EEWORLDEEWORLDEEWORLD

Part Number

Search

3CU2.5

Description
Circuit Breakers 2.5A MCB CCHAR 3 PL 480Y/277VAC UL508
CategoryCircuit protection    Circuit protection   
File Size233KB,1 Pages
ManufacturerAltech
Websitehttp://www.altechcorp.com/
Download Datasheet Parametric Compare View All

3CU2.5 Overview

Circuit Breakers 2.5A MCB CCHAR 3 PL 480Y/277VAC UL508

3CU2.5 Parametric

Parameter NameAttribute value
Reach Compliance Codeunknown
Circuit protection typeTHERMAL MAGNETIC
Base Number Matches1
V-EA-Series - UL508 Manual Motor Controller -
3 pole C-Trip
UL508 Listed
E137938
Standard Pack:
4
Weight:
0.3A - 63A
1.68kg (3.7 lb.)
Three Pole
35 mm
(1.38 in.)
91.5 mm
(3.60 in.)
70 mm
(2.76 in.)
35 mm
(1.38 in.)
Rated
Current
0.3A
0.5A
0.75A
0.8A
1.0A
1.6A
2.0A
2.5A
3.0A
3.5A
4.0A
5.0A
6.0A
8.0A
10A
12A
12.5A
13A
15A
16A
20A
25A
30A
32A
40A
50A
60A
63A
Type/
Cat. No.
3CU03
3CU05
3CU075
NA
3CU1
3CU1.6
3CU2
3CU2.5
3CU3
3CU3.5
3CU4
3CU5
3CU6
3CU8
3CU10
NA
NA
3CU13
3CU15
3CU16
3CU20
3CU25
3CU30
3CU32
3CU40
3CU50
3CU60
3CU63
Approvals
UL
UL
UL
UL
UL
UL
UL
UL
UL
UL
UL
UL
V-EA-C Trip
0.3A Through 10A Rated Current
1.13-1.45xI
N
60
40
Minutes
10
4
1
Thermal Overload
“Must Trip” < 1 hr = 145% RC
“Must Not Trip” > 1 hr = 113% RC
Tripping time t
10
4
1
0.4
10
-1
4x10
-2
Seconds
UL
UL
10
-2
4x10
-3
10
-3
1
2
3 4
5
6 8
10
20
40
100
UL
UL
UL
UL
UL
UL
Multiple of Rated Current
V-EA-C Trip
13A Through 63A Rated Current
1.13-1.45xI
N
60
40
Minutes
10
4
1
Thermal Overload
“Must Trip” < 1 hr = 145% RC
“Must Not Trip” > 1 hr = 113% RC
UL
UL
UL
UL
For ring tongue terminal version, replace “U”
with “R” in part number. For example
1BR20
instead of
1BU20.
Tripping time t
10
4
1
0.4
10
-1
4x10
-2
Voltage Rating
Seconds
480Y/277VAC
0.3-25A: 1 pole - 42VDC; 2 Pole - 80VDC
30-60A: 1 pole - 24VDC; 2 Pole - 60VDC
0.3-60A (RC): 10kA with UL-listed
RK5 back-up fuse or MCCB
0.3-10A (RC): 10kA; 12-60A (RC): 5kA
no branch circuit protection required
0.3-63A (RC): 10kA
40°C (104°F)
Top: 18-3 AWG; Bottom: 18-2 AWG
20 lb.in.
IP20
Short Circuit Withstand Rating
(UL/CSA - Ratings)
Group Short Circuit Withstand Rating
(UL/CSA - Ratings)
Interrupting Capacity (VDE - Ratings)
Calibration Temperature
Terminal Size Acceptability
Terminal Torque
Terminal Protection Degree
10
-2
4x10
-3
10
-3
1
2
3 4
5
6 8
10
20
40
100
Multiple of Rated Current
short circuit Withstand ratings for v-ea manual motor controller
Trip
Curve
all
all
all
all
*up to nearest rated current
Backup
Protection
Amp Range
0.3 - 10A
12 - 30/32A
40 - 50A
60 / 63A
UL-Listed
RK5-Fuse
up to 10kA
4xRC*
min 15A, max 70A
4xRC*
max 125A
4xRC*
max 200A
4xRC*
max 250A
UL-Listed
MCCB
up to 10kA
4xRC*
min 15A, max 70A
4xRC*
max 125A
4xRC*
max 200A
4xRC*
max 250A
No BCP
Required
up to:
10kA
5kA
5kA
5kA

3CU2.5 Related Products

3CU2.5 3CU50 3CU3.5 3CU5 3CU05 3CU30 3CU3 3CU32 3CU60
Description Circuit Breakers 2.5A MCB CCHAR 3 PL 480Y/277VAC UL508 Circuit Breakers 50A MCB CCHAR 3 PL 480Y/277VAC UL508 Circuit Breakers 3.5A MCB CCHARL 480Y/277VAC UL508 Circuit Breakers 5A MCB CCHAR 3 PL 480Y/277VAC UL508 Circuit Breakers 5A MCB CCHAR 3 PL 480Y/277VAC UL508 Circuit Breakers 30A CRT BRKR CCHAR 277VAC UL508 Circuit Breakers 3A MCB CCHAR 3 PL 480Y/277VAC UL508 Circuit Breakers 32A MCB CCHAR 3 PL 480Y/277VAC UL508 Circuit Breakers 60A MCB CCHAR 3 PL 480Y/277VAC UL508
Reach Compliance Code unknown unknown unknown - unknown unknown - unknown unknown
Circuit protection type THERMAL MAGNETIC THERMAL MAGNETIC THERMAL MAGNETIC - THERMAL MAGNETIC THERMAL MAGNETIC - THERMAL MAGNETIC THERMAL MAGNETIC
Base Number Matches 1 1 1 - 1 1 - 1 1

EEWorld
subscription
account

EEWorld
service
account

Automotive
development
circle

Robot
development
community

Index Files: 2864  2295  1243  832  122  58  47  26  17  3 
Datasheet   0 1 2 3 4 5 6 7 8 9 A B C D E F G H I J K L M N O P Q R S T U V W X Y Z
Room 1530, 15th Floor, Building B, No. 18 Zhongguancun Street, Haidian District, Beijing Telephone: (010) 82350740 Postal Code: 100190
Copyright © 2005-2026 EEWORLD.com.cn, Inc. All rights reserved 京ICP证060456号 京ICP备10001474号-1 电信业务审批[2006]字第258号函 京公网安备 11010802033920号