https://www.phoenixcontact.com/pi/products/3214080
Potential collective terminal - PTU 35/4X6/6X2,5 - 3214080
Please be informed that the data shown in this PDF Document is generated from our Online Catalog. Please find the complete data in the user's
documentation. Our General Terms of Use for Downloads are valid
(http://phoenixcontact.com/download)
Potential collective terminal, nom. voltage: 1000 V, nominal current: 105 A, connection method: Screw
connection, Push-in connection, number of connections: 11, cross section:1.5 mm² - 50 mm², AWG: 16 - 1/0,
width: 16.3 mm, color: gray, mounting type: NS 35/7,5, NS 35/15
Why buy this product
The terminal block base is ideal for use in building installation and machine building applications
The Push-in connection terminal blocks are characterized by the system features of the CLIPLINE complete system and by easy and tool-free
wiring of conductors with ferrules or solid conductors
The compact design and front connection enable wiring in a confined space
In addition to the testing facility in the double function shaft, all terminal blocks provide an additional test connection
Key Commercial Data
Packing unit
GTIN
GTIN
4055626167619
20 pc
Technical data
General
Note
Number of levels
Number of connections
Color
Insulating material
Flammability rating according to UL 94
Rated surge voltage
Degree of pollution
Overvoltage category
Insulating material group
In the end application, the applicable safety regulations for overload
and short-circuit protection on the connected conductors must be
considered.
1
11
gray
PA
V0
8 kV
2
III
I
10/04/2018 Page 1 / 7
https://www.phoenixcontact.com/pi/products/3214080
Potential collective terminal - PTU 35/4X6/6X2,5 - 3214080
Technical data
General
Maximum power dissipation for nominal condition
Connection method
Connection in acc. with standard
Maximum load current
Nominal current I
N
Nominal voltage U
N
Connection method
Connection in acc. with standard
Maximum load current
Nominal current I
N
Nominal voltage U
N
Open side panel
Shock protection test specification
Back of the hand protection
Finger protection
Result of surge voltage test
Surge voltage test setpoint
Result of power-frequency withstand voltage test
Power frequency withstand voltage setpoint
Result of the test for mechanical stability of terminal points (5 x
conductor connection)
Result of bending test
Bending test rotation speed
Bending test turns
Bending test conductor cross section/weight
4.06 W (the value is multiplied when connecting multiple levels)
Screw connection
IEC 60947-7-1
105 A (The maximum load current must not be exceeded by the total
current of all connected conductors.)
105 A
1000 V
Push-in connection
IEC 60947-7-1
41 A
41 A
1000 V
No
DIN EN 50274 (VDE 0660-514):2002-11
guaranteed
guaranteed
Test passed
9.8 kV
Test passed
2.2 kV
Test passed
Test passed
10 rpm
135
1.5 mm² / 0.4 kg
35 mm² / 6.8 kg
50 mm² / 9.5 kg
0.5 mm² / 0.3 kg
6 mm / 1.4 kg
10 mm² / 2 kg
0.14 mm² / 0.2 kg
2.5 mm² / 0.7 kg
4 mm² / 0.9 kg
Tensile test result
Conductor cross section tensile test
Tractive force setpoint
Conductor cross section tensile test
Tractive force setpoint
Conductor cross section tensile test
Tractive force setpoint
Test passed
1.5 mm²
40 N
35 mm²
190 N
50 mm²
236 N
10/04/2018 Page 2 / 7
2
https://www.phoenixcontact.com/pi/products/3214080
Potential collective terminal - PTU 35/4X6/6X2,5 - 3214080
Technical data
General
Conductor cross section tensile test
Tractive force setpoint
Result of tight fit on support
Tight fit on carrier
Setpoint
Result of voltage-drop test
Requirements, voltage drop
Result of temperature-rise test
Short circuit stability result
Conductor cross section short circuit testing
Short-time current
Conductor cross section short circuit testing
Short-time current
Result of aging test
Ageing test for screwless modular terminal block temperature cycles
Result of thermal test
Proof of thermal characteristics (needle flame) effective duration
Oscillation, broadband noise test result
Test specification, oscillation, broadband noise
Test spectrum
Test frequency
ASD level
Acceleration
Test duration per axis
Test directions
Shock test result
Test specification, shock test
Shock form
Acceleration
Shock duration
Number of shocks per direction
Test directions
Relative insulation material temperature index (Elec., UL 746 B)
Temperature index of insulation material (DIN EN 60216-1 (VDE
0304-21))
Static insulating material application in cold
Behavior in fire for rail vehicles (DIN 5510-2)
Flame test method (DIN EN 60695-11-10)
Oxygen index (DIN EN ISO 4589-2)
NF F16-101, NF F10-102 Class I
NF F16-101, NF F10-102 Class F
0.5 mm²
20 N
Test passed
NS 35
10 N
Test passed
≤ 1.6 mV
Test passed
Test passed
35 mm²
3 kA
50 mm²
4.8 kA
Test passed
192
Test passed
30 s
Test passed
DIN EN 50155 (VDE 0115-200):2008-03
Service life test category 2, bogie-mounted
f
1
= 5 Hz to f
2
= 250 Hz
6.12 (m/s ) /Hz
3.12 g
5h
X-, Y- and Z-axis
Test passed
DIN EN 50155 (VDE 0115-200):2008-03
Half-sine
30g
18 ms
3
X-, Y- and Z-axis (pos. and neg.)
130 °C
130 °C
-60 °C
Test passed
V0
>32 %
2
2
10/04/2018 Page 3 / 7
2 2
https://www.phoenixcontact.com/pi/products/3214080
Potential collective terminal - PTU 35/4X6/6X2,5 - 3214080
Technical data
General
Surface flammability NFPA 130 (ASTM E 162)
Specific optical density of smoke NFPA 130 (ASTM E 662)
Smoke gas toxicity NFPA 130 (SMP 800C)
Calorimetric heat release NFPA 130 (ASTM E 1354)
Fire protection for rail vehicles (DIN EN 45545-2) R22
Fire protection for rail vehicles (DIN EN 45545-2) R23
Fire protection for rail vehicles (DIN EN 45545-2) R24
Fire protection for rail vehicles (DIN EN 45545-2) R26
passed
passed
passed
28 MJ/kg
HL 1 - HL 3
HL 1 - HL 3
HL 1 - HL 3
HL 1 - HL 3
Dimensions
Width
Length
Height NS 35/7,5
Height NS 35/15
16.3 mm
110.4 mm
48.8 mm
56.3 mm
Connection data
Connection method
Connection in acc. with standard
Screw thread
Tightening torque, min
Tightening torque max
Stripping length
Conductor cross section solid min.
Conductor cross section solid max.
Conductor cross section AWG min.
Conductor cross section AWG max.
Conductor cross section flexible min.
Conductor cross section flexible max.
Min. AWG conductor cross section, flexible
Max. AWG conductor cross section, flexible
Conductor cross section flexible, with ferrule without plastic sleeve min.
Conductor cross section flexible, with ferrule with plastic sleeve min.
Conductor cross section flexible, with ferrule with plastic sleeve max.
2 conductors with same cross section, solid min.
2 conductors with same cross section, solid max.
Two conductors with the same cross section, AWG solid min.
Two conductors with the same cross section, AWG solid max.
2 conductors with same cross section, stranded min.
2 conductors with same cross section, stranded max.
Two conductors with the same cross section, AWG stranded, min.
Two conductors with the same cross section, AWG stranded, max.
Screw connection
IEC 60947-7-1
M6
3.2 Nm
3.7 Nm
18 mm
1.5 mm²
50 mm²
16
1/0
1.5 mm²
50 mm²
16
1/0
1.5 mm²
1.5 mm²
35 mm²
1.5 mm²
16 mm²
16
6
1.5 mm²
10 mm²
16
8
10/04/2018 Page 4 / 7
Conductor cross section flexible, with ferrule without plastic sleeve max. 35 mm²
https://www.phoenixcontact.com/pi/products/3214080
Potential collective terminal - PTU 35/4X6/6X2,5 - 3214080
Technical data
Connection data
2 conductors with same cross section, stranded, ferrules without plastic
sleeve, min.
2 conductors with same cross section, stranded, ferrules without plastic
sleeve, max.
Internal cylindrical gage
Connection method
Connection in acc. with standard
Stripping length
Conductor cross section solid min.
Conductor cross section solid max.
Conductor cross section AWG min.
Conductor cross section AWG max.
Conductor cross section flexible min.
Conductor cross section flexible max.
Min. AWG conductor cross section, flexible
Max. AWG conductor cross section, flexible
Conductor cross section flexible, with ferrule without plastic sleeve min.
Conductor cross section flexible, with ferrule with plastic sleeve min.
Conductor cross section flexible, with ferrule with plastic sleeve max.
2 conductors with same cross section, stranded, TWIN ferrules with
plastic sleeve, min.
2 conductors with same cross section, stranded, TWIN ferrules with
plastic sleeve, max.
Conductor cross section solid min.
Conductor cross section solid max.
Conductor cross section AWG min.
Conductor cross section AWG max.
Conductor cross section flexible, with ferrule with plastic sleeve min.
Conductor cross section flexible, with ferrule with plastic sleeve max.
Conductor cross section flexible, with ferrule without plastic sleeve min.
Connection method
Connection in acc. with standard
Stripping length
Conductor cross section solid min.
Conductor cross section solid max.
Conductor cross section AWG min.
Conductor cross section AWG max.
Conductor cross section flexible min.
Conductor cross section flexible max.
Min. AWG conductor cross section, flexible
1.5 mm²
10 mm²
B9
Push-in connection
IEC 60947-7-1
12 mm
0.5 mm²
10 mm²
20
8
0.5 mm²
6 mm²
20
10
0.5 mm²
0.5 mm²
6 mm²
0.5 mm²
1.5 mm²
1 mm²
10 mm²
18
8
1 mm²
6 mm²
1 mm²
Push-in connection
IEC 60947-7-1
8 mm ... 10 mm
0.14 mm²
4 mm²
26
12
0.14 mm²
2.5 mm²
26
10/04/2018 Page 5 / 7
Conductor cross section flexible, with ferrule without plastic sleeve max. 6 mm²
Conductor cross section flexible, with ferrule without plastic sleeve max. 6 mm²