This power supply is manufactured by SMD technology. The stress to P.C.B like twisting or bending causes the defect of the unit, so handle the unit with care.
*Make
sure necessary tests will be carried out on your end equipment with the power supply installed in accordance with any required EMC/EMI regulations.
MODEL
MAX OUTPUT WATTAGE[W]
DC OUTPUT
LMA100F-24-Y
103.2
24V 4.3A
LMA100F-24-HY
103.2 (206.4)
*2
24V 4.3A (8.6A)
*2
SPECIFICATIONS
MODEL
VOLTAGE[V]
CURRENT[A]
FREQUENCY[Hz]
INPUT
ACIN 100V
ACIN 200V
ACIN 100V
POWER FACTOR
ACIN 200V
ACIN 100V
INRUSH CURRENT[A]
ACIN 200V
LEAKAGE CURRENT[mA]
VOLTAGE[V]
CURRENT[A]
LINE REGULATION[mV]
*7
LOAD REGULATION[mV]
*7
0 to +50C
RIPPLE[mVp-p]
*3
-10 - 0C
0 to +50C
RIPPLE NOISE[mVp-p]
*3
-10 - 0C
0 to +50C
TEMPERATURE REGULATION[mV]
-10 to +50C
*4
DRIFT[mV]
START-UP TIME[ms]
HOLD-UP TIME[ms]
OUTPUT VOLTAGE ADJUSTMENT RANGE[V]
OUTPUT VOLTAGE SETTING[V]
OVERCURRENT PROTECTION
OVERVOLTAGE PROTECTION[V]
OPERATING INDICATION
REMOTE SENSING
REMOTE ON/OFF
*6
INPUT-OUTPUT.RC
INPUT-FG
*6
OUTPUT.RC-FG
*6
OUTPUT-RC
OPERATING TEMP.,HUMID.AND ALTITUDE
*5
STORAGE TEMP.,HUMID.AND ALTITUDE
VIBRATION
IMPACT
AGENCY APPROVALS (AT ONIY AC input)
CONDUCTED NOISE
HARMONIC ATTENUATOR
CASE SIZE/WEIGHT
COOLING METHOD
EFFICIENCY[%]
ACIN 100V
ACIN 200V
LMA100F-24-Y
LMA100F-24-HY
AC85 - 264 1f
1.4typ (Io=100%)
0.7typ (Io=100%)
50 / 60 (47 - 63)
84.0typ (Io=100%)
84.0typ (Io=100%)
86.0typ (Io=100%)
86.0typ (Io=100%)
0.99typ (Io=100%)
0.95typ (Io=100%)
15typ (Io=100%) (At cold start) (Ta=25C)
30typ (Io=100%) (At cold start) (Ta=25C)
0.10 / 0.25max (ACIN 100V / 240V 60Hz, Io=100%, According to IEC60601-1)
24
24
4.3
4.3 (Peak 8.6)
*2
96max
96max
150max
150max
120max
120max
160max
160max
150max
150max
180max
180max
240max
240max
290max
290max
96max
96max
350typ (ACIN 100V, Io=100%)
20typ (ACIN 100V, Io=100%)
19.20 to 27.50
19.20 to 27.50
24.00 to 24.96
24.00 to 24.96
Works over 105% of rating (works over 101% of peak current at option -H) and recovers automatically
27.60 to 33.60
27.60 to 33.60
Not provided
Not provided
Option (Required external power source.)
AC4,000V 1minute, Cutoff current = 10mA, DC500V 50MW min (At Room Temperature) 2MOOP
AC2,000V 1minute, Cutoff current = 10mA, DC500V 50MW min (At Room Temperature) 1MOOP
AC500V 1minute, Cutoff current = 25mA, DC500V 50MW min (At Room Temperature)
AC100V 1minute, Cutoff current = 25mA, DC100V 10MW min (At Room Temperature)
-10 to +70C, 20 - 90%RH (Non condensing), 3,000m (10,000feet) max
-20 to +75C, 20 - 90%RH (Non condensing), 9,000m (30,000feet) max
10 - 55Hz, 19.6m/s
2
(2G), 3minutes period, 60minutes each along X, Y and Z axis
196.1m/s
2
(20G), 11ms, once each X, Y and Z axis
ANSI/AAMI ES60601-1, EN60601-1 3rd, Complies with IEC60601-1-2 4th Ed.
Complies with FCC-B, VCCI-B, CISPR22-B, EN55011-B, EN55022-B
Optional chassis and cover material : Electric galvanizing steel board.
¶
Dimensions in mm, [ ]=inches
¶
Mounting torque (Mounting hole of chassis) :1.5N m (16kgf cm) max
¶
I/O Connector is Mfr. Tyco Electronics
¶
Option:-J1:VH(J.S.T) connector type.
20
LMA-3
[1.77]
45
[2.83]
3
Input(N)
3
62
72
CN2
Output(-)
4.5
5
5
[0.18]
FG
CN4
CN2
Output(-)
FG
Input(N)
1
2
1
36
AC-DC Power Supplies Medical Type
Ordering information
LMA150F
LM
1
2
A
3
150
4
F
5
-O
6
-O
R
Example recommended EMI/EMC filter
NAM-04-101
High voltage pulse noise type : NAP series
Low leakage current type : NAM series
*
A higher current rating EMI/EMC filter
may be recommended in view of the
other devices that could be connected
in parallel with the power supply.
1
Series name
2
Single output
3
Output wattage
4
Universal input
5
Output voltage
6
Optional
*1
C : with Coating
G : Low leakage current
H : with the function to be acceptable
to output peak current
J1 : VH(J.S.T.)connector type
R : with Remote ON/OFF
R2 : with Remote ON/OFF
S : with Chassis
SN: with Chassis & cover
P :Setting in the overcurrent
protection rating
This power supply is manufactured by SMD technology. The stress to P.C.B like twisting or bending causes the defect of the unit, so handle the unit with care.
*Make
sure necessary tests will be carried out on your end equipment with the power supply installed in accordance with any required EMC/EMI regulations.
MODEL
MAX OUTPUT WATTAGE[W]
DC OUTPUT
LMA150F-24-Y
151.2
24V 6.3A
LMA150F-24-HY
151.2 (302.4)
*2
24V 6.3A (12.6A)
*2
SPECIFICATIONS
MODEL
VOLTAGE[V]
CURRENT[A]
FREQUENCY[Hz]
INPUT
ACIN 100V
ACIN 200V
ACIN 100V
POWER FACTOR
ACIN 200V
ACIN 100V
INRUSH CURRENT[A]
ACIN 200V
LEAKAGE CURRENT[mA]
VOLTAGE[V]
CURRENT[A]
LINE REGULATION[mV]
*7
LOAD REGULATION[mV]
*7
0 to +50C
RIPPLE[mVp-p]
*3
-10 - 0C
0 to +50C
RIPPLE NOISE[mVp-p]
*3
-10 - 0C
0 to +50C
TEMPERATURE REGULATION[mV]
-10 to +50C
*4
DRIFT[mV]
START-UP TIME[ms]
HOLD-UP TIME[ms]
OUTPUT VOLTAGE ADJUSTMENT RANGE[V]
OUTPUT VOLTAGE SETTING[V]
OVERCURRENT PROTECTION
OVERVOLTAGE PROTECTION[V]
OPERATING INDICATION
REMOTE SENSING
REMOTE ON/OFF
*6
INPUT-OUTPUT.RC
INPUT-FG
*6
OUTPUT.RC-FG
*6
OUTPUT-RC
OPERATING TEMP.,HUMID.AND ALTITUDE
*5
STORAGE TEMP.,HUMID.AND ALTITUDE
VIBRATION
IMPACT
AGENCY APPROVALS (AT ONIY AC input)
CONDUCTED NOISE
HARMONIC ATTENUATOR
CASE SIZE/WEIGHT
COOLING METHOD
EFFICIENCY[%]
ACIN 100V
ACIN 200V
LMA150F-24-Y
LMA150F-24-HY
AC85 - 264 1f
2.0typ (Io=100%)
1.0typ (Io=100%)
50 / 60 (47 - 63)
85.0typ (Io=100%)
85.0typ (Io=100%)
87.0typ (Io=100%)
87.0typ (Io=100%)
0.99typ (Io=100%)
0.95typ (Io=100%)
15typ (Io=100%) (At cold start) (Ta=25C)
30typ (Io=100%) (At cold start) (Ta=25C)
0.10 / 0.25max (ACIN 100V / 240V 60Hz, Io=100%, According to IEC60601-1)
24
24
6.3
6.3 (Peak 12.6)
*2
96max
96max
150max
150max
120max
120max
160max
160max
150max
150max
180max
180max
240max
240max
290max
290max
96max
96max
350typ (ACIN 100V, Io=100%)
20typ (ACIN 100V, Io=100%)
19.20 to 27.50
19.20 to 27.50
24.00 to 24.96
24.00 to 24.96
Works over 105% of rating (works over 101% of peak current at option -H) and recovers automatically
27.60 to 33.60
27.60 to 33.60
Not provided
Not provided
Option (Required external power source.)
AC4,000V 1minute, Cutoff current = 10mA, DC500V 50MW min (At Room Temperature) 2MOOP
AC2,000V 1minute, Cutoff current = 10mA, DC500V 50MW min (At Room Temperature) 1MOOP
AC500V 1minute, Cutoff current = 25mA, DC500V 50MW min (At Room Temperature)
AC100V 1minute, Cutoff current = 25mA, DC100V 10MW min (At Room Temperature)
-10 to +70C, 20 - 90%RH (Non condensing), 3,000m (10,000feet) max
-20 to +75C, 20 - 90%RH (Non condensing), 9,000m (30,000feet) max
10 - 55Hz, 19.6m/s
2
(2G), 3minutes period, 60minutes each along X, Y and Z axis
196.1m/s
2
(20G), 11ms, once each X, Y and Z axis
ANSI/AAMI ES60601-1, EN60601-1 3rd, Complies with IEC60601-1-2 4th Ed.
Complies with FCC-B, VCCI-B, CISPR22-B, EN55011-B, EN55022-B
Optional chassis and cover material : Electric galvanizing steel board.
¶
Dimensions in mm, [ ]=inches
¶
Mounting torque (Mounting hole of chassis) :1.5N
-
m (16kgf
-
cm) max
¶
I/O Connector is Mfr. Tyco Electronics
¶
Option:-J1:VH(J.S.T) connector type.
20
LMA-5
47
[1.85]
4.5
[0.18]
85
CN1
7
[3.35]
1
Input(L)
CN1
CN3
Output(-)
5
3
1
CN3
Output(-)
42
FG
1
FG
Input(N)
Input(L)
1
[1.65]
AC-DC Power Supplies Medical Type
Ordering information
LMA240F
LM
1
2
A
3
240
4
F
5
-O
6
-O
R
Example recommended EMI/EMC filter
NAM-06-101
High voltage pulse noise type : NAP series
Low leakage current type : NAM series
*
A higher current rating EMI/EMC filter
may be recommended in view of the
other devices that could be connected
in parallel with the power supply.
1
Series name
2
Single output
3
Output wattage
4
Universal input
5
Output voltage
6
Optional
*1
C : with Coating
G : Low leakage current
H : with the function to be acceptable
to output peak current
J1 : VH(J.S.T.)connector type
R : with Remote ON/OFF
R2 : with Remote ON/OFF
S : with Chassis
SN: with Chassis & cover
P :Setting in the overcurrent
protection rating
This power supply is manufactured by SMD technology. The stress to P.C.B like twisting or bending causes the defect of the unit, so handle the unit with care.
*Make
sure necessary tests will be carried out on your end equipment with the power supply installed in accordance with any required EMC/EMI regulations.
MODEL
MAX OUTPUT WATTAGE[W]
DC OUTPUT
LMA240F-24-Y
300
Convection 24V 10A
Forced air 24V 12.5A
LMA240F-24-HY
300 (480)
*2
24V 10A (20A)
*2
24V 12.5A (20A)
*2
SPECIFICATIONS
MODEL
VOLTAGE[V]
CURRENT[A]
FREQUENCY[Hz]
INPUT
ACIN 100V
ACIN 200V
ACIN 100V
POWER FACTOR
ACIN 200V
ACIN 100V
INRUSH CURRENT[A]
ACIN 200V
LEAKAGE CURRENT[mA]
VOLTAGE[V]
Convection
CURRENT[A]
Forced air
LINE REGULATION[mV]
*7
LOAD REGULATION[mV]
*7
0 to +50C
RIPPLE[mVp-p]
*3
-10 - 0C
0 to +50C
RIPPLE NOISE[mVp-p]
*3
-10 - 0C
0 to +50C
TEMPERATURE REGULATION[mV]
-10 to +50C
*4
DRIFT[mV]
START-UP TIME[ms]
*9
HOLD-UP TIME[ms]
OUTPUT VOLTAGE ADJUSTMENT RANGE[V]
OUTPUT VOLTAGE SETTING[V]
OVERCURRENT PROTECTION
OVERVOLTAGE PROTECTION[V]
OPERATING INDICATION
REMOTE SENSING
REMOTE ON/OFF
*6
INPUT-OUTPUT.RC
INPUT-FG
*6
OUTPUT.RC-FG
*6
OUTPUT-RC
OPERATING TEMP.,HUMID.AND ALTITUDE
*5
STORAGE TEMP.,HUMID.AND ALTITUDE
VIBRATION
IMPACT
AGENCY APPROVALS (AT ONIY AC input)
CONDUCTED NOISE
HARMONIC ATTENUATOR
CASE SIZE/WEIGHT
COOLING METHOD
EFFICIENCY[%]
ACIN 100V
ACIN 200V
LMA240F-24-Y
LMA240F-24-HY
AC85 - 264 1f
3.9typ (Io=100%)
1.8typ (Io=100%)
50 / 60 (47 - 63)
86.0typ (Io=100%)
86.0typ (Io=100%)
88.0typ (Io=100%)
88.0typ (Io=100%)
0.99typ (Io=100%)
0.95typ (Io=100%)
15 / 30typ (Io=100%)
(Primary inrush current /Secondary inrush current) (More than 3 sec. to re-start)
30 / 30typ (Io=100%)
(Primary inrush current /Secondary inrush current) (More than 3 sec. to re-start)
0.15 / 0.40max (ACIN 100V / 240V 60Hz, Io=100%, According to IEC60601-1)
24
24
10
10 (Peak 20)
*2
12.5
12.5 (Peak 20)
*2
96max
96max
150max
150max
120max
120max
160max
160max
150max
150max
180max
180max
240max
240max
290max
290max
96max
96max
350typ (ACIN 100V, Io=100%)
20typ (ACIN 100V, Io=100%)
19.20 to 27.50
19.20 to 27.50
24.00 to 24.96
24.00 to 24.96
Works over 105% of rating (works over 101% of peak current at option -H) and recovers automatically
27.60 to 33.60
27.60 to 33.60
Not provided
Not provided
Option (Required external power source.)
AC4,000V 1minute, Cutoff current = 10mA, DC500V 50MW min (At Room Temperature) 2MOOP
AC2,000V 1minute, Cutoff current = 10mA, DC500V 50MW min (At Room Temperature) 1MOOP
AC500V 1minute, Cutoff current = 25mA, DC500V 50MW min (At Room Temperature)
AC100V 1minute, Cutoff current = 25mA, DC100V 10MW min (At Room Temperature)
-10 to +70C, 20 - 90%RH (Non condensing), 3,000m (10,000feet) max
-20 to +75C, 20 - 90%RH (Non condensing), 9,000m (30,000feet) max
10 - 55Hz, 19.6m/s
2
(2G), 3minutes period, 60minutes each along X, Y and Z axis
196.1m/s
2
(20G), 11ms, once each X, Y and Z axis
ANSI/AAMI ES60601-1, EN60601-1 3rd, Complies with IEC60601-1-2 4th Ed.
Complies with FCC-B, VCCI-B, CISPR22-B, EN55011-B, EN55022-B
When I was debugging the circuit, I found a problem. The chip is MSP430F149. When debugging with the emulator, the communication is normal. After the power is off, the serial port cannot communicate. ...
[align=left][font=Tahoma][size=3][color=#000000]Instrument amplifier, referred to as instrument amplifier, is usually used for high-precision low-frequency signal detection, such as temperature, press...
I have used some TI RF products. I used TI CC1121 before. This chip is very cheap, and its transmission function can reach 16dBm. It is also very powerful. I use CC1121 2FSK to transmit data between m...
[url=https://bbs.eeworld.com.cn/TI/TI_study20111008/index.html]https://bbs.eeworld.com.cn/TI/TI_study20111008/index.html[/url] After the event, it is very difficult to find the University Hall. It is ...
I want to ask the great god to pass on the application circuit information of the chip INA282 (in Chinese or English). I have all the information of the chip, but I just want the application circuit~~...
Chapter 15 DS18B20 (Temperature Sensor) Experiments DS18B20 (Temperature Sensor) Experiments A temperature sensor with a "single bus" interface launched by TSMC Semiconductor. Compared with traditiona...
In early 2002, I started to write a working program for an IC card prepaid electricity meter. The meter used Philips' 8-bit 51-expanded single-chip microcomputer
87LPC764
, and wa...[Details]
As a simple and practical input device, buttons have been used in various microcontroller application systems and are ubiquitous. However, the buttons used in different practical occasions are also...[Details]
At very low temperatures, certain metals and alloys lose their resistance to electric
current
and become
superconductors
. Two parameters that are often measured are the transition ...[Details]
Currently, each country is developing its own USB interface
charging specifications
, which leads to a major problem that a USB interface
charging
device manufactured in one country...[Details]
Traditional
virtual instruments
consist of a data acquisition
board
based on PCI bus and
corresponding software. However, with
the rapid development of
computer
network techno...[Details]
1 What is an LED floodlight?
LED downlights are also called spotlights, projection lamps, and spotlights. They are mainly used for architectural decorative lighting and commercial space lighti...[Details]
When developing electronic products with processors, how to improve anti-interference ability and electromagnetic compatibility?
1. The following systems should pay special attention to anti-...[Details]
Fairchild's FAN6208 is a synchronous rectification (SR) controller for isolated LLC or LC resonant converters that can drive two individual SR MOSFETs emulating the behavior of rectifier diodes. FAN62...[Details]
New Automobile
Hydraulic Clutch
The hydraulic control system uses almost 100% advanced engineering plastics, which overcomes the shortcomings of the main and branch cylinders of metal clutc...[Details]
1 Introduction
Intelligent cars are the embodiment of the cross-integration of multiple disciplines such as automotive electronics, artificial intelligence, pattern recognition, automatic con...[Details]
An intelligent vehicle is a robot that can automatically drive in an environment according to a pre-set mode, or it can autonomously perform specific operations according to the on-site situation. ...[Details]
Previously used primarily in high-power power supplies and large industrial and consumer power supplies, supercapacitors are now finding their way into products of all sizes, especially portable de...[Details]
First, the choice of charging location. Wireless charging technology is related to the distance and state of the charger and the charged device. That is to say, the distance between the two cannot...[Details]
AD7708 is a multi-channel 16-bit Σ-Δ analog-to-digital converter ADC. It supports 4 or 5 channels of true differential input and 8 or 10 channels of pseudo differential input. This chip allows two ...[Details]
0 Introduction
Gyroscope
is a sensitive measuring element of the platform stabilization system. It senses the angular motion signal of the platform and establishes the stability bench...[Details]