 120max 150max
50max 150max 180max 50max 150max 180max 50max 150max 180max 50max 150max
20max 48max 60max 20max 48max 60max 20max 48max 60max 20max 48max
20max (Minimum input, Io=100%)
Fixed
4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 4.85 - 5.25 11.40 - 12.60
Works over 105% of rating and recovers automatically
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
-20 to +71
C
, 20 - 95%RH (Non condensing) (Refer to DERATING CURVE), 3,000m (10,000feet)
-40 to +85
C
, 20 - 95%RH (Non condensing), 9,000m (30,000feet) max
10 - 55Hz, 98.0m/s
2
(10G), 3minutes period, 60minutes each along X, Y and Z axis
490.3m/s
2
(50G), 11ms, once each X, Y and Z axis
UL60950-1, EN60950-1, CSA C22.2 No.60950-1 Complies with IEC60950-1
35
X
7
X
23mm (W
X
H
X
D) / 16g max
Convection
ZUS34815
0.082typ
76typ
15
0.20
60max
120max
120max
150max
180max
60max
14.25 - 15.75
max
Rated input. 5V, 12V, 24V or 48V DC, Io=100%
Measured by 20MHz oscilloscope.
The drift is a change at 25C of ambient temperature and 30 minutes - 8 hours after the input voltage applied at rated input/output.
Series/Parallel operation with other model is not possible.
ZU/ZT-4
ZUS3
External view
¶Recomended
size for
processing PCB
(0.5)
35
Name plate
+V
-V
IN
OUT
+V
7.62 7.62
22.86
23
(TOP VIEW)
Outline
(1.25) (1.25)
Size between
case pins
2-º1.6
15.24
6.35
[0.25]
22.86
[0.6]
(3.81)
7.62
2-A part
2-B part
4 7
±0.3
¶Specification
at A part
¶Specification
at B part
[0.3]
0.4
0.4
(1.25)
16.51
[0.65]
(1.25) 4-º1.5
16.51
29.21
2.7
(9.245)
(2.895)
4-º1
±0.1
2.5
1
±0.1
2.5
¶Weight: 16g or less.
¶Tolerance:
±
0.5
¶Case material: Brass
29.21
[1.15]
The converter is in contact with the
slanted area of the P.C.B. To keep
mm
isolation, adequate wiring on the
¶Dimensions
in
[inch]
mounted side is required.
¶Div.:
0.1inch
Performance data
¡
STATIC CHARACTERISTICS (ZUS32405)
¡
RISE TIME & FALL TIME (ZUS32405)
[0.9]
-V
ZU/ZT
¡
OVERCURRENT CHARACTERISTICS (ZUS32405)
¡
DERATING CURVE
ZU/ZT-5
DC-DC Converters PCB Mount type
Ordering information
ZUS6
R
ZU
1
2
S
3
6
4
12
5
05
1Series
name
2Single
output
3Output
wattage
4Input
voltage
5Output
voltage
MODEL
MAX OUTPUT WATTAGE[W]
DC OUTPUT
ZUS6053R3
3.3
VOLTAGE[V] 3.3
CURRENT[A] 1.0
ZUS60505
5
5
1.0
ZUS60512
6
12
0.5
ZUS60515
6
15
0.4
ZUS61205
6
5
1.2
ZUS61212
6
12
0.5
ZUS61215
6
15
0.4
ZUS62405
6
5
1.2
ZUS62412
6
12
0.5
ZUS62415
6
15
0.4
ZUS6483R3
3.96
3.3
1.2
ZUS64805
6
5
1.2
ZUS64812
6
12
0.5
ZUS64815
6
15
0.4
SPECIFICATIONS
MODEL
VOLTAGE[V]
*
1
CURRENT[A]
INPUT
*
1
EFFICIENCY[%]
VOLTAGE[V]
CURRENT[A]
LINE REGULATION[mV]
LOAD REGULATION[mV]
*
2
RIPPLE[mVp-p]
OUTPUT
RIPPLE NOISE[mVp-p]
*
2
TEMPERATURE REGULATION[mV] -20 to +55
C
*
3
DRIFT[mV]
START-UP TIME[ms]
OUTPUT VOLTAGE ADJUSTMENT RANGE[V]
OUTPUT VOLTAGE SETTING[V]
PROTECTION
OVERCURRENT PROTECTION
CIRCUIT
INPUT-OUTPUT
ISOLATION INPUT-CASE
OUTPUT-CASE
OPERATING TEMP.,HUMID.AND ALTITUDE
STORAGE TEMP.,HUMID.AND ALTITUDE
ENVIRONMENT
VIBRATION
IMPACT
SAFETY
AGENCY APPROVALS
CASE SIZE/WEIGHT
OTHERS
COOLING METHOD
*1
*2
*3
*
ZU/ZT
ZUS6053R3 ZUS60505 ZUS60512 ZUS60515 ZUS61205 ZUS61212 ZUS61215 ZUS62405 ZUS62412 ZUS62415 ZUS6483R3 ZUS64805 ZUS64812 ZUS64815
DC4.5 - 9
DC9 - 18
DC18 - 36
DC36 - 72
0.94typ 1.41typ 1.63typ 1.63typ 0.69typ 0.65typ 0.65typ 0.35typ 0.33typ 0.33typ 0.09typ 0.18typ 0.17typ 0.17typ
70typ 71typ 74typ 74typ 73typ 78typ 78typ 73typ 78typ 78typ 73typ 73typ 78typ 78typ
3.3
5
12
15
5
12
15
5
12
15
3.3
5
12
15
1.0
1.0
0.5
0.4
1.2
0.5
0.4
1.2
0.5
0.4
1.2
1.2
0.5
0.4
20max 20max 48max 60max 20max 48max 60max 20max 48max 60max 20max 20max 48max 60max
40max 40max 100max 120max 40max 100max 120max 40max 100max 120max 40max 40max 100max 120max
80max 80max 120max 120max 80max 120max 120max 80max 120max 120max 80max 80max 120max 120max
120max 120max 150max 150max 120max 150max 150max 120max 150max 150max 120max 120max 150max 150max
50max 50max 150max 180max 50max 150max 180max 50max 150max 180max 50max 50max 150max 180max
20max 20max 48max 60max 20max 48max 60max 20max 48max 60max 20max 20max 48max 60max
20max (Minimum input, Io=100%)
Fixed
3.20 - 3.47 4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 4.85 - 5.25 11.40 - 12.60 14.25 - 15.75 3.20 - 3.47 4.85 - 5.25 11.40 - 12.60 14.25 - 15.75
Works over 105% of rating and recovers automatically
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
AC500V 1minute, Cutoff current = 10mA, DC500V 50M
W
min (20
t
15
C
)
-20 to +71
C
, 20 - 95%RH (Non condensing) (Refer to DERATING CURVE), 3,000m (10,000feet) max
-40 to +85
C
, 20 - 95%RH (Non condensing), 9,000m (30,000feet) max
10 - 55Hz, 98.0m/s
2
(10G), 3minutes period, 60minutes each along X, Y and Z axis
490.3m/s
2
(50G), 11ms, once each X, Y and Z axis
UL60950-1, EN60950-1, CSA C22.2 No.60950-1 Complies with IEC60950-1
44.5
X
7
X
28mm (W
X
H
X
D) / 25g max
Convection
Rated input. 5V, 12V, 24V or 48V DC, Io=100%
Measured by 20MHz oscilloscope.
The drift is a change at 25C of ambient temperature and 30 minutes - 8 hours after the input voltage applied at rated input/output.
Series/Parallel operation with other model is not possible.
ZU/ZT-6