Power Supply Featuring OMRON’s Unique, New Undervoltage Alarm Function with
Compact Body Contributing to Machine Downsizing
• New undervoltage alarm function assists in determining causes of errors (S8VM-@@@24A@/P@ only).
• Power failure alarm function provides notification of output voltage errors (300-, 600-, and 1,500-W models only).
• Broad range of possibilities with 8 capacities and 29 models to choose from.
• RoHS-compliant including lead-free construction.
• Safety standards: UL508/60950-1/1604, CSA C22.2 No. 14/No. 60950-1/No. 213, EN50178, EN60950-1 (The 300-, 600-, and
1,500-W models will not conform to safety standards if the customer replaces the fan.)
• Harmonic current emissions: Conforms to EN61000-3-2 (except for 15- and 30-W models).
• New, attentive design prevents screws from falling out of terminal block (except for output terminals of 300-, 600-, and 1,500-W
models).
• Finger protection prevents electric shock.
• DIN Rail mounting.
Note:
Refer to
Precautions for Safe Use
on page 32.
Model Number Structure
■
Model Number Legend
Note:
Not all combinations are possible. Please refer to the list of models in
Ordering Information
on page 2.
S8VM-
@@@@@@@
1
1. Power Ratings
015:
15 W
030:
30 W
050:
50 W
100: 100 W
150: 150 W
300: 300 W
600: 600 W
152: 1,500 W
2. Output Voltage
05: 5 V
12: 12 V
15: 15 V
24: 24 V
2
3 4
3. Configuration/Functions
None: Open-frame type Standard type
C:
Covered type
Standard type
A:
Covered type
Undervoltage alarm type (Sinking)
(See note 1.)
P:
Covered type
Undervoltage alarm type (Sourcing)
(See note 1.)
4. Configuration
None
Bottom mounting type (See note 2.)
D
DIN Rail mounting bracket type
Note: 1.
The housing and terminal of the connector for the undervoltage alarm output are provided with the S8VM-05024A@/P@, S8VM-
10024A@/P@ and S8VM-15024A@/P@.
2.
Bottom mounting models cannot be used for front mounting. For a front mounting configuration, use a DIN Rail mounting bracket model
or Mounting Brackets (sold separately).
3.
A forced-air cooling method with a fan is used with 300-, 600-, and 1,500-W models.
Switch Mode Power Supply
S8VM
1
Ordering Information
Note:
For details on normal stock models, contact your nearest OMRON representative.
Configura-
tion
Power
ratings
Input voltage
Output voltage
Output current
Bottom mounting
Standard model
Undervoltage alarm model
Sinking
Sourcing
S8VM-01505
---
---
S8VM-01512
---
---
S8VM-01515
---
---
S8VM-01524
---
---
S8VM-03005
---
---
S8VM-03012
---
---
S8VM-03015
---
---
S8VM-03024
---
---
S8VM-05005
---
---
S8VM-05012
---
---
S8VM-05015
---
---
S8VM-05024
---
---
S8VM-10005
---
---
S8VM-10012
---
---
S8VM-10015
---
---
S8VM-10024
---
---
S8VM-15005
---
---
(See note 2.)
S8VM-15012
---
---
S8VM-15015
---
---
S8VM-15024
---
---
S8VM-01505C
---
---
S8VM-01512C
---
---
S8VM-01515C
---
---
S8VM-01524C
S8VM-01524A (See note 1.)
S8VM-03005C
---
---
S8VM-03012C
---
---
S8VM-03015C
---
---
S8VM-03024C
S8VM-03024A (See note 1.)
S8VM-05005C
---
---
S8VM-05012C
---
---
S8VM-05015C
---
---
S8VM-05024C
S8VM-05024A S8VM-05024P
S8VM-10005C
---
---
S8VM-10012C
---
---
S8VM-10015C
---
---
S8VM-10024C
S8VM-10024A S8VM-10024P
S8VM-15005C
---
---
(See note 2.)
S8VM-15012C
---
---
S8VM-15015C
---
---
S8VM-15024C
S8VM-15024A S8VM-15024P
S8VM-30005C
---
---
S8VM-30012C
---
---
S8VM-30015C
---
---
S8VM-30024C
---
---
DIN Rail mounting bracket
Standard model
Undervoltage alarm model
Sinking
Sourcing
S8VM-01505D
---
---
S8VM-01512D
---
---
S8VM-01515D
---
---
S8VM-01524D
---
---
S8VM-03005D
---
---
S8VM-03012D
---
---
S8VM-03015D
---
---
S8VM-03024D
---
---
S8VM-05005D
---
---
S8VM-05012D
---
---
S8VM-05015D
---
---
S8VM-05024D
---
---
S8VM-10005D
---
---
S8VM-10012D
---
---
S8VM-10015D
---
---
S8VM-10024D
---
---
S8VM-15005D
---
---
(See note 2.)
S8VM-15012D
---
---
S8VM-15015D
---
---
S8VM-15024D
---
---
S8VM-01505CD ---
---
S8VM-01512CD ---
---
S8VM-01515CD ---
---
S8VM-01524CD S8VM-01524AD (See note 1.)
S8VM-03005CD ---
---
S8VM-03012CD ---
---
S8VM-03015CD ---
---
S8VM-03024CD S8VM-03024AD (See note 1.)
S8VM-05005CD ---
---
S8VM-05012CD ---
---
S8VM-05015CD ---
---
S8VM-05024CD S8VM-05024AD S8VM-05024PD
S8VM-10005CD ---
---
S8VM-10012CD ---
---
S8VM-10015CD ---
---
S8VM-10024CD S8VM-10024AD S8VM-10024PD
S8VM-15005CD ---
---
(See note 2.)
S8VM-15012CD ---
---
S8VM-15015CD ---
---
S8VM-15024CD S8VM-15024AD S8VM-15024PD
---
---
---
---
---
---
---
---
---
---
---
---
Open-frame 15 W
type
100 to 240 VAC
30 W
50 W
100 W
150 W
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
5V
12 V
15 V
24 V
3A
1.3 A
1A
0.65 A
6A
2.5 A
2A
1.3 A
10 A
4.3 A
3.5 A
2.2 A
20 A
8.5 A
7A
4.5 A
27 A
12.5 A
10 A
6.5 A
3A
1.3 A
1A
0.65 A
6A
2.5 A
2A
1.3 A
10 A
4.3 A
3.5 A
2.2 A
20 A
8.5 A
7A
4.5 A
27 A
12.5 A
10 A
6.5 A
60 A
27 A
22 A
14 A
Peak current:
16.5 A (200 VAC)
120 A
53 A
43 A
27 A
Peak current:
31 A (200 VAC)
65 A (100 VAC)
70 A (200 VAC)
Peak current:
105 A (200 VAC)
Covered
type
15 W
100 to 240 VAC
30 W
50 W
100 W
150 W
300 W
(See note
4.)
600 W
(See note
4.)
5V
12 V
15 V
24 V
S8VM-60005C
S8VM-60012C
S8VM-60015C
S8VM-60024C
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
---
1,500 W
(See note
4.)
24 V
S8VM-15224C
(See note 3.)
---
---
---
---
---
Note: 1.
2.
3.
4.
5.
No outputs are built into these models.
The output capacity of the S8VM-15005@@ is 135 W.
M8 bolts and nuts for the output terminals are not included with the S8VM-15224C.
The 300-, 600-, and 1,500-W models have fans.
To perform front mounting using the bottom mounting models, use the Mounting Brackets (S82Y-VM@@F, sold separately).
2
Switch Mode Power Supply
S8VM
Specifications
■
Ratings/Characteristics
Item
Efficiency
Power rating
5-V models
12-V models
15-V models
24-V models
Voltage (See note 1.)
Frequency (See note 1.)
Current
100-V input
200-V input
Power factor
100-V input
200-V input
Harmonic current emissions
Leakage current 100-V input
200-V input
Inrush current
100-V input
(See note 2.)
200-V input
Voltage adjustment range (See note 3.)
Ripple
15 W
30 W
50 W
100 W
150 W
75% min.
75% min.
80% min.
81% min.
81% min.
78% min.
79% min.
79% min.
81% min.
81% min.
78% min.
79% min.
79% min.
81% min.
81% min.
80% min.
81% min.
80% min.
82% min.
83% min.
100 to 240 VAC (85 to 264 VAC)
50/60 Hz (47 to 63 Hz)
0.5 A max.
0.9 A max.
0.8 A max.
1.4 A max.
2.0 A max.
0.25 A max.
0.45 A max.
0.4 A max.
0.7 A max.
1.0 A max.
---
0.98 min.
---
0.94 min.
---
Conforms to EN 61000-3-2
0.4 mA max. (at rated output)
0.75 mA max. (at rated output)
17.5 A max. (for cold start at 25°C)
35 A max. (for cold start at 25°C)
−20%
to 20% (with V. ADJ) (S8VM-@@@24A@/P@:
−10%
to 20%)
3.2% (p-p) max. (5 V),
3.2% (p-p) max. (5 V),
1.5% (p-p) max. (12 V),
1.5% (p-p) max. (12 V),
1.2% (p-p) max. (15 V),
1.2% (p-p) max. (15 V),
1.0% (p-p) max. (24 V),
0.75% (p-p) max. (24 V),
(at rated input/output voltage)
(at rated input/output voltage)
Input variation influence
0.4% max. (at 85 to 264 VAC input, 100%)
Load variation influence (rated input voltage)
0.8% max. (with rated input, 0 to 100% load)
Temperature variation influence
0.02%/°C max.
Start up time (See note 2.)
1,100 ms max. (at rated input/output voltage) 800 ms max. (at rated input/output voltage)
Hold time (See note 2.)
20 ms typ. (15 ms min.) (at rated input/output voltage)
Overload protection (See note 2.)
105% to 160% of rated load current, voltage 105% to 160% of rated load current,
drop, intermittent, automatic reset
voltage drop (12 V, 15 V, and 24 V),
voltage drop, intermittent (5 V), automatic reset
Overvoltage protection (See note 2.)
Yes (See note 4.)
Undervoltage alarm indication
Yes (color: yellow (DC LOW1), red (DC LOW2)) (S8VM-@@@24A@/P@ only)
Undervoltage alarm output
No
Yes (S8VM-@@@24A@/P@ only)
(Transistor output), 30 VDC max., 50 mA max. (See note 8.)
Power failure alarm indication
No
Power failure alarm output
No
Series operation
Yes
Parallel operation
No
Remote sensing function
No
Yes
Ambient operating temperature
Refer to the derating curve in
Engineering Data (15-W, 30-W, 50-W, 100-W, 150-W Models).
(with no icing or con-
densation) (See note 2.)
Storage temperature
−25
to 65°C
Ambient operating humidity
30% to 85% (Storage humidity: 25% to 90%)
Dielectric strength
3.0 kVAC for 1 min. (between all inputs and outputs; detection current: 20 mA)
2.0 kVAC for 1 min. (between all inputs and PE/FG terminals; detection current: 20 mA)
500 VAC for 1 min. (between all outputs and PE/FG terminals; detection current: 100 mA)
500 VAC for 1 min. (between all outputs (except the detection output terminals) and detection output terminals; de-
tection current: 20 mA) (S8VM-@@@24A@/P@ only)
Insulation resistance
100 MΩ min. (between all outputs and all inputs, PE/FG terminals) at 500 VDC
Vibration resistance
10 to 55 Hz, 0.375-mm single amplitude for 2 hours each in X, Y, and Z directions
Shock resistance
150 m/s
2
, 3 times each in
±X, ±Y, ±Z
directions
Output indicator
EMI
Conducted Emission
Radiated Emission
EMS
Approved standards
Yes (color: green)
Conforms to EN61204-3 EN55011 Class B and based on FCC Class B (See note 5.)
Conforms to EN61204-3 EN55011 Class B (See note 6.)
Conforms to EN61204-3 High severity levels
UL: UL508 (Listing), UL60950-1, UL1604 (Class
I/Division
2, Listing)
CSA: cUL: C22.2 No.14, No.213 (Class
I/Division
2), cUR: No. 60950-1
EN: EN50178, EN60950-1
SELV (EN60950-1)
According to VDE0160/P100
SEMI-F47 (200 VAC input)
180 g max.
220 g max.
290 g max.
460 g max.
Input
Output
Additional
functions
Other
Weight (See note 7.)
530 g max.
Note: 1.
Do not use the Inverter output for the Power Supply. Inverters with an output frequency of 50/60 Hz are available, but the rise in the internal temperature of the Power
Supply may result in ignition or burning.
2.
Refer to the
Engineering Data (15-W, 30-W, 50-W, 100-W, 150-W Models)
section on page 9 to 11 for details.
3.
If the V. ADJ adjuster is turned, the voltage will increase by more than +20% of the voltage adjustment range.
When adjusting the output voltage, confirm the actual output voltage from the Power Supply and be sure that the load is not damaged.
4.
To reset the protection, turn OFF the input power for three minutes or longer and then turn it back ON.
5.
Conducted emissions: The noise value is affected by factors such as the wiring method. The Power Supply conforms to Class B when the aluminum plate is laid under
the Power Supply. For 15-W models, insert a clamp filter (ZCAT2436-1330 by TDK: 50
Ω
min. [50 to 500 MHz], or the equivalent) in the output wire to reduce noise.
6.
Radiated emissions: The noise value is affected by factors such as the wiring method. The Power Supply conforms to Class B when the aluminum plate is laid under the
Power Supply. For 150-W models, insert a clamp filter (ZCAT2017-0930 by TDK: 35
Ω
min. [50 to 500 MHz], or the equivalent) in the input wire to reduce noise.
7.
The weight indicated is for bottom mounting, open-frame models.
20 ms typ. (15 ms min.) (at rated input/output voltage)
105% to 160% of rated load current (5 V, 12 V, and 15 V), 120% to 160% of rated 105% to 160% of rated load current (100 VAC),
load current (S8VM-30024C), 115% to 160% of rated load current (S8VM-
155% to 200% of rated load current (200 VAC),
60024C), voltage drop (12 V, 15 V, and 24 V), voltage drop, intermittent (5 V),
voltage drop, automatic reset (Turns OFF
automatic reset
when continuous for 5 s min.) (See note 4.)
Yes (See note 4.)
Yes (See note 4.)
No
No
Yes (color: red)
Yes (Transistor output), 30 VDC max., 50 mA max.
Yes
Yes (Up to 2 units)
Yes
Yes
Refer to the derating curve in
Engineering Data (300-W, 600-W, 1,500-W Models).
(with no icing or condensation) (See note 2.)
−25
to 65°C
30% to 85% (Storage humidity: 25% to 90%)
3.0 kVAC for 1 min. (between all inputs and outputs; detection current: 20 mA) 3.0 kVAC for 1 min. (between all inputs and
2.0 kVAC for 1 min. (between all inputs and PE terminals; detection current: 20 outputs; detection current: 20 mA)
mA)
2.0 kVAC for 1 min. (between all inputs and FG
500 VAC for 1 min. (between all outputs and PE terminals; detection current: 100 terminals; detection current: 20 mA)
mA)
500 VAC for 1 min. (between all outputs and
100 VAC for 1 min. (between all outputs and RC terminals; detection current: 100 FG terminals; detection current: 300 mA)
mA)
100 VAC for 1 min. (between all outputs and
500 VAC for 1 min. (between all outputs and PF terminals; detection current: 20 RC terminals; detection current: 100 mA)
mA)
500 VAC for 1 min. (between all outputs and
PF terminals; detection current: 20 mA)
100 MΩ min. (between all outputs and all inputs, PE terminals) at 500 VDC
100 MΩ min. (between all outputs and all in-
puts, FG terminals) at 500 VDC
10 to 55 Hz, 0.375-mm single amplitude for 2 hours each in X, Y, and Z directions 10 to 55 Hz, 0.15-mm single amplitude for 2
hours each in X, Y, and Z directions
150 m/s
2
, 3 times each in
±X, ±Y, ±Z
directions
Yes (color: green)
Conforms to EN61204-3 EN55011 Class B and based on FCC Class B
Conforms to EN61204-3 EN55011 Class B
Conforms to EN61204-3 High severity levels
UL: UL508 (Recognition) (5 V, 12 V, and 15 V)
UL508 (Listing) (24 V), UL60950-1
UL1604 (Class
I/Division
2, Listing) (24 V) (pending)
CSA: cUL: C22.2 No.14, cUR: CSA No. 60950-1
EN: EN50178, EN60950-1
SEMI-F47 (200 VAC input)
1,100 g max.
1,700 g max.
Conforms to EN61204-3 EN55011 Class A
and based on FCC Class A
Conforms to EN61204-3 EN55011 Class A
UL: UL508 (Recognition), UL60950-1
cUR: CSA C22.2 No.14, No. 60950-1
EN: EN50178, EN60950-1
SEMI-F47 (200 VAC input)
Weight
3,800 g max.
Note: 1.
Do not use the Inverter output for the Power Supply. Inverters with an output frequency of 50/60 Hz are available, but the rise in the internal temperature of
the Power Supply may result in ignition or burning.
2.
Refer to the
Engineering Data
section on page 15 to 17 for details.
3.
If the V. ADJ adjuster is turned, the voltage will increase by more than +20% of the voltage adjustment range. When adjusting the output voltage, confirm the
actual output voltage from the Power Supply and be sure that the load is not damaged.
4.
To reset the protection, turn OFF the input power for three minutes or longer and then turn it back ON. Alternatively, turn OFF the remote control signal and
then turn it back ON again.
5.
Conducted emissions: The noise value is affected by factors such as the wiring method. The Power Supply conforms to Class B when the aluminum plate
is laid under the Power Supply. For 600-W models, insert a clamp filter (ZCAT3035-1330 by TDK: 100
Ω
min. [50 to 500 MHz], or the equivalent) in the input
wire, and ring core (HF60T38X14X22 by TDK: 16
Ω
typ. [1 MHz], 46
Ω
typ. [10 MHz] , or the equivalent) in the output wire to reduce noise
6.
Radiated emissions: The noise value is affected by factors such as the wiring method. The Power Supply conforms to Class A when the aluminum plate is
laid under the Power Supply (1,500-W models).
7.
The measuring method conforms to JEITA standard RC-9131A. Refer to
Ripple
under
Safety Precautions
on page 34.
8.
The Power Supply will not conform to safety standards if the customer replaces the fan.