https://www.phoenixcontact.com/us/products/2906058
Hybrid motor starter - ELR H5-IES-PT-24DC/500AC-06-T - 2906058
Please be informed that the data shown in this PDF Document is generated from our Online Catalog. Please find the complete data in the user's
documentation. Our General Terms of Use for Downloads are valid
(http://phoenixcontact.com/download)
Hybrid motor starter for reversing 3~ AC motors up to 550 V AC, with 24 V DC input, 0.6 A output current,
emergency stop function, adjustable overload shutdown, higher transient voltage strength, and push-in
connection.
The figure shows the ELR H5-IES-
PT-24DC/500AC-06-T version
Product Features
Key commercial data
Packing unit
Weight per Piece (excluding packing)
Custom tariff number
Country of origin
1 pc
280.0 GRM
85371099
Germany
Technical data
Input data
Input name
Rated control supply voltage U
S
Voltage range with reference to U
S
Rated control supply current I
S
Protective circuit
Operating voltage display
Status display
Indication
Input name
Rated actuating voltage U
C
Voltage range with reference to U
C
Device supply
24 V DC (According to IEC 60947-1)
0.8 ... 1.25
≤ 40 mA
Protection against polarity reversal
Surge protection
Green LED
Yellow LED
Red LED
Control input right/left
24 V DC
0.8 ... 1.25
05/18/2015 Page 1 / 5
https://www.phoenixcontact.com/us/products/2906058
Hybrid motor starter - ELR H5-IES-PT-24DC/500AC-06-T - 2906058
Technical data
Input data
Rated actuating current I
C
Switching level "safe off"
Protective circuit
Typical response time
Typical turn-off time
≤ 5 mA
< 5 V DC
Protection against polarity reversal
< 35 ms
< 40 ms
Output data load output
Rated operating voltage U
e
Operating voltage range
Load current
Min. load current
Trigger characteristic in acc. with IEC 60947
Rated operating current at AC-51
Rated operating current at AC-53a
Leakage current
Residual voltage
Protective circuit
500 V AC
42 V AC ... 550 V AC
max. 600 mA (see derating curve)
75 mA
Class 10A
0.6 A
0.6 A
0 mA
< 0.2 V (at I
e
)
Surge protection Varistor
Output data reply output
Note
Contact type
Contact material
Maximum switching voltage
Minimum switching voltage
Min. switching current
Maximum inrush current
Limiting continuous current
Interrupting rating (ohmic load) max.
Note
Maximum switching voltage
Minimum switching voltage
Min. switching current
Limiting continuous current
Interrupting rating (ohmic load) max.
Confirmation 01: floating change-over contact, signal contact
1 PDT
AgSnO
2
, hard gold-plated
30 V AC
36 V DC
100 mV AC/DC (at 10 mA)
1 mA (at 24 V)
50 mA
50 mA
1.2 W (at 24 V DC)
the following values are applicable if a gold layer is destroyed
250 V AC/DC
5 V (at 100 mA)
10 mA (at 12 V)
6A
140 W (at 24 V DC)
20 W (at 48 V DC)
18 W (at 60 V DC)
23 W (at 110 V DC)
05/18/2015 Page 2 / 5
https://www.phoenixcontact.com/us/products/2906058
Hybrid motor starter - ELR H5-IES-PT-24DC/500AC-06-T - 2906058
Technical data
Output data reply output
40 W (at 220 V DC)
1500 VA (for 250 V AC)
Switching capacity according to IEC 60947-5-1
2 A (at 24 V, DC13)
0.2 A (at 110 V, DC13)
0.1 A (at 220 V, DC13)
3 A (at 24 V, AC15)
3 A (at 120 V, AC15)
3 A (at 230 V, AC15)
Measuring technology and signaling contact
Measuring via
Current transformer for line current on L1 and L3
Connection data
Connection method
Stripping length
Conductor cross section solid min.
Conductor cross section solid max.
Conductor cross section flexible min.
Conductor cross section flexible max.
Conductor cross section AWG min.
Conductor cross section AWG max.
Push-in connection
10 mm
0.2 mm²
2.5 mm²
0.2 mm²
2.5 mm²
24
14
General
Mounting position
Assembly instructions
Operating mode
Designation
Standards/regulations
Vertical (horizontal DIN rail)
Can be aligned with spacing = 20 mm
100% operating factor
Standards/regulations
IEC 60947-1
EN 60947-4-2
IEC 61508
ISO 13849
Designation
Standards/regulations
Rated surge voltage
Insulation
Air clearances and creepage distances between the power circuits
DIN EN 50178
6 kV
Safe isolation (EN 50178) for mains voltage ≤ 500 V AC
Safe isolation (IEC 60947-1) for mains voltage ≤ 300 V AC
Basic insulation (IEC 60947-1) for mains voltage of 300 ... 500 V AC
Rated insulation voltage
Pollution degree
500 V
2
05/18/2015 Page 3 / 5
https://www.phoenixcontact.com/us/products/2906058
Hybrid motor starter - ELR H5-IES-PT-24DC/500AC-06-T - 2906058
Technical data
General
Surge voltage category
Safety Integrity Level according to IEC 61508
Category acc. to EN ISO 13849
Performance level according to ISO 13849
III
SIL 3 (safe shutdown)
SIL 2 (motor protection)
3
e
Dimensions
Width
Height
Depth
22.5 mm
99 mm
114.5 mm
Ambient conditions
Ambient temperature (operation)
Ambient temperature (storage/transport)
Degree of protection
5 °C ... 70 °C
-40 °C ... 80 °C
IP20
UL data
Short-circuit current rating (SCCR)
100 kA (500 V AC (30 A CC/30 A J (high fault) fuse))
5 kA (500 V AC (20 A RK5 (standard fault) fuse))
Classifications
eCl@ss
eCl@ss 5.1
eCl@ss 6.0
27371601
27371601
ETIM
ETIM 5.0
EC001037
Approvals
Approvals
Approvals
UL Listed / cUL Listed / cULus Listed
Ex Approvals
ATEX
05/18/2015 Page 4 / 5
https://www.phoenixcontact.com/us/products/2906058
Hybrid motor starter - ELR H5-IES-PT-24DC/500AC-06-T - 2906058
Approvals
Approvals submitted
Approval details
UL Listed
cUL Listed
cULus Listed
Drawings
Diagram
Output current [A]
0,9
0,8
0,7
0,6
0,5
0,4
0,3
0,2
0,1
= aligned with 20 mm spacing
= aligned without spacing
5 10
20
30
40
50
60
70
Ambient temperature [°C]
Derating curve
Phoenix Contact 2015 © - all rights reserved
http://www.phoenixcontact.com
05/18/2015 Page 5 / 5