8.3kV E-Rated
Medium voltage fuses for feeder circuit, switchgear and transformer
protection
Features and benefits:
•
Current-limiting E-Rated medium voltage
fuses are defined by their melting
time-current characteristic that permit their
electrical interchangeability with other fuses
of the same E Rating.
E-Rated fuses must have a defined current
response time specified by ANSI C37.46.
E-Rated fuse of 100 amps and below must
melt in 300 seconds at an RMS current
within the range of 200% to 240% of the
fuse’s nameplate current rating. E-Rated
fuses greater than 100 amps must melt
in 600 seconds at an RMS current within
the range of 220% to 264% of the fuse’s
nameplate current rating.
E-Rated fuses are physically dimensioned for
easy installation in existing hardware.
Current-limiting fuses provide positive
interruption even on low fault currents.
The fuse limits the magnitude of
electromechanical stresses in the protected
apparatus.
Constructions available in ferrule, bolt-on
and clip lock, and specialty mount fuses for
AMPGARD™ motor starters.
Outdoor rating available on select catalog
numbers (requires installation in a suitable
enclosure).
Open fuse indicator easily integrates
into automation schemes and speeds
troubleshooting by providing a positive
visual indication of fuse operation.
50/60Hz operating frequency for worldwide
application.
Mountings are available in disconnect and
non-disconnect versions with porcelain or
glass polyester insulators.
Live parts and end fittings available.
•
•
•
Description:
•
E-Rated, current-limiting, medium voltage
fuses for feeder circuit, switchgear and
transformer protection.
•
•
•
•
•
•
Typical applications:
•
Medium voltage transformer primary
protection
Medium voltage feeder circuit protection
Medium voltage switches
Medium voltage metal-enclosed switchgear
•
•
•
Technical Data 10352
Effective December 2015
8.3kV E-Rated medium voltage fuses for
feeder circuit, switchgear and transformer protection
E-Rated medium voltage ferrule fuses
Catalog symbols:
•
•
•
Agency information:
E-Rated fuses meet the performance characteristics of
ANSI C37.46
B
A
8CLE-_E-D (10-25A)
8CLE-_E (10-350A)
8HLE-_E (10-350A)
Volts
•
8.3kV
Amps 10 to 350A
Interrupting ratings — 50kA RMS Sym
Ratings*:
•
•
•
* See catalog number tables for voltages, ampacities and interrupting ratings
by catalog number.
3.31
(84.1)
A
C
Recommended fuse holders:
Catalog number
Fuse
mounting
type*
Non-
disconnect
Disconnect
†
Non-
disconnect
Disconnect
†
Non-
disconnect
Disconnect
Non-
disconnect
Disconnect
†
Non-
disconnect
Disconnect
†
Voltage
BIL
(kV)
Approximate dimensions - in (mm)
Diameter Clip center Length
A
B
C
Mounting (including live parts, end fittings)**
Porcelain
insulator
Glass-polyester
insulator
Amp rating
CLE
10E-D–25E-D
30E–175E
Single barrel
15E–25E
Single Barrel
200E–350E
Double barrel
Live parts
(including
end fittings)
End fittings
(disconnect
only)
75
75
75
75
75
75
3.0 (76)
14 (356)
17.9 (455)
8CLE-PNM-D
8CLE-PDM-D
8CLE-GNM-D
8CLE-GDM-D
8CLE-GNM-C
8CLE-GDM-C
8CLE-GNM-E
8CLE-GDM-E
CLE-NL-D
CLE-DL-D
CLE-NL-C
CLE-DL-C
CLE-NL-E
CLE-DL-E
—
CLE-DF-D
—
CLE-DF-C
—
CLE-DF-E
2.0 (51)
14 (356)
15.5 (394)
8CLE-PNM-C
8CLE-PDM-C
3.0 (76)
14 (356)
17.9 (455)
8CLE-PNM-E
8CLE-PDM-E
HLE
10E-175E
Single barrel
200E–350E
Double barrel
75
75
75
75
3.0 (76)
12 (305)
15.9 (404)
3.0 (76)
12 (305)
15.9 (404)
8HLE-PNM-D
8HLE-PDM-D
8HLE-PNM-E
8HLE-PDM-E
8HLE-GNM-D
8HLE-GDM-D
8HLE-GNM-E
8HLE-GDM-E
CLE-NL-D
CLE-DL-D
CLE-NL-E
CLE-DL-E
—
CLE-DF-D
—
CLE-DF-E
* See page 4 for illustrations and dimensions
** End fittings supplied only when required.
Recommended fuseclips:
Description
Enclosed fuseclip
Enclosed fuseclip
Open fuseclip
Spring loaded open
fuseclip
Fuse diameter -
in (mm)
2 (51)
3 (76)
3 (76)
3 (76)
Clip dimensions - in (mm)
Figure
1
1
2
3
A
3.75 (95)
4.14 (105)
B
1.98 (50)
2.45 (62)
C
2.01 (51)
3.01 (76)
D
1.19 (30)
1.19 (30)
E
4.54 (115)
5.64 (143)
F
1.51 (38)
1.51 (38)
G
0.4 (10)
0.4 (10)
Catalog
number
A3354710*
A3354730*
1A0065
9078A67G04
See dimensions drawing
See dimensions drawing
Figure 1
*For single barrel applications only. Not sold in pairs.
Figure 2
Figure 3
C
A
B
D
G
F
E
2
Eaton.com/bussmannseries
8.3kV E-Rated medium voltage fuses for
feeder circuit, switchgear and transformer protection
CLE and HLE type fuses
Dimensions - in (mm)
Amp rating Length A
Diameter B
Clip centers C
14
14
14
14
14
14
14
14
14
14
14
14
14
14
14
14
14
14
14
14
12
12
12
12
12
12
12
12
12
12
12
12
12
12
12
12
12
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(356)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
(305)
Interrupting
rating kA
(RMS Sym.)
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
50
Number of
barrels
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
2
2
2
2
1
1
1
1
1
1
1
1
1
1
1
1
1
2
2
2
2
Technical Data 10352
Effective December 2015
Installation
location
Indoor/outdoor
Indoor
Indoor/outdoor
Indoor
Indoor/outdoor
Indoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Indoor/outdoor
Catalog
number
8CLE-10E-D
8CLE-15E*
8CLE-15E-D
8CLE-20E*
8CLE-20E-D
8CLE-25E*
8CLE-25E-D
8CLE-30E
8CLE-40E
8CLE-50E
8CLE-65E
8CLE-80E
8CLE-100E
8CLE-125E
8CLE-150E
8CLE-175E
8CLE-200E
8CLE-250E
8CLE-300E
8CLE-350E
8HLE-10E
8HLE-15E
8HLE-20E
8HLE-25E
8HLE-30E
8HLE-40E
8HLE-50E
8HLE-65E
8HLE-80E
8HLE-100E
8HLE-125E
8HLE-150E
8HLE-175E
8HLE-200E
8HLE-250E
8HLE-300E
8HLE-350E
CLE Long construction (Westinghouse)
10 17.9 (455)
3 (76)
15 15.5 (394)
2 (51)
15 17.9 (455)
3 (76)
20 15.5 (394)
2 (51)
20 17.9 (455)
3 (76)
25 15.5 (394)
2 (51)
25 17.9 (455)
3 (76)
30 17.9 (455)
3 (76)
40 17.9 (455)
3 (76)
50 17.9 (455)
3 (76)
65 17.9 (455)
3 (76)
80 17.9 (455)
3 (76)
100 17.9 (455)
3 (76)
125 17.9 (455)
3 (76)
150 17.9 (455)
3 (76)
175 17.9 (455)
3 (76)
200 17.9 (455)
3 (76)
250 17.9 (455)
3 (76)
300 17.9 (455)
3 (76)
350 17.9 (455)
3 (76)
HLE Short construction
10 15.9 (404)
3 (76)
15 15.9 (404)
3 (76)
20 15.9 (404)
3 (76)
25 15.9 (404)
3 (76)
30 15.9 (404)
3 (76)
40 15.9 (404)
3 (76)
50 15.9 (404)
3 (76)
65 15.9 (404)
3 (76)
80 15.9 (404)
3 (76)
100 15.9 (404)
3 (76)
125 15.9 (404)
3 (76)
150 15.9 (404)
3 (76)
175 15.9 (404)
3 (76)
200 15.9 (404)
3 (76)
250 15.9 (404)
3 (76)
300 15.9 (404)
3 (76)
350 15.9 (404)
3 (76)
* Fuses conform to dimensional standards established by Westinghouse.
Eaton.com/bussmannseries
3
Technical Data 10352
Effective December 2015
8.3kV E-Rated medium voltage fuses for
feeder circuit, switchgear and transformer protection
CLE and HLE type mountings - in (mm)
Catalog
number
A
†
Disconnect single barrel
8CLE-GDM-C 15.24 (387.1)
8CLE-GDM-D 15.24 (387.1)
8CLE-PDM-C 15.24 (387.1)
8CLE-PDM-C 15.24 (387.1)
8HLE-GDM-D 16.25 (412.8)
8HLE-PDM-D 16.25 (412.8)
Disconnect double barrel
†
8CLE-GDM-E 15.24 (387.1)
8CLE-PDM-E 15.24 (387.1)
8HLE-GDM-E 16.25 (412.8)
8HLE-PDM-E 16.25 (412.8)
Non-disconnect single barrel
8CLE-GNM-C 15.25 (387.3)
8CLE-PNM-C 15.25 (387.3)
8CLE-GNM-D 15.25 (387.3)
8CLE-PNM-D 15.25 (387.3)
8HLE-GNM-D 16.25 (412.7)
8HLE-PNM-D 16.25 (412.7)
Non-disconnect double barrel
8CLE-GNM-E 15.24 (387.1)
8CLE-PNM-E 15.24 (387.1)
8HLE-GNM-E 16.25 (412.7)
8HLE-PNM-E 16.25 (412.7)
Hole centers Overall length
B
C
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
6 (152.4)
28 (711.2)
25 (647.7)
28 (711.2)
25 (647.7)
23 (584.2)
23 (584.2)
25 (647.7)
25 (647.7)
23 (584.2)
23 (584.2)
24.5 (622.3)
24.5 (622.3)
25 (635)
25 (635)
23 (584.2)
23 (584.2)
25 (635)
25 (635)
23 (584.2)
23 (584.2)
Hole Inset
D
0.75 (19)
0.62 (15.7)
0.75 (19)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.75 (19)
0.75 (19)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
0.62 (15.7)
Hole centers
E
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
1.75 (44.4)
Contact
height Overall height BIL
F
G kV
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
7 (177.8)
12.25 (311.1)
14.22 (361.2)
12.25 (311.1)
14.22 (361.2)
11.72 (297.7)
11.72 (297.7)
17.78 (451.6)
17.78 (451.6)
17.78 (451.6)
17.78 (451.6)
9.75 (247.6)
9.75 (247.6)
11.29 (286.7)
11.29 (286.7)
8.79 (223.3)
8.79 (223.3)
14.98 (380.5)
14.98 (380.5)
14.98 (380.5)
14.98 (380.5)
75
75
75
75
75
75
75
75
75
75
75
75
75
75
75
75
75
75
75
75
CLE and HLE type disconnect mounting
†
G
D
F
CLE and HLE type non-disconnect mounting
G
D
F
E
E
A
C
A
C
E
E
D
B
D
B
† Disconnect mountings provide a means for fuse extraction only. Do not use
a disconnect mounting for load switching or fuse removal while energized.
4
Eaton.com/bussmannseries
8.3kV E-Rated medium voltage fuses for
feeder circuit, switchgear and transformer protection
Technical Data 10352
Effective December 2015
A
X.XX (XX.X)
B
E-Rated medium voltage specialty mount fuses
0.44 x 0.91
Catalog symbols:
•
•
•
Dimensions for HCL - in (mm)
Slots
0.44 (11.2) Dia. Hole
(11.2 x 23.1)
8AHLE-_E (special dimension fuses for use with 7.2kV rated,
800 amp AMPGARD motor starting assemblies)
8BHLE-_E (bolt-on version)
8HCL-_E (clip-lock version)
A
0.5 (12.7)
Indicator*
C
Ratings*:
•
4.31 (109.5)
1.25
(31.8)
1.25
(31.8)
4.31 (109.5)
B
0.25
(6.4)
Volts
•
8.3kV
10 to 350A
50kA RMS Sym
•
Amps
•
•
Interrupting ratings
•
7.94 (201.7)
7.94 (201.7)
* See catalog number tables for voltages, ampacities and interrupting ratings
by catalog number.
Agency information:
•
0.5 (12.7)
E-Rated fuses meet the performance characteristics of
ANSI C37.46
Catalog number HCL-NL-1
Recommended live parts for clip-lock fuses
•
11.62 (295.1)
0.38
(9.7)
3.00
(76.2)
11.62 (295.1)
Dimensions for BHLE - in (mm)
2.12
(53.8)
Indicator*
* Flush with surface in untripped position, trip force is 2lb (0.9kg)
B
C
A
Indicator to be
located here
3.31
(84.1)
B
2.12
(53.8)
C
A
Indicator to be
located here
3.31
(84.1)
3.31
(84.1)
B
2.12
(53.8)
C
A
Eaton.com/bussmannseries