https://www.phoenixcontact.com/pi/products/2700684
I/O module - AXL F DI8/2 110/220DC 1F - 2700684
Please be informed that the data shown in this PDF Document is generated from our Online Catalog. Please find the complete data in the user's
documentation. Our General Terms of Use for Downloads are valid
(http://phoenixcontact.com/download)
Axioline F, Digital input module, Digital inputs: 8, 110 V DC / 220 V DC, connection method: 2-wire,
corresponds to standard IEC 61850-3, transmission speed in the local bus: 100 Mbps, including bus base
module and Axioline F connectors
Product Description
The module is designed for use within an Axioline F station.
It is used to acquire digital DC voltage signals in the low-voltage range.
You can use low-voltage and extra-low voltage modules directly next to each other within an Axioline F station.
Why buy this product
8 digital inputs according to EN 61131-2 type 1
Connection of sensors in 2-wire technology
110 V DC / 220 V DC, 1.5 mA
Filter time of < 1 ms
Inputs are reverse polarity protected
Safe isolation according to EN 61010-2-201/IEC 61010-2-201
Device rating plate stored
Diagnostic and status indicators
Meets the requirements of IEC 61850-3 and IEEE 1613
Key Commercial Data
Packing unit
GTIN
GTIN
4046356916448
1 pc
Technical data
Dimensions
Width
Height
Depth
Note on dimensions
53.6 mm
126.1 mm
54 mm
The depth is valid when a TH 35-7,5 DIN rail is used (according to
EN 60715).
10/03/2018 Page 1 / 5
https://www.phoenixcontact.com/pi/products/2700684
I/O module - AXL F DI8/2 110/220DC 1F - 2700684
Technical data
Ambient conditions
Ambient temperature (operation)
-25 °C ... 60 °C (Mounting position: wall mounting on horizontal DIN rail,
input voltage: max. 264 V)
-25 °C ... 55 °C (Mounting position: any)
Ambient temperature (storage/transport)
Permissible humidity (operation)
Permissible humidity (storage/transport)
Air pressure (operation)
Air pressure (storage/transport)
Degree of protection
-40 °C ... 85 °C
5 % ... 95 % (non-condensing)
5 % ... 95 % (non-condensing)
70 kPa ... 106 kPa (up to 3000 m above sea level)
70 kPa ... 106 kPa (up to 3000 m above sea level)
IP20
Connection data
Designation
Connection method
Note on the connection method
Conductor cross section solid min.
Conductor cross section solid max.
Conductor cross section flexible min.
Conductor cross section flexible max.
Conductor cross section AWG min.
Conductor cross section AWG max.
Stripping length
Axioline F connector
Push-in connection
Please observe the information provided on conductor cross sections in
the “Axioline F: system and installation” user manual.
0.2 mm²
1.5 mm²
0.2 mm²
1.5 mm²
24
16
8 mm
General
Mounting type
Net weight
Note on weight specifications
Degree of pollution
DIN rail
173 g
with connectors and bus base module
2
Interfaces
Designation
No. of channels
Connection method
Transmission speed
Axioline F local bus
2
Bus base module
100 Mbps
Axioline potentials
Designation
Supply voltage
Current consumption
Power consumption
Designation
Protection
Axioline F local bus supply (U
Bus
)
5 V DC (via bus base module)
max. 120 mA
max. 600 mW
Supply for digital input modules (U
I
)
max. 8 A ()
Digital inputs
10/03/2018 Page 2 / 5
https://www.phoenixcontact.com/pi/products/2700684
I/O module - AXL F DI8/2 110/220DC 1F - 2700684
Technical data
Digital inputs
Input name
Description of the input
Connection method
Connection technology
Number of inputs
Type of protection
Input filter time
Input voltage
Digital inputs
according to EN 61131-2 type 1
Push-in connection
2-wire
8
Polarity reversal protection of the inputs
< 1 ms
110 V DC (Nominal voltage)
220 V DC (Nominal voltage)
max. 300 V DC
Input voltage range "0" signal
Input voltage range "1" signal
Input voltage range
Nominal input current at U
IN
-41 V DC ... 41 V DC
88 V DC ... 300 V DC
-300 V DC ... 300 V DC
1.5 mA
Electrical isolation
Test section
I/Os / logic 4 kV Rated surge voltage (safe isolation according to EN
61010-2-201/IEC 61010-2-201)
I/Os / logic 5 kV Pulse test voltage according to EN 61850/IEC 61850
I/O / functional earth ground 4 kV Rated surge voltage (safe isolation
according to EN 61010-2-201/IEC 61010-2-201)
I/O / functional earth ground 5 kV Pulse test voltage according to EN
61850/IEC 61850
I/O / I/O (adjacent connectors) 2.5 kV Pulse test voltage according to EN
61850/IEC 61850
Logic / functional earth ground 1 kV Pulse test voltage according to EN
61850/IEC 61850
Standards and Regulations
Mechanical tests
Vibration resistance in acc. with EN 60068-2-6/IEC 60068-2-6 5g
Shock in acc. with EN 60068-2-27/IEC 60068-2-27 30g
Continuous shock according to EN 60068-2-27/IEC 60068-2-27 10g
Developed according to standard
IEC 61850-3 Electrostatic discharge (ESD) EN 61000-4-2/
IEC 61000-4-2 Criterion A; 8 kV contact discharge; 8 kV air discharge
IEC 61850-3 Electromagnetic fields EN 61000-4-3/IEC 61000-4-3
Criterion A, 20 V/m up to 1 GHz, 10 V/m up to 3 GHz
IEC 61850-3 Fast transients (burst) EN 61000-4-4/IEC 61000-4-4
Criterion A, 4 kV
IEC 61850-3 Transient overvoltage (surge) EN 61000-4-5/
IEC 61000-4-5 Criterion A, ±2 kV (symmetrical), ±4 kV (asymmetrical)
IEC 61850-3 Conducted interference EN 61000-4-6/IEC 61000-4-6
Criterion A; Test voltage 10 V
IEC 61850-3 Immunity to magnetic fields, EN 61000-4-8/IEC 61000-4-8
300 A/m continuous, 1000 A/m for 1 s
IEC 61850-3 Immunity to attenuated oscillating magnetic fields,
EN 61000-4-10/IEC 61000-4-10 100 A/m
10/03/2018 Page 3 / 5
https://www.phoenixcontact.com/pi/products/2700684
I/O module - AXL F DI8/2 110/220DC 1F - 2700684
Technical data
Standards and Regulations
IEC 61850-3 Immunity to conducted common-mode interference,
EN 61000-4-16/IEC 61000-4-16 30 V continuous, 300 V for 1 s
IEC 61850-3 Attenuated oscillating waves, EN 61000-4-18/
IEC 61000-4-18 1 kV symmetrical, 2.5 kV asymmetrical
IEC 61850-3 Radio interference properties EN 55022 Class B
Environmental Product Compliance
China RoHS
Environmentally friendly use period: unlimited = EFUP-e
No hazardous substances above threshold values
Drawings
Connection diagram
00
01
02
03
Dimensional drawing
53,6
54
10
11
12
13
IN 1
+ 110 / 220 V DC
IN 5
20
21
22
23
IN 4
+ 110 / 220 V DC
30
31
32
33
+ 110 / 220 V DC
122,4
Connection of sensors when using external busbars
Block diagram
U
Bus
C
Local bus
13
4x
10
00
00
Input
circuit 8
Input
circuit 5
Input
circuit 1
10
20
30
IN 1...8
Internal wiring of the terminal points
Approvals
Approvals
10/03/2018 Page 4 / 5
126,1
+ 110 / 220 V DC
https://www.phoenixcontact.com/pi/products/2700684
I/O module - AXL F DI8/2 110/220DC 1F - 2700684
Approvals
Approvals
UL Listed / cUL Listed / cULus Listed
Ex Approvals
Approval details
UL Listed
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/index.htm
FILE E 238705
cUL Listed
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/index.htm
FILE E 238705
cULus Listed
Phoenix Contact 2018 © - all rights reserved
http://www.phoenixcontact.com
PHOENIX CONTACT GmbH & Co. KG
Flachsmarktstr. 8
32825 Blomberg
Germany
Tel. +49 5235 300
Fax +49 5235 3 41200
http://www.phoenixcontact.com
10/03/2018 Page 5 / 5